Roland, 

NFPA 101 paragraph 11.8.3.1 states "High-rise buildings shall be protected 
throughout by an approved, supervised automatic sprinkler system in accordance 
with NFPA 101, Section 9.7. A sprinkler control valve and a waterflow device 
shall be provided for each floor. 

As per the 2006 IBC paragraph 403.3 "Reduction in fire resistance rating" 
states "The fire-resistance-rating reductions listed in Sections 403.3.1 and 
403.3.2 shall be allowed in buildings that have sprinkler control valves 
equipped with supervisory initiating devices and water-flow initiating devices 
for each floor". Most architects and building owners use this section of the 
IBC to reduce the thickness of fire proofing material applied to the structural 
steel members of the thickness of concrete between the exterior of a concrete 
structural member and the steel bar reinforcement.

We all need to pay attention to what are the legal codes being enforced in a 
jurisdiction, especially when the Fire Marshall is enforcing the NFPA codes and 
the building department is using the IBC.

Have a fire safe day.

Regards

Jim  


Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, January 13, 2011 3:46 PM
To: [email protected]
Subject: Re: Hydraulic Calcs

I concur with everything you said and the alarm requirements are very  
explicit regarding on supervision IF a component is present.  Where  
does the IBC say you have to have a water flow switch on EVERY floor  
of a hi-rise?

Roland

On Jan 13, 2011, at 12:28 PM, Jim Davidson wrote:

> In the IBC (2006 Edition) paragraph 903.4 "Sprinkler system  
> monitoring and alarms", states;
> All valves controlling the water supply for automatic sprinkler  
> systems, pumps, tanks, water levels and temperatures, critical air  
> pressures and water-flow switches on all sprinkler systems shall be  
> electrically supervised. And paragraph 903.4.1 Signals, requires that;
> Alarm, supervisory and trouble signals shall be distinctly different  
> and automatically transmitted to an approved central station, remote  
> supervising station or proprietary supervising station as defined in  
> NFPA 72 or, when approved by the fire code official, shall sound an  
> audible signal at a constantly attended location.
>
> Paragraph  903.4.3 "Floor control valves" states that;
> Approved supervised indicating control valves shall be provided at  
> the point of connection to the riser on each floor in high-rise  
> buildings.
>
> The IBC does require the supervision of fire sprinkler systems  
> especially where IBC sprinkler trade off are used in the design of  
> the building.
>
> Have a fire safe day.
>
>
>
> Jim Davidson
>
> Davidson Associates
> Fire Protection * Medical Gas * Code Consulting
> 302-994-9500   Fax:302-234-1781
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to