I have a project where the local authority requires us to put sprinklers 
in a concealed space.  The building is masonry walls and bar joist 
construction (typical school).  However, per the local AHJ definition of 
combustible spaces, we are required to provide upright sprinklers in the 
concealed spaces.  Since this would classify as a non-combustible space 
in any other part of the country, would it be permissible to install the 
system utilizing CPVC piping?  If the space above the ceiling is 
considered an exposed installation, then it meets all of the 
requirements required for a blazemaster installation.  So, would you do 
this? I have put a call into tech services, but nothing back yet.

-- 
Please feel free to call if you have any questions or comments.