I did a similar project a couple of years ago. We had two areas: one with sprinklers about 15 ft above the partitions and the other area about 2 ft. . The 15 ft area I just ignored the partitions. In the 2 ft space, we had so many heads because of former walls, etc. that there are two sprinklers over most compartments. It becomes a judgement call. Without looking at it personally, I would hesitate to make a call, but at 5'-6", all things being equal, ignoring the partitions might be reasonable.
At 06:20 PM 2/9/2010, you wrote: >Scenario, mini storage with multiple 10' x 10', 10' x 8' and so on cubicles >with partitions stopping at 8'-0 with a 6" x 6" open grate/wire 1/8" >diameter fence ceiling at 8'-0. Existing calculated ordinary hazard group >II, .20 gpm over 1500 sq. ft. with upright fire sprinklers at 10' x 12' >spacing. Existing upright fire sprinkler deflectors are at 13'-6, placing >them 5'-6 above the 6" x 6" open grate/wire ceiling. NFPA 13 2007 8.6.5.2.2 >addresses floor mount vertical obstructions for light hazard only. NFPA 13 >2007 8.14.12 addresses open-grid ceilings. Since the sprinkler deflector is >greater than 36" above the open grated/wire ceiling, the existing system is >in compliance 8.14.12. However, since NFPA 13 dose not address the vertical >obstructions for ordinary hazard in this situation, the vertical partitions >would be an obstruction. Therefore, the existing upright fire sprinkler >spacing would need to be modify to either place the sprinkler directly over >the partition or over each cubical. In other words, you could not ignore >the vertical partition in this situation. Am I looking at the correct? > >Thanks, >Gregg Fontes >Cen-Cal Fire Systems, Inc. >209-334-9119 > > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)