NFPA 1 (2009) Section 18.4 may be of help.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Pielow, Robert
Sent: Tuesday, January 18, 2011 2:11 PM
To: [email protected]
Subject: RE: UFC 3-600-1 Fire Flow

Under UFC 3-600-01 the required fire flow for a sprinklered building is the 
sprinkler demand plus the hose demand.  The appendix does not apply for 
sprinklered buildings.

Robert J. Pielow, P.E.
Fire Protection & Life Safety


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ronl.Fletcher
Sent: Tuesday, January 18, 2011 2:08 PM
To: [email protected]
Subject: RE: UFC 3-600-1 Fire Flow

I tried that but the FPE says that IFC is not applicable.


Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Tuesday, January 18, 2011 1:06 PM
To: [email protected]
Subject: RE: UFC 3-600-1 Fire Flow

I believe that the UFC's reference the I-code set, so I would assume -
absent any compelling prescriptive otherwise - you'd use the table in
the IFC.   The question is what reduction you can take for sprinklers.
Code says "up to" 75% with approval of the AHJ; obviously, most
municipal FD's offer 50%.   What NAVFAC or another DOD AHJ will offer is
likely subjective and/or project-specific.

Steve 

 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Ronl.Fletcher
Sent: Tuesday, January 18, 2011 12:02 PM
To: [email protected]
Subject: UFC 3-600-1 Fire Flow

Anyone out there know how to determine the required fire flow for a
fully sprinklered building using UFC 3-600-1? Appendix C Section C-1
says "Use the following procedures to determine the required fire flow
demand and duration for buildings that are not fully sprinklered." It
doesn't say what to use for fully protected or am I missing something?


Ron Fletcher
Aero Automatic
Phoenix, AZ



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to