That's the way I read it, but I've been wrong once or twice (today, lol) I'd also add you are reading the chart backwards in your first sentence, I do this a lot too. If you are 30" from the partition you need to be a MINIMUM of 18" above. If 40" or 7' still a MINIMUM of 18". If on top of the wall a MINIMUM of 3", 11.5", 18" and 22.8966" would also be fine. In other words on top of the wall potentially violates the normal 18" above rules and if in LH you have an exception to go lower. 18" complies with all the horizontal distances in the chart. Chris -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chad Sent: Wednesday, February 10, 2010 12:45 PM To: [email protected] Subject: RE: Floor Mount Vertical Obstructions
So the chart for Light Hazard occupancy shows that if the vertical distance is 18", than the sprinkler has to be 30" or more from the vertical obstruction. So regardless of light or ordinary hazard, you can ignore the vertical obstructions if they are greater than 18" down? So If you can ignore the vertical partitions due to them being greater than 18" below, you can also ignore any horizontal spacing to the partitions. You could end up with a sprinkler horizontally 7' off of two walls of the individual cubical. Therefore, the s x l would not apply to each individual cubical, since theoretically, there are no partitions. Correct? Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc. 11780 North Hwy. 99 Lodi, CA 95240 Phone (209) 334-9119 Fax (209) 334-2923 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Wednesday, February 10, 2010 6:10 AM To: [email protected] Subject: RE: Floor Mount Vertical Obstructions If it's over 18" why would you be looking at the floor mounted rules? Aren't these rules to allow an exception to the general rule to keep things out of the zone 18" below the deflector? And yes the exception is only for LH. Clearance to storage...18", obstructions that prevent the discharge from reaching the hazard...18". Go to the library stack section, again 18". So I think you are fine down to 18" above the top of the wall. On the clg. not sure I would have even questioned 6" x 6" open grate with 1/8" wire. The rules as supported by the annex are intended to concern them selves with horizontal flow of water. Even if you were 18" above this "clg" I don't think this is what the open grid clg rules are a concerned with. But even applying the rules you comply so it's a moot point. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Gregg Fontes Sent: Tuesday, February 09, 2010 5:21 PM To: [email protected] Subject: Floor Mount Vertical Obstructions Scenario, mini storage with multiple 10' x 10', 10' x 8' and so on cubicles with partitions stopping at 8'-0 with a 6" x 6" open grate/wire 1/8" diameter fence ceiling at 8'-0. Existing calculated ordinary hazard group II, .20 gpm over 1500 sq. ft. with upright fire sprinklers at 10' x 12' spacing. Existing upright fire sprinkler deflectors are at 13'-6, placing them 5'-6 above the 6" x 6" open grate/wire ceiling. NFPA 13 2007 8.6.5.2.2 addresses floor mount vertical obstructions for light hazard only. NFPA 13 2007 8.14.12 addresses open-grid ceilings. Since the sprinkler deflector is greater than 36" above the open grated/wire ceiling, the existing system is in compliance 8.14.12. However, since NFPA 13 dose not address the vertical obstructions for ordinary hazard in this situation, the vertical partitions would be an obstruction. Therefore, the existing upright fire sprinkler spacing would need to be modify to either place the sprinkler directly over the partition or over each cubical. In other words, you could not ignore the vertical partition in this situation. Am I looking at the correct? Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc. 209-334-9119 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)