If you're taking WON'T make it with exhauster then no bet. If you're taking WILL make it with exhauster then I'll give you whatever odds you like. "Ceptin' I never bet money. There is not a good whisky bar in the area but you can get good whiskey at Paddy Coynes in Tacoma. We can settle up there.
On Mon, May 4, 2009 at 8:38 AM, Roland Huggins <[email protected]> wrote: > One minor problem -where you going to find a new exhauster? The > reference to exhausters in NFPA 13 has been removed for the 2010 > edition since they are no longer manufactured. > > Even with one, any bets that a 2-1/2 minute water delivery after valve > trip will still not make the combined 60 sec maximum? > > Roland > > On May 2, 2009, at 8:08 PM, Ed Vining wrote: > >> You point out that the valve now trips in 50 seconds, where before >> it was >> 80. This indicates the accelerator is working, but not fast enough. >> Possibly because of the accelerator itself. A restriction in the IT >> discharge line could cause it too. If the pipe to the ITV is very >> long, >> trip time could be reduced by upping the size. Even if the >> accelerator >> tripped much faster, it seems the delivery time would be too long >> >> An exhauster would certainly help, particularly if it is way out on >> the >> system. One has to be careful, though, when both an exhauster and >> accelerator are used. The exhauster must trip first. >> >> A manufacturer could tell you if the 19 psi is outside the working >> range of >> his exhauster. Spec sheets usually list only the maximum rated >> pressure. >> The speed of operation of an exhauster can be adjusted, but it must >> be done >> carefully. If it is too sensitive, the system could trip on normal >> variations in pressure. >> >> Ed >> >> -- >> Ed Vining >> 4819 John Muir Rd >> Martinez CA 94553 >> 925-228-8792 >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) >> > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)