So the chart for Light Hazard occupancy shows that if the vertical distance
is 18", than the sprinkler has to be 30" or more from the vertical
obstruction.  So regardless of light or ordinary hazard, you can ignore the
vertical obstructions if they are greater than 18" down?  So If you can
ignore the vertical partitions due to them being greater than 18" below, you
can also ignore any horizontal spacing to the partitions.  You could end up
with a sprinkler horizontally 7' off of two walls of the individual cubical.
Therefore, the s x l would not apply to each individual cubical, since
theoretically, there are no partitions.  Correct?   



Thanks,
 
Gregg Fontes
 
Cen-Cal Fire Systems, Inc.
11780 North Hwy. 99
Lodi,  CA   95240
Phone (209)  334-9119
Fax (209)  334-2923

 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, February 10, 2010 6:10 AM
To: [email protected]
Subject: RE: Floor Mount Vertical Obstructions

If it's over 18" why would you be looking at the floor mounted rules?
Aren't these rules to allow an exception to the general rule to keep things
out of the zone 18" below the deflector?  And yes the exception is only for
LH.  Clearance to storage...18", obstructions that prevent the discharge
from reaching the hazard...18".  Go to the library stack section, again 18".
So I think you are fine down to 18" above the top of the wall.  

On the clg. not sure I would have even questioned 6" x 6" open grate with
1/8" wire.  The rules as supported by the annex are intended to concern them
selves with horizontal flow of water.  Even if you were 18" above this "clg"
I don't think this is what the open grid clg rules are a concerned with.
But even applying the rules you comply so it's a moot point.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gregg Fontes
Sent: Tuesday, February 09, 2010 5:21 PM
To: [email protected]
Subject: Floor Mount Vertical Obstructions

Scenario, mini storage with multiple 10' x 10', 10' x 8' and so on cubicles
with partitions stopping at 8'-0 with a 6" x 6" open grate/wire 1/8"
diameter fence ceiling at 8'-0.  Existing calculated ordinary hazard group
II, .20 gpm over 1500 sq. ft. with upright fire sprinklers at 10' x 12'
spacing.  Existing upright fire sprinkler deflectors are at 13'-6, placing
them 5'-6 above the 6" x 6" open grate/wire ceiling.  NFPA 13 2007 8.6.5.2.2
addresses floor mount vertical obstructions for light hazard only.  NFPA 13
2007 8.14.12 addresses open-grid ceilings.  Since the sprinkler deflector is
greater than 36" above the open grated/wire ceiling, the existing system is
in compliance 8.14.12.  However, since NFPA 13 dose not address the vertical
obstructions for ordinary hazard in this situation, the vertical partitions
would be an obstruction.  Therefore, the existing upright fire sprinkler
spacing would need to be modify to either place the sprinkler directly over
the partition or over each cubical.  In other words, you could not ignore
the vertical partition in this situation.  Am I looking at the correct?  
 
Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to