Fran, We had a long narrow warehouse that had a large dry system in it that gave us trouble. Due to the geometry of the building most of our volume was in our supply mains. Our solution was to use an InBal DPV. We had it custom built for our situation. It took a rocket scientist to figure out the trim but it worked. Another problem we had was custom built = 2 month delivery. Here's a link to their site;
http://www.inbalvalves.com/ I don't like to plug products, but this worked for us in a similar situation. Randy Knutson Shilo Automatic Sprinkler, Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Frans Stoop Sent: Saturday, May 02, 2009 7:17 PM To: [email protected] Subject: Slow responding dry pipe valves Thank you all for your responses! Forest: It is not about the annual trip test. It is the acceptance test for a new system. The exhauster is a good idea. However, the Victaulic dry pipe valves use a lower air pressure (1.3 bar = 19 psi) than other brands. Victaulic themselves don't have an exhauster in their product range. And I don't know if exhausters of other brands are suited to operate with such a low air pressure. Ron: The elapsed time is 3 minutes from opening the IT to water delivery. Almost 80 seconds to trip and 100 seconds from trip to waterdelivery. Water pressure: static 9.3 bar (135 psi), dynamic during filling pipe system 7 bar (100 psi) roughly 2700 dm3/min (713 GPM), dynamic during water delivery by the IT 8 bar (116 psi). Air pressure before opening the IT: 1.3 bar (19 psi). The high volume is caused by the size of the protected area and the distance between the area and the heated valve room. Ed: Good idea, we will check the accelerator and if it appears to be connected correctly I will propose tripping with the accelerator on and off. Draining the system after each test is a complication: it takes 2 man half a day each time! Allen: I don't think it is an obstruction in this case: the flow test downstream the pump performs OK. Mike: A too high air pressure, due to a defective pressure gauge could be the cause of a delayed trip time. I will propose to check the actual pressure and the pressure gauge. The air supply is coming from a tank mounted compressor by way of an air maintenance device. Craig: The water supply is existing. The static and dynamic pressures readings are the same as before. The dry pipe system is a new system, added to an existing sprinkler system with several wet and dry pipe systems. Gregg: There is no past; this is acceptance testing of a new system. For trip time, water pressure and air pressure see the answers to Ron above. Again, thank you all for your suggestions. Meanwhile Victaulic has replaced the accelerator and the trip time has been reduced to 50 seconds. The total time between IT open and water delivery is 2.5 minutes now. Still too slow. Could any undrained water in the distribution piping slow down the filling time? Frans Stoop TOS architecture & fire protection Netherlands <[email protected]> Tel. +31-24-324 0112 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)