RE: Butterfly valve, monitered or not?

2014-02-17 Thread Eric Tysinger
I would say no. It would be no different than a drain valve, which isn't required to be tampered. I would however use a model that doesn’t have a built in tamper. It doesn't control anything. Eric Tysinger CET NICET III - 108988 Project Manager – Fort Myers Branch Wayne Auto

RE: Alabama Elevators

2013-10-03 Thread Eric Tysinger
A17.1, but it isn't coming from A17. Eric Tysinger CET NICET III - 108988 Project Manager – Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 For Fire Alarm Service and Monitorin

RE: Different K factor in each floor practical?

2013-08-13 Thread Eric Tysinger
psi available at the roof. Eric Tysinger CET NICET III - 108988 Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 For Fire Alarm Service and Monitoring questions contact us

RE: Different K factor in each floor practical?

2013-08-13 Thread Eric Tysinger
the k-factors would only limit your starting head pressures, the pressure available on each floor would still remain the same. Eric Tysinger CET NICET III - 108988 Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433

RE: Wording in NFPA 13 (2007)

2013-03-07 Thread Eric Tysinger
where required by the AHJ Roland On Mar 7, 2013, at 7:48 AM, Eric Tysinger wrote: > Good morning all, > Here is a strange issue I ran into this morning. Take a look at 8.15.7.3 and > 8.15.7.4, "Sprinklers shall be permitted to be omitted" and then take a look > at 8

Wording in NFPA 13 (2007)

2013-03-07 Thread Eric Tysinger
quired by code or allowed to be omitted if the criteria is met. Eric Tysinger CET NICET III - 108988 Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 For Fire Alarm Ser

RE: 13R covered entrance

2012-10-19 Thread Eric Tysinger
x figures A.6.6.5 (a) (b) (c) (d) and (e) to explicitly clarify what is an open corridor or breezeway. Even though the corridor or breezeway bisects the buildings in multiple directions, sprinklers are not required. Eric Tysinger CET NICET III - 108988 Project Manager - Fort Myers Branch Wayne Aut

RE: thermal barrier

2012-08-31 Thread Eric Tysinger
require a sprinkler and the toilet room can be omitted, provided you have the thermal barrier all the way around the toilet room. Eric Tysinger CET NICET III - 108988 Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (23

RE: thermal barrier

2012-08-31 Thread Eric Tysinger
I would assume you are referencing NFPA 13R, 2002 edition. In the 2007 edition the requirement for the thermal barrier has been removed. 2002 edition, section 6.8.2 - thermal barrier required. 2007 edition, section 6.9.2 - not required Eric Tysinger CET NICET III - 108988 Project Manager - Fort

RE: EC Heads with 401 style plates?

2012-08-01 Thread Eric Tysinger
NFPA 13, 2007. Please look at 6.2.7, in a nut shell. If not recessed, flush or concealed the only listing requirement is for non-metallic escutcheons. Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort

RE: EC Heads with 401 style plates?

2012-07-31 Thread Eric Tysinger
tated in 13, I just don't have my book around to look up the section. Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (23

RE: Hydraulic calcs for back-flow devices;

2012-05-23 Thread Eric Tysinger
or manufacturers. If a replacement other than the like for like is used pressure loss may actually increase. Thanks, Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030

RE: Hydraulic calcs for back-flow devices;

2012-05-23 Thread Eric Tysinger
Another point to make note of is, without knowing why there was a second backflow installed. It might actually be required to be replaced with a working one. In that case you would might also lose more pressure. Thanks, Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers

RE: Mechanical fitting in wall

2012-04-26 Thread Eric Tysinger
obviously isn't a firewall. Thanks, Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 -Original Message- From:

RE: Mechanical fitting in wall

2012-04-26 Thread Eric Tysinger
cated within floor trusses or above a drywall ceiling. The only NFPA requirement is that valves be in an accessible location. Fittings are installed within inaccessible locations every day. Thanks, Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers Branch Wayne Automatic

RE: Florida Elevators

2012-01-20 Thread Eric Tysinger
hal's about it. I have seen them both lose the battle and win the battle. Your situation maybe one of those that they won. Thanks, Eric Tysinger CET NICET III - 108988 Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p

RE: Dual floor control assembies

2011-10-28 Thread Eric Tysinger
Yes, thanks George that's what I meant. Thanks, Eric Tysinger CET NICET III - 108988 Designer - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 -Original Message-

