Sounds reasonable and prudent, Travis.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Tuesday, February 02, 2010 10:09 AM
To: [email protected]
Subject: CPVC in a concealed space

I have a project where the local authority requires us to put sprinklers 
in a concealed space.  The building is masonry walls and bar joist 
construction (typical school).  However, per the local AHJ definition of 
combustible spaces, we are required to provide upright sprinklers in the 
concealed spaces.  Since this would classify as a non-combustible space 
in any other part of the country, would it be permissible to install the 
system utilizing CPVC piping?  If the space above the ceiling is 
considered an exposed installation, then it meets all of the 
requirements required for a blazemaster installation.  So, would you do 
this? I have put a call into tech services, but nothing back yet.

-- 
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)