You always start with a guess. Try this and it doesn't work don't do that
again. If it works then do it a lot. Hammurabi didn't dictate how to build
a building, just what the punishments would be if you blew it. Want to
build your mud bricks a little smaller than standard, go ahead, we'll see
what happens. Oops. Clint dead. Deep do-do.

The first spacing rules I can find are from John Wormald (really good
guesser) and EH is 60 sqft max and OH is 90 sqft. That's it.

On Fri, Mar 6, 2015 at 1:00 PM, Brad Casterline <[email protected]>
wrote:

> Most sprinkler people are shocked when I tell them that Roland, but it is
> true. "had nothing to do with fire", not 'have'.
> Early '70s Kansas City, Ks contractor with big 3M projects, lots of 8"
> pipe.
> "What if we make the 2nd piece 1.25" instead of 1"?, could we make the main
> 6"? The first calculations were done to compare what a scheduled system
> would produce with a low, medium, and high Water Supply, and VOILA!...
> calcs
> are born. Another quote from the same man is "pipe scheduled systems had
> worked fine for 90 years at the time", so why bring fire into it? :)
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]]
> On Behalf Of Roland Huggins
> Sent: Friday, March 06, 2015 2:38 PM
> To: [email protected]
> Subject: Re: Beauty Salon/Day Spa
>
> I'm at a loss in how one could say the curves have nothing to do with the
> fire while the definitions are all about fire related variables.  Granted
> they are not quantified but are relative descriptions of a fire.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>
>
>
>
>
> > On Mar 6, 2015, at 12:31 PM, Brad Casterline <[email protected]>
> wrote:
> >
> > Actually, if one thinks about it, IBC has as much to do with density as
> NFPA
> > 13 does in a way, because the density/area curves "had nothing to do with
> > fire" according to the first person to use the curves (he invented them).
> > NFPA #13 Occupancy Classifications are based on Low, Moderate and High,
> > Quan/Comb and HRR, and "example occupancies" are given instead of
> numbers.
> >
> > Brad
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to