RE: Dual floor control assembies

2011-10-27 Thread Eric Tysinger
from each stairwell. Thanks, Eric Tysinger CET NICET III - 108988 Designer - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firespr

RE: Dual floor control assembies

2011-10-26 Thread Eric Tysinger
I've seen it done quite a few times. In my opinion, not best practice, service nightmare down the road. Yes the signs are required, but once they fall off, is the next inspection company going to know there are (2) valves on the floor and replace the required signage. Thanks, Eric Tys

RE: Underground Air Line

2011-09-13 Thread Eric Tysinger
tape to help protect it from being cut. Thanks, Eric Tysinger CET NICET III - 108988 Designer - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703 -Original Message- From

RE: CPVC encased in concrete

2011-09-12 Thread Eric Tysinger
The only times I have seen this done, regular PVC was used as a sleeve. Then after the pour the cpvc was fed through the sleeves and Styrofoam block outs were placed where fitting needed to be. Thanks, Eric Tysinger CET NICET III - 108988 Designer - Fort Myers Branch Wayne Automatic Fire

RE: How much discharge from a 2" system drain

2011-08-02 Thread Eric Tysinger
I've seen as much as 400-500gpm out of a single 2½" hose valve at around 175psi static starting pressure. Thanks, Eric Tysinger CET NICET III - 108988 Designer - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240

RE: Virginia Shop drawing stamp?

2011-06-13 Thread Eric Tysinger
I did a job a few months back in Augusta County and they did require a PE stamp. Thanks, Eric Tysinger CET NICET III - 108988 Designer - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240f: (239)433-3263 C: (239)633-9703

Limited Area Systems

2011-05-18 Thread Eric Tysinger
a residential one for 13D and 13R. Does anyone know of one that is listed for non-residential applications? I know none of those things are required but they are paying for it. We are also going to have fun tying a 4x2½x2½ FDC into a 1" line. Thanks, Eric Tysinger CET NICET III - 1

RE: EC Sidewall Heads

2011-04-25 Thread Eric Tysinger
n the sidewalls. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinkler

RE: EC Sidewall Heads

2011-04-25 Thread Eric Tysinger
into a problem is with the sidewalls placed back to back. Since sidewalls also throw back you would have to use a baffle of some sort between them, which would be near impossible anyway. I say stick to the 2 lines. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic

RE: IBC and Breezeways

2011-04-07 Thread Eric Tysinger
brings in the requirement to install in accordance with 13R, he has to recognize 13R. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message

RE: IBC and Breezeways

2011-04-07 Thread Eric Tysinger
rg [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric Tysinger Sent: Wednesday, April 06, 2011 4:18 PM To: sprinklerforum@firesprinkler.org Subject: IBC and Breezeways Good afternoon all, I have a NFPA 13R (Type V) project that falls under the 2009 IBC. I know per 903.3.1.2.1, balconies, decks a

IBC and Breezeways

2011-04-06 Thread Eric Tysinger
is? I don't think it does, that section specifically refers to dwelling units as does the commentary. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (23

RE:

2011-03-21 Thread Eric Tysinger
I have used a single 2½" female hose x male thread adapter, about a foot off the floor. Then you use a short piece of 2½" fire hose for testing. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (70

RE: Galvanized Pipe

2011-03-07 Thread Eric Tysinger
Also look at NFPA 13, 2002. Table 14.4.4.5. They wouldn't give you c-values for black dry pipe and pre-action systems if you couldn't use it. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (70

RE: Plastic Escutcheons

2011-03-04 Thread Eric Tysinger
reality you are making it look pretty. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun

RE: Spool piece for wafer style butterfly valve

2011-02-21 Thread Eric Tysinger
Are there other outlets that come off of this 12" line? If not, why not remove the valves and just slide the piping together and use (1) longer spool piece. Or slide every other piece together and use a couple of longer spool pieces. Thanks, Eric Tysinger CET NICET III - 108988 Designer

RE: Hangers and pressure surges

2011-01-20 Thread Eric Tysinger
If I'm not mistaken, this only applies to armovers above a ceiling supplying pendents below a ceiling, per NFPA 13, 2007. I would think it would apply to any situation where the pressure can be expected to exceed 100psi. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Auto

RE: NICET III

2010-12-08 Thread Eric Tysinger
your testing using Work Elements. After September 30, 2011, all tests will only be offered using the CBT format. Note that to qualify for testing in the cycle that ends on September 30, 2011, your application needs to be postmarked by June 30, 2011." Thanks, Eric Tysinger CET NICET II

RE: NICET III

2010-12-08 Thread Eric Tysinger
ar or I would have be asking the same question. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum

RE: NFPA 13R Bathroom

2010-12-03 Thread Eric Tysinger
I agree, the 2007 & 2010 NFPA 13R definition of a bathroom specifically addresses that. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Orig

RE: 13D Sprinklers at peak

2010-11-15 Thread Eric Tysinger
are other options. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerf

RE: 13R sprinkler temperatures

2010-11-12 Thread Eric Tysinger
Check the manufacturer's paperwork. I know that tyco, viking and reliable all have residential design guides. I know the tyco one specifically address temperatures, and they even have pictures/diagrams. I'm sure the other manufacturers do as well. Thanks, Eric Tysinger CET NICET II

RE: NON-METALLIC COUPLING

2010-11-04 Thread Eric Tysinger
n the building. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum

RE: 13D Backflow prevention

2010-11-03 Thread Eric Tysinger
rom a separate tap, then 9 out of 10 times a backflow is required. Some purveyors require a RPZ where there is a FDC, 13D doesn't require an FDC but some AHJ's do. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28

RE: Elevator Shafts

2010-10-08 Thread Eric Tysinger
I understand all of that, however the fact is that ASME A17.1 requires "non-combustible" shaft and passenger car, unless I am mistaken. So if the shaft and car are IAW ASME then it should be considered non-combustible, correct? Thanks, Eric Tysinger CET NICET III - 108988 Desi

Elevator Shafts

2010-10-08 Thread Eric Tysinger
ASME A17.1 requires the car and shaft to be non-combustible. I know that 13R added the "combustible" wording in the 2007 edition as some states have not adopted the ASME requirements. Am I wrong, by thinking this AHJ is incorrect, is it considered combustible and are sprinklers really req

RE: Hose Demand

2010-10-05 Thread Eric Tysinger
your supply to the pump would be 250 short if not accounted for. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From

RE: Hose Demand

2010-10-05 Thread Eric Tysinger
I think this is meant to refer to inside and/or outside hose that is supplied from a hydrant or hose valve down stream of the pump. I think that you would still be required to account for it from a hydrant prior to the pump. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic

RE: Owner refusal

2010-10-05 Thread Eric Tysinger
A quick little heads up call to the AHJ/Inspector before the inspection does wonders for situations like that. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633

RE: PRV's in Calc's

2010-07-28 Thread Eric Tysinger
o 165. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum

RE: hydrant spacing

2010-07-14 Thread Eric Tysinger
, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

RE: Self Storage

2010-07-14 Thread Eric Tysinger
hanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum

RE: Self Storage

2010-07-14 Thread Eric Tysinger
I have seen these done at GRP 2 in the past. Don't forget misc storage of class I-IV less than 12'-0 is only grp 2 per 2002ed. Section 12.1.10. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (70

RE: limits on velocity

2010-06-25 Thread Eric Tysinger
NCDOI has a velocity limit in their standards, where it comes from, who knows. Potter flow switches have a maximum surge of 18fps on the VSR models. Is maximum surge the same has velocity? Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370

RE: Mixing QR and SR Heads

2010-06-04 Thread Eric Tysinger
Sorry guys, I retract that statement. That reference to element is in a different section. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original

RE: Mixing QR and SR Heads

2010-06-04 Thread Eric Tysinger
I agree here, the code actually states that they must be the same response element and even if the sprinkler is only listed as SR at extended coverage's, it is still a QR element. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport

RE:

2010-05-11 Thread Eric Tysinger
ooks. When we know it shouldn't be right next to it. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: spri

RE:

2010-05-11 Thread Eric Tysinger
uot;residential areas" not residential sprinklers. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun.

RE:

2010-05-11 Thread Eric Tysinger
8.3.2.5(c) is for residential sprinklers. Worth indicates light hazard/quick response. 8.3.2.5(A)(B) do not have any requirements in regards to light fixtures. All based on 2007 edition. 2002 is the same. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers

RE: Calc Area

2010-04-20 Thread Eric Tysinger
you don't you go back and start over. If you do the you move on. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From:

RE: CC sprinklers

2010-04-14 Thread Eric Tysinger
SSU are not specifically listed for CC spaces less than 36" in depth. They are listed for CC spaces though. Which is what drove the manufacturers to produce the "CC" heads. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorspor

RE: CC sprinklers

2010-04-14 Thread Eric Tysinger
8.14.1.6 states "horizontal combustible concealed spaces". There is no reference to exclude trusses, joists or TJI's. Unless I am missing something. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28

RE: CC sprinklers

2010-04-14 Thread Eric Tysinger
Actually NFPA 13 2002, requires the use of sprinklers specifically listed for CC spaces less than 36" deep. Section 8.14.1.6 Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795

RE: CC sprinklers

2010-04-14 Thread Eric Tysinger
Viking has a CC head. Its called "COIN". Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinkler

RE: 2'x4' Light Obstruction

2010-03-29 Thread Eric Tysinger
Cliff, Hey man what's up. I think the concern is that the 4' maybe considered the width by some. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (23

RE: 2'x4' Light Obstruction

2010-03-29 Thread Eric Tysinger
I have always looked at the width as being the shortest side. Take for instance a 2' wide duct that is 15' long. Is it really 15' wide and 2' long? Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord,

RE: Grooved Underground, Thrust Blocks Required?

2010-03-25 Thread Eric Tysinger
NFPA 24, 2007 ed - 10.8.1.2 states that thrust blocks are not required with mechanical type joints, grooved being specifically included. However there may be an issue with galv steel in some jurisdictions. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Eric Tysinger
to calc it. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinkler

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Eric Tysinger
Correct, however as you stated the separation barrier is left up to interpretation. I think with the use of QR sprinklers, even in ordinary hazard occupancies, they will activate and start controlling the fire well before even a 30 minute barrier is compromised. Thanks, Eric Tysinger CET NICET

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Eric Tysinger
Another note, correct me if I am wrong. A typical stud wall (wood or metal) and 1/2" gypsum (on both sides) provides a minimum of a 30 minute rating, although the attachment method to the floor/ceiling assembly may be an added factor. Thanks, Eric Tysinger CET NICET III - 108988 Designer

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Eric Tysinger
losing. In either hazard the walls must be rated to the duration of the water supply required. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -Origin

Plans and Specs?

2010-02-25 Thread Eric Tysinger
Good afternoon all (or morning to some), We have a job (plans and specs) we are looking at, wet and dry systems. Has anyone ever run into an engineer spec'ing thermo wells? What about the phrase "All threaded process piping to be back welded." Thanks, Thanks, Eric Tysinge

RE: CPVC and Nail plates

2010-02-16 Thread Eric Tysinger
We feel regardless of code, it is well worth the added protection. While it my not stop a nail gun it will stop the random drywall screw and finishing nails. Thanks, Eric Tysinger CET NICET 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782

RE: Beam obstruction rules

2010-02-08 Thread Eric Tysinger
.5.1.2 (2) then you are arranging the sprinklers on each side of the obstruction to share the responsibility off covering under it. Thanks, Eric Tysinger CET NICET 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 f: (704)795-6838 C

RE: Elevator machine rooms

2010-01-28 Thread Eric Tysinger
s own requirements. It's really going to depend on the elevator inspector and the edition of the code they are currently using. Thanks, Eric Tysinger CET NICET 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 f: (704)795-6838 C

RE: Elevator machine rooms

2010-01-28 Thread Eric Tysinger
he elevator? It couldn't happen with the sprinkler line feeding only the elevator areas with it's own flow switch. Thanks, Eric Tysinger CET NICET 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 f: (704)795-6838 C: (239)633-970

RE: Electrical Rooms

2010-01-04 Thread Eric Tysinger
to be omitted. I try to use these to avoid the questions all together. Thanks, Eric Tysinger CET NICET 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum

RE: Vote for Residential Sprinklers - NOW please!

