The top two fig. measure the head spacing to the "WALL" the lower two Fig's
measure the head spacing to the "Window Glass" for bay windows that create
floor space. 

Your example does not create floor space so you measure to the wall. The
concealed combustible space under the window should be filled with non-
combustible insulation, to avoid having to provide sprinkler protection in
this area.(8.15.1.2.7) The 160FT3 you refer to is for ceilings of
combustible construction above dry wall. (8.15.1.2.6 or 8.15.1.2.8)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Wednesday, September 10, 2008 2:48 PM
To: [email protected]
Subject: Bay Window

 
NFPA 13, 2007; section 8.5.3.2.4

Exhibit 8.8 shows two diagrams. One for "no floor area" and the other "with
floor area".

Both diagrams appear to be the same. Am I drunk or is one diagram incorrect?

Another question. A school with classrooms having bay windows, similar to
exhibit 8.8, except there is a combustible concealed space forming part of
the wall below the window.

                      __________________ <--- CEILING
                                     I I
                                     I I
                                     I I <--- WALL            
                                     I I
                                     I I__________
                                     I__________  I
                                               I  II
                                               I  II <--- WINDOW
                                               I  II
                                               I  II
                                     __________I  I
                                     I            I
                                     I            I
                                     I            I
                                     I        <---I------- COMBUSTIBLE
CONCEALED SPACE   
                                     I____________I  

This concealed space is 12 feet long 3 feet wide and 3 feet deep. The Fire
Marshall is asking for sprinklers in this combustible concealed space. My
thoughts are it is less than 160 cubic feet, so should not need sprinklers.
However, I don't see a code section relating specifically to this situation.
Any comments?

Tony          

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to