Under UFC 3-600-01 the required fire flow for a sprinklered building is the sprinkler demand plus the hose demand. The appendix does not apply for sprinklered buildings.
Robert J. Pielow, P.E. Fire Protection & Life Safety -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ronl.Fletcher Sent: Tuesday, January 18, 2011 2:08 PM To: [email protected] Subject: RE: UFC 3-600-1 Fire Flow I tried that but the FPE says that IFC is not applicable. Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Tuesday, January 18, 2011 1:06 PM To: [email protected] Subject: RE: UFC 3-600-1 Fire Flow I believe that the UFC's reference the I-code set, so I would assume - absent any compelling prescriptive otherwise - you'd use the table in the IFC. The question is what reduction you can take for sprinklers. Code says "up to" 75% with approval of the AHJ; obviously, most municipal FD's offer 50%. What NAVFAC or another DOD AHJ will offer is likely subjective and/or project-specific. Steve -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ronl.Fletcher Sent: Tuesday, January 18, 2011 12:02 PM To: [email protected] Subject: UFC 3-600-1 Fire Flow Anyone out there know how to determine the required fire flow for a fully sprinklered building using UFC 3-600-1? Appendix C Section C-1 says "Use the following procedures to determine the required fire flow demand and duration for buildings that are not fully sprinklered." It doesn't say what to use for fully protected or am I missing something? Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)