This sounds to me like a "concealed space", and if non-combustible construction, then no sprinkler required. We typically consider all sorts of spaces to be concealed that are accessible by hatches (or loosely laid ceiling tiles), it is only when the hatch begins to turn into a door that we remove the use of the term concealed from the conversation. The fact that there is a fan in the space changes nothing. Most typical high rise office buildings have "fans" in the un-sprinklered, non-combustible, concealed space above the ceiling, along with some limited amount of somewhat combustible wiring.
We believe that the above interpretation meets the intent of NFPA 13. Rich Richardson Seattle Fire Department _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)