For some reason this stuck in my mind, now I have an answer you might
pursue. 

I think the deluge solution might have some merit.  Often I think we forget
to separate the 2 distinct functions of a sprinkler head.  First and I do
mean first it is a heat detector.  Second it water distribution
valve/device.  The Code deals with both - heads within 12"....3x rule...

I don't see a reason you can't get equivalent detection from some other
device.  Could even be a smoke detector as they are faster than heats.  Next
make sure the head distribution covers the floor with the minimum density.
There isn't even a reason to locate the heads near the ceiling as long as
the distribution is adequate. Probably a few, 4' or 5' above the floor would
be adequate.  And with a deluge you are getting extensive pre-wetting far in
excess or standard wet, dry, PA systems.  

Now this isn't a sprinkler contractor solution as it is outside the Code.
Will require a PE to be legal.  And obviously AHJ agreement. 

Chris Cahill

>
> -----Original Message-----
> From: Greg McGahan<[email protected]>
> Sender: [email protected]
> Date: Thu, 02 Dec 2010 16:46:25
> To:<[email protected]>
> Reply-To: [email protected]
> Subject: difficult one
>
> The situations is this:
>
> Preface - I have already exhausted the "you can't because" in trying to
> convince him to run two lines exposed in this space.
>
> Light Hazard
> Corridor / Lobby  with a center section Sloped, exposed construction 8
> in on 12in - 20' in width
> On each side the ceiling drops about 4' to smooth flat ceilings
>
> The architect wants to find a way to eliminate exposed pipe. He prefers
> to use sidewalls on the vertical 4' sides which I told him we could not
do..
> His question is can he install detection at the peak, use sidewalls as
> described above with a deluge valve.
>
> Does anyone have any other creative ideas for this situation?
>
> Thanks,
> Greg
>

-- 
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road 
Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to