100
>
> 1150 #1 Evergreen Rd
>
> Redway, CA 95560
>
> www.greenwired.com
>
> [image: Description: signature]
>
>
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> ] *On Behalf Of *
> palumbo1...@gmail.com
> *Sent:* Thursday
lf Of *palumbo1...@gmail.com
*Sent:* Thursday, September 05, 2019 7:48 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Large off-grid inverter/storage
Is “25 Kw per hour” a real value? For us old school people there is kW
and they is kWh (kilowatt hours). I’m guessing that it is 25 kWh per
av
Hi Andrew,
Any phrase that includes “per hour” while describing power use, generation or
storage in a RE system is probably a misnomer. Think about it: you could just
as well say 25kW per second or per month. That’s because kW is a term that
describes a rate or power, not a quantity of energy u
-wrenches
Subject: Re: [RE-wrenches] Large off-grid inverter/storage
Is “25 Kw per hour” a real value? For us old school people there is kW and they
is kWh (kilowatt hours). I’m guessing that it is 25 kWh per average day, or,
about 750 KWh / month.
Dave Palumbo
Hyde Park, VT
Sent from my iPhone
s ON BEHALF OF Andrew
SENT:
Thursday, September 05, 2019 3:15 PM
TO: RE-wrenches
SUBJECT:
[RE-wrenches] Large off-grid inverter/storage
Hey Everyone,
I have
been recently been getting more and more inquiries for some quite large
off-grid sytems(25kw per hour) and seeing what you guys have for
PV # 028374
>>
>> NABCEP # 051112-136 www.solarwork.com
>> <http://www.solarwork.com/>
>> "Responsible Technologies for Responsible People since 1988"
>>
>> P Please consider the environment before printing this email.
>>
Please consider the environment before printing this email.
>
>
>
>
>
> *From:* RE-wrenches *On
> Behalf Of *Andrew
> *Sent:* Thursday, September 05, 2019 3:15 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Large off-grid inverter/storage
>
>
>
> Hey Everyo
Is “25 Kw per hour” a real value? For us old school people there is kW and they
is kWh (kilowatt hours). I’m guessing that it is 25 kWh per average day, or,
about 750 KWh / month.
Dave Palumbo
Hyde Park, VT
Sent from my iPhone
> On Sep 5, 2019, at 5:15 PM, Andrew wrote:
>
> Hey Everyone,
>
"
P Please consider the
environment before printing this email.
FROM: RE-wrenches ON BEHALF OF
Andrew
SENT: Thursday, September 05, 2019 3:15 PM
TO: RE-wrenches
SUBJECT:
[RE-wrenches] Large off-grid inverter/storage
Hey Everyone,
I have
been recently been getting more and more inquiri
quot;Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email.
From: RE-wrenches On Behalf Of
Andrew
Sent: Thursday, September 05, 2019 3:15 PM
To: RE-wrenches
Subject: [RE-wrenches] Large off-grid inverter/storage
Hey Everyone,
I have been recently been getting more and more inquiries
for some quite large off-grid sytems(25kw per hour) and seeing what you guys
have for suggestions on bigger inverters and storage systems? I could do 2
triple stack Schneider's and a bunch of HUPS industrial b
gt; new technology, but I instinctively avoid parallel battery strings.
>>
>>
>>
>> William Miller
>>
>>
>>
>>
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>&g
to energy
consuming devices." W. Miller
FROM: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org [6]] ON BEHALF OF Lou
Russo
SENT: Saturday, July 20, 2019 1:50 PM
TO: RE-wrenches
SUBJECT: Re:
[RE-wrenches] Large Off-Grid Residential System
Blue Ion 2.0 with Outback
or SMA. W
tallations. My customers are asking for
>> new technology, but I instinctively avoid parallel battery strings.
>>
>>
>>
>> William Miller
>>
>>
>>
>>
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 934
t;
>
>
> William Miller
>
>
>
>
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
> Quote of the month: “As they age, batteries transition from energ
www.millersolar.com
>
> CA Lic. 773985
>
>
>
> Quote of the month: “As they age, batteries transition from energy
>
> storage devices to energy consuming devices.“ W. Miller
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>
s-boun...@lists.re-wrenches.org] *On
Behalf Of *Lou Russo
*Sent:* Saturday, July 20, 2019 1:50 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Large Off-Grid Residential System
Blue Ion 2.0 with Outback or SMA. Works every time.
Blue Planet's tech support is great, the warranty is even bette
I was just reminded that exeltech can do up to 125kw.
Jay
> On Jul 21, 2019, at 3:05 AM, Tump wrote:
>
> Victron has the Quattro 10kW inverters w/ 100A pass thru and they have a good
> battery management for their Li battery line. They have also started to have
> their products UL lis
Victron has the Quattro 10kW inverters w/ 100A pass thru and they have a good
battery management for their Li battery line. They have also started to have
their products UL listed. GOOD robust product and good support. Allen formerly
of Magnum is cc ed here.
Up to 6 Quattro units can operate in
The other 2 that I can think of are Pika (not sure they can parallel stack) and
Princeton energy for an all in one unit.
Yea so far Schneider can only do 4 x 6800w single phase.
Jay
> On Jul 20, 2019, at 2:13 PM, Mac Lewis wrote:
>
> I think Outback is the only major inverter manufacturer
Si senor. 7 kW surge.
On Saturday, July 20, 2019, Jay wrote:
> Hi Marco,
>
> Is the max surge 7kw, which is what is listed on line?
>
> Jay
> Peltz Power
>
> On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf
> wrote:
>
> Seven to eight Tesla Powerwalls will get you that assuming that the
> service
I think Outback is the only major inverter manufacturer that can do split
phase 120/240 to that size. You have to go 3 phase for 36 kW continuous
capacity with either Schneider or SMA.
Good luck, sounds like a fun system to design.
On Sat, Jul 20, 2019 at 2:50 PM Lou Russo wrote:
> Blue Ion 2.
Blue Ion 2.0 with Outback or SMA. Works every time.
Blue Planet's tech support is great, the warranty is even better.
Aloha,
Lou Russo
l...@spreesolarsystems.com
808 345 6762
Spree Solar Systems LLC
CT-34322
On Sat, Jul 20, 2019 at 10:36 AM Jay wrote:
> Hi Marco,
>
> Is the max surge 7kw, wh
I would look to Iron-Edison as they build systems up to this size using
LiFe PO
On Fri, Jul 19, 2019, 4:24 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> What are current popular options for battery based systems in the 100kWh
> range? Preferably Lithium.
>
> Also, what inverte
Hi Marco,
Is the max surge 7kw, which is what is listed on line?
Jay
Peltz Power
> On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf wrote:
>
> Seven to eight Tesla Powerwalls will get you that assuming that the service
> entrance is no bigger than 200A.
>
> marco
>
>> On Friday, July 19, 201
Mangelsdorf
SENT: Friday, July 19, 2019 6:10 PM
TO: RE-wrenches
SUBJECT:
[RE-wrenches] Large Off-Grid Residential System
Seven to eight Tesla
Powerwalls will get you that assuming that the service entrance is no
bigger than 200A.
marco
On Friday, July 19, 2019, Jason Szumlanski
wrote:
However they are not useable for off-grid, only grid tied, as I understand it.
Glenn
From: RE-wrenches On Behalf Of
Marco Mangelsdorf
Sent: Friday, July 19, 2019 6:10 PM
To: RE-wrenches
Subject: [RE-wrenches] Large Off-Grid Residential System
Seven to eight Tesla Powerwalls will get
Seven to eight Tesla Powerwalls will get you that assuming that the service
entrance is no bigger than 200A.
marco
On Friday, July 19, 2019, Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> What are current popular options for battery based systems in the 100kWh
> range? Preferably
Jason
I have seen Outback/Blue ion systems well into this size, personally l have
systems with well into this range, l am to understand that PR has been
going with the Blue Planet Energy Blue Ion with great sucess all over the
size scale.
Jerry
On Fri, Jul 19, 2019, 2:24 PM Jason Szumlanski <
ja..
What are current popular options for battery based systems in the 100kWh
range? Preferably Lithium.
Also, what inverter pairing is suggested with total stacked capacity of
36kW, 120/240V?
