l set of utility plans is made available the calcs
will be adjusted accordingly. At this point I like the idea of going
with the more stringent of the two ideas.
I appreciate all the help, and thanks Todd for pointing out the obvious
fact that I missed about the static pressure.
/Thank you
I don't know where the mains will be. There is no location yet, I have
only guessed at what I think they will do.
They haven't located where hydrants will be. All I have is the loop
around the building and that there will be piping from the pump house.
/Thank you,
Bob Knigh
x27;m just going to use the numbers from the pump test and re-verify
everything at a future date.
Does this sound reasonable?
--
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
--
This email has been checked for viruses by AVG antivirus software.
w
Yes, there is a roof deck above that is sprinklered. I have put
sprinklers below the grating using shields on the sprinklers. Just
second guessing myself.
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 4/12/2024 4:41 PM, Bob Knight wrote:
I have
e member (1 1/2") or the width between
openings (15/16") or the actual thickness on the material (1/4")?
It's late on a Friday and I'm tired. Thanks for the help.
--
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
--
This email
not
much more than Class IV products.
The problem I see right off the bat, is secondary containment of the
sprinkler water runoff. There are super fast deluge systems but not sure
deflagration hazards are a good match for subterranian storage
opportunities.
my two cents
Bob
Bob Caputo, CFPS
Craig,
Yep, not even pdf's of the building. At least I could work off those.
As one person just told me, "all I need is a bigger hammer".
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 3/18/2024 4:33 PM, Prahl, Craig wrote:
S
I was sent a project with a Navisworks file (nwd). I am being told that
this is all there is, that there are no other files. No CAD, nothing.
Has anyone else run into this? If so, how do you use the NWD file to
create sprinkler plans?
--
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight
Does anyone have a detail for how to hang to SIPS panels.
I have looked at four or five manufactures and none of them have hanging
details for any trade, at least not that I have found.
--
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
--
This email
if it is 1' to <18"
than it can be no more than 2-1/2" above the tee, and etc
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 2/9/2024 2:37 PM, Jackie Ward wrote:
I have 18” wide concrete beams extending 24” from the bottom of t
23.4.4.2.5.
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 2/8/2024 9:54 AM, Matt Grise wrote:
We are looking at an auto repair facility that has a very small tire
storage room (apx 300sf). The tire storage space is open on one side
to the misc parts st
😉
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/compan
.
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american
criteria. For example, where fuel fired equipment is located in an
otherwise unprotected attic, sprinkler protection is required to be
installed above it….
I hope that helps.
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w
minimum
standard for the design and installation of standpipes which will be used
by the first responders – who should be the only one’s deciding the design
criteria and the location of equipment to be used in fighting fires.
That’s my 2 cents – I hope that helps.
bc
*Bob Caputo, CFPS
the arm over (but if it’s long
enough….)
I’m sitting in an airport without a book so there might be other opinions
Bob Caputo
On Thu, Oct 19, 2023 at 11:35 AM George Medina Jr. <
los_amigos_b...@yahoo.com> wrote:
> I have an armover that is 2'-4" in length. The SEOR is requ
Actually, I was thinking "ahh, the good ol' days". LOL
/Bob Knight//
/
On 8/17/2023 2:20 PM, AKS-Gmail-IMAP wrote:
Very well put Joan. I sadly bet every guy on this forum did not notice
this.
On Aug 17, 2023, at 12:45 PM, Joan Leedy wrote:
Huh - no women!😂
Sent from my
It is added at the point of connection. So wherever your line connects
to the existing system you add an inside hose demand at the most remote
point of connection. Basically, in your case it will be the point that
you have connected to the existing grid.
/Thank you,
Bob Knight, CET III
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 8/7/2023 1:21 PM, Fpdcdesign wrote:
I am working on a wood framed residential building, with some steel
columns, that has a full 13 system (Type V-B construction). The steel
columns are 4” diameter and ar
13D has a section that states that it is permissible to use Residential
sprinklers outside of their listings in circumstances like yours (see
8.1.3.1.2, 2016). You may need to a four sprinkler calc instead of 2,
if I remember correctly.
