Failed on the first try. Let's try again. Peter -Original Message- From: Peter Tarver [mailto:peter.tar...@sanmina.com] Sent: Friday, December 14, 2001 8:57 AM To: 'EMC-PSTC Forum' Cc: 'Barry Esmore' Subject: RE: 2 Phases in North America This is a recurring topic. While

RE: HiPot testing of DC mains powered products

2001-11-13 Thread Peter Tarver
Rich - While I can't speak for Chris, there are a few reasons to perform production line ESTs on 48V dc mains powered equipment. 1) in 48Vdc SMPSs, the voltages present on transformer insulation are typically in excess of ELV limits. If the power supply has had fault testing performed that

RE: DC voltage ratings

2001-10-25 Thread Peter Tarver
Dave - Perhaps I was misinformed, but it was my understanding that 70V battery was not panEuropean, but is specific to Germany and Austria, and then not necessarily ubiquitous in those countries. I'd appreciate your expanding on this. Regards, Peter L. Tarver, PE Product Safety Manager

Failure analysis

2001-10-24 Thread Peter Tarver
We are looking for a good failure analysis company in the SF Bay area. Anyone have any leads for companies you've had a positive experience with? Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com

RE: TNV Circuits

2001-10-23 Thread Peter Tarver
Perry - A note of general concurrence with Joe's take on your circuits. The various DSL power feeds are at this time treated as hazardous voltage circuits. There is activity in IEC, TC47, to consider requirements for remote feeding circuits, but publication is not imminent. The UL/CSA

Test Equipment manual

2001-10-23 Thread Peter Tarver
Good morning. I have a Yokogawa Electric, Model 2509, digital wattmeter for which I have no manual. I searched both Manuals Plus' and Manual Merchant's web sites and came up negative. Even though this is a very simple meter, I would like to have a manual for each piece of equipment in my

RE: UL - marking - gentle warning not to extrapolate.

2001-10-18 Thread Peter Tarver
Rich - Regarding UL Recognized Component Appliance Wiring Material, the yellow book states that the marking must be on a tag, the reel or smallest unit container, not surface marked on the wire insulation, as referred to by Greg. Very few UL FUS folks will accept surface marking, though I had

RE: UL - marking - gentle warning not to extrapolate.

2001-10-18 Thread Peter Tarver
Gary - Or for the less scrupulous than careless, to remove the certification mark from a product and place it one that is not safety certified. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com From: Gary McInturff The Product

RE: UL - marking - gentle warning not to extrapolate.

2001-10-18 Thread Peter Tarver
Peter - If you have such a memo, please do provide a copy. I my years working at UL and working with them since, it was ever abundantly and adamantly maintained (by UL's FUS Label Services group) that the Control Number is a required part of the Listing Mark and there is no substitution for it.

RE: UL - marking - gentle warning not to extrapolate.

2001-10-18 Thread Peter Tarver
Rich is quite right, in general. There are UL Listing Marks available, but they won't have the other three required elements that make up the complete marking (some may include the word Listed). The page Rich referred to in a UL Follow-Up Services Procedure, though, is separate from the Section

RE: Lithium Ion Batteries

2001-10-17 Thread Peter Tarver
Sorry. I clicked too fast during spell checking. I meant, thank you. -Original Message- From: Peter Tarver Think you, Angus. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit

RE: Lithium Ion Batteries

2001-10-17 Thread Peter Tarver
Think you, Angus. The title for this standard is: Primary Batteries - Part 4: Safety Standard for Lithium Batteries In my case, and I think this is true of all Li ion cells and batteries, it is a secondary battery, meaning rechargeable. Primary batteries can't be or aren't intended to be

RE: Lithium Ion Batteries

2001-10-16 Thread Peter Tarver
: Peter Tarver I am looking for safety standards related to large lithium-ion secondary batteries (nonautomotive). I've searched several standards web sites (IEC, ANSI, IEEE, CENELEC, BSI, UL, CSA) and there appears to be nothing specific to lithium-ion cells. Your help will be appreciated

