Yes, that was my plan to run everything off of 120v except the VFD.

JT

On 12/26/2015 2:58 PM, Bertho Stultiens wrote:
> On 12/26/2015 09:32 PM, John Thornton wrote:
>>>>> Not sure how I might isolate the VFD from the chassis at this moment.
>>>>> Well I could machine some delrin standoffs... I have a machine shop.
>>>> No problem. If you ensure that the chassis connection is firm and
>>>> electrically sound, then you just ommit the earth wire (my comment in
>>>> the drawing).
>>> One more comment. If you are unsure that the internal earth/chassis
>>> connection in the VFD controller holds, then you usually see a
>>> connection as seen in the attached image. A short thick wire is run from
>>> the earth screw connection to one of the chassis mounting bolts.
>> Ok that is easy to do, I have some huge stranded ground wire from a CT
>> scanner... I've attached my updated drawing of the VFD panel.
>>
>> The monitor can only run on 120v so it is necessary to transform from
>> 240 to 120 for the PC and monitor.
> Hm, then you may want to run everything off of the 120V section and
> ensure that you connect both computer and monitor to the star-connection
> for earth.
>
> Doing a 240/120 split between computer and monitor will get you again
> into trouble. In that case you have a monitor (assuming VGA) cable that
> bridges the power domains.
>
> Please note that you still need the serial isolator, regardless from
> where the computer and monitor are powered.
>


------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to