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight
engineers
Bob Caputo
On Thu, Jun 15, 2023 at 6:15 AM Fpdcdesign wrote:
> I am working on an installation where the fire pump is going to be
> installed above and already poured radiant heat floor. Outside of not being
> able to drill into the floor, is there anything else I should be
see playing
out every day – this is not the place for it.
Thank you.
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/af
Sorry, I didn’t see the word, “sidewall” when I responded. I need more
sleep 😉
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://tw
terial
equivalent to the web construction so that individual channel areas do not
exceed 300 ft2 (28 m2)
But I’m guessing your situation doesn’t meet that definition….
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext
primary
industry topics.
Best regards,
Bob
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/103952834536773222
warrant a warning. There can be no pricing discussions or anything
close to it.
Thank you all and I hope this forum will continue to be a valuable resource
for our members!
Best regards,
Bob
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214
Tony,
Never mind. I should have read everything. It says for Residential
Applications only.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
From: Bob Knight [mailto:b...@firebyknight.com]
Sent: Saturday, April 01, 2023 12:20 PM
To: 'Discussion list on i
support. We sit on over 30 standards and have 5 FPE’s on staff.
Many of our training programs are available remotely as well. If you visit
our website: www.firesprinkler.org you may find our association useful as
well.
Best regards,
Bob
*Bob Caputo, CFPS*
*President*
*American
having pdf’s and they offer a free trial to try it before you
buy it.
LINK is the alternative to pdf’s and hard copies.
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.
tell AHJ’s to expect.
Bob
*From:* Fpdcdesign
*Sent:* Monday, February 20, 2023 7:14 AM
*To:* Discussion list on issues relating to automatic fire sprinklers <
sprinklerforum@lists.firesprinkler.org>
*Subject:* [Sprinklerforum] Re: Once upon a grid...
Rule of thumb: if the num
minimum level of
protection – nothing says we cannot or should not do more. Yes, I know I
am preaching to the choir with this angle but our codes and standards
cannot address every situation specifically and the AHJ probably has a
reasonable thought in their request.
Just my 2 cents
*Bob
flow, a hydrant or even the annual fire
pump test or standpipe flow testing could qualify as the means to perform a
forward flow test
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<ht
of a problem on this one?
Bob
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/103952834536773222
inal suppression.
Much of this needs to be discussed with the municipal AHJ and maybe the
insurance company.
So, the answer to your question is probably, “depends”
Best regards,
Bob Caputo, CFPS
*It should be noted that the above is my opinion. It has not been
processed as a formal interpreta
you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
From: Luis Perea [mailto:lpe...@demek.com]
Sent: Wednesday, October 05, 2022 3:19 PM
To: 'Discussion list on issues relating to automatic fire sprinklers'
Subject: [Sprinklerforum] ESFR Sprinkler Under Obstruction
H
California has its own version of NFPA 25, which is enforced statewide.
Main Drain tests are annual only in the CA edition. They have lined through
the monthly requirement. In addition, the State of California has its own
forms which are required whether electronic or paper.
*Bob Caputo
get a
computer generated report or we take a static read and make believe we had
a 10% drop to predict the residual.
Just sayin’
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<ht
ing it.
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054 (fax)
>
> 860-608-4559 (cell)
>
> _________
> SprinklerForum mailing list:
>
carports, porte cocheres, and stairs that are open and attached"?
The ANNEX shows examples that are all pass through corridors. So, I'm
questioning myself about the dead end style.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208
Thank you Mr. Leyton for self-policing and reminding everyone the forum is
not the place for advertisements of any kind.
The forum is solely for the purpose of peer review information and the
exchange of ideas, technical (informal) interpretations of codes and
standards. Participants are not per
.
- (4) Minimum ceiling design of OH2 shall be used.
Your AHJ should be able to accept this under section 1.5 of whatever
edition you’re using
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
nal consultation or services.*
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https:
posted causes me to remind everyone to avoid doing
so.
