Bob,
Look at NFPA 15 for conveyor protection for water spray systems, this may
reinforce what you are looking at, perhaps substitute sprinklers instead of
water spray
Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer
[cid:image001.png@01D3EB87.1D50C020]
American Fire
www.american-fire.com<h
Good Job Travis.
Merry Christmas!!
Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer
[cid:image003.png@01D378B7.4650E010]
American Fire Protection, LLC
5525 Eastcliff Industrial Loop | Birmingham, AL 35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)
[http
See figure A*.6.5.1.2 from NFPA 13, 2016
[cid:image007.png@01D28CE9.3EDD6110]
Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer
[cid:image008.png@01D28CE9.3EDD6110]
American Fire Protection, LLC
5525 Eastcliff Industrial Loop | Birmingham, AL 35210
205-591-9111 ext. 1452 | 205-317
cation by practicing engineering.
Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer
[cid:image005.png@01D2513A.37965DC0]
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop | Birmingham, AL 35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)
[http://www.sfpe
,
“11.2.3.2.2.3 For extended coverage sprinklers, the minimum design area shall
be that corresponding
to the hazard in Figure 11.2.3.1.1 or the area protected by five sprinklers,
whichever is greater.”
Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer
[cid:image002.png@01D1DD1D.D0067810
inside that storage unit.
Jeff Hewitt, PE, SET, PMSFPE
Corporate Engineer
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop | Birmingham, AL 35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)
Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire
Travis,
The question is does a mezzanine count as a story? My past experience has
been, NO, a mezzanine, that fits the definition of mezzanine in IBC, cannot
also be a story, rather it is considered a part of the story within which it is
contained.
Excerpts from IBC 2012
Jeff Hewitt
Mark,
Which edition if IFC are you looking in?
Sent from my iPhone
> On Dec 5, 2014, at 9:09 PM, "mphe...@aerofire.com"
> wrote:
>
> Where are you guys finding these specific methods of "proving" the adequacy
> of the fire flow requirements? I don't find any language close to this in the
What is the occupancy of your job?
> On Sep 15, 2014, at 4:34 PM, "Rod DiBona" wrote:
>
>
> Just had an Engineer tell us that ASCE 7 is going to be changing so that
> seismic design category B will require EQ for fire sprinkler systems and that
> is why they are being proactive and requirin
Just wondering how an architect can be an EOR. An architect is not an engineer.
Sent from my iPhone
> On Jun 26, 2014, at 10:25 AM, "Tim Stone" wrote:
>
> Craig,
>
> In this case I was hired by the Architect to design a Sprinkler system for a
> brand new Church. The project is in a rural sett
It is also possible that 4 standard coverage heads at 225-sq.ft could fill out
a 900-sq.ft. remote area, but NFPA 13 requires a minimum of 5 heads.
Jeff Hewitt, PE, SET
Corporate Engineer
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL 35210
205-591-9111 ext
. remote area,
it is possible that you could fill out your 900-sq.ft remote area with just 3
extended coverage heads (3 x 400-sq.ft. = 1200-sq.ft.), but NFPA 13 requires a
minimum of 5 heads to be calculated.
Jeff Hewitt, PE, SET
Corporate Engineer
American Fire Protection, Inc.
5525 Eastcliff
Check this link
http://nfpatoday.blog.nfpa.org/2012/08/new-anti-freeze-tias-approved-.html
Jeff Hewitt, PE, SET
Corporate Engineer
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL 35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell
When specifically did you receive this NFSA EOD opinion?
Jeff Hewitt, PE, SET
Corporate Engineer
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL 35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)
-Original Message-
From: sprinklerforum
Why install sprinklers according to NFPA 13 then? It's just a standard, a
regulation. Why not just do what you want?
Jeff Hewitt, PE, SET
Corporate Engineer
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL 35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
20
Check NFPA 13, 2013, 6.2.1.1
Jeff Hewitt, PE, SET | Corporate Engineer
NICET #102015 | Water Based Layout - Level IV
Inspection Testing & Maintenance - Level III
241 Hughes Lane | St. Charles, MO 63301
Office 636-946-0011 | Fax 636-946-5172
Cell 314-574-6989 | www.bistatefire
6.1. The clear space beneath a sprinkler is needed for the spray
pattern to fully develop to allow proper wetting of the floor and not the
wall."
