For some reason this stuck in my mind, now I have an answer you might pursue.
I think the deluge solution might have some merit. Often I think we forget to separate the 2 distinct functions of a sprinkler head. First and I do mean first it is a heat detector. Second it water distribution valve/device. The Code deals with both - heads within 12"....3x rule... I don't see a reason you can't get equivalent detection from some other device. Could even be a smoke detector as they are faster than heats. Next make sure the head distribution covers the floor with the minimum density. There isn't even a reason to locate the heads near the ceiling as long as the distribution is adequate. Probably a few, 4' or 5' above the floor would be adequate. And with a deluge you are getting extensive pre-wetting far in excess or standard wet, dry, PA systems. Now this isn't a sprinkler contractor solution as it is outside the Code. Will require a PE to be legal. And obviously AHJ agreement. Chris Cahill > > -----Original Message----- > From: Greg McGahan<[email protected]> > Sender: [email protected] > Date: Thu, 02 Dec 2010 16:46:25 > To:<[email protected]> > Reply-To: [email protected] > Subject: difficult one > > The situations is this: > > Preface - I have already exhausted the "you can't because" in trying to > convince him to run two lines exposed in this space. > > Light Hazard > Corridor / Lobby with a center section Sloped, exposed construction 8 > in on 12in - 20' in width > On each side the ceiling drops about 4' to smooth flat ceilings > > The architect wants to find a way to eliminate exposed pipe. He prefers > to use sidewalls on the vertical 4' sides which I told him we could not do.. > His question is can he install detection at the peak, use sidewalls as > described above with a deluge valve. > > Does anyone have any other creative ideas for this situation? > > Thanks, > Greg > -- Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax 850-937-1852 _______________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)