2009-12-21 Thread Eric Tysinger
655/105 Keep them going. Thanks, Eric Tysinger CET NICET 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 f: (704)795-6838 C: (239)633-9703 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-02 Thread Eric Tysinger
gt; > -Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron > Greenman > Sent: Tuesday, December 01, 2009 12:24 PM > To: sprinklerforum@firesprinkler.org > Subject: Re: Domestic Demand Require

RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-02 Thread Eric Tysinger
allowance. So what I am gathering for these posts is that I should have accounted for 104000 gpm? Even at the number of buildings we actually did it would have been 5200gpm. I'm sorry but this really sounds way off and definitely not covered by 13R. Thanks, Eric Tysinger CET NICET 108988 Des

RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-01 Thread Eric Tysinger
cts I have seen. Eric Tysinger -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Tuesday, December 01, 2009 3:12 PM To: sprinklerforum@firesprinkler.org Subject: Re: Domestic Demand Require

Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-01 Thread Eric Tysinger
n the situation of a community subdivision where the city main is tapped once, then the water main runs throughout the project feeding hydrants, domestic and fire lines, and the same arrangement as figure A.6.5.3(b) is used, would this require domestic demand to be accounted for? Thanks, Eric Tys

RE: Sprinklered apartment building burns

2009-10-29 Thread Eric Tysinger
It's unfortunate that two fire fighters were injured, but the article doesn't say any residents were. Being a 13R system it did it's job. Everyone egressed the building. Imagine what the losses would have been without the sprinklers. Thanks, Eric Tysinger CET NICET 108988

RE: Pipe passing thru Electrical Equipment Rooms

2009-04-07 Thread Eric Tysinger
with 110.26 (F)(1)a through (F)(1)(d). Please see the above F-1-a through F-1-d. It provides all the requirements for entering and exiting the dedicated equipment spaces. Thanks, Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Ft. Myers, Florida 33905 www.waynefir

RE: NFPA 13R/D and ceiling pockets

2009-04-06 Thread Eric Tysinger
The 2002 edition of NFPA 13/13R/13D doesn't address ceiling pockets in residential occupancies. It is first addressed in the 2007 edition of 13R and D. Section 6.8.1.5.4 of 13R and in section 8.6.7 of 13D, 2007 edition that is. Hope this helps. Eric Tysinger Design Manager Wayne Automatic

RE: NFPA 13R/D and ceiling pockets

2009-04-06 Thread Eric Tysinger
ts the requirements of NFPA 13/13R/13D for omitting the sprinkler protection then the depth is not a factor, only floor coverage is required. Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Ft. Myers, Florida 33905 www.waynefire.com Ph: (239) 433-3030 ext. 231

RE: Residential Heads under Soffit

2009-03-10 Thread Eric Tysinger
NFPA 13R, 2007 edition has added the ceiling pocket rule for residential sprinklers. Section 6.8.1.5.4 Thanks, Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Ft. Myers, Florida 33905 www.waynefire.com Ph: (239) 433-3030 ext. 231 Fax: (239) 433-3263 Cell: (239

RE: Working plan info - NFPA 13-22.1.3

2009-02-25 Thread Eric Tysinger
eliminating the sprinkler when the size of the space meets certain criteria. Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Ft. Myers, Florida 33905 www.waynefire.com Ph: (239) 433-3030 ext. 231 Fax: (239) 433-3263 Cell: (239) 633-9703 Nextel: 158*117*8012

RE: Bay Window

2008-09-10 Thread Eric Tysinger
cu.ft. volume limitation can be applied. Any other thoughts? Tony -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Eric Tysinger Sent: September 10, 2008 3:19 PM To: sprinklerforum@firesprinkler.org Subject: [Suspected Spam]RE: Bay Window Take a look at

RE: Bay Window

2008-09-10 Thread Eric Tysinger
Take a look at NFPA 13 2002; section 8.14.6.2 or NFPA 13 2007; section 8.15.6.1 I would try to approach it as a platform and your situation defininetly meets all the requirements listed. Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Ft. Myers, Florida 33905

RE: Plans Examiner rights to customer contracts

2008-04-16 Thread Eric Tysinger
why company "A" is doing the job instead of company "B". Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Ft. Myers, Florida 33905 www.waynefire.com Ph: (239) 433-3030 ext. 231 Fax: (239) 433-3263 Cell: (239) 633-9703 Nextel: 158*117*8012

RE: thermal barrier

2008-04-11 Thread Eric Tysinger
metal stud wall as at least one-hour. Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez Sent: Friday, April 11, 2008 7:35 AM To: sprinklerforum@firesprinkler.org Subject: R

RE: Check valves and dry systems

2008-04-10 Thread Eric Tysinger
maintenance. With dry systems there is nothing on the system side except for possibly air or what have you. The check valve in that case would be usless. Eric Tysinger Design Manager Wayne Automatic Fire Sprinklers, Inc. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED