So in essence it's down to the fact NFPA 13 states wall and not boundary.       

Sent from my iPhone

On 7 Dec 2011, at 15:13, Sprinkler Academy - C Bilbo <[email protected]> 
wrote:

> 
> This is one of those GREAT questions!!  And it doesn't have a very good 
> answer....
> 
> In practice, spacing sprinklers to the beams is VERY common.  I've done it 
> and I think anyone that has laid out a warehouse has done it.  However, the 
> black and white text of the rules does say "twice the distance to the wall or 
> the distance to the next sprinkler, whichever is greater" (paraphrased off 
> the top of the head...)  
> 
> The technical committees have avoided this question because we didn't think 
> that there was a huge problem out there with it....  (VERY UNOFFICIAL 
> DISCUSSIONS and NOT the NFPA's official position!)
> 
> I think it would be a great proposal for next cycle.  And for the record, 
> when it comes up at the technical meeting, I will be speaking in favor of the 
> practice.
> 
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the AFSA, NFSA, 
> NFPA, nor any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo 
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217.607.0325
> www.sprinkleracademy.com
> [email protected]
> 
> OUR STUDENTS SAVE LIVES!!
> 
> 
> 
> 
>> From: [email protected]
>> To: [email protected]
>> Subject: RE: Sprinkler spacing 101
>> Date: Wed, 7 Dec 2011 09:02:16 -0600
>> 
>> But if your sprinkler can't spray under the beam because it is too deep,
>> then you do your spacing off of the beam for proper coverage in that bay and
>> then make sure you have proper spacing for the next bay on the other side
>> of the beam. You are not going to get any water on the other side of the
>> beam if the spray is blocked.
>> 
>> Cliff Whitfield, SET
>> President
>> Fire Design, Inc.
>> Ph: 337-261-8807
>> Fx: 337-261-8808
>> 
>> 
>> 
>> [email protected]
>> www.fire-design.com
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd Williams
>> Sent: Wednesday, December 07, 2011 8:58 AM
>> To: [email protected]
>> Subject: RE: Sprinkler spacing 101
>> 
>> 
>>> I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when
>> determining the area of the sprinkler.
>> 
>> Part (b) of that section states "Choose the larger of either twice the
>> distance to the wall or obstruction of the distance to the next sprinkler"
>> 
>> Twice the distance to the wall is 10', the distance between the sprinklers
>> is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, as
>> Mike stated. 
>> 
>> That was looking at it from the 12 x 10 side. If you look at it from the 8 x
>> 15 side, twice the distance is 15 ft and the distance between sprinklers is
>> 13'-6. Therefore that side is OK, but the other is not.
>> 
>> n'est pas?
>> 
>> 
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>                         
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/fe2dc4d4/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to