[Sprinklerforum] Re: Protecting underground storage of explosives.

2024-04-05 Thread Bob Caputo
and not much more than Class IV products. The problem I see right off the bat, is secondary containment of the sprinkler water runoff. There are super fast deluge systems but not sure deflagration hazards are a good match for subterranian storage opportunities. my two cents Bob Bob Caputo, CFPS

[Sprinklerforum] Re: Sprinkler age magazine.

2024-01-28 Thread Bob Caputo
 *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https://www.linkedin.com/compan

[Sprinklerforum] Re: Dry System Aux. Drain

2024-01-03 Thread Bob Caputo
. *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https://www.linkedin.com/company/american

[Sprinklerforum] Re: Definitions

2023-12-11 Thread Bob Caputo
criteria. For example, where fuel fired equipment is located in an otherwise unprotected attic, sprinkler protection is required to be installed above it…. I hope that helps. *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w

[Sprinklerforum] Re: [EXTERNAL] Re: Pressure Regulating Valves Residual Pressures

2023-11-02 Thread Bob Caputo
is a minimum standard for the design and installation of standpipes which will be used by the first responders – who should be the only one’s deciding the design criteria and the location of equipment to be used in fighting fires. That’s my 2 cents – I hope that helps. bc *Bob Caputo, CFPS

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread Bob Caputo
the arm over (but if it’s long enough….) I’m sitting in an airport without a book so there might be other opinions Bob Caputo On Thu, Oct 19, 2023 at 11:35 AM George Medina Jr. < los_amigos_b...@yahoo.com> wrote: > I have an armover that is 2'-4" in length. The SEOR is requi

[Sprinklerforum] Re: Pump installation over radiant heat floor

2023-06-15 Thread Bob Caputo
engineers Bob Caputo On Thu, Jun 15, 2023 at 6:15 AM Fpdcdesign wrote: > I am working on an installation where the fire pump is going to be > installed above and already poured radiant heat floor. Outside of not being > able to drill into the floor, is there anything else I should be

[Sprinklerforum] Re: Back-to-back sidewalls at Mar-a-Lago?

2023-06-10 Thread Bob Caputo
see playing out every day – this is not the place for it. Thank you. *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/af

[Sprinklerforum] Re: Sidewalls for 18 Inches Down

2023-05-23 Thread Bob Caputo
Sorry, I didn’t see the word, “sidewall” when I responded. I need more sleep  *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter

[Sprinklerforum] Re: Sidewalls for 18 Inches Down

2023-05-23 Thread Bob Caputo
terial equivalent to the web construction so that individual channel areas do not exceed 300 ft2 (28 m2) But I’m guessing your situation doesn’t meet that definition…. *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext

[Sprinklerforum] Re: Need help with a sanity check - Estimate - Open records on safety professionals

2023-04-27 Thread Bob Caputo
to primary industry topics. Best regards, Bob *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/103952834536773222

[Sprinklerforum] Re: Need help with a sanity check - Estimate

2023-04-26 Thread Bob Caputo
to warrant a warning. There can be no pricing discussions or anything close to it. Thank you all and I hope this forum will continue to be a valuable resource for our members! Best regards, Bob *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214

[Sprinklerforum] Re: - NFPA13:2022 pdf version

2023-03-08 Thread Bob Caputo
for support. We sit on over 30 standards and have 5 FPE’s on staff. Many of our training programs are available remotely as well. If you visit our website: www.firesprinkler.org you may find our association useful as well. Best regards, Bob *Bob Caputo, CFPS* *President* *American

[Sprinklerforum] Re: - NFPA13:2022 pdf version

2023-03-07 Thread Bob Caputo
having pdf’s and they offer a free trial to try it before you buy it. LINK is the alternative to pdf’s and hard copies. *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.

[Sprinklerforum] Re: Once upon a grid...

