Re: Leakage current test conundrum
Hi Charles: a) Does anyone one know the genesis of the requirement to lift the Neutral AND the Ground simultaneously during a leakage current test?? (I am referring to UL6500) While I am not familiar with UL 6500 per se, I believe I can comment on the lift of the neutral. In times past, non-polarized products used a single-pole power switch. Since the products were non-polarized, the single-pole power switch could be in the neutral rather than in the phase conductor. When the switch is in the neutral and is open, the leakage current essentially doubles compared to the value when the switch is closed (assuming the switch is ahead of the line filter). (Draw the circuit and you can readily see why the leakage current doubles.) Certainly, leakage current should be measured (and controlled) for both the ON and OFF positions of a power switch, especially a single-pole power switch. b) What human body model is appropriate for UL6500? Can I use the one in UL1950?? Since you are referencing UL standards, the correct measuring circuit (i.e, human model) is the ANSI circuit (C39.5?). In practice, just use an ordinary ammeter. This will give you a slightly (~5%) pessimistic measurement. So, unless you are very close to the leakage current limit, you need not use the humand body model for leakage current measurements. For more details on both these questions, see my article in the Product Safety Newsletter, Volume 7, Number 1, January-February 1994. You can download a pdf version of this PSN: http://www.ewh.ieee.org/soc/emcs/pstc/psn/ The file name is: 94v07n1.pdf Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Methenamine timed burning tablet
Some fire tests use a methenamine timed burning tablet. This tablet is specified in USA government standards for furniture flammablity testing. (See 16 CFR Part 1630.4 or CPSC standard FF 1-70.) It is also specified in ASTM D2859. I have also seen it used to test fire enclosures in Europe. Until February of this year, Eli Lilly supplied this tablet as Catalog No. 1588. In February, 2002, Eli Lilly discontinued the tablet. According to Eli Lilly, no other US manufacturer has picked up this tablet; they did not know if a Euro manufacturer was making the tablet. I am looking for a source for this methenamine tablet. If you can provide some pointers, I would appreciate it. Thanks, and best regards from San Diego, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
minimum distance for PWB inner layers (was creepage)
Hi Tom: In 60950, applicable clauses are 2.10.5.3 and 2.10.5.1 (I'm not reading genuine IEC/EN 60950, and I'm sorry if I'm wrong) - the former states that distance through insulation would be applied in such situation, and the latter set minimum thickness of 0.4mm for supplementary and reinforced insulation for peak working voltage greater than 71V. Agree. However, I think applying minimum distance for pollution degree 1 or that for coated PCBs (clause 2.10.6) for inner layers when designing PCBs are not bad idea, although both of them wouldn't be applied here. The latter set, for example, minimum distance of 1.2mm for reinforced insulation for working volgage up to 250V on coated PCBs. Anyone may, of course, use any distance through insulation that he chooses, provided the distance is at least 0.4 mm. However, I would caution against rationalizing the distance for conductors on inner layers of printed wiring boards by applying criteria that are not in any way applicable to the construction. These requirements (for creepage distances based on pollution degree and for coated printed wiring boards) are based on reasonable principles of engineering and physics. Requirements for pollution degree 1 creepage distances apply to the interface between solid insulation and air insulation, not to inner layers of multilayer boards where creepage does not exist. The inner layer conductors of an ideal multilayer board are imbedded in solid insulation. The requirements for creepage distances presume a long-term accumulation of pollution, which does not occur to the inner layers of a multilayer PWB. Likewise, requirements for coated printed wiring boards apply to coated PWBs, not to inner layers of multilayer boards. Thin coatings are not of uniform thickness, and bend around the surface conductors, both of which contribute to highly localized voltage stresses on the coating. The requirements for coatings account for these localized stresses, which do not occur to the inner layers of a multilayer PWB. Rationalizing larger distances by applying these requirements to inner layers of PWBs is contrary to the basis of the requirements. Such rationalization generates confusion among designers and among fellow safety professionals. Indeed, this thread originated because of just such a confusion! If the belief is that the 0.4 mm distance is too small for inner layers of PWBs, then a greater distance should be specified. But, please don't rationalize the larger dimension by applying inapplicable requirements. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Creepage on PCB Internal Layers
Hi Chris: To me, it's sort of funny in that it just says that the Creepage and Clearance distances do not apply on inner layers of void free PCBs. That's nice; but I can't find where a distance is specified. I mean, I would think that there should be some minimum distance between an AC line and a 5V SELV line on an inner layer of the board Our layout guy has a military specification that specifies insulation for 300-500V circuits. It specifies .100 on external layers and .010 on internal layers...which would work out to a factor of 10 reduction between surface layers and inner layers Ideally, the conductors of inner layers of printed wiring boards are imbedded in void-free solid insulation. For Basic Insulation, there are no requirements for distance through solid insulation. For Supplementary Insulation, IEC 60950 and maybe other standards specify a minimum distance of 0.4 mm (regardless of voltage) through the solid insulation. The principal property of any insulation is that of electric strength. Electric strength is the maximum volts per unit distance at which the insulation will not fail (break down). The electric strength of solid insulations are typically at least two orders of magnitude greater than that of air insulation. Consequently, the distance between conductors of inner layers of a printed wiring board can be quite close together compared to those conductors on the surface of the printed wiring board. One theory of solid insulation failure is that of partial discharge in air-filled voids. The problem of thin solid insulation is that the volts per unit distance can be quite high. Recall that an electric field exists between any two conductors. The electric field is defined by a set of equipotential lines within the solid insulation. The thinner the insulation, the closer the equipotential lines. Air breaks down when the absolute potential exceeds about 300 V rms AND the potential per unit distance exceeds about 1500 V rms/mm. So, if the voltage across an insulator exceeds 300 V rms, and the equipotential lines are closer than 1500 V/mm, then partial discharge can occur in a void in solid insulation. If the partial discharge is allowed to continue, then the air in the void will break down (arc). The heat of the arc will decompose the insulating material, resulting in a carbon path through the void. This effectively shorts out a part of the solid insulation. The equipotential lines are re-distributed, and the remaining solid insulation has a higher V/mm, at least near the void. The higher V/mm can cause other voids to partial discharge and arc. We then have a cascading effect, with the end-result being a carbon path through the solid insulation. (I've assumed the insulating material is organic; inorganic materials don't necessarily have this same failure mechanism, which is why many high- voltage insulators are porcelain.) Best regards, Rich From owner-emc-p...