I did a similar project a couple of years ago. We had two areas: one 
with sprinklers about 15 ft above the partitions and the other area 
about 2 ft. . The 15 ft area I just ignored the partitions. In the 2 
ft space, we had so many heads because of former walls, etc. that 
there are two sprinklers over most compartments. It becomes a 
judgement call. Without looking at it personally, I would hesitate to 
make a call, but at 5'-6", all things being equal, ignoring the 
partitions might be reasonable.


At 06:20 PM 2/9/2010, you wrote:
>Scenario, mini storage with multiple 10' x 10', 10' x 8' and so on cubicles
>with partitions stopping at 8'-0 with a 6" x 6" open grate/wire 1/8"
>diameter fence ceiling at 8'-0.  Existing calculated ordinary hazard group
>II, .20 gpm over 1500 sq. ft. with upright fire sprinklers at 10' x 12'
>spacing.  Existing upright fire sprinkler deflectors are at 13'-6, placing
>them 5'-6 above the 6" x 6" open grate/wire ceiling.  NFPA 13 2007 8.6.5.2.2
>addresses floor mount vertical obstructions for light hazard only.  NFPA 13
>2007 8.14.12 addresses open-grid ceilings.  Since the sprinkler deflector is
>greater than 36" above the open grated/wire ceiling, the existing system is
>in compliance 8.14.12.  However, since NFPA 13 dose not address the vertical
>obstructions for ordinary hazard in this situation, the vertical partitions
>would be an obstruction.  Therefore, the existing upright fire sprinkler
>spacing would need to be modify to either place the sprinkler directly over
>the partition or over each cubical.  In other words, you could not ignore
>the vertical partition in this situation.  Am I looking at the correct?
>
>Thanks,
>Gregg Fontes
>Cen-Cal Fire Systems, Inc.
>209-334-9119
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to