Good point. I blew some dust off a different book, "Layout, Detail and Calculation of Fire Sprinkler Systems" by Kenneth Isman. It's pretty much a basic rundown of system layouts and such, but the spacing issues are consistent in the terms of spacing limits / values to walls or the adjacent sprinkler.
As I'm reading the various points, one thing is for sure - installations across the country over the years obviously have both concepts applied. LOL I'm not sure if I should push for a formal interpretation or concede to a difference of opinion where the owner will obviously decide the less expensive interpretation and consider the beam a wall. To not stall the project in paperwork and keep it moving forward I'm thinking that's where we're at. Mike Gallello C&H Fire Suppression Systems Inc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ben Young Sent: Wednesday, December 07, 2011 1:30 PM To: [email protected] Subject: Re: Sprinkler spacing 101 There is some guidance in the handbook explanatory text further on that supports Mike & Todd's position. In the 2007 edition, after 8.5.3.1.5 it states: "If the spacing of branch lines is uneven, the greatest distance between sprinklers on the branch lines, measured between the centerline of the sprinklers, should be used to determine how far apart sprinklers can be spaced from each other along the branch lines." Benjamin Young On Wed, Dec 7, 2011 at 12:39 PM, Bobby Gillett < [email protected]> wrote: > I think if the floor area is covered it is correct. > > Bobby Gillett > Sr. Project Manager > Key Fire Protection, Inc. > (731) 424-0130 office (731) 424-9285 fax > (731) 267-4853 cell > www.keyfireprotection.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Spencer > Allen > Sent: Wednesday, December 07, 2011 11:34 AM > To: [email protected] > Cc: FORUM > Subject: Re: Sprinkler spacing 101 > > So in essence it's down to the fact NFPA 13 states wall and not boundary. > > > Sent from my iPhone > > On 7 Dec 2011, at 15:13, Sprinkler Academy - C Bilbo > <[email protected]> wrote: > > > > > This is one of those GREAT questions!! And it doesn't have a very good > answer.... > > > > In practice, spacing sprinklers to the beams is VERY common. I've done > it > and I think anyone that has laid out a warehouse has done it. However, the > black and white text of the rules does say "twice the distance to the wall > or the distance to the next sprinkler, whichever is greater" (paraphrased > off the top of the head...) > > > > The technical committees have avoided this question because we didn't > think that there was a huge problem out there with it.... (VERY UNOFFICIAL > DISCUSSIONS and NOT the NFPA's official position!) > > > > I think it would be a great proposal for next cycle. And for the record, > when it comes up at the technical meeting, I will be speaking in favor of > the practice. > > > > It should be recognized that the above is my opinion as a member of the > NFPA, and has not been processed as a formal interpretation in accordance > with the NFPA Regulations Governing Committee Projects and should therefore > not be considered, nor relied upon, as the official position of the the > AFSA, NFSA, NFPA, nor any of their technical committees. > > > > Sincerely, > > > > > > Cecil Bilbo > > Academy of Fire Sprinkler Technology > > Champaign, IL > > 217.607.0325 > > www.sprinkleracademy.com > > [email protected] > > > > OUR STUDENTS SAVE LIVES!! > > > > > > > > > >> From: [email protected] > >> To: [email protected] > >> Subject: RE: Sprinkler spacing 101 > >> Date: Wed, 7 Dec 2011 09:02:16 -0600 > >> > >> But if your sprinkler can't spray under the beam because it is too deep, > >> then you do your spacing off of the beam for proper coverage in that bay > and > >> then make sure you have proper spacing for the next bay on the other > side > >> of the beam. You are not going to get any water on the other side of the > >> beam if the spray is blocked. > >> > >> Cliff Whitfield, SET > >> President > >> Fire Design, Inc. > >> Ph: 337-261-8807 > >> Fx: 337-261-8808 > >> > >> > >> > >> [email protected] > >> www.fire-design.com > >> > >> > >> -----Original Message----- > >> From: [email protected] > >> [mailto:[email protected]] On Behalf Of Todd > Williams > >> Sent: Wednesday, December 07, 2011 8:58 AM > >> To: [email protected] > >> Subject: RE: Sprinkler spacing 101 > >> > >> > >>> I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when > >> determining the area of the sprinkler. > >> > >> Part (b) of that section states "Choose the larger of either twice the > >> distance to the wall or obstruction of the distance to the next > sprinkler" > >> > >> Twice the distance to the wall is 10', the distance between the > sprinklers > >> is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, > as > >> Mike stated. > >> > >> That was looking at it from the 12 x 10 side. If you look at it from the > 8 x > >> 15 side, twice the distance is 15 ft and the distance between sprinklers > is > >> 13'-6. Therefore that side is OK, but the other is not. > >> > >> n'est pas? > >> > >> > >> Todd G. Williams, PE > >> Fire Protection Design/Consulting > >> Stonington, CT > >> 860.535.2080 > >> www.fpdc.com > >> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20111207/fe2dc4d4/attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment%0As/20111207/fe2dc4d4/attachment.html> > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > ----- > No virus found in this message. > Checked by AVG - www.avg.com > Version: 2012.0.1873 / Virus Database: 2102/4665 - Release Date: 12/07/11 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/8efac988/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum