Everyone is WAY overthinking the purpose and the operation of a sidewall 
sprinkler on a building column.  Put in a 5.6K sprinkler and be done with it.  
You don't need to calculate the inverse velocity pressure with regard to the 
position of Mars in July for a vertically installed horizontal sideway pendent 
water discharge device sprinkler.

Also aiming the discharge upward, is of no value.  You want the discharge to 
run down the column where the fire source will be whether that be stored 
commodities or pool fires.  You already have sprinklers overhead.  The other 
issue with an upward pointed sidewall is that if it were the sprinkler to fuse 
first it could cold solder overhead sprinklers preventing them from activating 
so as stated previously, I'd seriously challenge a fire official on this idea.  
It just makes no sense in any way shape or form.

All the sprinkler is intended to accomplish is to prevent the steel from 
reaching its point failure temperature.  Typically that is in the neighborhood 
of 1200 (F).  The direct water impingement on the columns has been tested and 
evidently found to accomplish this task with little regard for pressures and 
flow rate.

You do want the sprinkler close to the column so that the discharge is 
collected within the web of the column.  Whether you use a horizontal or 
vertical sidewall is more a matter of piping preference than functionality.  
They will both accomplish the same thing.   


So to quote the most famous inspirational speaker of all time, Shia Labeouf, 
JUST DO IT!


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of å... ....
Sent: Tuesday, July 07, 2015 7:53 AM
To: [email protected]
Subject: Re: Column Protection

We can use the sprinkler nozzle pressure, but as a means to the end of 
estimating how high the sprinkler will project water:

1. use the nozzle pressure with K-factor to get flow = Q,
2. with Q, divide by  sprinkler orifice area (A) to get velocity.   This is
the max possible velocity as deflector will slow 90% of the spray.
3.  from velocity, use Bernoullis at v2= 0 m/s velocity, to predict the height 
water will rise 4.  note, once the water is outside the sprinkler, the pressure 
is essentially ambient, so P1 ~ P2 in Bernoulli's equation.
5.  solve for z, maximum height the water will rise from vertically oriented 
sprinkler.

This seems like a lot of energy and discussion for a relatively minor sprinkler 
design point.
I mean, if we have gotten to the point of a fire where a column sprinkler is to 
save the structure, perhaps we earlier missed some more important fire 
protectioin design-issues, at least more important than sidewall horiztonal or 
sidewall down/up.

Do you think sometimes we put more energy into debating the simple points, 
because they are simpler to think about, and we spend less time debating the 
not-so-clear subject material, because we don't want to spend the mental 
energy, even though that is the effort that would yield the-most-design value 
for the time?



Scot Deal
Excelsior Fire/Risk Engineering
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to