Craig, I have 1978.
4.4.11 Decks. Sprinklers shall be installed under decks and galleries which are over 4 ft. wide. slatting of decks, walkways or the use of open gratings as a substitute for such sprinklers is not acceptable. 4-4.13 is the usual about ducts but I can't find anything about "vessels." Got other words we can play with? On Wed, Feb 9, 2011 at 5:57 AM, <[email protected]> wrote: > Got an issue with a client. Industrial chemical processing building, built > circa 1940's give or take. Building has sprinklers. Sometime possibly in > the 60's -70's an access platform was built (20ft by 40ft+/-) and no > sprinklers were provided below. Also some vessels were not provided with > sprinklers below. > > Here's the question to whoever has the oldest edition of NFPA 13, what > edition do you have and does it address sprinklers below obstructions? What > is the specific wording? > > If you can PDF that page with the edition and e-mail it to me that would be > most excellent! > > Thanks, > > Craig L. Prahl, CET > Fire Protection > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)