I would say no. It would be no different than a drain valve, which isn't
required to be tampered. I would however use a model that doesn’t have a built
in tamper. It doesn't control anything.
Eric Tysinger CET
NICET III - 108988
Project Manager – Fort Myers Branch
Wayne Auto
A17.1, but it isn't coming from A17.
Eric Tysinger CET
NICET III - 108988
Project Manager – Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
For Fire Alarm Service and Monitorin
psi available at
the roof.
Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
For Fire Alarm Service and Monitoring questions contact us
the k-factors
would only limit your starting head pressures, the pressure available on each
floor would still remain the same.
Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433
where required by the AHJ
Roland
On Mar 7, 2013, at 7:48 AM, Eric Tysinger wrote:
> Good morning all,
> Here is a strange issue I ran into this morning. Take a look at 8.15.7.3 and
> 8.15.7.4, "Sprinklers shall be permitted to be omitted" and then take a look
> at 8
quired by code or
allowed to be omitted if the criteria is met.
Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
For Fire Alarm Ser
x figures A.6.6.5 (a) (b) (c) (d) and (e)
to explicitly clarify what is an open corridor or breezeway. Even though the
corridor or breezeway bisects the buildings in multiple directions, sprinklers
are not required.
Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Aut
require a sprinkler and the toilet
room can be omitted, provided you have the thermal barrier all the way around
the toilet room.
Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (23
I would assume you are referencing NFPA 13R, 2002 edition. In the 2007 edition
the requirement for the thermal barrier has been removed.
2002 edition, section 6.8.2 - thermal barrier required.
2007 edition, section 6.9.2 - not required
Eric Tysinger CET
NICET III - 108988
Project Manager - Fort
NFPA 13, 2007.
Please look at 6.2.7, in a nut shell.
If not recessed, flush or concealed the only listing requirement is for
non-metallic escutcheons.
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort
tated in 13, I just
don't have my book around to look up the section.
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (23
or manufacturers. If a replacement
other than the like for like is used pressure loss may actually increase.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030
Another point to make note of is, without knowing why there was a second
backflow installed. It might actually be required to be replaced with a working
one. In that case you would might also lose more pressure.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers
obviously isn't a
firewall.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
-Original Message-
From:
cated within floor
trusses or above a drywall ceiling. The only NFPA requirement is that valves be
in an accessible location. Fittings are installed within inaccessible locations
every day.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic
hal's about it. I have seen
them both lose the battle and win the battle. Your situation maybe one of those
that they won.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p
Yes, thanks George that's what I meant.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
-Original Message-
from each stairwell.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firespr
I've seen it done quite a few times. In my opinion, not best practice, service
nightmare down the road. Yes the signs are required, but once they fall off, is
the next inspection company going to know there are (2) valves on the floor and
replace the required signage.
Thanks,
Eric Tys
tape to help protect
it from being cut.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
-Original Message-
From
The only times I have seen this done, regular PVC was used as a sleeve. Then
after the pour the cpvc was fed through the sleeves and Styrofoam block outs
were placed where fitting needed to be.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer - Fort Myers Branch
Wayne Automatic Fire
I've seen as much as 400-500gpm out of a single 2½" hose valve at around 175psi
static starting pressure.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240
I did a job a few months back in Augusta County and they did require a PE stamp.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240f: (239)433-3263
C: (239)633-9703
a residential
one for 13D and 13R. Does anyone know of one that is listed for non-residential
applications?
I know none of those things are required but they are paying for it. We are
also going to have fun tying a 4x2½x2½ FDC into a 1" line.
Thanks,
Eric Tysinger CET
NICET III - 1
n the sidewalls.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinkler
into a problem
is with the sidewalls placed back to back. Since sidewalls also throw back you
would have to use a baffle of some sort between them, which would be near
impossible anyway.
I say stick to the 2 lines.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic
brings in
the requirement to install in accordance with 13R, he has to recognize 13R.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message
rg
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric Tysinger
Sent: Wednesday, April 06, 2011 4:18 PM
To: sprinklerforum@firesprinkler.org
Subject: IBC and Breezeways
Good afternoon all,
I have a NFPA 13R (Type V) project that falls under the 2009 IBC. I know per
903.3.1.2.1, balconies, decks a
is? I don't think it does,
that section specifically refers to dwelling units as does the commentary.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (23
I have used a single 2½" female hose x male thread adapter, about a foot off
the floor. Then you use a short piece of 2½" fire hose for testing.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (70
Also look at NFPA 13, 2002.
Table 14.4.4.5.
They wouldn't give you c-values for black dry pipe and pre-action systems if
you couldn't use it.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (70
reality you are
making it look pretty.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun
Are there other outlets that come off of this 12" line? If not, why not remove
the valves and just slide the piping together and use (1) longer spool piece.
Or slide every other piece together and use a couple of longer spool pieces.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
If I'm not mistaken, this only applies to armovers above a ceiling supplying
pendents below a ceiling, per NFPA 13, 2007. I would think it would apply to
any situation where the pressure can be expected to exceed 100psi.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Auto
your testing
using Work Elements. After September 30, 2011, all tests will only be offered
using the CBT format. Note that to qualify for testing in the cycle that ends
on September 30, 2011, your application needs to be postmarked by June 30,
2011."
Thanks,
Eric Tysinger CET
NICET II
ar or I would have be
asking the same question.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum
I agree, the 2007 & 2010 NFPA 13R definition of a bathroom specifically
addresses that.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Orig
are other options.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerf
Check the manufacturer's paperwork. I know that tyco, viking and reliable all
have residential design guides. I know the tyco one specifically address
temperatures, and they even have pictures/diagrams. I'm sure the other
manufacturers do as well.
Thanks,
Eric Tysinger CET
NICET II
n the building.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum
rom a separate tap, then 9
out of 10 times a backflow is required. Some purveyors require a RPZ where
there is a FDC, 13D doesn't require an FDC but some AHJ's do.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28
I understand all of that, however the fact is that ASME A17.1 requires
"non-combustible" shaft and passenger car, unless I am mistaken. So if the
shaft and car are IAW ASME then it should be considered non-combustible,
correct?
Thanks,
Eric Tysinger CET
NICET III - 108988
Desi
ASME A17.1
requires the car and shaft to be non-combustible. I know that 13R added the
"combustible" wording in the 2007 edition as some states have not adopted the
ASME requirements. Am I wrong, by thinking this AHJ is incorrect, is it
considered combustible and are sprinklers really req
your supply to the
pump would be 250 short if not accounted for.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From
I think this is meant to refer to inside and/or outside hose that is supplied
from a hydrant or hose valve down stream of the pump. I think that you would
still be required to account for it from a hydrant prior to the pump.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic
A quick little heads up call to the AHJ/Inspector before the inspection does
wonders for situations like that.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633
o 165.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum
,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
hanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum
I have seen these done at GRP 2 in the past. Don't forget misc storage of class
I-IV less than 12'-0 is only grp 2 per 2002ed. Section 12.1.10.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (70
NCDOI has a velocity limit in their standards, where it comes from, who knows.
Potter flow switches have a maximum surge of 18fps on the VSR models. Is
maximum surge the same has velocity?
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370
Sorry guys, I retract that statement. That reference to element is in a
different section.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original
I agree here, the code actually states that they must be the same response
element and even if the sprinkler is only listed as SR at extended coverage's,
it is still a QR element.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport
ooks. When we know it
shouldn't be right next to it.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: spri
uot;residential areas" not
residential sprinklers.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun.
8.3.2.5(c) is for residential sprinklers. Worth indicates light hazard/quick
response.
8.3.2.5(A)(B) do not have any requirements in regards to light fixtures.
All based on 2007 edition. 2002 is the same.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers
you don't you go back and
start over. If you do the you move on.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From:
SSU are not specifically listed for CC spaces less than 36" in depth. They are
listed for CC spaces though. Which is what drove the manufacturers to produce
the "CC" heads.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorspor
8.14.1.6 states "horizontal combustible concealed spaces". There is no
reference to exclude trusses, joists or TJI's. Unless I am missing something.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28
Actually NFPA 13 2002, requires the use of sprinklers specifically listed for
CC spaces less than 36" deep. Section 8.14.1.6
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795
Viking has a CC head. Its called "COIN".
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinkler
Cliff, Hey man what's up. I think the concern is that the 4' maybe considered
the width by some.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (23
I have always looked at the width as being the shortest side. Take for instance
a 2' wide duct that is 15' long. Is it really 15' wide and 2' long?
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord,
NFPA 24, 2007 ed - 10.8.1.2 states that thrust blocks are not required with
mechanical type joints, grooved being specifically included. However there may
be an issue with galv steel in some jurisdictions.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers
to calc it.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinkler
Correct, however as you stated the separation barrier is left up to
interpretation. I think with the use of QR sprinklers, even in ordinary hazard
occupancies, they will activate and start controlling the fire well before even
a 30 minute barrier is compromised.
Thanks,
Eric Tysinger CET
NICET
Another note, correct me if I am wrong. A typical stud wall (wood or metal) and
1/2" gypsum (on both sides) provides a minimum of a 30 minute rating, although
the attachment method to the floor/ceiling assembly may be an added factor.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
losing. In either hazard
the walls must be rated to the duration of the water supply required.
Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
-Origin
Good afternoon all (or morning to some),
We have a job (plans and specs) we are looking at, wet and dry systems. Has
anyone ever run into an engineer spec'ing thermo wells? What about the phrase
"All threaded process piping to be back welded."
Thanks,
Thanks,
Eric Tysinge
We feel regardless of code, it is well worth the added protection. While it my
not stop a nail gun it will stop the random drywall screw and finishing nails.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782
.5.1.2 (2) then you are
arranging the sprinklers on each side of the obstruction to share the
responsibility off covering under it.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032
f: (704)795-6838
C
s own
requirements. It's really going to depend on the elevator inspector and the
edition of the code they are currently using.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032
f: (704)795-6838
C
he elevator? It couldn't happen
with the sprinkler line feeding only the elevator areas with it's own flow
switch.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032
f: (704)795-6838
C: (239)633-970
to be omitted. I try
to use these to avoid the questions all together.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum
655/105 Keep them going.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032
f: (704)795-6838
C: (239)633-9703
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
gt;
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron
> Greenman
> Sent: Tuesday, December 01, 2009 12:24 PM
> To: sprinklerforum@firesprinkler.org
> Subject: Re: Domestic Demand Require
allowance. So what I am gathering for these posts is that I should
have accounted for 104000 gpm? Even at the number of buildings we actually did
it would have been 5200gpm. I'm sorry but this really sounds way off and
definitely not covered by 13R.
Thanks,
Eric Tysinger CET
NICET 108988
Des
cts I have seen.
Eric Tysinger
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Tuesday, December 01, 2009 3:12 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Domestic Demand Require
n the situation of a community subdivision where the city main is tapped once,
then the water main runs throughout the project feeding hydrants, domestic and
fire lines, and the same arrangement as figure A.6.5.3(b) is used, would this
require domestic demand to be accounted for?
Thanks,
Eric Tys
It's unfortunate that two fire fighters were injured, but the article doesn't
say any residents were. Being a 13R system it did it's job. Everyone egressed
the building. Imagine what the losses would have been without the sprinklers.
Thanks,
Eric Tysinger CET
NICET 108988
with 110.26 (F)(1)a through
(F)(1)(d).
Please see the above F-1-a through F-1-d. It provides all the requirements for
entering and exiting the dedicated equipment spaces.
Thanks,
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Ft. Myers, Florida 33905
www.waynefir
The 2002 edition of NFPA 13/13R/13D doesn't address ceiling pockets in
residential occupancies. It is first addressed in the 2007 edition of 13R and
D. Section 6.8.1.5.4 of 13R and in section 8.6.7 of 13D, 2007 edition that is.
Hope this helps.
Eric Tysinger
Design Manager
Wayne Automatic
ts the requirements of NFPA 13/13R/13D for omitting
the sprinkler protection then the depth is not a factor, only floor coverage is
required.
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Ft. Myers, Florida 33905
www.waynefire.com
Ph: (239) 433-3030 ext. 231
NFPA 13R, 2007 edition has added the ceiling pocket rule for residential
sprinklers. Section 6.8.1.5.4
Thanks,
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Ft. Myers, Florida 33905
www.waynefire.com
Ph: (239) 433-3030 ext. 231
Fax: (239) 433-3263
Cell: (239
eliminating the sprinkler when the size of the space
meets certain criteria.
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Ft. Myers, Florida 33905
www.waynefire.com
Ph: (239) 433-3030 ext. 231
Fax: (239) 433-3263
Cell: (239) 633-9703
Nextel: 158*117*8012
cu.ft. volume limitation can be applied. Any
other thoughts?
Tony
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Eric
Tysinger
Sent: September 10, 2008 3:19 PM
To: sprinklerforum@firesprinkler.org
Subject: [Suspected Spam]RE: Bay Window
Take a look at
Take a look at NFPA 13 2002; section 8.14.6.2 or NFPA 13 2007; section
8.15.6.1
I would try to approach it as a platform and your situation defininetly
meets all the requirements listed.
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Ft. Myers, Florida 33905
why company "A" is doing the job instead of company "B".
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Ft. Myers, Florida 33905
www.waynefire.com
Ph: (239) 433-3030 ext. 231
Fax: (239) 433-3263
Cell: (239) 633-9703
Nextel: 158*117*8012
metal stud wall as at
least one-hour.
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez
Sent: Friday, April 11, 2008 7:35 AM
To: sprinklerforum@firesprinkler.org
Subject: R
maintenance. With dry systems there is nothing on
the system side except for possibly air or what have you. The check
valve in that case would be usless.
Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED