If you use tyco's CC1 or CC2 heads, they are specifically listed to be used 
with CPVC piping in combustible concealed spaces.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, February 02, 2010 9:17 AM
To: [email protected]; [email protected]
Subject: RE: CPVC in a concealed space

Sounds reasonable and prudent, Travis.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Tuesday, February 02, 2010 10:09 AM
To: [email protected]
Subject: CPVC in a concealed space

I have a project where the local authority requires us to put sprinklers 
in a concealed space.  The building is masonry walls and bar joist 
construction (typical school).  However, per the local AHJ definition of 
combustible spaces, we are required to provide upright sprinklers in the 
concealed spaces.  Since this would classify as a non-combustible space 
in any other part of the country, would it be permissible to install the 
system utilizing CPVC piping?  If the space above the ceiling is 
considered an exposed installation, then it meets all of the 
requirements required for a blazemaster installation.  So, would you do 
this? I have put a call into tech services, but nothing back yet.

-- 
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to