2023-02-20 Thread Bob Caputo
I don’t weigh in on forum matters often, but as one who has done a significant amount of (contract) plan reviews, if the number of sprinklers on the branch lines outside of the grid visually appears to potentially present a greater demand, I would ask for calcs to prove they are not. Any

[Sprinklerforum] Re: Roof Hydrant

2022-11-30 Thread Bob Caputo
a minimum level of protection – nothing says we cannot or should not do more. Yes, I know I am preaching to the choir with this angle but our codes and standards cannot address every situation specifically and the AHJ probably has a reasonable thought in their request. Just my 2 cents *Bob

[Sprinklerforum] Re: BFP on underground supply

2022-11-18 Thread Bob Caputo
flow, a hydrant or even the annual fire pump test or standpipe flow testing could qualify as the means to perform a forward flow test *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <ht

[Sprinklerforum] Re: BFP on underground supply

2022-11-18 Thread Bob Caputo
of a problem on this one? Bob *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/103952834536773222

[Sprinklerforum] Re: NFPA 14 Hose Systems

2022-10-28 Thread Bob Caputo
inal suppression. Much of this needs to be discussed with the municipal AHJ and maybe the insurance company. So, the answer to your question is probably, “depends” Best regards, Bob Caputo, CFPS *It should be noted that the above is my opinion. It has not been processed as a formal interpreta

[Sprinklerforum] Re: [EXTERNAL] Re: Pressure on placard greater that static.

2022-09-27 Thread Bob Caputo
California has its own version of NFPA 25, which is enforced statewide. Main Drain tests are annual only in the CA edition. They have lined through the monthly requirement. In addition, the State of California has its own forms which are required whether electronic or paper. *Bob Caputo

[Sprinklerforum] Re: [EXTERNAL] Re: Pressure on placard greater that static.

2022-09-26 Thread Bob Caputo
get a computer generated report or we take a static read and make believe we had a 10% drop to predict the residual. Just sayin’ *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <ht

[Sprinklerforum] Re: Intumescent Paint

2022-09-01 Thread Bob Caputo
> > > Todd G Williams, PE > > Fire Protection Design/Consulting > > Stonington, CT > > 860-535-2080 (ofc) > > 860-554-7054 (fax) > > 860-608-4559 (cell) > > _____ > SprinklerForum mailing list: > https://lists.firesprinkler

[Sprinklerforum] Re: Hydraulic Design Information sign

2022-04-22 Thread Bob Caputo
Thank you Mr. Leyton for self-policing and reminding everyone the forum is not the place for advertisements of any kind. The forum is solely for the purpose of peer review information and the exchange of ideas, technical (informal) interpretations of codes and standards. Participants are not

[Sprinklerforum] Re: Idle Plastic Pallet Storage

2022-04-06 Thread Bob Caputo
. - (4) Minimum ceiling design of OH2 shall be used. Your AHJ should be able to accept this under section 1.5 of whatever edition you’re using *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org

[Sprinklerforum] Re: Idle Plastic Pallet Storage

2022-04-06 Thread Bob Caputo
nal consultation or services.* *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https:

[Sprinklerforum] Just a reminder

2022-04-05 Thread Bob Caputo
posted causes me to remind everyone to avoid doing so. Please refer to the material without reproducing it. If need be, to a small snippet *might* be ok [image: Image removed by sender.] *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349

[Sprinklerforum] Re: Velocity - Rant leeway for the AHJ

2022-03-22 Thread Bob Caputo
out on my statement. *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https://w

[Sprinklerforum] Re: What happened to the Misc. Storage verbage of 14.2.3.1 in the 2019 edition?

2022-03-15 Thread Bob Caputo
2019 incorporated Miscellaneous and Low Piled Storage requirements into the chapters addressing sprinkler technology for storage applications (CMDA, CMSA, ESFR and Rack Storage) as opposed to having its own chapter as it did in 2016 *Bob Caputo, CFPS* *President* *American Fire Sprinkler

[Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

2022-03-15 Thread Bob Caputo
stuff, as long as you can still remember it *Bob Caputo, CFPS* *President* *American Fire Sprinkler Association* c: 760-908-7753 p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/103952834536773222

RE: Distilled spirits

2022-03-07 Thread Bob Caputo via Sprinklerforum
Steve, I suggest looking at the FM Guidelines on distilled spirits, I have a copy somewhere if you need it or any help drinking the evidence Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Steve Leyton via Sprinklerforum Sent: Monday, March 7, 2022 3:23 PM

RE: INDOOR SPORTS FACILITY FIELD HOUSE

2022-02-07 Thread Bob Caputo via Sprinklerforum
not adequate. When I look at the foam in landing pits of gymnasiums or even the bleachers, I'd have a hard time seeing a simple gymnasium as light hazard. This is a personal opinion. Bob Caputo, CFPS President American Fire Sprinkler Association -Original Message- From: Sprinklerforum

RE: swimming pool

2022-02-07 Thread Bob Caputo via Sprinklerforum
are addressed by NFPA 25 and addressed the corrosive nature of the environment on the sprinklers, but the committee rejected the proposal to omit sprinklers above the indoor pool. Bob Caputo, CFPS President American Fire Sprinkler Association Expand your business with ITM. Professionalize the role of your

Re: UNUSED ATTIC DEFINITION

2022-01-15 Thread Bob Caputo via Sprinklerforum
kilos) Bob Caputo, President AFSA On Sat, Jan 15, 2022 at 9:24 AM tstone52--- via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > The building is new wood frame with insulated roof deck over the Attics. > The > roof pitches range from 8:12 – 12:12. Occupancy is

Re: Airing of Grievances

2021-12-29 Thread Bob Caputo via Sprinklerforum
or removal from the forum at the discretion of AFSA management and leadership. This is not open to debate. Thank you for your understanding and Happy New Year to one and all. Bob Caputo, President AFSA > On Dec 28, 2021, at 6:03 PM, Bob Caputo wrote: > > Leyton, > >

Re: Airing of Grievances

2021-12-28 Thread Bob Caputo via Sprinklerforum
keep comments generic or offline. Thank you, the management Bob Caputo - Sent from my iPhone > On Dec 28, 2021, at 4:01 PM, 321 via Sprinklerforum > wrote: > > Guys, > Having been in this business for almost 50 years, I have learned that the > quality of a Fire Sp

RE: Purpose of Subdividing Dry Systems?

2021-12-21 Thread Bob Caputo via Sprinklerforum
is opinion should net be relied upon as consultation. Bob Caputo, CFPS President American Fire Sprinkler Association -Original Message- From: Sprinklerforum On Behalf Of J H via Sprinklerforum Sent: Tuesday, December 21, 2021 1:34 PM To: sprinklerforum@lists.firesprinkler.org Cc: J H S

Re: Sprinkler protection in a freezer warehouse - with plastics

2021-12-14 Thread Bob Caputo via Sprinklerforum
trays is listed as a Group A plastic in the annex list…. Not sure NFPA 13 has any dark corners, though the color of the new edition is dark gray ;-) Bob Caputo, Lurking the dark corners of Dubai this week AFSA On Wed, Dec 15, 2021 at 2:49 AM Prahl, Craig/GVL via Sprinklerforum < sprinklerfo

Re: NFPA #30 Containment

2021-12-14 Thread Bob Caputo via Sprinklerforum
hope that helps Bob Caputo AFSA On Wed, Dec 15, 2021 at 4:08 AM James Crawford via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Hope some can help, I seem to remember there was a time frame of the > sprinkler demand plus largest container in order to figure ou

Re: Mechanical roll-grooved fittings for fire pipe

2021-12-14 Thread Bob Caputo via Sprinklerforum
with any other brand. As always, the opinions expressed herein are my personal opinions and may not be considered as the opinion of NFPA or its committees. This opinion should not be considered or used as consultation services. Bob Caputo, President AFSA On Wed, Dec 15, 2021 at 8:55 AM Jamie Seidl

RE: Paint Booth Duct Protection

2021-12-03 Thread Bob Caputo via Sprinklerforum
and they should be on a separate (independent) control valve. It really depends on the content of the fumes (flammability) Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Dennis Wilson via Sprinklerforum Sent: Friday, December 3, 2021 10:48 AM To: sprinklerforum

Re: Paint Booth Duct Protection

2021-12-02 Thread Bob Caputo via Sprinklerforum
_ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Bob Caputo, CFPS *President* *American Fire Sprinkler Association* p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.

RE: theft of FDC inlets

2021-10-15 Thread Bob Caputo via Sprinklerforum
%20department%20connection. https://www.youtube.com/watch?v=GOUMQFSTJ6E Bob Caputo, CFPS President American Fire Sprinkler Association -Original Message- From: Sprinklerforum On Behalf Of BRUCE VERHEI via Sprinklerforum Sent: Thursday, October 14, 2021 3:12 PM To: e...@bamfordfire.com

RE: Attic protection over a storage occupancy

2021-10-06 Thread Bob Caputo via Sprinklerforum
. Just my thoughts Bob Caputo Have you visited afsasafetyportal.com yet? It's AFSA's member-only safety resource! This virtual library delivers the accident-prevention and safety-related information you need to educate your staff, help prevent claims, and create a safe work environment. Click here

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Bob Caputo via Sprinklerforum
NFPA 20 is clear that the pump room is to be protected per EH2. By definition of EH2, the presence of the diesel fuel makes it EH2. See 4.14.1.3 Bob Caputo, CFPS President American Fire Sprinkler Association -Original Message- From: Sprinklerforum On Behalf Of James Crawford via

RE: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread Bob Caputo via Sprinklerforum
Not to mention it’s a horrible practice in my opinion Bob Caputo, President American Fire Sprinkler Association -Original Message- From: Prahl, Craig/GVL Sent: Thursday, August 19, 2021 5:07 PM To: Bob Caputo ; sprinklerforum@lists.firesprinkler.org Cc: John Denhardt Subject: RE

RE: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread Bob Caputo via Sprinklerforum
position of the AFSA, and/or NFPA or its technical committees. AFSA cannot provide design or consulting engineering services, and this opinion should therefore not be considered, nor relied upon, as such. Bob Caputo, President American Fire Sprinkler Association -Original Message

RE: Material Prices !!

2021-08-05 Thread Bob Caputo via Sprinklerforum
you for your understanding. Bob Caputo, CFPS President American Fire Sprinkler Association Get in the (Fitter) Zone! AFSA's "Fitter Zone" features live webinars designed specifically for fire sprinkler fitters. These live presentations are held on Saturdays whenever possible, so you

Re: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
with a forklift so…. Bob Caputo - Sent from my iPhone > On Jul 1, 2021, at 2:52 PM, BRUCE VERHEI via Sprinklerforum > wrote: > > From an old fire guys perspective I’d be more concerned with accidental head > breakage than water dispersal. > > Best. > > >> On 0

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
Pete, You are correct. Where the closet is less than 400 ft3, no clearance is required below the deflector Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To: sprinklerforum

RE: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-05-19 Thread Bob Caputo via Sprinklerforum
considered the opinion of AFSA, NFPA or any technical committee upon which I serve. (13/25/24/291) Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Mark.Phelps via Sprinklerforum Sent: Friday, April 23, 2021 11:47 PM To: sprinklerforum@lists.firesprinkler.org Cc: Mark.Phelps S

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Bob Caputo via Sprinklerforum
 On Fri, May 7, 2021 at 11:23 AM Michael Hill via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > There goes my logic, right out the window..again. > > Mike Hill > > -Original Message- > From: Sprinklerforum On > Behalf Of Bob Caput

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Bob Caputo via Sprinklerforum
evation pressure, or do I need to > design and calc as though the tank is nearly depleted? > > -Kyle M > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/

Re: Hydrant barrel loss

2021-04-26 Thread Bob Caputo via Sprinklerforum
Sincerely you’re measuring the flow and pressure at the hydrant in the first place, why would you need to know that? Just curious... Reverse engineering the water supply in the water main below? On Mon, Apr 26, 2021 at 3:57 PM Steve Leyton via Sprinklerforum <

Re: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-04-23 Thread Bob Caputo via Sprinklerforum
move water and add pressure, they can’t add water. Again, just my 2 cents wort…. Not be be considered the opinion of NFPA, AFSA or any technical committee nor the formal opinion of the NFPA 13, 24, 291 or 25 committees. Bob Caputo, CFPS President American Fire Sprinkler Association

Re: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-04-23 Thread Bob Caputo via Sprinklerforum
, and they bring a pump in the engine when they show up - so its more likely you’d need to add a water storage tank if fire flow is the concern. Fire flow is not a NFPA 13 issue but section 11.1.5.3 is. Just adding my 2 cents... Bob Caputo, CFPS President American Fire Sprinkler Association p

Re: Old sprinklers

2021-04-08 Thread Bob Caputo via Sprinklerforum
This may have been approved by the local AHJ, which would be the appropriate assumption based on NFPA 25. We are not doing a design analysis. On Thu, Apr 8, 2021 at 9:34 AM Dale Wingard via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Sounds like the intent was to protect

Re: Different Levels of protection open to each other in the same hazard

2021-03-19 Thread Bob Caputo via Sprinklerforum
! Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org <http://firesprinkler.org/> <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https://www

Re: Different Levels of protection open to each other in the same hazard

2021-03-19 Thread Bob Caputo via Sprinklerforum
and the opinion of the writer and may not be considered a formal interpretation of the standard, may not express the opinion of NFPA or its technical committees. Bob Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org <h

Re: Question about a drop pipe size

2021-03-18 Thread Bob Caputo via Sprinklerforum
of NFPA or its technical committees. Best regards, Bob Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org <http://firesprinkler.org/> <https://www.facebook.com/firesprinkler.org/> <https://twitter.

Re: leaving abandoned sprinkler piping in place

2021-03-17 Thread Bob Caputo via Sprinklerforum
NFPA 13, 2019 edition actually addresses this in section 29.2 Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org <http://firesprinkler.org/> <https://www.facebook.com/firesprinkler.org/> <https://t

Re: Fire Retardant Coating used in Combustible concealed spaces

2021-02-10 Thread Bob Caputo via Sprinklerforum
sued over my response - so I know this answer really well Bob Caputo On Wed, Feb 10, 2021 at 11:44 AM tstone52--- via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Project is a 100 year old 6 story Steel & Concrete Hotel building. The roof > is steel fram

Re: Distilled Spirits

2021-02-03 Thread Bob Caputo via Sprinklerforum
FM Global has a standard for this specifically. I recommend downloading it from their website. Great information that might provide guidance for you. Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org <h

Re: schedule 7 pipe?

2021-01-20 Thread Bob Caputo via Sprinklerforum
in the “damned” area regardless of pitch of pipe or the rating of the gasket used with the coupling (in dry pipe or reaction systems). Bob Caputo > On Jan 20, 2021, at 1:07 PM, Jeff Normand via Sprinklerforum > wrote: > > I have been designing with sch 7 pipe for over 25 yea

Re: Merry Christmas,

2020-12-25 Thread Bob Caputo via Sprinklerforum
Thank youSame to you and yours On Fri, Dec 25, 2020 at 10:38 AM Mario Berrios via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Merry Christmas, > mario berrios > ___ > Sprinklerforum mailing list >

Re: potential freezing in ESFR system

2020-12-22 Thread Bob Caputo via Sprinklerforum
. Just my opinion - and is not intended to represent the opinion of AFSA, NFPA or any NFPA Committee Bob Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org <http://firesprinkler.org/> <https://www.fac

RE: FIRE PUMP: Urgent

2010-04-12 Thread Bob Caputo
represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide consultation or services. Bob Caputo -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: FIRE PUMP: Urgent

2010-04-12 Thread Bob Caputo
to make it more safe.? any thoughts? Regards Sam On Mon, Apr 12, 2010 at 10:44 AM, Bob Caputo bcap...@cox.net wrote: Since your pump is not listed, you don't comply with NFPA 20 so why does it matter if the standard allows an automatic shut off? For your use, the 2010 edition of NFPA

RE: NFPA 25 QUALIFICATIONS FOR WORKING ON FIRE PUMP

2010-04-07 Thread Bob Caputo
are intended to provide a precautionary advisory that we shouldn't stick our mitts into stuff we don't really know enough about, lest we be severely injured or killed Have a nice day. Bob Caputo Oh, yeah - the opinion stated above is a personal opinion which may not be considered

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
to the requirements of the local AHJ in each case where sprinklers are used in lieu of rated glass? Please know I am not looking to argue - just looking to be clear or to verify that I've misunderstood this code allowance for years. Best regards, Bob Caputo, CFPS, CET 657 Cantara Lane, Vista, CA 92081

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
Thom, I'm hopeful Mr. Izzo will shed more light on this for us... it's not a NFPA 13 allowance - it's a building code issue and my expertise is limited to scuba diving. Bob Caputo, CFPS, CET SSI Master Diver Certified I doubt you could be Wong. -Original Message- From

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
cannot sell!! Best Regards, Salvatore J. Izzo, P.E. SFPE Manager - Reliable Technical Services From: sprinklerforum-boun...@firesprinkler.org [sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo [bcap...@cox.net] Sent: Monday, March 08, 2010 4:11

RE: Epoxy hanger point?

2010-03-05 Thread Bob Caputo
Hilti has an epoxy hanger listed but you have to drill the holes 1st so you may as use the post installed anchors. Let us know which brands will have the concrete dust so we can eat something else... bc -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: 2 Buildings with 1 AS Riser

2010-02-16 Thread Bob Caputo
or services. Best regards, Bob Caputo -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Haji, Jaber M Sent: Tuesday, February 16, 2010 6:33 AM To: sprinklerforum@firesprinkler.org Subject: 2 Buildings with 1 AS Riser

RE: CPVC and Nail plates

2010-02-15 Thread Bob Caputo
It's not an NFPA requirement - it's a Building Code requirement - specifically in the IRC bc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Forest Wilson Sent: Monday, February 15, 2010 3:47 PM To:

RE: CPVC and Nail plates

2010-02-15 Thread Bob Caputo
Geo, We struggled with this on a project some years ago after a drywall contractor shot a nail through the 3 x 5 plate we'd installed causing considerable water damage to his dry wall. Of course he then tried to blame us for not using a thick enough plate... turned out he had a legit argument

RE: Accidental Fusing

2010-02-05 Thread Bob Caputo
. Bob Caputo, CFPS, CET 657 Cantara Lane, Vista, CA 92081 Fire Life safety America Company 3017 Vernon Rd., Richmond, VA 23228 Mobile: 804-263-1577 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Sent

RE: How the Heck Did You Come Up With 0.58 over 2000?

2010-01-27 Thread Bob Caputo
Beginning with the 2007 edition of NFPA 13, section 24.6 requires a General Information Sign on the riser so that all of these design considerations are posted for future use. The annex includes a sample of the sign but the data required meets what you're asking for... bc -Original

Occupancy

2010-01-21 Thread Bob Caputo
or an engineer of record - not the contractor. (again - just stating my opinion) Bob Caputo, CFPS, CET 657 Cantara Lane - Vista, CA 92081 Fire Life Safety America Company 3017 Vernon Rd - Richmond, VA 23228 Office: (804) 222-1381 Cell: (804) 263-1577

RE: Occupancy

2010-01-21 Thread Bob Caputo
://www.ch2m.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo Sent: Thursday, January 21, 2010 3:44 PM To: sprinklerforum@firesprinkler.org Subject: Occupancy In my opinion, the question isn't directly

RE: identification of antifreeze loops

2010-01-21 Thread Bob Caputo
an answer today. Bob Caputo, CFPS, CET 657 Cantara Lane - Vista, CA 92081 Fire Life Safety America Company 3017 Vernon Rd - Richmond, VA 23228 Office: (804) 222-1381 Cell: (804) 263-1577 -Original Message- From: sprinklerforum-boun

RE: tri seal gaskets

2009-12-08 Thread Bob Caputo
Other than NFPA 13, section 6.5.3.3 Grooved fittings, including gaskets used on dry-pipe, preaction, and deluge systems, shall be listed for dry pipe service ? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf

RE: Fire Pump Alternate Power

2009-08-20 Thread Bob Caputo personal
reliable or unless there are other considerations for the requirement. Have I missed your point? Bob Caputo, CFPS 657 Cantara Lane - Vista, CA 92081 Fire Life Safety America Company 3017 Vernon Rd - Richmond, VA 23228 Office: (804) 222-1381 Cell: (804) 263-1577

RE: Southwest Airlines FALSE advertisement

2009-03-23 Thread Bob Caputo
commercials - those are all true. Bob Caputo, CFPS VP National Accounts Fire Life Safety America -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Monday, March 23, 2009 12:37 PM