This is slightly larger than some of the systems I have worked with
recently. I'm a bit out of the loop, part
Do they know what they are asking for? I'm/sure/ they have filled out a
load sheet? Don't waste your time until they have carefully and
thoughtfully listed ALL their loads. I had someone sure they were going
to be off-grid, had an ENORMOUS list of loads including charging 2
Teslas. Next
ly-23-18 4:29 PM
To: RE-wrenches
Subject: [RE-wrenches] Large off grid
What do you say to the person who wants "200 amp" electrical service from their
off grid system. I generally use Schneider xw+ inverters. Is it even possible
to put 4 or 6 of them together? How many radians can
onday, July 23, 2018 7:28 PM
*Subject:* [RE-wrenches] Large off grid
What do you say to the person who wants "200 amp" electrical
service from their off grid system. I generally use Schneider
xw+ inverters. Is it even possible to put 4 or 6 of them
together? How many rad
enches] Large off grid
What do you say to the person who wants "200 amp" electrical service from their
off grid system. I generally use Schneider xw+ inverters. Is it even possible
to put 4 or 6 of them together? How many radians can be put together? I'm
curious to know how ot
Definitely can stack 6 XW+ 6848's. Plenty of info on the Schneider site.
You can PM me for info on this. --Dave
On Mon, 23 Jul 2018 17:28:46
-0600, Aaron Mandelkorn wrote: What do you say to the person who wants
"200 amp" electrical service from their off grid system. I generally use
Schneide
Mandelkorn
> To: RE-wrenches
> Sent: Monday, July 23, 2018 7:28 PM
> Subject: [RE-wrenches] Large off grid
>
> What do you say to the person who wants "200 amp" electrical service from
> their off grid system. I generally use Schneider xw+ inverters. Is it even
bject: [RE-wrenches] Large off grid
What do you say to the person who wants "200 amp" electrical service from
their off grid system. I generally use Schneider xw+ inverters. Is it even
possible to put 4 or 6 of them together? How many radians can be put together?
I'm curious
What do you say to the person who wants "200 amp" electrical service from
their off grid system. I generally use Schneider xw+ inverters. Is it
even possible to put 4 or 6 of them together? How many radians can be put
together? I'm curious to know how others would proceed or is this to
unreasonab
up of 250 kW synchronized
>> generators that can ramp up/down based on demand. Perhaps similar tech
>> to what Tesla is doing in Australia.
>>
>> Kevin
>>
>>
>> -Original Message-
>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenche
There are many large 250kw to multi mw battery based inverters that should
cover this project.
Most are coming out of china, so I don’t know if UL is something they have.
Princeton is one here in the USA, looks like 250kw and 500kwh is their largest
on the web site.
Sun Grow is one of many out
nt: April-25-18 12:37 PM
To: RE-wrenches
Subject: [RE-wrenches] Large Off Grid Inverter?
Greetings Fellow Wrenches;
We are consulting on a power system for a large off grid facility that is
currently operating on a 1500 kW gen set. The loads are enormous for normal
off grid: in the neighborh
t; generators that can ramp up/down based on demand. Perhaps similar tech to
> what Tesla is doing in Australia.
>
> Kevin
>
>
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Ray
> Sent: April-25-18 12:
Try a three phase soft starter. Programmable start ramp time with relay
bypass. Not as expensive as a full blown VFD.
Frank BZP.
On 4/26/2018 9:17 AM, Dave Angelini Offgrid Solar wrote:
Agree with Daryl here at the end. You have to solve the motor surge with
variable frequency drive and go 3
Sent: April-25-18 12:37 PM
To: RE-wrenches
Subject: [RE-wrenches] Large Off Grid Inverter?
Greetings Fellow Wrenches;
We are consulting on a power system for a large off grid facility that is
currently operating on a 1500 kW gen set. The loads are enormous for normal
off grid: in the neighborho
A tough assignment, but Daryl has the right idea.
A company I used to work for did large off grid systems and would use something
they called a rotary capacitor (or something like that). It was a large
induction motor paralleled into the grid. It had a DC pony motor and some
synchro hardware/s
We're not too worried about reducing the surge at this point; the
existing soft start controller is currently programmed for a fast start,
because their electrician was worried about motor damage if the
controller was set to limit current. It is currently surging to 700% of
run current, so we
Agree with Daryl here at the end. You have to solve the motor surge with
variable frequency drive and go 3 phase. If there is a reasonable cost to
use the grid I would not even bother with quoting an off the grid
solution. It is what the grid is best at and batteries are the wrong way
for this.
Da
you have a problem that is much bigger than I work on. But on a large
motor heavy starting loads problem, we used an extra capacitor on the DC
bus of the frequency drive. the drive on its own greatly reduced the start
surge, if the load can be started slowly. If the motor must ramp up
quickly t
Greetings Fellow Wrenches;
We are consulting on a power system for a large off grid facility that
is currently operating on a 1500 kW gen set. The loads are enormous for
normal off grid: in the neighborhood of 600 amps continuous at 480 v 3
phase. Surges are close to 2000 amps, but we are wo
Yes... and we finally get the second AC input we have wanted for so long... the
price? $13,000.00... wow
Todd
On Friday, August 19, 2011 2:35pm, "Jeff Oldham" said:
Yes it does!
From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative
SOLutions
__
Yes it does!
>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative
>SOLutions
57-Year-Old Mom Looks 25
Mom Reveals $5 Wrinkle Trick That Has Angered Doctors!
http://thirdpartyoffers.juno.com/TGL3131/4e4ed78245a3e77
Jeff:
Will it do generator support?
William Miller
At 02:23 PM 8/19/2011, you wrote:
The new Outback Radian GS8048 (aptly nicknamed "The Beast") is one
extremely impressive inverter! I've been beta testing one on a customer's
system for a couple of months and it is a beast alright! Howeve
The new Outback Radian GS8048 (aptly nicknamed "The Beast") is one extremely
impressive inverter! I've been beta testing one on a customer's system for a
couple of months and it is a beast alright! However, it will not do 3 phase at
this time. It has 2) 4kW 120/240V modules in it, if one fails t
for off grid use when the power goes down. Each inverter
> CAN drive its own AC branch load
> though.
>
> boB
>
>
>
>
>
>
>> *From:* Darryl Thayer
>> *To:* RE-wrenches
>> *Cc:* Julie Haugh
>> *Sent:* Monday, August 15, 2011 10:43 AM
>>
hayer
*To:* RE-wrenches
*Cc:* Julie Haugh
*Sent:* Monday, August 15, 2011 10:43 AM
*Subject:* Re: [RE-wrenches] Large, off grid
Another method is to use the 120 volt VFX 3648, with one master and 14
slaves. (15 total, 5 in paralled on each leg) Check this with Outback
as the 3 phase is differen
: Re: [RE-wrenches] Large, off grid
Hi Daryl,
You might look at the new Outback 8kw 120/240v
I know that you can connect up to 10 in parallel, i don't know if you can do
it 3 phase however.
jay
peltz power
On Aug 12, 2011, at 8:42 AM, penobscotso...@midmaine.com wrote:
> Hello
-wrenches] Large, off grid
Hi Daryl,
You might look at the new Outback 8kw 120/240v
I know that you can connect up to 10 in parallel, i don't know if you can do
it 3 phase however.
jay
peltz power
On Aug 12, 2011, at 8:42 AM, penobscotso...@midmaine.com wrote:
> Hello wrenches
Hi Daryl,
You might look at the new Outback 8kw 120/240v
I know that you can connect up to 10 in parallel, i don't know if you can do
it 3 phase however.
jay
peltz power
On Aug 12, 2011, at 8:42 AM, penobscotso...@midmaine.com wrote:
> Hello wrenches,
> We have an opportunity to ins
SMA Multi-Cluster Box, 3-phase up to 60kW using Sunny Islands
http://www.grosolar.com/documents/doc_details/294-smacluster-spec-sheet.html
On Fri, Aug 12, 2011 at 8:42 AM, wrote:
> Hello wrenches,
> We have an opportunity to install a very large (60 kw) off grid system
> in Mexico. It is cur
Darryl,
Exeltech makes 60 kW three-phase off-grid inverters.
Contact me off-list.
Dan
Sr. Engineer
Exeltech
--- On Fri, 8/12/11, penobscotso...@midmaine.com
wrote:
> From: penobscotso...@midmaine.com
> Subject: [RE-wrenches] Large, off grid
> To: "RE-wrenches"
> D
Hello wrenches,
We have an opportunity to install a very large (60 kw) off grid system
in Mexico. It is currently three phase. I do have the option of
changing out the air conditioners (36 of them) to 120 single phase, but
it is an added layer of complexity/cost that it would be nice to avoid.
61 matches
Mail list logo