You point out that the valve now trips in 50 seconds, where before it was
80. This indicates the accelerator is working, but not fast enough.
Possibly because of the accelerator itself.  A restriction in the IT
discharge line could cause it too.  If the pipe to the ITV is very long,
trip time could be reduced by upping the size.  Even if the accelerator
tripped much faster, it seems the delivery time would be too long

An exhauster would certainly help, particularly if it is way out on the
system.  One has to be careful, though, when both an exhauster and
accelerator are used.  The exhauster must trip first.

A manufacturer could tell you if the 19 psi is outside the working range of
his exhauster.  Spec sheets usually list only the maximum rated pressure.
The speed of operation of an exhauster can be adjusted, but it must be done
carefully.  If it is too sensitive, the system could trip on normal
variations in pressure.