Re: [PSES] So, what is up with the CENELEC website?

2012-04-05 Thread Ralph . McDiarmid
I good webmaster can make all the difference. I for one find that website next to useless. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From

Re: [PSES] Mains voltage in Europe

2012-03-21 Thread Ralph . McDiarmid
By under-excitement and over-excitement, do you mean lagging and leading power factors? ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From

Re: [PSES] Mains voltage in Europe

2012-03-21 Thread Ralph . McDiarmid
overheating) Not all utilities (network operators) do a good job with voltage regulation across their longer MV distribution feeders. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA

Re: [PSES] Is this common knowledge - Electrical Ratings

2012-01-30 Thread Ralph . McDiarmid
But electrical equipment does on occasion get moved and reinstalled, so the nameplate provides information which might otherwise be lost. ( as in the all important and rarely read user instruction manual). ___ Ralph

Re: [PSES] OT - common knowledge - Electrical Ratings

2012-01-27 Thread Ralph . McDiarmid
WWII. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | - This message is from the IEEE Product Safety Engineering Society emc

Re: [PSES] Is this common knowledge - Electrical Ratings

2012-01-27 Thread Ralph . McDiarmid
A very nice example of another use of the 120/240V nameplate marking ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From: Don Gies don.g

Re: [PSES] power plugs and outlets

2012-01-25 Thread Ralph . McDiarmid
i.e. basic insulation remains after failure of the grounding means. (e.g. a metal chassis still touch-safe) ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance

Re: [PSES] Power Amp for IEC 61000-4-16

2012-01-25 Thread Ralph . McDiarmid
that one fb loop) used to claim THD 0.05% to at least 20kHz. So 1% THD out to 150kHz might not be unreachable, at least for those older amps. Slew rate limit might be a gotcha. ___ Ralph McDiarmid | Schneider Electric

Re: [PSES] Power Amp for IEC 61000-4-16

2012-01-24 Thread Ralph . McDiarmid
should satisfy the 30Vrms requirement, but the THD might be a problem at the highest frequencies. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering

Re: [PSES] Cable required for USB Drive testing?

2012-01-23 Thread Ralph . McDiarmid
. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From: John Woodgate j...@jmwa.demon.co.uk To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 01/23/2012 09:55 AM Subject: Re: [PSES

Re: [PSES] Thermal Protection of Lithium Ion Batteries

2012-01-12 Thread Ralph . McDiarmid
, there shouldn't be a problem, but how do they wear out? _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: jral...@productsafetyinc.com

Re: [PSES] Steady State Conditions

2012-01-11 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: John Woodgate j...@jmwa.demon.co.uk To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 01/11/2012

Re: [PSES] Steady State Conditions

2012-01-11 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: Aldous, Scott scott.ald...@aei.com To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 01/11/2012 07:39 AM Subject: Re: [PSES] Steady State

Re: [PSES] Protect An EMI Receiver

2012-01-03 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: ce-test, qualified testing bv - Gert Gremmen g.grem...@cetest.nl To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12/27/2011

Re: [PSES] Semi-Anechoic Chamber Question - Correction Factor

2011-12-23 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: ce-test, qualified testing bv - Gert Gremmen g.grem...@cetest.nl To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12

Re: [PSES] Orgalime: UL an effective barrier to trade

2011-12-23 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: Aldous, Scott scott.ald...@aei.com To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12/23/2011 08:29 AM Subject: Re: [PSES] Orgalime: UL an effective barrier

Re: [PSES] EN 60950-1:2006+A12:2011

2011-12-09 Thread Ralph . McDiarmid
One antenna, two antennae is an exception I suppose. As I have told my friends and family many times; I'll learn a second language only after I have mastered English. _ Ralph McDiarmid | Schneider

Re: [PSES] FW: [PSES] Calibration practice for EMI test transducers

2011-12-07 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: ce-test, qualified testing bv - Gert Gremmen g.grem...@cetest.nl To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12/07/2011 12:59 AM Subject: [PSES] FW: [PSES