@majordomo.ieee.org Tue Aug 13 15:44:23 PDT 2002 Received: from sanrel1.sdd.hp.com (sanrel1.sdd.hp.com [15.80.36.45]) by hpsdlfsa.sdd.hp.com (8.9.3 (PHNE_18546)/8.9.3 SMKit7.02 sdd epg) with ESMTP id PAA15457 for ri...@hpsdlfsa.sdd.hp.com; Tue, 13 Aug 2002 15:44:23 -0700 (PDT) Received: by sanrel1.sdd.hp.com (Postfix) id D45139490; Tue, 13 Aug 2002 15:44:22 -0700 (PDT) Received: from localhost.sdd.hp.com (unknown [127.0.0.1]) by sanrel1.sdd.hp.com (Postfix) with SMTP id 7FD9F94A5 for ri...@sdd.hp.com; Tue, 13 Aug 2002 15:44:19 -0700 (PDT) Received: from ruebert.ieee.org (ruebert.ieee.org [140.98.193.10]) by sanrel1.sdd.hp.com (Postfix) with ESMTP id D4BD3949F for ri...@sdd.hp.com; Tue, 13 Aug 2002 15:44:17 -0700 (PDT) Received: (from daemon@localhost) by ruebert.ieee.org (Switch-2.1.0/Switch-2.1.0) id g7DK9no01090 for emc-pstc-resent; Tue, 13 Aug 2002 16:09:49 -0400 (EDT) From: j...@aol.com Message-ID: 15f.12358e09.2a8ac...@aol.com Date: Tue, 13 Aug 2002 16:09:32 EDT Subject: Re: Creepage on PCB Internal Layers To: chris.maxw...@nettest.com, richard.pa...@exgate.tek.com, emc-p...@majordomo.ieee.org MIME-Version: 1.0 Content-Type: multipart/alternative; boundary=part1_15f.12358e09.2a8ac17c_boundary X-Mailer: AOL 7.0 for Windows US sub 10503 Sender: owner-emc-p...@majordomo.ieee.org Precedence: bulk Reply-To: j...@aol.com X-Resent-To: Multiple Recipients emc-p...@majordomo.ieee.org X-Listname: emc-pstc X-Info: Help requests to emc-pstc-requ...@majordomo.ieee.org X-Info: [Un]Subscribe requests to majord...@majordomo.ieee.org X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org --part1_15f.12358e09.2a8ac17c_boundary Content-Type: text/plain; charset=US-ASCII Content-Transfer-Encoding: 7bit In a message dated 8/13/2002, you write: To me, it's sort of funny in that it
Re: Creepage on PCB Internal Layers
Hi Chris: To me, it's sort of funny in that it just says that the Creepage and Clearance distances do not apply on inner layers of void free PCBs. That's nice; but I can't find where a distance is specified. I mean, I would think that there should be some minimum distance between an AC line and a 5V SELV line on an inner layer of the board To answer this comment, we need to look at what a creepage is and its role in the scheme of the product. Almost all product constructions employ solid and air insulations, both in parallel and in series, between conductors. We call solid insulation solid insulation. We call air insulation clearance. We call the interface between solid insulation and air insulation creepage. Note that solid insulation and air insulation are truly electrical insulations. Creepage is NOT an insulation. Creepage is not a material. It is simply a surface at which solid and air insulations meet. The surface of solid insulation is subject to deposition of airborne pollution. Typical products provide little or no control of airborne materials to prevent deposition of the polluting material onto the surface of a solid insulating material. Polluting material is a solid, uncontrolled (i.e., not a known insulating) material in parallel with the solid (and air) insulations. The polluting material bridges the solid insulation, and therefore could jeopardize the safety function provided by the solid insulation. When sufficient polluting material accumulates on the surface of the solid insulation, the voltage across the insulator and the pollution causes micro-arcs in the pollution. These micro-arcs are high temperature, and cause thermal decomposition of the surface of the solid insulation. When organic materials decompose, they free up the carbon atoms, leaving a tiny carbon resistor on the surface of the solid insulation. Each tiny carbon resistor is in parallel with the adjacent solid insulation beneath the surface of the solid insulation. So the tiny carbon resistor is shorting out a small part of the surface of the solid insulation. This phenomenon is known as treeing due to the tracking pattern of the carbon path on the solid insulation surface. To account for the effect of pollutants on the surface of organic solid insulations, we require the creepage distance to be larger than the air distance (clearance). Because some materials are more resistant to tracking across the surface, the creepage distance is a function of the relative tracking index characteristic of the insulation. Where a solid insulation is not subject to pollution, there is no requirement for a creepage distance. Many standards specify that a hermetically sealed assembly is not subject to creepage distance requirements. Likewise, the inner layer of a multi-layer printed wiring board is not subject to pollution and therefore is not subject to creepage distance requirements. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Marking Languages for Canada
Hi Kris: The markings on the power supply are: (also as per UL file) Date code model number electrical ratings Class 2 transformer The additional markings are: CAUTION, Risk of electric shock and Dry location use only and Do not expose to liquid, vapor, or rain As I said before: only in english, not in french, but approved for: - UL1310, 4th ed. 1994 , including revisions through April 4th, 2000 and - CAN CSA C22.2. No. 223 by UL and having the C UL US logo. As I understand from some people: I am allowed to import my product with this power supply in the US but not in Canada. Is this interpretation still correct? If YES, I'm probably one of the many mftr's in this nice situation. Having checked the Official Languages Act, Consumer Packaging and Labelling Act, Consumer Packaging and Labelling Regulations, Standards Council of Canada, I have concluded that the language requirement is imposed by CSA in their the standard, CAN CSA C22.2 No. 223. As near as I can tell, none of the above references requires a product warning be marked in both official languages. (However, the product identifier must be marked in both French and English, at least on the packaging.) Based on the information so far, my guess is that UL overlooked the language requirement of 223. Having said that, Kris asks about importation into Canada. The cUL mark qualifies the product for importation. The fact that UL *may* have made an error in evaluating the power supply against the standard does not negate the requirement that the unit be certified. All we can say is that an error *may* have been done in the evaluation. I don't believe the issue is importation, but connection to the public power network. The local hydro authorities are the folks who require safety certification of electrical equipment. I'm not sure that the hydro authorities have control over Canadian customs for inspection of cert marks. I know that not all electrical equipment is required to be safety certified. If you are looking for advice as to what action you should take... I would notify the power supply manufacturer that UL *may* have made an error in that 233 requires warning markings be in both French and English. I would ask them to verify that with UL, and take any corrective action that may come from such an inquiry. In the meantime, I would import the units into Canada as the units do have the correct safety certification mark. I feel it is important to separate the issues so that they can be dealt with. I would not self- impose a no-import position based on our/your reading of the requirements. If you were not familiar with the language rules, and only familiar with the certification rules, then the unit is certified and is acceptable in Canada. This is really no different than a constructional error that might exist within the power supply where you could not see it. I suggest you ask the question of your supplier, and load the monkey onto his back. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Marking Languages for Canada
Hi Kris: A product from manufacturer X is delivered with a (direct plug-in) power supply from mftr Y to customers in Canada. Regarding the power supply, it is UL approved + UL listed and has the UL marking with C and US. The warning marking on the power supply is only in english. Question: Is it required that the marking is also in french (en francais) when the product is sold in Canada? If YES, is there any reason why the marking is not in both languages if there is an approval for US+Canada? Your question generates a number of questions: 1) Is the warning marking required by the applicable standard, or did the manufacturer voluntarily apply the warning? (We, too, use UL/cUL direct-plug-in power supplies. To my recollection, there are no warnings on our power supplies. So, I question whether or not the warning is required by the standard.) 2) Is the warning marking required by the US standard? If yes, then the warning is for the US and not for Canada. 3) Is the warning marking required by the Canadian standard? If yes, then does the standard require the warning marking to be in French? In my experience with UL, UL requires compliance to the standard. If the standard does not require a specific language, then UL does not require a specific language. If language is a requirement of a national law (and not a standard), then compliance to that law applies to the manufacturer, not to UL. UL does not require compliance to national laws of countries other than the USA. However, when UL is aware of a law that might specify requirements in addition to those in the standard, UL will call this to the attention of the manufacturer, usually by letter. This is a very common UL practice, especially when UL issues a CB Report. The cover letter to the CB Report will often mention that the language of the instruction manual, for example, was not evaluated. The cover letter will state something to the effect that certain countries may require the language of the manual to be the local langauge. (To my knowledge, IEC standards do not specify language except in the very broadest terms, e.g., the language of a warning must be in a language acceptable to country authorities.) Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Compliance Primer
It has been some time since I have had to explain or justify product safety activity to a high-level manager-type. As others have said, it is fraught with difficulties. Success depends on first determining the mindset of the person asking the question. I believe I would first ask a number of questions to find out where the person is coming from, why he is asking, and what his objective is in learning about product safety activity. Then, I would enter into a conversation where there is a lot of back-and- forth so that I could continuously read the person as to what he wants to know. For a business, product safety, EMC, and other regulatory or compliance activity usually represent a cost without a benefit, a cost without an associated income. No wonder management will occasionally inquire as to what happens in the compliance department. There is no income derived or guaranteed from having a set of bumper-stickers on your product. In some cases, those bumper-stickers may comprise a passport for the product, but in themselves, they generate no revenue. Indeed, some organizations can and do get by without the bumper-stickers, but usually not for the long term. Making a product safe, or complying with EMC and other regulatory issues can prevent fines, and can prevent a government-ordered product recall. One management question is: How much money do I spend to prevent a recall? And, does spending that money guarantee no recall? As a general rule, the cost of a recall exceeds the per-unit profit. Its a money-loser. And, even the best of us cannot foresee every product safety event. A product safety recall is almost inevitable at least once in the lifetime of a company. Consultants universally advise that each company should have a product recall plan in place before the recall. I address the question of Why product safety? by stating that a company has a moral (as well as legal) obligation not to injure its customers. Depending on mindset, management may only agree with this principle for major injuries, not for minor injuries (and management decides which injury is major and which is minor). Do I sound pessimistic? Scott raised another issue in that we don't have such things as primers on compliance and similar subjects. Nor do we have papers on more complex subjects (in the field of product safety). Some years ago, we had the Product Safety Newsletter. We used this newsletter as a means for publishing papers on safety topics (although none was published on this subject). With thanks to Jim Bacher, many of the old PSNs are now available for download from: http://www.ewh.ieee.org/soc/emcs/pstc/psn/ While the IEEE EMC society has several publications, the product safety folks have nothing. We need to develop both authors and a publication medium. We have the medium, the mindcruiser web site. While it is not perfect, it is usable. http://ieeepstc.mindcruiser.com/ We intend this web site as an electronic version of the PSN. But, we haven't yet developed a cadre of authors who would post papers to this web. This is an open invitation to post papers of general interest to the product safety, emc, and telecom communities to this web site. We're looking for the equivalent of an editor to oversee this function. Volunteers please contact me or Jim Bacher. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: medical-grade transformers
Hi Ged: In transformers with REINFORCED INSULATION or DOUBLE INSULATION the insulation between 1ary and 2ary windings shalll consist of - - 1 insulation layer having thickness at least 1mm, or - at least 2 insulation layers with total thickness not less than 0.3mm, or - 3 layers provided each combination of 2 layers can withstand the dielectric strenght test for REINFORCED INSULATION Can anyone explain ther rationale behind these requirements ? Thin insulation is presumed to be subject to pin-holes. If 1 layer of insulation, then the insulation must be thick rather than thin, hence 1 mm thickness. We presume no pin-holes in thick insulation, and the insulation comprises reinforced insulation. If 2 layers of thin insulation, then presume a pin-hole in one layer, and that the pin-hole will not overlay a pin-hole in the other layer. If that pin-hole is 0.15 mm, then we know that the air in that pin-hole will at least withstand the mains voltage. Therefore, the construction still has two insulations in series, one being the 0.15 mm air of the pin-hole, the other being the 0.15 mm thick solid insulation. The 2 insulations in series comprise double insulation. If 3 layers of thin insulation, then presume a pin-hole in one layer, and that the pin-hole will not ovelay a pin-hole in the adjacent layer. The remaining 2 layers comprise double insulation. (In IEC 60960, the requirement for 1 layer in a 2-layer system is 0.4 mm thickness.) Best regards, Rich ps: I'm not certain of my explanation for 2 layers. This rationale came from 60950, and I have applied it to 60601. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Bonding Impedance
Hi Ron: Two years ago, Jim Bacher presented my paper, Equipotentiality and Grounding -- Deriviation of Grounding Resistance for Equipment at the IEEE EMC Symposium Product Safety Workshop. This paper is available for download from the IEEE PSTC Mindcruiser web site: http://ieeepstc.mindcruiser.com/ On the left side, click on Infopieces, then Latest postings. Scroll down to the bottom, and click on the title. Then, click on download. This paper discusses the 0.1 ohm value for equipment and how this value performs in terms of prevention of electric shock. You will see that values up to 0.5 ohm will also provide the same degree of protection against electric shock. As for the 25-amp test current, I have no answer for the rationale. We do know that a circuit-breaker will operate for no more than 1 minute at twice rated current. So, for a 15-amp branch circuit, 30 amps would be a rational test current (and is the required current under CSA standards). I have conducted tests that show that the 25-amp test current will not show any flaws or defects in the current path that an ohmmeter will not show. The test will not find a loose connection! And, a short length of #22 AWG wire will pass the test. I believe the 25-amp test is of no value. The high-current circuit path must be visually inspected for robust construction techniques. Wires must be at least 18 AWG. Screwed connections must use lock-washers that provide gas-tight connections between metal parts. Crimp connections must be according to crimp parts manufacturer's instructions. Etc. Best regards, Rich From owner-emc-p...@majordomo.ieee.org Wed Jul 24 16:17:44 PDT 2002 Received: from sanrel1.sdd.hp.com (sanrel1.sdd.hp.com [15.80.36.45]) by hpsdlfsa.sdd.hp.com (8.9.3 (PHNE_18546)/8.9.3 SMKit7.02 sdd epg) with ESMTP id QAA07580 for ri...@hpsdlfsa.sdd.hp.com; Wed, 24 Jul 2002 16:17:44 -0700 (PDT) Received: by sanrel1.sdd.hp.com (Postfix) id EC8DE93DD; Wed, 24 Jul 2002 16:17:44 -0700 (PDT) Received: from localhost.sdd.hp.com (unknown [127.0.0.1]) by sanrel1.sdd.hp.com (Postfix) with SMTP id 5788693F7 for ri...@sdd.hp.com; Wed, 24 Jul 2002 16:17:42 -0700 (PDT) Received: from ruebert.ieee.org (ruebert.ieee.org [140.98.193.10]) by sanrel1.sdd.hp.com (Postfix) with ESMTP id CAC8893DD for ri...@sdd.hp.com; Wed, 24 Jul 2002 16:17:40 -0700 (PDT) Received: (from daemon@localhost) by ruebert.ieee.org (Switch-2.1.0/Switch-2.1.0) id g6OKved25121 for emc-pstc-resent; Wed, 24 Jul 2002 16:57:40 -0400 (EDT) Message-ID: 999f6f1e8eb8d311ac190090277a772608658...@axcs08.cos.agilent.com From: ron_well...@agilent.com To: emc-p...@majordomo.ieee.org Subject: Bonding Impedance Date: Wed, 24 Jul 2002 14:57:33 -0600 MIME-Version: 1.0 X-Mailer: Internet Mail Service (5.5.2653.19) Content-Type: text/plain; charset=iso-8859-1 Sender: owner-emc-p...@majordomo.ieee.org Precedence: bulk Reply-To: ron_well...@agilent.com X-Resent-To: Multiple Recipients emc-p...@majordomo.ieee.org X-Listname: emc-pstc X-Info: Help requests to emc-pstc-requ...@majordomo.ieee.org X-Info: [Un]Subscribe requests to majord...@majordomo.ieee.org X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org Hello all, I recent issue has come up for me regarding why some safety standards specify 100 milliohms as the acceptable impedance for a protective earth ground bonding test. I am curious as to what the rationale is for this specific value and why 25 amps is chosen as the default test current. Regards, +=+ |Ronald R. Wellman|Voice : 408-345-8229 | |Agilent Technologies |FAX : 408-553-2412 | |5301 Stevens Creek Blvd.,|E-Mail: ron_well...@agilent.com| |Mailstop 54L-BB |WWW : http://www.agilent.com | |Santa Clara, California 95052 USA| | +=+ --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and
Admin message: posted advertisement
Today, a message was posted that violates IEEE emc-pstc rules against advertising. Here is our rule: - 5. Blatant or overt advertising of goods or services is not permitted. The listserver is provided as a service by the IEEE, whose policies prohibit anything that might be construed as conflict of interest. Exceptions: a) Short, non-promotional trailers or signature lines for the sole purpose of identifying the sender and the sender's organization. b) Answers to queries about goods or services, where the intent of the answer is to inform, but not promote. (When in doubt, send the questioner a private message.) c) New or used equipment wanted, or used equipment offered for sale (not offered by the manufacturer). d) This guideline is specific to the use of the this listserver, and in no way inhibits individuals from contacting members privately and independently. - This violation has been addressed by the list administrators. Action has been taken. A copy of our rules was sent to you when you subscribed to this listserver. If you want a new copy of our rules, send an e-mail message to: majord...@majordomo.ieee.org and place only the following commands (2 separate lines) in the body of the message: info emc-pstc end If you want to discuss this violation, please contact me or Dave Heald or Ron Pickard or Jim Bacher. Please do not discuss this on the list- server as this is an off-topic topic. Best regards, Rich Richard Nute IEEE emc-pstc co-administrator c/o Hewlett-Packard Company San Diego Tel: 858-655-3329 e-mail: ri...@ieee.org --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Product safety job at Hewlett-Packard San Diego
Hewlett-Packard Company San Diego site is looking for a high-level product safety engineer. The major job function is that of advising product designers on 1) innovative safeguards for new products, and 2) safety certification requirements for new products. The ideal candidate would be capable -- in time -- of taking over the HBSE course support, and would be capable -- in time -- of taking over the technical advisor position to TC 108. Note that I used the word capable; the job may never include these functions. I used this description to give an idea of the term high-level. If you are interested in this job, go to the HP jobs web site: http://www.jobs.hp.com/ Click on search jobs in hp. In the next window, scroll to the bottom and enter: 808093 in the keyword box. This will bring up the job data. At the bottom of this page, click on Safety design engineer. This will bring up the complete job description. If you want to apply, follow the instructions on the web pages. You can also send a resume directly to me. If you want more details on the job, I have a detailed job description I can send you. I urge you to evaluate yourself against this detailed job description before applying. After we review your resume, the next step for qualified candidates will be a phone screen interview. Successful phone screen candidates will be subject to further interviews, probably by a team of HP engineers. Feel free to call or e-mail me about the job. Best regards, Rich Tel: 858-655-3329 e-mail: rich_n...@hp.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: TOUCH CURRENT LIMIT
Hi Xing Weibing: We can read from table 5A of IEC60950:1999: Touch current limit for accessible parts and circuits not connected to protective earth: 0.25 mA question 1 : How does it (0.25mA) come from and what it is based on? For grounded (Class I) equipment for the home, the UL leakage current is 0.5 mA. (This is NOT a 60950 limit.) UL reasoned that if 0.5 mA arises from both real and stray capacitance, then, for double-insulated (Class II) equipment, the current should be one-half of 0.5 mA because the standard requires the same insulation to be applied again (i.e., the second half of double insulation), thus halving the capacitance. Half of the capacitance results in half of the current, therefore 0.25 mA. UL carried this concept from their generic double-insulation standard into IEC 60950. The UL reasoning is faulty because in real life the two capacitances need not be equal. And, this is certainly not the case for reinforced insulation. Furthermore, the current, 0.5 mA, is deemed acceptable in terms of the safe current that can be applied to the body. Therefore, the 0.25 mA limit is not related to the effects of the current on the body, but presumes a product construction comprised of double insulation where each insulation system provides exactly the same capacitance. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
EMC-PSTC now functional
The EMC-PSTC listserver was down from Friday afternoon until today, Monday, late morning (Pacific Daylight Time). If you attempted to post a message during this time, the message was lost. Please re-send. We apologize for the inconvenience. If you have any questions or comments about this outage, please contact me or one of the other administrators off-line. Best regards, Richard Nute Chief Administrator, IEEE emc-pstc listserver Richard Nute Hewlett-Packard Company 16399 West Bernardo Drive San Diego, California 92127-1899 Tel: 858-655-3329 FAX: 858-655-4374 e-mail: ri...@sdd.hp.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Changing our safety standards (was 0.1 uF discharge)
Hi Gert: I also tried the discharge between two fingers, and found the result to be unpleasant at least. Time to change standards... Now we must ask the question: Is the purpose of the standard to prevent injury or to prevent an unpleasant experience? I presume that you would want to adjust the various values of current (in our standards) so that either there is no sensation, or the sensations of the various conditions are the same. If you try the same test with 3.5 mA leakage current, I believe you will also find the result to be unpleasant. Here's another test: Using a 2-wire external power supply with a barrel-type output connector (such as the type power supply used with a laptop computer), rub the metal barrel lightly on the inside of your forearm. I believe you will find this unpleasant. Simply, we cannot eliminate the sensation of electric current -- from an ac voltage source -- through a capacitance. Somewhere, someone will sense the current. We *may* be able to eliminate the sensation of electric current from a charged capacitor by selecting small-value capacitors. But, is that the purpose of our safety standards -- to eliminate sensation of electric current? What should be the body response criterion used in safety standards? Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Changing our safety standards (was 0.1 uF discharge)
Hi Gert: I also tried the discharge between two fingers, and found the result to be unpleasant at least. Time to change standards... Now we must ask the question: Is the purpose of the standard to prevent injury or to prevent an unpleasant experience? I presume that you would want to adjust the various values of current (in our standards) so that either there is no sensation, or the sensations of the various conditions are the same. If you try the same test with 3.5 mA leakage current, I believe you will also find the result to be unpleasant. Here's another test: Using a 2-wire external power supply with a barrel-type output connector (such as the type power supply used with a laptop computer), rub the metal barrel lightly on the inside of your forearm. I believe you will find this unpleasant. Simply, we cannot eliminate the sensation of electric current -- from an ac voltage source -- through a capacitance. Somewhere, someone will sense the current. We *may* be able to eliminate the sensation of electric current from a charged capacitor by selecting small-value capacitors. But, is that the purpose of our safety standards -- to eliminate sensation of electric current? What should be the body response criterion used in safety standards? Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Question: Discharge capacitance 0.1 uF
Hi Tom: So, for voltage up to 450V d.c. (i.e. up to 318V a.c.), capacitor up to 0.1uF will become a Limited Current Circuit, hence the voltage is not Hazardous Voltage (1.2.8.4) - no additional condition would be required for the capacitor connected to the primary circuit. Electric shock (or electrically-stimulated sensation) is a function of BOTH voltage and current. For an electric shock to occur, the source must exceed, say, 30 V rms and 0.5 mA rms. As a general rule, we say that any voltage not exceeding 30 V rms is not hazardous, regardless of current. We identify this voltage as ELV or SELV. Likewise, we say that any current not exceeding 0.5 mA rms is not hazardous, regardless of voltage. We identify this current as Limited Current. Furthermore, Limited Current addresses capacitors charged to voltages exceeding 42.4 V dc. In this case, we control the capacitance, or the charge, or the stored energy, and deem the transient discharge current equivalent to a steady state current. In the case of an across-the-line capacitor installed on the supply side of the power switch, the capacitor can be charged to the peak of the line voltage if the plug is disconnected at the peak of the line voltage. As has already been noted in this forum, the discharge is not a pleasant sensation, and may very well result in an involuntary reaction, depending on the individual. By comparison, the sensation from 3.5 mA steady-state leakage current (allowed by some standards for Class I equipment) is also not a pleasant sensation and may result in an involuntary reaction. The initial discharge current of a charged capacitor is limited only by the body resistance. Regardless of capacitance value, the initial current is the same. The effect of capacitance value is the duration of the current. If the current has a short duration, the body will not sense it. Assuming all bodies have the same resistances, then the duration of the current is a function of the value of the capacitance. The standards happen to draw the line at 0.1 uF. Any value less than 0.1 uF is deemed acceptable. Any value greater than 0.1 uF is deemed unacceptable. Consequently, for capacitors less than 0.1 uF, the discharge time is short and the body is less likely to sense the current. If the capacitor is more than 0.1 uF, the discharge time is long, and body is likely to sense the current. Another factor, of course, is the magnitude of the voltage to which the capacitor is charged. If the capacitor is charged to the peak of the 230 V mains, the discharge is almost always sensed. The same capacitor charged to the peak of a 120 V mains is barely detectable. The lower the voltage, the lower the initial current. The fact that the initial discharge current is limited only by body resistance also applies to leakage current through Y capacitors. At the moment the body is inserted into the circuit, the initial current is limited only by the body resistance. Thereafter, the current is the steady-state current due to the capacitive reactance. However, the Y capacitors are much smaller in value, and therefore the discharge is much shorter in time. (You can test this by putting a switch in series with the leakage current; if the switch closes at the peak of the line voltage, you will feel an initial sharp sensation.) By the way, the sensation of leakage current from a Y capacitor is greater than the sensation of leakage current from a resistor whose value is equal to the value of capacitive reactance. This is due to the same phenomenon, namely the initial discharge of the capacitance. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Question: Discharge capacitance 0.1 uF
Hi Tom: So, for voltage up to 450V d.c. (i.e. up to 318V a.c.), capacitor up to 0.1uF will become a Limited Current Circuit, hence the voltage is not Hazardous Voltage (1.2.8.4) - no additional condition would be required for the capacitor connected to the primary circuit. Electric shock (or electrically-stimulated sensation) is a function of BOTH voltage and current. For an electric shock to occur, the source must exceed, say, 30 V rms and 0.5 mA rms. As a general rule, we say that any voltage not exceeding 30 V rms is not hazardous, regardless of current. We identify this voltage as ELV or SELV. Likewise, we say that any current not exceeding 0.5 mA rms is not hazardous, regardless of voltage. We identify this current as Limited Current. Furthermore, Limited Current addresses capacitors charged to voltages exceeding 42.4 V dc. In this case, we control the capacitance, or the charge, or the stored energy, and deem the transient discharge current equivalent to a steady state current. In the case of an across-the-line capacitor installed on the supply side of the power switch, the capacitor can be charged to the peak of the line voltage if the plug is disconnected at the peak of the line voltage. As has already been noted in this forum, the discharge is not a pleasant sensation, and may very well result in an involuntary reaction, depending on the individual. By comparison, the sensation from 3.5 mA steady-state leakage current (allowed by some standards for Class I equipment) is also not a pleasant sensation and may result in an involuntary reaction. The initial discharge current of a charged capacitor is limited only by the body resistance. Regardless of capacitance value, the initial current is the same. The effect of capacitance value is the duration of the current. If the current has a short duration, the body will not sense it. Assuming all bodies have the same resistances, then the duration of the current is a function of the value of the capacitance. The standards happen to draw the line at 0.1 uF. Any value less than 0.1 uF is deemed acceptable. Any value greater than 0.1 uF is deemed unacceptable. Consequently, for capacitors less than 0.1 uF, the discharge time is short and the body is less likely to sense the current. If the capacitor is more than 0.1 uF, the discharge time is long, and body is likely to sense the current. Another factor, of course, is the magnitude of the voltage to which the capacitor is charged. If the capacitor is charged to the peak of the 230 V mains, the discharge is almost always sensed. The same capacitor charged to the peak of a 120 V mains is barely detectable. The lower the voltage, the lower the initial current. The fact that the initial discharge current is limited only by body resistance also applies to leakage current through Y capacitors. At the moment the body is inserted into the circuit, the initial current is limited only by the body resistance. Thereafter, the current is the steady-state current due to the capacitive reactance. However, the Y capacitors are much smaller in value, and therefore the discharge is much shorter in time. (You can test this by putting a switch in series with the leakage current; if the switch closes at the peak of the line voltage, you will feel an initial sharp sensation.) By the way, the sensation of leakage current from a Y capacitor is greater than the sensation of leakage current from a resistor whose value is equal to the value of capacitive reactance. This is due to the same phenomenon, namely the initial discharge of the capacitance. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute:
Re: safety testing in the USA
Hi Rob: I am in discussions with a potential supplier of IT equipment, Its our usual policy to request testing to a listed standard such as UL 60950 for safety in North America. The supplier has replied that this is not mandatory. Is he correct? what compels safety testing for IT equipment in this geography? is it mandated by law? I am going to interpret your statement of safety testing as meaning safety certification. In the USA, there are two sets of regulations that are mandated by law: 1. Workplace regulations (OSHA). 2. Electrical installation regulations (NEC). Between these two sets of regulations, almost every sales situation is covered. Each of these has two alternatives: 1. Test each unit in place. 2. Third-party certification. Technically, your supplier is correct. Third-party safety certification is NOT mandatory (because testing each unit in place is the alternative). Practically, your supplier is wrong. Third-party safety certification avoids testing each unit in place. In the USA, governments cannot mandate testing by a private party (which is the case of third-party safety certification houses). Consequently, the regulations promulgated under various laws prescribe testing in place, with an alternative of third- party certification to a national standard, i.e., an ANSI standard. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: safety testing in the USA
Hi Rob: I am in discussions with a potential supplier of IT equipment, Its our usual policy to request testing to a listed standard such as UL 60950 for safety in North America. The supplier has replied that this is not mandatory. Is he correct? what compels safety testing for IT equipment in this geography? is it mandated by law? I am going to interpret your statement of safety testing as meaning safety certification. In the USA, there are two sets of regulations that are mandated by law: 1. Workplace regulations (OSHA). 2. Electrical installation regulations (NEC). Between these two sets of regulations, almost every sales situation is covered. Each of these has two alternatives: 1. Test each unit in place. 2. Third-party certification. Technically, your supplier is correct. Third-party safety certification is NOT mandatory (because testing each unit in place is the alternative). Practically, your supplier is wrong. Third-party safety certification avoids testing each unit in place. In the USA, governments cannot mandate testing by a private party (which is the case of third-party safety certification houses). Consequently, the regulations promulgated under various laws prescribe testing in place, with an alternative of third- party certification to a national standard, i.e., an ANSI standard. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
double-pole switching and fusing
Hi John: I read in !emc-pstc that Crabb, John jo...@exchange.scotland.ncr.com wrote (in B6CD5947CF30D411A1350050DA4B75FF03C2341C@sgbdun200.scotland.n cr.com) about 'South Korean Power System', on Wed, 20 Feb 2002: Typically I would expect IT equipment to be safe if line and neutral were reversed, except for the issues relating to a single pole disconnect device and fusing. See Tables 2E and 2F in IEC/EN60950:2000. Double-pole switching and fusing is almost always necessary in practice. Tables 2E and 2F are invoked only by the Note 2 to Sub-clause 2.7.4. A Note is informative, not a requirement. Note 2 specifically addresses the situation where protection devices are integral to the equipment. It further states that the examples are not necessarily valid for protective devices in the building installation. For earth faults in plug-and-socket-connected equipment, the equipment need not include double-pole fusing as the protective device in the building installation provides the earth-fault protection. This is the basis for the robustness requirements of the equipment protective earthing circuit. So, in practice, double-pole fusing is seldom necessary. Double-pole switching, on the other hand, is almost always necessary in practice. The exception is where both the supply and the equipment connection to the supply are polarized, in which case a single- pole switch in the phase conductor is acceptable. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Using PCB traces as transient voltage suppressor
Hi Chris: 1. Can anyone else verify the breakdown voltage of 1Megavolt/meter for air? Seems different than what I can remember; but I don't have a reference handy. It also seems to me that this would be very dependent upon humidity and pollution degree? In a separate message, I will send you the air breakdown voltage curves from IEC 664. Humid air has a very slightly higher electric strength than dry air. (Water vapor, a gas, has quite different properties than water as a liquid.) I believe air temperature has more effect on electric strength than does humidity. Pollution affects the electric strength of the scheme because it is deposited on the electrodes. This tends to reduce the electric strength between the two electrodes. This is a larger effect than humidity. The biggest factor affecting the electric strength of air is air pressure. Pollution, temperature, and humidity have relatively low effects. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Safety of Indicating LEDs
Hi Scott: The scope of EN 60825-1 says LEDs are included whenever the word laser is used, meaning they are to be evaluated the same way lasers are. Does this apply to status indicating LEDs (non-lasing)? If so, are manufacturers expected to test every status-indicating LED on the product as if it were a laser? Yes. At least one certification house demands measurement data for each indicator LED. Emission class must be identified on the product or in the manual. (Note that emission class is determined under single-fault conditions in the driving circuit.) However, in practice, other certification houses use a get-out for indicator LEDs. Usually this is in the form of a not tested, but may be required by some authorities statement in the report. Most indicator LED manufacturers do not know of EN 60825-1, and have no idea how to test. Measurement is not easy, especially the determination of the aperture. Most indicator LEDs will open before achieving Class 2 emission levels. The above does not apply to automotive LEDs or to traffic signal LEDs. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: South Korean Power System
Hi Ed: With few exceptions, most power distribution systems have one pole of the supply, the neutral, grounded. (Indeed, the definition of neutral for single-phase systems is the grounded conductor.) In the IEC scheme of the world, a power distribution system where the neutral is grounded is known as a TN or TT system. The first letter identifies the grounding scheme for the neutral wire. The second letter identifies the grounding scheme for the protective wire. T = terra (a ground rod) N = neutral In North America, the scheme is TN. The neutral is connected to a ground rod at the service entrance. The protective wire is connected to the neutral in the breaker panel. I believe Korea uses the TN system. So, at any socket-outlet, one pin will be at the phase voltage, 220, and the other pin will be at the neutral voltage, 0. Polarity is a separate issue. By polarity, I mean that the neutral identification is maintained through the plug/socket-outlet scheme. Polarity is not maintained where the plug can be reversed in the socket-outlet. The SCHUKO plug is a plug that can be reversed in the socket outlet. Not only that, but the socket-outlet is symmetrical, so the wiring to the socket-outlet cannot be such that the neutral is always wired to the same pin. Among the world's plugs/socket-outlet combinations, relatively few maintain the polarity through the system. These are: the British 13-A plug/socket-outlet in UK, Ireland, Hong Kong, Singapore, etc. the old British 15-A plug/socket outlet in South Africa and India, etc. the Australian plug/socket-outlet the North American grounding plug/socket-outlet the North American two-wire plug/socket-outlet with one wide blade The French plug/socket-outlet with its grounding pin scheme COULD be polarized, but is not so wired. Likewise, the Danish, Chilean, and Chinese plug/socket-outlet could be polarized, but I cannot say if they are. Polarized plugs and socket-outlets always bear markings indicating the pole of each pin. For North American plugs and socket- outlets, the white or silver-colored screws or terminals are the neutral pins. Other plugs and socket-outlets bear molded in letters such as L, N, E or PE or G. Virtually all safety standards include the requirement that the neutral wire within the equipment shall be treated as if it was at mains voltage rather than at zero voltage. This is because, in many installations, errors may occur in the wiring of the socket- outlet. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Japan mains frequency
