Top:
You forgot to add (Chris!) "Don't try this at home, we're what you cal
professionals" (AKA Myth Busters)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Top Myers
Sent: Monday, May 18, 2009 9:15 PM
To: [email protected]
Subject: RE: Re[2]: CPVC w/o water between riser and FDC

Yes Thom you are right.  In certain situations we have shown water hammer
can blow anything apart.  Cut groove is better but really that has more to
do with schedule 40 vs. light wall.  By the way normal burst pressure for
CPVC is around 1400 PSI in 2" size.


Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
Office 610-321-2415   Cell 610-952-0965
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Friday, May 15, 2009 5:30 PM
To: [email protected]
Subject: RE: Re[2]: CPVC w/o water between riser and FDC

If a pump (weather fixed or on wheels) hammers a system hard enough, it
won't matter what kind of pipe you use. Top Myers had some interesting
claims on standpipes where that happened. You out there Top? Seem to
remember something about cut groove being less susceptible than roll
grooves.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, May 15, 2009 3:33 PM
To: [email protected]
Subject: RE: Re[2]: CPVC w/o water between riser and FDC

I wasn't thinking static test, I was thinking actual water flow


At 05:25 PM 5/15/2009, you wrote:
>Same here! We test all of our systems including the FDC to 200/2hrs. If

>it has an FDC your required to test same as all 13, even if 13D.
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Charles 
>Thurston
>Sent: Friday, May 15, 2009 1:18 PM
>To: Todd Williams
>Subject: Re[2]: CPVC w/o water between riser and FDC
>
>Hello Todd,
>
>We pump into em with 200 for the final with no problems. Last one was 
>about 90 feet underground.
>
>Friday, May 15, 2009, 2:43:55 PM, you wrote:
>
> > Has anybody tried pumping 150 psi into an FDC piped with 40 ft of 
> > CPVC? Are there water hammer issues? Can the glued fittings handle
it?
> > Any additional restraint required? The listing issue may be one 
> > thing, but the actual installation may have some unforeseen
consequences.
>
>
>
> > At 02:28 PM 5/15/2009, you wrote:
> >>As Long as the pipe is not exposed or if it is it meets the normal 
> >>restrictions for cpvc, it should be ok.
> >>
> >>Thom McMahon, SET
> >>Firetech, Inc.
> >>2560 Copper Ridge Dr
> >>P.O. Box 882136
> >>Steamboat Springs, CO 80488
> >>Tel:  970-879-7952
> >>Fax: 970-879-7926
> >>
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of R 
> >>Richardson
> >>Sent: Friday, May 15, 2009 12:25 PM
> >>To: [email protected]
> >>Subject: RE: CPVC w/o water between riser and FDC
> >>
> >>In this particular case it is a run of about 40 ft. through some 
> >>sprinklered rooms.  Still seems OK?
> >>
> >>Rich Richardson
> >>Seattle Fire Department
> >>
> >> >>> "Steve Leyton" <[email protected]> 05/15/2009 10:07
> >> >>> >>>
> >>We have never been concerned with this and I'd say it's standard
> >>practice on most 13R systems throughout the Southwest.   It's
generally
> >>a short run of pipe if the FDC is on the wall.
> >>
> >>Steve Leyton
> >>Protection Design & Consulting
> >>San Diego, CA
> >>
> >>
> >>
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of R 
> >>Richardson
> >>Sent: Friday, May 15, 2009 10:04 AM
> >>To: [email protected]
> >>Subject: CPVC w/o water between riser and FDC
> >>
> >>We are reviewing a proposal for a wet pipe sprinkler system using 
> >>CPVC
>pipe.
> >>However, there is a run of CPVC pipe between the FDC and the riser 
> >>that is dry, is this standard practice or acceptable?
> >>
> >>Thanks,
> >>
> >>Rich Richardson
> >>Seattle Fire Department
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>
> >>__________ Information from ESET NOD32 Antivirus, version of virus 
> >>signature database 4080 (20090515) __________
> >>
> >>The message was checked by ESET NOD32 Antivirus.
> >>
> >>http://www.eset.com
> >>
> >>
> >>
> >>__________ Information from ESET NOD32 Antivirus, version of virus 
> >>signature database 4080 (20090515) __________
> >>
> >>The message was checked by ESET NOD32 Antivirus.
> >>
> >>http://www.eset.com
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
>
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> > [email protected]
>
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
>
>
>--
>Best regards,
>  Charles Thurston
mailto:[email protected]
>   Coastal Fire Protection
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: 
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: 
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to