Yes, that 50 second trip time with the new accelerator still appears too long. Is the air maintenace device working properly? Perhaps left in fill mode rather than switched to operating mode? Or the orifice is missing from the operating side of the AMD?
Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated --- On Sat, 5/2/09, Ed Vining <[email protected]> wrote: From: Ed Vining <[email protected]> Subject: Re: Slow responding dry pipe valves To: [email protected] Date: Saturday, May 2, 2009, 10:08 PM You point out that the valve now trips in 50 seconds, where before it was 80. This indicates the accelerator is working, but not fast enough. Possibly because of the accelerator itself. A restriction in the IT discharge line could cause it too. If the pipe to the ITV is very long, trip time could be reduced by upping the size. Even if the accelerator tripped much faster, it seems the delivery time would be too long An exhauster would certainly help, particularly if it is way out on the system. One has to be careful, though, when both an exhauster and accelerator are used. The exhauster must trip first. A manufacturer could tell you if the 19 psi is outside the working range of his exhauster. Spec sheets usually list only the maximum rated pressure. The speed of operation of an exhauster can be adjusted, but it must be done carefully. If it is too sensitive, the system could trip on normal variations in pressure. Ed -- Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)