Jeff Hewitt, PE, SET | Corporate Engineer
NICET #102015 | Water Based Layout - Level IV
Inspection Testing & Maintenance - Level III
241 Hug
Should a NICET technician be determining this design criteria?
Jeff Hewitt, PE, SET | Corporate Engineer
NICET #102015 | Water Based Layout - Level IV
Inspection Testing & Maintenance - Level III
241 Hughes Lane | St. Charles, MO 63301
Office 636-946-0011 | Fax 636-946-
Randy,
There is no error. Not all ESFR are created equal. K25 and K22 will not
protect the same things that K14 and K17 will.
Jeff Hewitt, PE, SET
Corporate Engineer
BI-STATE
FIRE PROTECTION
C O R P O R A T I O N
636-946-0011 office
636-946-5172 fax
314
Roland,
Thank you for the correction. I forgot about that change in 2010 edition,
which is actually not referenced yet by any building code, so depending on
the jurisdiction, we may not be able to use that.
Jeff Hewitt, PE, SET
Corporate Engineer
BI-STATE
FIRE PROTECTION
If this design does move forward, another concern would be your design area.
Sounds like you may need more than 12 heads to fill up your minimum 960
sq.ft.
Jeff Hewitt, PE, SET
Corporate Engineer
BI-STATE
FIRE PROTECTION
C O R P O R A T I O N
636-946-0011
Lard oil, bottled/cartoned, or lard, packaged/cartoned, will still be a
Class IIIB Liquid
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire
classified as a Class IIIB Liquid in NFPA
30.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them
Bobby,
I would suggest that the use of a sleeve depends on the UL Through
Penetration System you choose to use for the penetration. Some do not
require the use of sleeves.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
I agree George,
I left that part out in my previous post do it as a simple wet system, with
SR, IM or High temp. fusible link heads
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636
occurred prior to sprinkler activation.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them
Ken,
based conversations I have had with ICC, and based on standard English
punctuation, and the presence of the comma, the intent is to allow sprinkler
penetrations, regardless of sole service to the stairway or not. The
wording has changed slightly over time.
Jeff Hewitt, PE, SET, SFPE
protected with my log, and would welcome suing the pants off
anyone that I caught using my stamp/identity.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell
Try NFPA 13, 2002, Table 12.3.2.4.2.1
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them
because
a concealed space has not been created (due to the described space being
open on all sides).
Providing sprinklers at the deck for 24-ft. beyond, on all sides is not
correct.
Just my opinion.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection
Try IBC, 2009 713.3.2 Exception 5
And associated Figure 713.3.2(2)
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives
h sides of the "canopy"
if it is against the wall.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can Y
ieve compliance with this
requirement."
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without The
OK, I stand corrected. The plumber that prepared the FP specs did not know
which boxes to click from their master spec writing software.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
If this is not a design-build project, and the specs do not require them,
even though the AHJ does, then I agree, the plumber that wrote the FP specs
blew it.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO
When I took the exam in 1995 it was 75%. I do not know if that is still
accurate.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers
ified or not.
Check out this link to see an outline for what is actually covered on the
NCEES FPE exam
http://www.ncees.org/Documents/Public/PE%20Fire%20Oct%202004.pdf
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Ch
Tony,
My take is that you are obligated to provide protection at the deck 1st, and
then everything else becomes a potential obstruction to sprinkler discharge
below. In this case it seems you will also need to drop protection into the
levels of clouds at the 8' level as well.
Jeff Hewit
I suggest you get your hands on a copy of "Sprinkler Hydraulics" by Harold Wass
Jeff Hewitt, PE, SET
Corporate Engineer
Bi-State Fire Protection Corporation
636-946-0011
--- On Wed, 12/8/10, Ron Greenman wrote:
From: Ron Greenman
Subject: Re: NICET III
To: spri
stem to
get their permit. How is the public safety served by such abuse?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save li
nswer...
How can a PE that is not qualified by training, education, or experience
(any PE, not just an FPE) legitimately claim to provide personal or
immediate supervision over said work?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
process in general, not about you specifically.
You cannot tell me that what I described does not occur everyday all over
this country, by those that either do not know, are willing to risk it, or
do not care, and not just in our field of fire protection.
Jeff Hewitt, PE, SET, SFPE (Professional
gally, and
therefore your professional liability and errors and omissions coverage is
denied.
