So in essence it's down to the fact NFPA 13 states wall and not boundary.
Sent from my iPhone On 7 Dec 2011, at 15:13, Sprinkler Academy - C Bilbo <[email protected]> wrote: > > This is one of those GREAT questions!! And it doesn't have a very good > answer.... > > In practice, spacing sprinklers to the beams is VERY common. I've done it > and I think anyone that has laid out a warehouse has done it. However, the > black and white text of the rules does say "twice the distance to the wall or > the distance to the next sprinkler, whichever is greater" (paraphrased off > the top of the head...) > > The technical committees have avoided this question because we didn't think > that there was a huge problem out there with it.... (VERY UNOFFICIAL > DISCUSSIONS and NOT the NFPA's official position!) > > I think it would be a great proposal for next cycle. And for the record, > when it comes up at the technical meeting, I will be speaking in favor of the > practice. > > It should be recognized that the above is my opinion as a member of the NFPA, > and has not been processed as a formal interpretation in accordance with the > NFPA Regulations Governing Committee Projects and should therefore not be > considered, nor relied upon, as the official position of the the AFSA, NFSA, > NFPA, nor any of their technical committees. > > Sincerely, > > > Cecil Bilbo > Academy of Fire Sprinkler Technology > Champaign, IL > 217.607.0325 > www.sprinkleracademy.com > [email protected] > > OUR STUDENTS SAVE LIVES!! > > > > >> From: [email protected] >> To: [email protected] >> Subject: RE: Sprinkler spacing 101 >> Date: Wed, 7 Dec 2011 09:02:16 -0600 >> >> But if your sprinkler can't spray under the beam because it is too deep, >> then you do your spacing off of the beam for proper coverage in that bay and >> then make sure you have proper spacing for the next bay on the other side >> of the beam. You are not going to get any water on the other side of the >> beam if the spray is blocked. >> >> Cliff Whitfield, SET >> President >> Fire Design, Inc. >> Ph: 337-261-8807 >> Fx: 337-261-8808 >> >> >> >> [email protected] >> www.fire-design.com >> >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected]] On Behalf Of Todd Williams >> Sent: Wednesday, December 07, 2011 8:58 AM >> To: [email protected] >> Subject: RE: Sprinkler spacing 101 >> >> >>> I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when >> determining the area of the sprinkler. >> >> Part (b) of that section states "Choose the larger of either twice the >> distance to the wall or obstruction of the distance to the next sprinkler" >> >> Twice the distance to the wall is 10', the distance between the sprinklers >> is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, as >> Mike stated. >> >> That was looking at it from the 12 x 10 side. If you look at it from the 8 x >> 15 side, twice the distance is 15 ft and the distance between sprinklers is >> 13'-6. Therefore that side is OK, but the other is not. >> >> n'est pas? >> >> >> Todd G. Williams, PE >> Fire Protection Design/Consulting >> Stonington, CT >> 860.535.2080 >> www.fpdc.com >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/fe2dc4d4/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum