yes, except the vault was not heated. The PIV is in the vault. We inherited this problem. We reset the dry valve, then one person goes outside and opens the PIV, while the inside man watches the dry valve and gauges. It is a real time waster, but has been that way for years. I do not know if that arrangement does or does not meet code, the system was installed sometime in the 1970s.

Douglas Hicks
General Fire Equipment of Eastern Oregon, Inc
-----Original Message----- From: kpurvis
Sent: Wednesday, February 09, 2011 8:48 AM
To: [email protected]
Subject: Dry pipe control valve

Has anyone ever used a PIV in a hot box in the yard as the control valve for
a dry pipe system. It was my understanding that you needed a control valve
on the actual riser (this by looking at the diagram at 8.15.1.1). Is there
something that says that you can use the PIV as the control. Keep in mind
this is using the 2002 13 code.

 K a r e n  P u r v i s          | senior designer
FACILITY SYSTEMS CONSULTANTS, LLC
713 South Central Street, Suite 101
Knoxville, Tennessee 37902
Ph: (865) 246-0164  x227
Fx: (865) 246-1084


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to