This is not another PE vs. layout technician thing. Rather, this is a
statement that if a PE is required, then do it correctly.
Just my 2-cents. Sorry for the rant, and no offense intended towards Bobby.
J
int, it is already designed (and
perhaps in for permit and rejected), and now you want to add a PE and come
back with the same design stamped by a PE, I would reject that as well, as
it is obvious the PE just stamped the plans after the fact, and did not do
or supervise the design.
Good luck.
Jeff
Travis,
It's in the IBC code
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
-Ori
t is ultimately fed from a public utility source?
>
>Jeff Hewitt, PE, SET, SFPE (Professional Member)
>Corporate Engineer
>Bi-State Fire Protection Corporation
>
>241 Hughes Lane
>St. Charles, MO 63301
>636-946-0011
>636-946-5172 (fax)
>314-574-6989 (cell)
&
Is it actually a private separate water supply, or just a private water main
that is ultimately fed from a public utility source?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946
With most control mode, you have Group A plastic and pallet storage
limitations that you would NOT have with ESFR K14 or K17. If these are
areas of concern, then that would be an issue.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241
Sounds like your consultant is correct in accordance with NFPA 13. But that
does not address whether there are any specially adopted requirements via
the Department of Health.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes
The K14 and K17 are the only ESFR with the 32-ft building option. It is
allowable to utilize the 35-ft. building design criteria instead.
Please be aware that K25 ESFR does not protect the same things that K14 and
K17 do, mainly idle pallets, and uncartoned or exposed Group A Plastics.
Jeff
Steve,
I do not disagree, just wanted to make the point. Also, if the AHJ accepts
it, that would be another route to take.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
nd if it cannot, then
your argument loses validity.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Li
Yes, you do. It is not for you to decide or investigate, let the regulatory
agency do their job. If they get enough similar "standard of care" or "area
of expertise" complaints it very well may add up to them taking action. To
do nothing means nothing will ever happen.
y need to investigate these bad
actors, then we have NO right to complain.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save l
Yes.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
-Original Message-
From
It was also amended by the 2004 IBC Supplement to IBC 2003, and the 2007 IBC
Supplement to IBC 2006
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell
Hydrogen hydroxide
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
-Original Message
NFPA 13, 2007 11.2.3.3.6 for Room Design Method, and 11.2.3.3.7 otherwise
both state"or when extended coverage sprinklers are installed, all
sprinklers contained within 75 linear feet in the corridor"
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-
in it. I have been trying to
find that document for quite a while, but nobody seems to have a copy of it.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (ce
How about a "false ceiling"
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
---
You are allowed to move up to 1-ft. to avoid obstructions to discharge,
either along branch lines, or between lines, but not both at the same time.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636
specifically
listed/referenced.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save lives.
Can You Live Without Them?
-Origin
I think you are missing the point.
You have found the references within each Code, but do the Codes apply to
Fire Suppression piping?
Read the SCOPE of each document and you will find that it does NOT include
Fire Suppression piping.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate
Ron,
it's better not to use hangers on this one, put it under water.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)
Fire Sprinklers Save
scribed in the
commentary of NFPA 13 on this topic. The ASCE 7 and IBC documents make no
clarification on this. At least for this issue, there seems to be a lack of
consistency.
Just my 2-cents.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corpo
Joe,
I do not have it in front of me, but, the 2007 Supplement to the 2006 IBC
specifically added a new line stating that NFPA 13 satisfies IBC.
Perhaps someone on this Forum has the specific excerpt available.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire
Travis,
Since we have no specific guidance on this topic, my recommendation is that
you must protect to deck first, and deal with the obstructions second.
With this criteria, I would recommend both above and below the clouds.
Just my thoughts
Jeff Hewitt, PE, SET, SFPE (Professional Member
kinda like nuclear vs nucular
--- On Wed, 1/14/09, bill.bro...@brooksfpe.com
wrote:
From: bill.bro...@brooksfpe.com
Subject: Sprinklered vs Sprinkled
To: sprinklerforum@firesprinkler.org
Date: Wednesday, January 14, 2009, 10:47 PM
Actually this is a serious question.
Is there anywhere in the
come to an agreement whether the
storage configuration was a solid unit load.
just my 2 cents..
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
St. Charles, MO 63301
636-946-0011
636-946-5172 (fax)
--- On Tue, 12/23/08, Dewayne Martinez
other equipment,
including a pressure maintenance (jockey) pump."
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From: [EMAIL PROTECTED] [mai
That's a good story!!
PE's like that deserve to be "cut off at the knees".
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Messa
Thank you Thom,
That is my point exactly. The PE profession is self policing. Regulating
boards will not and cannot act unless someone files a complaint. Let them
look into it, that's their job, but by all means FILE the COMPLAINT.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corp
regulating agency/board.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL
about
this if we believe otherwise.
Just my 2 cents.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
So, that makes it ok, then?
You know better, but you go ahead and do it wrong anyway?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From
Just curious
If you have NO intentions of listening to the good advice you are getting
here on this forum, why ask the question to begin with?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636
I'd love to hear your logic on that interpretation.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[
requirement could lead to including MORE than 2 additional heads in an ESFR
remote area.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From
many
unanswered questions here. The NFPA 13 standard states that you do not have
to include heads added due to obstructions to the hydraulic calculations,
for a head or two here and there, but to apply it to an entire 50 x 50
mezzanine is a BIG stretch. Just my 2 cents
Jeff Hewitt, PE, SET,
Will NFPA 13, 2007, 8.15.1.5 work for you?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED
Ray,
NFPA 30 or even 30B if you have any aerosols is a good place to start. If
you don't find anything to your liking, you may also want to review the
applicable FM Data Sheets on Flammable and Combustible Liquids to see if
they have a protection scheme to match your situation.
Jeff Hewit
Andy,
Be careful with this one. It seems to me that the storage as described
would constitute Uncartoned (Exposed) Expanded Group A Plastics (NOT Class
IV), which have VERY limited applicability for ESFR.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire
appreciate
others' perspectives on issues such as this.
I make NO apologies for this.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments a
the
ceiling, and I would not entertain any offers to make a contrary judgement.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are
an to make this decision, or
for that matter to try to "sell" it to the local AHJ. Do you really want
that liability? Not to mention whether you are exceeding your "authority"
under NICET rules for practicing engineering?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Co
Brian,
Sorry,
I don't see it that way. It does not say that this only applies to
obstructions up to 9-in wide or your up a creek.
What it does say is that if you are 36-in away that is all the further you
need be.
Contact me by phone to discuss this. I am in the office.
Jeff H
gardless of the actual 4 times dimension.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
Brian,
I believe it should be read to mean that the most/furthest away you have to
be is a maximum of 36-in. The 36-in. is the maximum limit. Without this
provision, you would instead need to be 4 times away or 96-in.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi
maybe thinking
this is an ordinary hazard occupancy, and ESFR is allowed over OH
occupancies?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attach
Fully sprinklered building, 1000-gpm max. for standpipes.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be
Russell,
My take is that if you are using residential heads, and residential head
design criteria, then the 3000 sq.ft area does not apply because you are not
utilizing an area/density design.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection
Joe,
I was wondering the same thing.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
or
Bobby,
I hope this works for your application. Besides corrosion, our concern was
with hot water and steam eventually eroding any wax coating.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636
head that is non-ferrous brass, with a plastic concealer housing, but
still no corrosion resistance listing on it.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
T
Brian,
Just curious...
What were the circumstances that led you to use a test conducted by the Fire
Department? Are there conservation limitations imposed or something like
that? Why would you not have performed your own test?
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate
ng
> > else as an area of expertise when they are not actually qualified.
> >
> > Turn them in! And don't get fed up if nothing happens right
> > away. Their investigations may take a while.
> >
> > Again, rather than seeing all of these complaints about inept
while.
>
> Again, rather than seeing all of these complaints about inept
> specifying engineers, let's all do something different now, or it
> will only get worse.
>
> Gather your facts, file the complaint, and turn them in.
>
>
> Jeff Hewitt, PE, SET, MSFPE (P
rather than seeing all of these complaints about inept specifying
engineers, let's all do something different now, or it will only get worse.
Gather your facts, file the complaint, and turn them in.
Jeff Hewitt, PE, SET, MSFPE (Professional Member)
Corporate Engin
"pre-engineered", that the
plumber won't have to do any engineering? Who will evaluate these and other
changes?
Just my 2 cents.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946
g, and is not, in my
opinion, is an ordinary hazard area rather than light hazard. And because
it's storage, and you don't know what could go in there, OH1 ain't good
enough, it needs to be OH2.
Just my opinion
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporat