Craig,

"NFPA 13, 1955, 715. (a) Decks. Sprinklers should be installed under decks and 
galleries unless they do not exceed 4 feet in width, with at least 6 inches 
clearance from the wall or partition and with arrangements to keep all stock a 
similar distance from the wall or partition.  See section 201."
Inside front cover in definitions: "The word "should" indicates advisory 
provisions."

I don't see anything else about obstructions, but there are actually several 
pages in the location and spacing chapter.

Let me know if you need more.

Scott Futrell
 
(763) 425-1001 Office
(612) 759-5556 Cell

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, February 09, 2011 7:58 AM
To: [email protected]
Subject: How far back in NFPA 13 - Obstructions

Got an issue with a client.  Industrial chemical processing building, built 
circa 1940's give or take.  Building has sprinklers.  Sometime possibly in the 
60's -70's an access platform was built (20ft by 40ft+/-) and no sprinklers 
were provided below.  Also some vessels were not provided with sprinklers below.

Here's the question to whoever has the oldest edition of NFPA 13,  what edition 
do you have and does it address sprinklers below obstructions?  What is the 
specific wording?

If you can PDF that page with the edition and e-mail it to me that would be 
most excellent!

Thanks,

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to