Craig,

I have 1978.

4.4.11 Decks. Sprinklers shall be installed under decks and galleries
which are over 4 ft. wide. slatting of decks, walkways or the use of
open gratings as a substitute for such sprinklers is not acceptable.

4-4.13 is the usual about ducts but I can't find anything about
"vessels." Got other words we can play with?

On Wed, Feb 9, 2011 at 5:57 AM,  <[email protected]> wrote:
> Got an issue with a client.  Industrial chemical processing building, built 
> circa 1940's give or take.  Building has sprinklers.  Sometime possibly in 
> the 60's -70's an access platform was built (20ft by 40ft+/-) and no 
> sprinklers were provided below.  Also some vessels were not provided with 
> sprinklers below.
>
> Here's the question to whoever has the oldest edition of NFPA 13,  what 
> edition do you have and does it address sprinklers below obstructions?  What 
> is the specific wording?
>
> If you can PDF that page with the edition and e-mail it to me that would be 
> most excellent!
>
> Thanks,
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to