Re: [PSES] Calibration practice for EMI test transducers

2011-12-07 Thread Ralph . McDiarmid
Many times there seems a disconnect between what is required by a standard and what is needed for compatibility. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA

Re: [PSES] Average detector/s

2011-12-06 Thread Ralph . McDiarmid
For in-house pre-compliance testing, we use a VBW of 10Hz to approximate the time response of an AVG detector. Seems to work quite well. _ Ralph McDiarmid | Schneider Electric | Renewable Energies

Re: [PSES] Calibration practice for EMI test transducers

2011-12-06 Thread Ralph . McDiarmid
Yet how far would you take that argument? If it's say 11.1db at 110MHz and 11.5dB at 112MHz, would you still worry about factor at 111MHz? At some point surly this all becomes rather silly. _ Ralph

Re: [PSES] Average detector/s

2011-12-06 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: don_borow...@selinc.com To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12/06/2011 02:03 PM Subject: Re: [PSES] Average detector/s Bill- Seeing as how I am seldom at a loss

Re: [PSES] Average detector/s

2011-12-06 Thread Ralph . McDiarmid
. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: Ken Javor ken.ja...@emccompliance.com To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12/06/2011 02:56 PM Subject: Re: [PSES

Re: [PSES] Average detector/s

2011-12-06 Thread Ralph . McDiarmid
) _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: Ken Javor ken.ja...@emccompliance.com To: EMC-PSTC@LISTSERV.IEEE.ORG Date: 12/06/2011 01:45 PM Subject: Re: [PSES] Average detector/s If video averaging

Re: [PSES] Calibration practice for EMI test transducers

2011-12-06 Thread Ralph . McDiarmid
I sure hope that standard practice and practicality (pardon me) go hand-in-hand. If not, the committees members need to give their head a shake. _ Ralph McDiarmid | Schneider Electric | Renewable

Re: [PSES] Quasi-peak

2011-12-05 Thread Ralph . McDiarmid
receivers. It would seem to be a simple as that with no post-processing by receiver or computer necessary. The book is 35 years old, but I suspect QP detectors haven't changed since then. _ Ralph McDiarmid

Re: [PSES] Quasi-peak

2011-12-01 Thread Ralph . McDiarmid
Gracefully degradation is a term often associated with software systems. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From

Re: [PSES] Quasi-peak

2011-12-01 Thread Ralph . McDiarmid
And by response do you mean the time-constant used in a typical AM receiver AVC? . _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering

Re: [PSES] UL assessment of plastics - DC vs AC

2011-11-30 Thread Ralph . McDiarmid
are compliant and you control what solid insulation is used as a critical component, I think you need only look for breakdown, not leakage. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business

Re: [PSES] DC Supply

2011-11-18 Thread Ralph . McDiarmid
How about four 12V car batteries in series with a fuse and battery charger handy. _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering

Re: [PSES] MOV requirements

2011-11-14 Thread Ralph . McDiarmid
Does the industry really need another standard, I wonder? _ Ralph McDiarmid | Schneider Electric | Renewable Energies Business | CANADA | Regulatory Compliance Engineering From: John Woodgate

Re: [PSES] CE marking of deep-fat fryer

2011-11-14 Thread Ralph . McDiarmid
and in accordance with its operation instructions, these devices are in fact quite safe. Clearly some devices are truly not intended for use by anyone. _ Ralph McDiarmid | Schneider Electric | Renewable

Re: [PSES] CE marking of deep-fat fryer

2011-11-14 Thread Ralph . McDiarmid
here, but alas with all the litigation on this side of the pond, it will likely never happen. On the other hand, CSA and UL do employ a lot of good people. _ Ralph McDiarmid | Schneider Electric

RE: Calibration Standards for LISN

2009-01-27 Thread Ralph McDiarmid
I don't have a copy of CISPR 16 to reference and so I am curious about how one calibrates an AMN? (or an antenna for that matter). I can see characterizing the AMN so that its transducer factor versus frequency is known and can be then used to calculate a uV level. Ralph McDiarmid, AScT

RE: Calibration Standards for LISN

2009-01-27 Thread Ralph McDiarmid
Could the interaction between a facility mains filter and the line-side impedance of an AMN result in a network with at least one resonant frequency? Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf

RE: Calibration Standards for LISN

2009-01-27 Thread Ralph McDiarmid
True also for an antenna, I assume. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John Woodgate Sent: Tuesday, January 27, 2009 11:25 AM snip In the case of an LISN, there are no adjustable

RE: Thevenin equivalent circuit for SMPS emission sources - issues

2008-12-22 Thread Ralph McDiarmid
Ground is a commonly misunderstood term by many analogue, digital, safety and EMC specialists. Return or Common are likely far more useful terms. I like local reference too. Ralph McDiarmid, AScT Xantrex Technology Inc. From: emc-p...@ieee.org on behalf of John Woodgate Sent: Mon 12/22

RE: EMC Eduction and Training

2008-12-16 Thread Ralph McDiarmid
I would only add that there are those who learn something and those who simply learn how to pass a course. The two groups normally find different career paths in the technology sector. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc From: emc-p...@ieee.org

RE: EMI Receiver

2008-12-04 Thread Ralph McDiarmid
That's my understanding too. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Clif Brick Sent: Thursday, December 04, 2008 8:50 AM To: Gert Gremmen; emc-p...@ieee.org Subject: RE: EMI Receiver I could

FW: New Official Journal list of EMC standards

2008-11-05 Thread Ralph McDiarmid
EN50178:1997 is missing from this list. Has it been superseded, or is it now a rogue standard? Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian Jones Sent: Wednesday, November 05, 2008 1:23 AM

RE: New Official Journal list of EMC standards

2008-11-05 Thread Ralph McDiarmid
Thanks Brian. The 'light-bulb' went on shortly after I sent my e-mail. I realized too late that I was looking in the wrong list. Time for a cup of coffee. :-) Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc From: Brian Jones [mailto:e...@brianjones.co.uk

RE: HP Hardware Update

2008-10-31 Thread Ralph McDiarmid
I dare say that you can likely find a NIB replacement CRT from one or two vendors in the USA.A Google search may be all that’s needed to locate one. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf

RE: IEC60225-5 surge test impedance?

2008-10-07 Thread Ralph McDiarmid
Is it possible to insert a resistor between surge generator and CDN to provide the correct impedance? Here is one source of high-voltage, power resistors. http://www.caddock.com/Online_catalog/high_voltage/high_voltage.html Ralph McDiarmid, AScT Compliance Engineering Group Xantrex

RE: FM Modulator Information - off topic

2008-08-13 Thread Ralph McDiarmid
Option B? I thought I was the only one left with a cassette player in my car. :-) Not sure why anyone would bother with satellite radio, I find terrestrial AM and FM broadcasts still have decent variety. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From

RE: IEC61000-3-5 and -3-11 (Flicker)

2008-06-26 Thread Ralph McDiarmid
These two standards appear to be identical, at least in scope with both applying to equipment rated 75A and below. Does anyone know why this is so? Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. - This message is from the IEEE Product Safety Engineering Society

RE: IEC and EN standard relationships

2003-11-14 Thread Ralph McDiarmid
What would be an example of a Common Deviation? thanks, Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: John Allen [mailto:ja014d7...@blueyonder.co.uk] Sent: November 14, 2003 12:13 PM To: Ablewisp - Compliance Engineers; Emc-Pstc Subject: Re: IEC and EN

RE: EN 61000-3-2:2000

2003-11-10 Thread Ralph McDiarmid
this one in question cannot be written sufficiently clearly, then I suggest they be withdrawn and rewritten and then carfully assessed. Some have questioned whether 61000-3-2 is even an EMC standard! Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: Jim Ericson

RE: Arcing Sparking

2003-09-22 Thread Ralph McDiarmid
I suggest that an arc is something continuous and producing light or illumination. A spark is something abrupt and short lived. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: Speakman, Jim [mailto:jim.speak...@uk.thalesgroup.com] Sent: September 22, 2003 8

RE: Fly-back Switched-Mode Power Supplies

2003-05-12 Thread Ralph McDiarmid
the fewest parts. With current-mode controllers, both discontinuous and continuous mode operation are usually easy to make stable in a closed-loop control design. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. www.xantrex.com tel: (604) 422 2622 fax: (604) 420 1591

RE: NEW EMC DIRECTIVE

2003-05-09 Thread Ralph McDiarmid
I agree. It seems rather silly to specify a mains or other cable included with the equipment in the DoC or to have separate DoCs for each cable. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. www.xantrex.com tel: (604) 422 2622 fax: (604) 420 1591 From: Gordon,Ian

RE: Performance Criterion

2003-04-30 Thread Ralph McDiarmid
. No damage to the product is allowed as a result of any EMC immunity test described or referenced in this standard. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. www.xantrex.com tel: (604) 422 2622 fax: (604) 420 1591 From: John Woodgate [mailto:j

RE: FCC Limits - 150kHz transformer

2003-04-29 Thread Ralph McDiarmid
I would expect a 50/60Hz transformer to be a very poor transformer at 150kHz. The leakage inductance alone would attenuate the signal substantially. The iron laminate material in the core would also be very lossy at that frequency. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex

RE: Check list for PCB Layout

2003-04-29 Thread Ralph McDiarmid
Here's a text we have found useful: Printed Circuit Board Design Techniques for EMC Compliance A Handbook for Designers by Mark I. Montrose Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. www.xantrex.com tel: (604) 422 2622 fax: (604) 420 1591 This message

RE: Thermocouple glue

2003-04-28 Thread Ralph McDiarmid
I agree with you. If an agency disallows a particular test set-up or procedure, they should be able to articulate that concern in writing and justify it as well. I know that may sound somewhat idealistic. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc

RE: Thermocouple glue

2003-04-28 Thread Ralph McDiarmid
things they simply don't understand or have no experience with. Fair enough, I suppose, I can see their point of view and they must take a conservative approach at all times. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. www.xantrex.com From: Brian O'Connell

RE: Performance Criterion

2003-04-25 Thread Ralph McDiarmid
which accompanies the equipment. (no more Criteria A,B or C) Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: John Woodgate [mailto:j...@jmwa.demon.co.uk] Sent: April 25, 2003 2:19 PM To: emc-p...@majordomo.ieee.org Subject: Re: Performance Criterion I read

RE: Performance Criterion

2003-04-25 Thread Ralph McDiarmid
and it should be carefully defined. Thanks also to all you have responded so far. I encourage the discussion to continue. Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. www.xantrex.com tel: (604) 422 2622 fax: (604) 420 1591 From: Frazee, Douglas (Douglas) [mailto:dfra

Performance Criterion

2003-04-25 Thread Ralph McDiarmid
interpretation? Thanks, Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc.

VDE701-1 vs 60990

2003-02-14 Thread Ralph McDiarmid
I would like to know if there are significant differences between VDE701-1 and IEC60990 with regard to test circuits for measuring leakage currents and touch currents. Both IEC1010-1 and EN60950 both refer to test circuits which appear to be derived from 60990. Thank you, Ralph McDiarmid

RE: electronic copies of EN

2002-11-22 Thread Ralph McDiarmid
You can also do that at the IEC webstore. Ralph McDiarmid, AScT Member Technical Staff Engineering Services Xantrex Technology Inc. www.xantrex.com tel: (604) 422 2622 fax: (604) 420 1591 Confidentiality Notice: This email message, including any attachments, is for the sole use

RE: Shield Room Lighting

2002-10-31 Thread Ralph McDiarmid
We use four florescent screw-in lights in our 3-metre chamber and detect some emission 3dB or so above the noise floor. Ralph McDiarmid, AScT Member Technical Staff Engineering Services Xantrex Technology Inc. -Original Message- From: POWELL, DOUG [mailto:doug.pow...@aei.com] Sent

RE: Measuring AC Line Impedance

2002-10-31 Thread Ralph McDiarmid
I would have expected that the inductance would dominate the branch impedance at line frequency and its harmonics. Ralph McDiarmid, AScT Member Technical Staff Engineering Services Xantrex Technology Inc. www.xantrex.com -Original Message- From: John Woodgate [mailto:j

<    1   2   3