Please refer to the material without reproducing it. If need be, to a small
snippet *might* be ok
[image: Image removed by sender.]
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349
ndent from one another. So my
question is, do we need to include a hose allowance in the hydraulic
calculations?
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
FBK-LOGO-EMAIL
_
SprinklerForum mailing l
out on my statement.
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://w
2019 incorporated Miscellaneous and Low Piled Storage requirements into
the chapters addressing sprinkler technology for storage applications
(CMDA, CMSA, ESFR and Rack Storage) as opposed to having its own chapter as
it did in 2016
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler
stuff, as long as you can still
remember it
*Bob Caputo, CFPS*
*President*
*American Fire Sprinkler Association*
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/103952834536773222
Steve,
I suggest looking at the FM Guidelines on distilled spirits, I have a
copy somewhere if you need it or any help drinking the evidence
Bob Caputo
-Original Message-
From: Sprinklerforum On
Behalf Of Steve Leyton via Sprinklerforum
Sent: Monday, March 7, 2022 3:23 PM
To
adequate.
When I look at the foam in landing pits of gymnasiums or even the
bleachers, I'd have a hard time seeing a simple gymnasium as light hazard.
This is a personal opinion.
Bob Caputo, CFPS
President
American Fire Sprinkler Association
-Original Message-
From: Sprinklerforu
addressed by NFPA 25 and
addressed the corrosive nature of the environment on the sprinklers, but the
committee rejected the proposal to omit sprinklers above the indoor pool.
Bob Caputo, CFPS
President
American Fire Sprinkler Association
Expand your business with ITM.
Professionalize the role of your
kilos)
Bob Caputo, President
AFSA
On Sat, Jan 15, 2022 at 9:24 AM tstone52--- via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> The building is new wood frame with insulated roof deck over the Attics.
> The
> roof pitches range from 8:12 – 12:12. Occupancy is
be omitted,
does this make it's not fully sprinklered? No. It is sprinklered
throughout per the requirements of that standard.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.or
or removal from
the forum at the discretion of AFSA management and leadership. This is not open
to debate.
Thank you for your understanding and Happy New Year to one and all.
Bob Caputo, President
AFSA
> On Dec 28, 2021, at 6:03 PM, Bob Caputo wrote:
>
> Leyton,
>
> Whi
keep comments generic or
offline.
Thank you, the management
Bob Caputo - Sent from my iPhone
> On Dec 28, 2021, at 4:01 PM, 321 via Sprinklerforum
> wrote:
>
> Guys,
> Having been in this business for almost 50 years, I have learned that the
> quality of a Fire Sprinkl
is opinion should net be
relied upon as consultation.
Bob Caputo, CFPS
President
American Fire Sprinkler Association
-Original Message-
From: Sprinklerforum On
Behalf Of J H via Sprinklerforum
Sent: Tuesday, December 21, 2021 1:34 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: J H
S
trays is listed as a Group A plastic in the annex list….
Not sure NFPA 13 has any dark corners, though the color of the new edition
is dark gray ;-)
Bob Caputo, Lurking the dark corners of Dubai this week
AFSA
On Wed, Dec 15, 2021 at 2:49 AM Prahl, Craig/GVL via Sprinklerforum <
sprinklerfo
hope that helps
Bob Caputo
AFSA
On Wed, Dec 15, 2021 at 4:08 AM James Crawford via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> Hope some can help, I seem to remember there was a time frame of the
> sprinkler demand plus largest container in order to figure ou
any other brand.
As always, the opinions expressed herein are my personal opinions and may
not be considered as the opinion of NFPA or its committees. This opinion
should not be considered or used as consultation services.
Bob Caputo, President
AFSA
On Wed, Dec 15, 2021 at 8:55 AM Jamie Seidl
klers and they should be on a separate (independent) control valve.
It really depends on the content of the fumes (flammability)
Bob Caputo
-Original Message-
From: Sprinklerforum On
Behalf Of Dennis Wilson via Sprinklerforum
Sent: Friday, December 3, 2021 10:48 AM
To: sprinkler
__
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
--
Bob Caputo, CFPS
*President*
*American Fire Sprinkler Association*
p: 214-349-5965 ext124
w: firesprinkler.org
<https://www.face
ir spec and NFPA 13 (16 ed.)
