Scenario, mini storage with multiple 10' x 10', 10' x 8' and so on cubicles with partitions stopping at 8'-0 with a 6" x 6" open grate/wire 1/8" diameter fence ceiling at 8'-0. Existing calculated ordinary hazard group II, .20 gpm over 1500 sq. ft. with upright fire sprinklers at 10' x 12' spacing. Existing upright fire sprinkler deflectors are at 13'-6, placing them 5'-6 above the 6" x 6" open grate/wire ceiling. NFPA 13 2007 8.6.5.2.2 addresses floor mount vertical obstructions for light hazard only. NFPA 13 2007 8.14.12 addresses open-grid ceilings. Since the sprinkler deflector is greater than 36" above the open grated/wire ceiling, the existing system is in compliance 8.14.12. However, since NFPA 13 dose not address the vertical obstructions for ordinary hazard in this situation, the vertical partitions would be an obstruction. Therefore, the existing upright fire sprinkler spacing would need to be modify to either place the sprinkler directly over the partition or over each cubical. In other words, you could not ignore the vertical partition in this situation. Am I looking at the correct? Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc. 209-334-9119
_______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)