It is a three floors level area, what are the minimum requirements to convert 
such wet system to a double interlock pre-action system? 
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Reed Roisum 
[[email protected]]
Sent: Friday, September 04, 2009 3:46 PM
To: '[email protected]'
Subject: RE: Fire Sprinker System Changes in Vis Lab

Jaber,

What kind of advisement are you looking for?  The plan for protecting this 
space with NOVEC 1230 and using VESDA early warning detection sounds like the 
way to go.  Are you questioning removing the sprinkler system?  You will most 
likely need AHJ approval to install only the clean agent system in lieu of 
sprinklers (although this isn't IBC world is it?).  You might want to advise 
the owner to consider having a sprinkler system 'back up'.  Sounds like a 
pre-action system would be warranted with the level of fear it sounds like they 
have.  You can also try to dispel some of the unfounded fears they probably 
have regarding accidental discharges, but don't expect them to be ok with a wet 
system remaining in this space.
There are a number of other considerations to be made...such as sealing of the 
room.  Does it have a drop ceiling?
We can discuss more once I know what you are after.


Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:    Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Haji, Jaber M
Sent: Friday, September 04, 2009 5:52 AM
To: [email protected]
Subject: Fire Sprinker System Changes in Vis Lab

Your insights/advised are highly appreciated pertaining to a new visualization 
lab in new university protected by automatic sprinkler system and the vendor of 
the visualization equipment is worried about sprinkler leakage. Have a look at 
his draft letter highlighted bellow and advise us accordingly. Thanks in 
advance.

-------------------------------------------------------------------------------------------------

Changes to sprinkler system in Vislab Area of building one.

The current sprinkler arrangement in the vislab section of building
puts our visualization equipment at significant risk.  The water based
system if it goes off could easily ruin millions of dollars of
equipment in a very short period of time.  Including all Sony
projectors that drive the CAVE and MPR areas.

For this reason it is imperative that we make changes in these spaces
to the current fire system.  Visualization laboratory a plan for
corrective action has been prepared and is recommended as
the best course of action.

First the building fire detection system should be extended to the Vis
lab Data Center, Recording Room, DS1, DS2/3, CAVE and MPR Projection
spaces.  This will ensure timely notification of any emergency to the
response team.

Second the current sprinkler system in the above areas should be
closed and drained of water to ensure no accidents can cause loss of
equipment through water damage.  Additional Fire Extinguishers should
be placed in these areas as well.

Third a permanent solution utilizing VESDA detection system and NOVEC
fire suppression system should be installed in all of these areas. The 
installation should be carried out
in such a way to minimize laboratory downtime to a maximum of
a single week.  We believe this can be done by the careful removal of
the most delicate equipment from the lab space, covering the remainder
in protective plastic and having NOVEC piping installed and configured
after the delicate equipment has been removed.

A similar adjustment must be made to the two lecture hall projection
rooms containing Sony 4K projectors.

We  believe that these changes would be in the best interest of a long term 
protection of its investment in its visualization equipment.

The contents of this email, including all related responses, files and 
attachments transmitted with it (collectively referred to as "this Email"), are 
intended solely for the use of the individual/entity to whom/which they are 
addressed, and may contain confidential and/or legally privileged information. 
This Email may not be disclosed or forwarded to anyone else without 
authorization from the originator of this Email. If you have received this 
Email in error, please notify the sender immediately and delete all copies from 
your system. Please note that the views or opinions presented in this Email are 
those of the author and may not necessarily represent those of Saudi Aramco. 
The recipient should check this Email and any attachments for the presence of 
any viruses. Saudi Aramco accepts no liability for any damage caused by any 
virus/error transmitted by this Email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to