Lithium Ion Batteries

2001-10-11 Thread Peter Tarver
I am looking for safety standards related to large lithium-ion secondary batteries (nonautomotive). I've searched several standards web sites (IEC, ANSI, IEEE, CENELEC, BSI, UL, CSA) and there appears to be nothing specific to lithium-ion cells. Your help will be appreciated. Regards, Peter

RE: AS/NZS 60950

2001-10-11 Thread Peter Tarver
the ACA on the topic of when AS60950 will replace AS3260. So my question stands. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com -Original Message- From: Peter Tarver Sent: Wednesday, October 10, 2001 2:27 PM Does any one have

AS/NZS 60950

2001-10-10 Thread Peter Tarver
Does any one have a view of when (or if) AS/NZS 60950 (based on IEC60950, Third Edition) will become the legally required standard for ITE in Australia and/or New Zealand (whether independently or through TS001)? Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services

RE: RTI on Plastics

2001-10-04 Thread Peter Tarver
. Peter -Original Message- From: John Woodgate Sent: Wednesday, October 03, 2001 10:45 AM I read in !emc-pstc that Peter Tarver peter.tar...@sanmina.com wrote some stuff Yes, there can be confusion about these terms. However, I suspect that the TC28 'material category' takes

RE: RTI on Plastics

2001-10-03 Thread Peter Tarver
John - The RTI you are referencing from IEC TC28 appears to be not the same parameter as being discussed. In UL parlance, as you surmised, RTI represents Relative Temperature Index and gives a maximum operating temperature at which a polymeric material may experience for its other properties to

RE: RTI on Plastics

2001-10-02 Thread Peter Tarver
Tony - The UL746 series of standards are referenced in CSA/UL60950, Annex P.2. RTI is a material property evaluated in UL746B, Polymeric Materials - Long Term Property Evaluations. IIRC, guidance on the applicability of RTI is given in UL746C, Polymeric Materials - Use in Electrical Equipment

RE: current carrying conductors

2001-08-17 Thread Peter Tarver
Yes. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com -Original Message- From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Stone, Richard A (Richard) Group, can you

FDA harmonization effort for laser compliance

2001-07-27 Thread Peter Tarver
The infamous Laser notice 50. The following is Excerpted from Federal Register / Vol. 66, No. 144 / Thursday, July 26, 2001 / Notices under the heading titled, Laser Products—Conformance with IEC 60825–1, Am. 2 and IEC 60601–2–22 (Laser Notice 50). CDRH intends to amend its standards for laser

RE: Products Electrical Ratings De-rated for Eurpoean Branch Circuits

2001-06-26 Thread Peter Tarver
The tardiness of this reply is due to my employer's insistence upon performance of tasks of their choosing to accommodate remuneration in the locally common monetary exchange units. Jim Eichner pointed out a fallacy in my below statement and I must acquiesce. By operating from memory (but I

RE: LED's Lasing

2001-06-20 Thread Peter Tarver
Ed - First and foremost, there must exist a resonant cavity formed inside the semiconductor or in combination of the semiconductor die and its packaging. Then the threshold current (for population inversion of the lasing medium) must be exceeded. Only the latter is related to external faults

RE: Products Electrical Ratings De-rated for Eurpoean Branch Circuits

2001-06-20 Thread Peter Tarver
I don't have the answer to Glenn's question, but do have a comment on Nick's response. Nick states: The rating of a UL rated fuse is more or less the current at which it blows. The rating of a fuse to IEC 127 (used throughout Europe) is more or less the working current of the fuse and the

RE: AC Power Primer?

2001-05-07 Thread Peter Tarver
Not so. Most household appliances contain motors (excluding entertainment appliances). Motors (ac induction types; the most commonly used) are generally less efficient at lower voltages (largely by virtue of their increased I^2*R loss) and draw more current to perform the same amount of work or

RE: Remote Hazrdous Secondary Voltage Power Feeding on Lan Cabling

2001-04-19 Thread Peter Tarver
Peter - 1) Agreed. Keep in mind that IEEE 802.3 compliant signals are unearthed SELV and how SELV is derived in the power source was not specified. 2) There are potential problems, but this is not to say insurmountable. I doubt, however, that LAN cable meeting Reinforced insulation

RE: UL1950 vs EN60950

2001-04-19 Thread Peter Tarver
Amund - For the most part, installation code issues, component standard issues, power cross (overvoltage) testing and a number of other items sprinkled throughout the standard. You will need to buy a copy of the standard to get the full picture. It is not simple enough to place in an e-mail.

RE: Air Flow Meters

2001-02-27 Thread peter . tarver
I have a Kurz, model 441s hot wire probe unit. Refer to http://www.kurz-instruments.com/ Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com -Original Message- From: Kurt Mikolajewski [mailto:kmiko...@catena.com] Sent: Monday,

Job opportunity - Product Integrity

2001-01-26 Thread peter . tarver
Job Title: Product Integrity Engineer Job Location: San Jose, CA Company Description:Sanmina is a Tier-1 electronics manufacturing services (EMS) company with over 50 world class manufacturing facilities. Sanmina provides a full spectrum of integrated, value-added services that

Job opportunity - Product Safety

2001-01-26 Thread peter . tarver
Job Title: Product Safety Engineer Job Location: San Jose, CA Company Description:Sanmina is a Tier-1 electronics manufacturing services (EMS) company with over 50 world class manufacturing facilities. Sanmina provides a full spectrum of integrated, value-added services that includes:

RE: Cell Phone Suit Will Get Its Day in Court

2001-01-24 Thread peter . tarver
The same is easily said of other products, Rick, like firearms (where there are politically motivated lawsuits in progress and also directly analogous to the tobacco lawsuits on many levels), hot coffee from MacDonalds, ad infinitum. That a product is known to be hazardous or dangerous is not

Cell Phone Suit Will Get Its Day in Court

2001-01-24 Thread peter . tarver
From the Telecom Digest Monty Solomon wrote: Cell Phone Suit Will Get Its Day in Court NEW ORLEANS, La. - In ruling that could shake the cell phone industry, a federal judge let stand a lawsuit that says companies are making and selling cell phones with the knowledge that they may be

RE: Laser approval

2001-01-11 Thread peter . tarver
The component is marked, does not comply...? I haven't seen that one yet. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com -Original Message- From: acar...@uk.xyratex.com [mailto:acar...@uk.xyratex.com] Sent: Wednesday,

RE: Laser approval

2001-01-11 Thread peter . tarver
Hi, KB. It is incorrect that IEC825 does not apply to components. In the case of components, the worst case emissions, based on power supply and any other factors that affect output power/energy must be considered. The FDA requirements in 21CFR requires all laser sources, devices or products to

RE: Laser approval

2001-01-10 Thread peter . tarver
I need to add the following to clarify my below statements regarding FDA certification. 21CFR, Chapter I, Section 1002.1(b) allows exemption for components intended for sale exclusively to other manufacturers for use in other products. The implication is that, if the component might be sold

RE: UL60950, Third Edition

2001-01-03 Thread peter . tarver
...@mail.monarch.com'; peter.tar...@sanmina.com; Peter Tarver, in the message below, mentions he obtained a new edition of the IT safety standard CSA60950/UL60950. I have been unable to locate a Dec. 1, 2000 edition of UL60950 on the IHS Global DOcument website, nor have I found a CSA60950

UL60950, Third Edition

2000-12-21 Thread peter . tarver
Early this week I received a copy of CSA60950/UL60950, Third Edition, the new Bi-National Standard, based on IEC60950, Third Edition. The edition number was maintained to correspond with the IEC standard edition number. Publication date is 1DEC2000. Nifty. Regards, Peter L. Tarver, PE

RE: Got another beef about an NRTL (haven't we all?)

2000-10-26 Thread Peter Tarver
At one time or another, we certainly all do. Each NRTL has its own level of absurdity, whether by being too harsh or too lax. There is one NRTL the international safety community of a previous employer had agreed was lax to the point of not accepting any component or OEM device that certified

RE: Got a beef with an NRTL ...