20.3.3, hope it helps a little bit.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, Novemb
%20department%20connection.
https://www.youtube.com/watch?v=GOUMQFSTJ6E
Bob Caputo, CFPS
President
American Fire Sprinkler Association
-Original Message-
From: Sprinklerforum On
Behalf Of BRUCE VERHEI via Sprinklerforum
Sent: Thursday, October 14, 2021 3:12 PM
To: e...@bamfordfire.com
attic.
Just my thoughts
Bob Caputo
Have you visited afsasafetyportal.com yet?
It's AFSA's member-only safety resource! This virtual library delivers the
accident-prevention and safety-related information you need to educate
your staff, help prevent claims, and create a safe work
environment
NFPA 20 is clear that the pump room is to be protected per EH2. By
definition of EH2, the presence of the diesel fuel makes it EH2. See
4.14.1.3
Bob Caputo, CFPS
President
American Fire Sprinkler Association
-Original Message-
From: Sprinklerforum On
Behalf Of James Crawford via
Not to mention it’s a horrible practice in my opinion
Bob Caputo, President
American Fire Sprinkler Association
-Original Message-
From: Prahl, Craig/GVL
Sent: Thursday, August 19, 2021 5:07 PM
To: Bob Caputo ;
sprinklerforum@lists.firesprinkler.org
Cc: John Denhardt
Subject: RE
position of the AFSA, and/or NFPA or its technical
committees. AFSA cannot provide design or consulting engineering services,
and this opinion should therefore not be considered, nor relied upon, as
such.
Bob Caputo, President
American Fire Sprinkler Association
-Original Message
you for your understanding.
Bob Caputo, CFPS
President
American Fire Sprinkler Association
Get in the (Fitter) Zone!
AFSA's "Fitter Zone" features live webinars designed specifically for fire
sprinkler fitters. These live presentations are held on Saturdays whenever
possible, so yo
a forklift so….
Bob Caputo - Sent from my iPhone
> On Jul 1, 2021, at 2:52 PM, BRUCE VERHEI via Sprinklerforum
> wrote:
>
> From an old fire guys perspective I’d be more concerned with accidental head
> breakage than water dispersal.
>
> Best.
>
>
>> On 0
Pete,
You are correct. Where the closet is less than 400 ft3, no clearance is
required below the deflector
Bob Caputo
-Original Message-
From: Sprinklerforum On
Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 10:36 AM
To: sprinklerforum
considered the opinion of AFSA, NFPA
or any technical committee upon which I serve. (13/25/24/291)
Bob Caputo
-Original Message-
From: Sprinklerforum On
Behalf Of Mark.Phelps via Sprinklerforum
Sent: Friday, April 23, 2021 11:47 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mark.Phel
😀
On Fri, May 7, 2021 at 11:23 AM Michael Hill via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> There goes my logic, right out the window..again.
>
> Mike Hill
>
> -Original Message-
> From: Sprinklerforum On
> Behalf Of Bob Caput
of that elevation pressure, or do I need to
> design and calc as though the tank is nearly depleted?
>
> -Kyle M
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/lis
Sincerely you’re measuring the flow and pressure at the hydrant in the
first place, why would you need to know that? Just curious...
Reverse engineering the water supply in the water main below?
On Mon, Apr 26, 2021 at 3:57 PM Steve Leyton via Sprinklerforum <
sprinklerforum@lists.firesprinkler
move water and add pressure, they
can’t add water.
Again, just my 2 cents wort…. Not be be considered the opinion of NFPA, AFSA or
any technical committee nor the formal opinion of the NFPA 13, 24, 291 or 25
committees.
Bob Caputo, CFPS
President
American Fire Sprinkler Association
they bring a pump in the engine when they show up - so its more likely
you’d need to add a water storage tank if fire flow is the concern. Fire flow
is not a NFPA 13 issue but section 11.1.5.3 is.
Just adding my 2 cents...
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p
This may have been approved by the local AHJ, which would be the
appropriate assumption based on NFPA 25. We are not doing a design
analysis.
On Thu, Apr 8, 2021 at 9:34 AM Dale Wingard via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> Sounds like the intent was to protect the
!
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org <http://firesprinkler.org/>
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www
and the opinion
of the writer and may not be considered a formal interpretation of the
standard, may not express the opinion of NFPA or its technical committees.
Bob
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org &
I have a city requiring 4 1/2" FDC and I am having difficulty finding a source
SincerelyBob
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
NFPA or its technical
committees.
Best regards,
Bob
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org <http://firesprinkler.org/>
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.
NFPA 13, 2019 edition actually addresses this in section 29.2
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org <http://firesprinkler.org/>
<https://www.facebook.com/firesprinkler.org/>
<https://t
at there can be more than one criteria for any given area. Yours
just happens to involve two different types of systems each with their
own specific area/density criteria.
I hope you get this worked out,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
above. It's a pain in the neck but other than one more step in the
calc that's it.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Joe Burtell via Spri
sued over my
response - so I know this answer really well
Bob Caputo
On Wed, Feb 10, 2021 at 11:44 AM tstone52--- via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> Project is a 100 year old 6 story Steel & Concrete Hotel building. The roof
> is steel fram
FM Global has a standard for this specifically. I recommend downloading it
from their website. Great information that might provide guidance for you.
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org <h
in the
“damned” area regardless of pitch of pipe or the rating of the gasket used with
the coupling (in dry pipe or reaction systems).
Bob Caputo
> On Jan 20, 2021, at 1:07 PM, Jeff Normand via Sprinklerforum
> wrote:
>
> I have been designing with sch 7 pipe for over 25 yea
s not exceed the limits of 9.3.4.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of J H via Sprinklerforum
Sent: Wednesday, December 30, 2020 1:24 PM
To: sprinkler
Sprigs do not require sway bracing, but there is this: 9.3.6.6 Sprigs 4
ft or longer shall be restrained against lateral movement.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun
Thank youSame to you and yours
On Fri, Dec 25, 2020 at 10:38 AM Mario Berrios via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> Merry Christmas,
> mario berrios
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprin
.
Just my opinion - and is not intended to represent the opinion of AFSA, NFPA or
any NFPA Committee
Bob
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org <http://firesprinkler.org/>
<https://www.fac
That was my answer, I was just hoping.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack via Sprinklerforum
Sent: Friday, December 18, 2020 12
I've been doing this for a while, so I'm about to ask a question that I
think I know the answer too.
I'm just hoping for a different answer.
Is schedule 40 threaded piping 2-1/2" and smaller required to be sway
braced? What about 3" threaded?
Thank you,
Probably because the DV-5 is a TYCO valve and not Viking.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of JD Gamble via Sprinklerforum
Sent: Thursday, December
Does anyone have a 3D block of Vikings DV-5 Deluge Valve in 3 & 4"?
I can only find Revit files on their site, and I don't have Revit, so I
would need dwg if possible.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
why would this be any different? The domestic demand
needs to be added only when sharing the water supply from the same line for
each individual building. This is not a collective requirement.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message
JD, I'm not working out of the 19 version yet, but this criteria has been
the same or similar for some time.
So, the answer is the sprinklers are not required when meeting the
conditions you mentioned.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Me
One of my top three favorite answers:
1) Because I'm the AHJ.
2) Because I said so.
3) It's in the book.
Joking aside. Find out what "book". I'm not aware of additional clearances
other than the electrical.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
20
ts of Table Q."
This would include when passing through holes in TJI type joist.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mike Hairfield via Sprinkler
Thanks for the input.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jim Davidson via Sprinklerforum
Sent: Tuesday, September 15, 2020 3:09 PM
To: b
Based on the limited info that I have, it's open. I'll look at FM and see
what they offer.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Cra
1 - 100 of 707 matches
Mail list logo