There is some guidance in the handbook explanatory text further on that
supports Mike & Todd's position.

In the 2007 edition, after 8.5.3.1.5 it states:
"If the spacing of branch lines is uneven, the greatest distance between
sprinklers on the branch lines, measured between the centerline of the
sprinklers, should be used to determine how far apart sprinklers can be
spaced from each other along the branch lines."

Benjamin Young



On Wed, Dec 7, 2011 at 12:39 PM, Bobby Gillett <
[email protected]> wrote:

> I think if the floor area is covered it is correct.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> www.keyfireprotection.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Spencer
> Allen
> Sent: Wednesday, December 07, 2011 11:34 AM
> To: [email protected]
> Cc: FORUM
> Subject: Re: Sprinkler spacing 101
>
> So in essence it's down to the fact NFPA 13 states wall and not boundary.
>
>
> Sent from my iPhone
>
> On 7 Dec 2011, at 15:13, Sprinkler Academy - C Bilbo
> <[email protected]> wrote:
>
> >
> > This is one of those GREAT questions!!  And it doesn't have a very good
> answer....
> >
> > In practice, spacing sprinklers to the beams is VERY common.  I've done
> it
> and I think anyone that has laid out a warehouse has done it.  However, the
> black and white text of the rules does say "twice the distance to the wall
> or the distance to the next sprinkler, whichever is greater" (paraphrased
> off the top of the head...)
> >
> > The technical committees have avoided this question because we didn't
> think that there was a huge problem out there with it....  (VERY UNOFFICIAL
> DISCUSSIONS and NOT the NFPA's official position!)
> >
> > I think it would be a great proposal for next cycle.  And for the record,
> when it comes up at the technical meeting, I will be speaking in favor of
> the practice.
> >
> > It should be recognized that the above is my opinion as a member of the
> NFPA, and has not been processed as a formal interpretation in accordance
> with the NFPA Regulations Governing Committee Projects and should therefore
> not be considered, nor relied upon, as the official position of the the
> AFSA, NFSA, NFPA, nor any of their technical committees.
> >
> > Sincerely,
> >
> >
> > Cecil Bilbo
> > Academy of Fire Sprinkler Technology
> > Champaign, IL
> > 217.607.0325
> > www.sprinkleracademy.com
> > [email protected]
> >
> > OUR STUDENTS SAVE LIVES!!
> >
> >
> >
> >
> >> From: [email protected]
> >> To: [email protected]
> >> Subject: RE: Sprinkler spacing 101
> >> Date: Wed, 7 Dec 2011 09:02:16 -0600
> >>
> >> But if your sprinkler can't spray under the beam because it is too deep,
> >> then you do your spacing off of the beam for proper coverage in that bay
> and
> >> then make sure you have proper spacing for the next bay on the other
> side
> >> of the beam. You are not going to get any water on the other side of the
> >> beam if the spray is blocked.
> >>
> >> Cliff Whitfield, SET
> >> President
> >> Fire Design, Inc.
> >> Ph: 337-261-8807
> >> Fx: 337-261-8808
> >>
> >>
> >>
> >> [email protected]
> >> www.fire-design.com
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Todd
> Williams
> >> Sent: Wednesday, December 07, 2011 8:58 AM
> >> To: [email protected]
> >> Subject: RE: Sprinkler spacing 101
> >>
> >>
> >>> I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when
> >> determining the area of the sprinkler.
> >>
> >> Part (b) of that section states "Choose the larger of either twice the
> >> distance to the wall or obstruction of the distance to the next
> sprinkler"
> >>
> >> Twice the distance to the wall is 10', the distance between the
> sprinklers
> >> is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150,
> as
> >> Mike stated.
> >>
> >> That was looking at it from the 12 x 10 side. If you look at it from the
> 8 x
> >> 15 side, twice the distance is 15 ft and the distance between sprinklers
> is
> >> 13'-6. Therefore that side is OK, but the other is not.
> >>
> >> n'est pas?
> >>
> >>
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> 860.535.2080
> >> www.fpdc.com
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL:
> <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20111207/fe2dc4d4/attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment%0As/20111207/fe2dc4d4/attachment.html>
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.1873 / Virus Database: 2102/4665 - Release Date: 12/07/11
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/8efac988/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to