2000-10-19 Thread Peter Tarver
I've had this kind of thing pulled on me before, to. Start with their team leader, then group leader , then section head, then dept. manager, until you get satisfaction. Peter Tarver ptar...@nortelnetworks.com -Original Message- From: Doug [mailto:dmck...@gte.net] Sent: Thursday

RE: Centralized DC power systems

2000-10-16 Thread Peter Tarver
Gary - The below may be a little more than you bargained for, but here goes. My apologies, if this is more basic than your question. Each of the drawings in Figures NAB.1 and NAB.2 show grounding electrodes at the bottom. In Figure NAB.1, the electrode is used to earth the centralized dc power

RE: Color coding for U.S. 3 phase

2000-10-13 Thread Peter Tarver
Kurt - Except under special circumstances, the USNEC does not use color coding for phase conductors. There are reserved insulation colors for ground (green, with one or more yellow stripes) and for neutral (white or natural gray [whatever that is]). Otherwise, your free to use whatever color

RE: PCB temp ratings, etc...

2000-10-11 Thread Peter Tarver
Richard - Then the answer is no. The MOT, as Pete Perkins pointed out, establishes the test points for thermal conditioning, but solder resists are then tested in conjunction with the PWB only for flammability classification. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com

RE: PCB temp ratings, etc...

2000-10-11 Thread Peter Tarver
You're welcome, Richard. MOTs are developed for a copper clad industrial laminate and verified by certain tests on a finished PWB. Conformal coatings are not a normal part of this process, though I suppose a board house could ask for such considerations to be made for a selection of coatings.

RE: PCB temperature ratings

2000-10-10 Thread Peter Tarver
Richard - Basically, yes, though you may want to throw in a fudge factor to assuage your caution/due diligence monkey. FYI: The Maximum Operating Temperature (this is a normal operating condition temperature) for a PWB is based on accelerated aging testing, and comparing as received performance

RE: Australia Safety

2000-10-10 Thread Peter Tarver
Richard - What is required is approval by any of the individual state's governmental bodies in Australia. I can't find my list of authorities at the moment, but perhaps someone else can. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com -Original Message- From:

RE: Overcurrent Protection: One or Both Sides?

2000-10-10 Thread Peter Tarver
Chris Maxwell asks: Can anybody shoot a hole in this theory with a single fault condition? This subject has been debated before, on this list and elsewhere. Safety is always relative. In the scenarios you painted, Chris, the phase conductor always has an intact fuse after the neutral fuse

RE: Overcurrent Protection: One or Both Sides?

2000-10-09 Thread Peter Tarver
There seems to be some confusion regarding terminology and the location of the overcurrent protective devices being discussed. In the US and Canada, if a circuit breaker is located in the panelboard, John is generally correct that the neutral will not be controlled by the circuit breaker. On the

RE: Have I baffled the Product Safety Technical Committee?????

2000-10-09 Thread Peter Tarver
There is no correlation between air filter flammability class and the UL94 classifications. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com -Original Message- From: Jim Eichner [mailto:jim.eich...@xantrex.com] Sent: Friday, October 06, 2000 10:17 PM To: 'emc-p...@ieee.org'

RE: Protection or Control?

2000-09-23 Thread Peter Tarver
Bimetal switches have been used for decades and proven generally to provide an adequate or better safety protection function. Not all bimetal switches are autoreset types; some require manual resetting. I've also experience bimetallic thermal protectors in motors in an open failure mode, more

RE: UL Listed Class 2 Transformers

2000-09-22 Thread Peter Tarver
Tamura makes a good quality product, but most of their transformers are UL Recognized, rather than Listed. You can search UL's web site in their Certifications area, using the CCN XOKV and probably get the latest set of companies with Listings. Regards, Peter L. Tarver, PE

RE: Protection or Control?

2000-09-21 Thread Peter Tarver
Luiz - Bimetal switched are used as manual and automatic reset thermal protectors in electric motors, transformers. Very common and has been for many years. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com -Original Message- From: jim_bac...@mail.monarch.com

RE: Double Retention

2000-09-20 Thread Peter Tarver
Rich and Andy - There is an additional reference in 4.3.9 of IEC60950, Second Edition, and applies where certain types of required insulation can be bridged, rather than being limited to just power supply cord conductors (though this could easily have been the origin of the requirement [actually,

RE: Wiring under raised floors

2000-09-20 Thread Peter Tarver
Ted - At issue, really, is whether or not the under side of the raised floor is used for environmental air, not simply that it's in a computer room. For the question at hand, though, I'll assume that's the case. My first inclination is to say it's not allowed. If you also look at 300-22 of the

RE: DC power distribution

2000-09-20 Thread Peter Tarver
Lisa - While I can't speak directly to the case in EN61326, this sounds a lot like the concept of a centralized dc power system, as addressed in UL1459 and carried over into CSA950/UL1950 and working it's way into IEC60950 as a dc mains supply (there is only reference in IEC60950, Third Edition,

RE: Using fuse to protect wire undersized for load?

2000-09-14 Thread Peter Tarver
Lauren - I'm not familiar with NFPA79, so I'll answer only with regard to NFPA70 (the US NEC). The 125% issue in the NEC is for two items: attachment plugs sizing and circuit breaker sizing (1/1.25 = 0.80), both relative to load current. Attachment plugs for equipment that contain motors must

RE: PCB fuse trace

2000-09-14 Thread Peter Tarver
My experience with safety agencies is they do not want to rely on traces opening to act as fuses and no standards have been developed, that I am aware of, to address this issue. Fuses certification gets involved in the metallic alloys used, to the fraction of a percent, the conductor size,

RE: PCB fuse trace

2000-09-14 Thread Peter Tarver
but to rely on that mechanism for fire prevention is a bit far fetched. From my limite experience with fuses, there is generally a large structure that is enclosed in sand to prevent a fire from spreading. Jim Freeman Peter Tarver wrote: My experience with safety agencies is they do not want

RE: UL 723

2000-09-08 Thread Peter Tarver
Richard is absolutely correct. It's like trying to compare a match stick to a bon fire. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com -Original Message- From: wo...@sensormatic.com I just went through this myself. There is no real correlation between UL94 flame ratings and

RE: RE: EN55024 question

2000-09-01 Thread Peter Tarver
Bandele - Please forgive an ignorant question: I'm not going to pretend to be an EMC standards expert, but I fail to see how the presence or absence of processing an incoming signal has anything to do with whether there is a direct or indirect connection to outside lines. To wit: outside is

RE: Test voltage for products to the U.K.

2000-08-03 Thread Peter Tarver
Further on HD topics, I reviewed several HDs on the IHS web site and found them to not be of much use, beyond giving standard references in each country for the point of harmonization, with dates of withdrawal, and the like. I didn't find any, in the dozen or so I looked at, covering diverse

RE: Flame Spread

2000-07-31 Thread Peter Tarver
Richard - I have no direct evidence to support a claim either way, but if a material can only meet HB requirements, I have strong doubts about its ability to have a FS of 200, using ASTME84 test. The Steiner Tunnel testing uses a significantly different method from the 1/2 in. flame test used

RE: Home safety

2000-07-31 Thread Peter Tarver
Other items include: service entrance equipment panelboards and circuit breakers (in general) insulated wiring GFCI outlets flue dampers double-walled flue pipes Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com -Original Message- From: Price, Ed Sent: Monday, July 31, 2000

RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-20 Thread Peter Tarver
Peter - Thermistors are in common usage and my limited experience with them indicates they are reliable for their intended function. The thermal issues have been discussed, and the usual regimen for high temperature components applies. I'm not aware of any other particular safety concerns.

RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-20 Thread Peter Tarver
I really don't have a clear idea of whether or not your solution will work. Let us know. NTCs, as with most thermistors, get very hot when in their switched state. For the NTC, that's it's steady-state condition. I wouldn't put this in a junction box with other wiring, unless you're absolutely

RE: UL1950/UL2601 Thermals

2000-06-28 Thread Peter Tarver
That's really just a rule of thumb. A working premise that provides reasonable results in a relatively short time. As Kaz mentioned, it's not uncommon for some circuits/parts to exhibit a cycling of temperature, either by cyclical loads presented to them or some form of (generic) limiting

RE: Resistors Between TNV-3 and SELV

2000-06-27 Thread Peter Tarver
Peter - UL has no problem with components bridging the insulation, provided you comply with the appropriate testing in the standard and provide otherwise appropriate clearances and creepages (just as you expected). In Europe, the Nordic countries require Supplementary insulation between SELV and

RE: MITI/Dentori-T

2000-06-20 Thread Peter Tarver
Not so dumb. It's probably a translation issue, since Kenji and the English alphabet are nothing alike. I've mostly seen it spelled in all-caps as DENTORI. Regards, Peter L. Tarver, PE Homologation Engineering Nortel Networks ptar...@nortelnetworks.com -Original Message- From:

RE: CE Markings for A.C. Mains

2000-06-14 Thread Peter Tarver
For ITE, refer to IEC60950, 3rd ed, Subclause 1.7.7.2, first dashed paragraph. Regards, Peter L. Tarver, PE Homologation Engineering Nortel Networks ptar...@nortelnetworks.com -Original Message- From: bur...@andovercontrols.com [mailto:bur...@andovercontrols.com] Sent: Wednesday, June

RE: Terminal Blocks-Field Wiring Requirements

2000-06-09 Thread Peter Tarver
Don - There are additional details beyond the following, but in essence, there are pull-out and wire retention tests that are done for field wiring purposes that may or may not have been done for factory wiring purposes. Field wiring terminal blocks are subjected to the full range of tests

RE: ITE Requirements for Australia

2000-06-08 Thread Peter Tarver
Hi, Peter. From: Peter Merguerian [mailto:pmerguer...@itl.co.il] Dear All, 1. For ITE (without a connection to a telecommunication network), what are the applicable standards and requirements? I assume AS3260 (safety) and AS3548 (emc) and the manufacturer applies the C-Tick Mark (ie

RE: High voltage testing and altitude correction factor

2000-06-07 Thread Peter Tarver
Hi Rich. The exception being Table G.2 of IEC60950, 3rd ed. Table G.2 clearly states its applicability up to 2km, when using Annex G and its Alternative method for determining minimum clearances. Peter L. Tarver, PE ptar...@nortelnetworks.com From: Rich Nute [mailto:ri...@sdd.hp.com] Hi

FW: Laser Classification

2000-05-26 Thread Peter Tarver
My apologies for not sending this to the group originally. Others may have interest. Regards, Peter L. Tarver, PE Homologation Engineering Nortel Networks ptar...@nortelnetworks.com -Original Message- From: Tarver, Peter [SC1:4N02:EXCH] Sent: Thursday, May 25, 2000 1:16 PM To:

RE: Hazardous Infrared radiation ?

2000-05-23 Thread Peter Tarver
IEC60825-1 contains requirements for noncoherent infrared radiation. Likewise does EN60825-1, with Amendment A11. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com From: Israel Yeshurun [mailto:israel_yeshu...@creoscitex.com] Can some comment on this ? Can Infrared

RE: UL certification and Underwriter Laboratory

2000-05-15 Thread Peter Tarver
From: Ned Devine [mailto:ndev...@entela.com] Hi, Hi, Ned. OK, I wasn't going to say anything, but. 1.A UL Listed product complies with all of the applicable requirements. Usually from a standard. 2.A UL Recognized Component does not comply with all of the applicable

RE: UL certification and Underwriter Laboratory

2000-05-15 Thread Peter Tarver
All - In addition to all of the other comments (all essentially true), I would like to clarify one issue, touched on by Rich Nute, but not made as clear as could be. The backwards UR ligature is copyrighted by UL and can not be applied to a product certified by another NRTL, without violating

RE: Old Yokogawa meter for '950?

1999-11-30 Thread Peter Tarver
Jim - Most any calibratable voltmeter with 1000+ Ohms/V should work OK. The Ohms/V information should be on the indicator plate. Is there a specific test you're concerned about using this meter for, or is it for general applications? For the manual, try posting to sci.electronics.equipment and

RE: US NEC and Canadian CEC

1999-07-22 Thread Peter Tarver
Peter - These are all in the CEC and US NEC. You need to purchase one or both (they're significantly similar on all of your points in question). Regards, Peter L. Tarver, PE Homologation Engineering Nortel Networks ptar...@nortelnetworks.com -Original Message- From:

RE: PCB coating questions

1999-03-08 Thread Peter Tarver
Arjen - Check the Conditions of Acceptability on the coatings you're interested in using. UL Recognized conformal coatings are, for the most part, are tested for use on the bare board (base laminate) and are not tested for use on solder masks. Regards, Peter L. Tarver Nortel Networks

National Semiconductor

1998-12-23 Thread Peter Tarver
Happy holidays, to one and all. I am looking for a contact for product safety certifications at National Semiconductor. The operators at their Santa Clara facility are useless, unless you have a name. Regards, Peter L. Tarver, PE Nortel Networks ptar...@nortelnetworks.com - This

RE: Why are CB reports truly useful?

1998-11-24 Thread Peter Tarver
The key word below is allow. There is no requirement that one NCB accept the report of another NCB. I am aware of one case where a CB Scheme Test Report from one NCB was refused out of hand by another NCB in the same country (both shall remain nameless), without any rational qualification. I

RE: Added paragraph

1998-10-09 Thread Peter Tarver
Better yet, how about the subscribers taking the additional two or three seconds it takes to do the responsible thing and delete it themselves? Peter L. Tarver Nortel ptar...@nt.com -Original Message- From: Robert Macy [SMTP:m...@california.com] Sent: Thursday, October 08, 1998 12:05

RE: Re[2]: US NRTL required ?

1998-09-24 Thread Peter Tarver
_ Subject: RE: US NRTL required ? Author: Peter Tarver peter.tarver.ptar...@nt.com at INTERNET Date:9/22/98 11:17 AM Require? No. Will they? Yes, under certain circumstances and certain product categories, like ITE. Laptops for instance

RE: US NRTL required ?

1998-09-21 Thread Peter Tarver
Richard - For a long time, UL (and I believe CSA) thought any device deriving power from a Class 2 source needed listing. In fact, they were adamantly opposed to it, even when requests for such certification were made. UL's primary basis was that the NEC didn't care what was supplied by a Class

RE: Query: US safety required for ITE?

1998-09-16 Thread Peter Tarver
To muddy the waters further, Ron, I offer a converse reminder: many Authorities Having Jurisdiction are still using versions of the NEC the precede the introduction of 800-4 (and the previous location of the same idea in the 1990 NEC that eludes me). I've known of some jurisdictions to use the

RE: Are all these agencies really necessary?

1998-09-14 Thread Peter Tarver
Even though it wasn't you point, Daniel, it should be noted that the CB Scheme provides for participating NCBs to accept one anothers' test data, but by no means guarantees that an NCB reviewing a CB Scheme Test Report will not ask to perform some testing. The testing might be required by an NCB

RE: Re[2]: EN 60950 A5

1998-08-28 Thread Peter Tarver
right now, according to their latest literature. Jim __ Reply Separator _ Subject: RE: EN 60950 A5 Author: Peter Tarver peter.tarver.ptar...@nt.com at Internet Date:08/28/1998 1:51 PM Jim

RE: isopropyl alcohol

1998-07-10 Thread Peter Tarver
Just to fill the pot with more speculation, my recollection of college chemistry tells me that alcohol readily absorbs moisture from the atmosphere, so that any container opened to normal atmospheric conditions for more than a few seconds will autodilute to somewhere around 93% (that's the number

RE: Wire Markings Mandatory?

1998-06-29 Thread Peter Tarver
Jim - Yes, that's pretty much how respooling works. The most odd aspect was that this was wiring already in a wiring harness, taken from a box with the appropriate wiring harness labeling. The FUS Rep wanted to see our drawings to verify the design of the harness, which is normal, but

RE: Wire Markings Mandatory?

1998-06-26 Thread Peter Tarver
In the following, I'll speak only to UL certified wire. To get an official reading, call the nearest UL office and ask for the client advisor, then ask them to direct you to an engineer working with wire and cable. One of the best resources for information about any UL product category is the

RE: Translations

1998-06-24 Thread Peter Tarver
A few safety type markings are translated into French in Annex NAA of CSA950/UL1950. Regards, Peter L. Tarver Nortel ptar...@nt.com -- From: ron_pick...@hypercom.com[SMTP:ron_pick...@hypercom.com] Sent: Tuesday, June 23, 1998 3:06 PM Hello from quite sunny

RE: Ground Wire Markings

1998-06-24 Thread Peter Tarver
A point of clarification here. UL Recognized AWM isn't required to be surface marked at all. The marking is perfectly legitimate if it is on the spool the wire is taken from. Yet another voice chiming in that it was probably not traceable as being R/C AWM. Regards, Peter L. Tarver Nortel

RE: CB scheme

1998-06-23 Thread Peter Tarver
Gary - You seem to be doing just fine for your current market. As you market expands (you mentioned GOST), however, the CB Scheme Test Report does offer portability to a greater degree than a lesser. Many of the agencies will want a sample for a looksee, a few may want to perform minor

RE: generating 50Hz power in the US

1998-06-15 Thread Peter Tarver
Richard - In addition to the previously mentioned manufacturers, there is also Behlman http://www.behlman.com/ also sold through Electro Venture http://www.electroventure.com/ Regards, Peter L. Tarver Nortel ptar...@nt.com -- From: Richard

RE: Coated Printed Boards

1998-05-08 Thread Peter Tarver
Alan - I'm not certain about the origin of the application of Tables 3, 4 and 5 in your example, but since Tables 3, 4 and 5 generally have lesser distances for the same voltages than are found in Table 6, this seems primarily an academic exercise for which I'd need a specific safety concern to

RE: LEDs and the Laser standard - question

1998-04-30 Thread Peter Tarver
Heber - This may depend on who's doing the certification of your equipment. I've heard of certain agencies ignoring faceplate LEDs, but not yet of any wanting to test. According to Jerome Dennis of the CDRH (at the 1997 International Laser Safety Conference), discussions at the IEC TC76

RE: UL 1950 3rd, and IEC 950

1998-04-29 Thread Peter Tarver
As with many things in life, there is no simple answer to your whole question list, but I'll address what I can in a short form. A telco is a utility and normally a monopolistic entity. The systems and equipment the telco use are maintained (supposedly) to a much higher degree (at least inside

RE: NRTL Value

1998-04-28 Thread Peter Tarver
George - While I have not found myself in quite the same predicament as you describe, I have had good success with your Option D. This quite often clarifies the applicable requirements for a product's audit and has also quite often exposes misunderstanding on the part of the inspector as to what

RE: Use of MOV's ???

1998-04-21 Thread Peter Tarver
Jeff - This rumor doesn't make much sense as an across-the-board requirement, especially considering UL has a component product category for MOVs and other transient voltage surge suppressors, along with some product standards that allow reductions of over-surface and through-air electrical

RE: IEC 332 vs. CL2, CL2P, etc.

1998-04-01 Thread Peter Tarver
Mike - Hearsay alert but it may get this discussion rolling and I'm most certainly interested in the outcome. I don't have specifics on IEC 332 and I can not strictly testify to the accuracy of the following, but from discussions with a coworker in the UK, EEA countries generally dislike plenum

Delta transformer grounding (was: RE: GFCI in IT (three phase) Ne tworks)

1998-03-06 Thread Peter Tarver
Doug - Delta-delta transformers are popular with the utilities for economy's sake (they are less expensive than WYE transformers) For similar reasons, some industrial applications distribute and use power within their plants on delta feeds. In office environments, however, it's typical to use a