Really, deluge?   Since many people freak out with wet systems and the 
potential of one sprinkler opening I can't imagine an architect or owner 
embracing a deluge system in this type of environment.  Although if you tell 
them it's a sprinkler system like they've seen in the movies maybe they would 
think that as being OK.  

Also there are spacing restrictions on discharge nozzles which are more 
restrictive than for wet systems, 10 ft horizontally unless the nozzle is 
specifically listed for spacing exceeding that amount.

And in this type of environment under these conditions, I'd personally would 
never suggest using a smoke detector.  Too many potential for false trips 
unless you cross-zone them by using Ion and PE types.  Heat detection would be 
my first choice unless there would be some extenuating circumstances that would 
prevent their use.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Friday, December 03, 2010 9:34 AM
To: [email protected]
Subject: RE: difficult one

For some reason this stuck in my mind, now I have an answer you might
pursue. 

I think the deluge solution might have some merit.  Often I think we forget
to separate the 2 distinct functions of a sprinkler head.  First and I do
mean first it is a heat detector.  Second it water distribution
valve/device.  The Code deals with both - heads within 12"....3x rule...

I don't see a reason you can't get equivalent detection from some other
device.  Could even be a smoke detector as they are faster than heats.  Next
make sure the head distribution covers the floor with the minimum density.
There isn't even a reason to locate the heads near the ceiling as long as
the distribution is adequate. Probably a few, 4' or 5' above the floor would
be adequate.  And with a deluge you are getting extensive pre-wetting far in
excess or standard wet, dry, PA systems.  

Now this isn't a sprinkler contractor solution as it is outside the Code.
Will require a PE to be legal.  And obviously AHJ agreement. 

Chris Cahill

>
> -----Original Message-----
> From: Greg McGahan<[email protected]>
> Sender: [email protected]
> Date: Thu, 02 Dec 2010 16:46:25
> To:<[email protected]>
> Reply-To: [email protected]
> Subject: difficult one
>
> The situations is this:
>
> Preface - I have already exhausted the "you can't because" in trying to
> convince him to run two lines exposed in this space.
>
> Light Hazard
> Corridor / Lobby  with a center section Sloped, exposed construction 8
> in on 12in - 20' in width
> On each side the ceiling drops about 4' to smooth flat ceilings
>
> The architect wants to find a way to eliminate exposed pipe. He prefers
> to use sidewalls on the vertical 4' sides which I told him we could not
do..
> His question is can he install detection at the peak, use sidewalls as
> described above with a deluge valve.
>
> Does anyone have any other creative ideas for this situation?
>
> Thanks,
> Greg
>

-- 
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road 
Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to