A good source is http://kropla.com/electric2.htm http://kropla.com/electric2.htm . According to that site: Japan100V50/60 Hz* *Eastern Japan 50 Hz (Tokyo, Kawasaki, Sapporo, Yokohoma, and Sendai) *Western Japan 60 Hz (Osaka, Kyoto, Nagoya, Hiroshima) According to a history told to me by a GE old-timer... Japan has two frequencies because, in the early days of electric power in Japan, Western Japan bought its first generator from General Electric (60 Hz), and Eastern Japan bought its first generator from Russia (50 Hz). So, this is an easy way to remember what part of the country is 60 Hz and what part is 50 Hz: The western part is closest to North America (60 Hz), and the eastern part is closest to Russia (50 Hz). (However, the cities listed above seem to be in the opposite parts of Japan than as listed.) Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Admin message -- format of posted messages should be plain text
A request from your list administrators... Except... I (and other classic Compuserve users) won't see these messages at all, unless and until they appear in someone else's REPLY in a form Compuserve can send. It LOOKS great - but please don't send HTML to the list. Cortland is not alone. Some mail systems simply don't show messages in formats other than plain text or ASCII. UNIX mail (which I use) is another scheme that has difficulty displaying some message formats. For this reason, we ask that all messages to the listserver be posted in plain text/ASCII mode. Please set your mail program to send messages to the listserver in plain text or ASCII mode, not in rtf, htm, or html mode. (If you need help in doing this, please contact your local IT folks, or send e-mail to Jim Bacher, our e-mail admin guru.) In Outlook, when in the reply (or send) mode, click on format and plain text before sending. (If Outlook won't let you change the format of a reply, then initiate a new message and copy the original text into your reply.) In Outlook, if you have emc-pstc in your address book, select the address, click on properties, click on smtp-address, click on send options, click on I want to specify the format... click on MIME and plain text. This will automatically set your postings to plain text (ASCII) mode. If you want to discuss this request, please do so off-line so that we don't contaminate our technical discussions with admin stuff. Thanks for observing this protocol, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: OEM
Hi Richard: We may soon be privately labeling our products for a particular customer, and I have a question concerning the EU Declaration of Conformity. We will be shipping products to our customer's distribution center, and they will be responsible for sales to their customers. By shipping the product to our customer's distribution center, have we placed the product on the market and must therefore issue a Declaration of Conformity? When we buy products from an OEM (whether or not they go to our distribution center), we ask the OEM for their DoC (and copies of reports supporting the DoC). Using the OEM DoC (and reports), we issue our own DoC as if we designed and manufactured the product. (If we have all the applicable reports, then we can issue our own DoC regardless of whether the OEM has issued a DoC.) This doen't answer your question as to whether shipping the product to your customer's distribution center constitutes placing the product on the market. However, in using this process, the question does not arise as a DoC has been issued by both organizations. I guess the answer is: If you issue a DoC, then you have met your obligation. If you do not issue a DoC, then you may or may not have met your obligation. I doubt your customer would want to ship your DoC with his product. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: My subscription may have terminated
Hi Dan: I have received no emails today. Did my subscription cease? No, your emc-pstc subscription is not terminated. Today is the most unusual day in the history of emc-pstc in that there were no postings to the listserver between 5:30 PM PST Tuesday and 11 AM PST Wednesday. I, too, was a bit alarmed that the server might be down or there was some other problem. We checked, and everything is in working order. We've simply had no postings. Today, up to the time of your message, there was only one topic posted to the listserver. Best regards, Rich Administrator, emc-pstc listserver --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Flammabilty requirement for cloth used on loudspeaker / UL6500
Hi Pierre: Unfortunately, Hexamine is temporarely unavailable from IMSPLUS, and, furthermore, this product cannot be sold outside the US. If somebody knows another source, he's welcome ! I did a Google search and found at least one more source: http://www.omahas.com/store/commerce.pl?product=Messkits I believe there are some Euro sources in the Google results, but I did not check all the listed sources. Good luck and best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Flammabilty requirement for cloth used on loudspeaker / UL6500
Hi Pierre: Reading the standard, I understand that the cloth used on the front of the loudspeaker (external to fire enclosure) has to be tested according the tablet test (see Table 13). As I recall (from the UL standard), the tablet is hexamine. I have purchased tablets from: IMS Plus (International Military Surplus) http://www.imsplus.com/ims28.htm I purchased the tablets on-line. My first order was lost, but they sent the second order without charging me for the lost order. Do you know this test ? No. (Some years ago, I required some means of igniting something. I did some research of the UL standards and found that UL used the hexamine tablet for igniting speaker cloth. Since the tablet was an established source of ignition, I've used it since then whenever I want to test for ignition of some- thing.) Do you know if this information can be provided by the cloth manufacturer ? You might check to see if the cloth is UL-Recognized. If yes, then the cloth manufacturer submitted the cloth to UL for testing. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Teslars???
Hi Joe: We have a customer that is concerned about how our product, laboratory equipment, will respond to electromagnetic disturbances from a high speed train that runs close to their lab. The customer states that the disturbance will be around 0.7-1.2 m Teslar. I believe you mean tesla (with a lower-case t), not Teslar. The symbol for tesla is upper case T. According to ISO Standards Handbook 2, the tesla is a unit of magnetic flux density. The magnetic flux density is an axial vector quantity such that the force exerted on an element of current is equal to the vector product of this element and the magnetic flux density. 1 T = 1 N/(A*m) 1 T = 1 Wb/m^2 1 T = 1 V*s/m^2 I'm sure your customer is referring to an electric train. I recall a suburban electric train line where the stations had color TV monitors to announce the train and its schedule. A few minutes before the train arrived in the station (and usually before you could see the train), the monitor's colors would go awry. The degradation would increase until the train arrived, at which time the normal colors were restored. Upon departure, the colors would again go awry, and then gradually return to normal. The color degradation was due to the magnetic field around the overhead wire. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: TUV NRTL
Hi George: However, for the U.S. OSHA establishes acceptable NRTLs, and the CFR uses the words NRTL, so I do not see how an electrical inspector could object to what the Federal Government has sanctioned. The inspector must abide by the certifications approved by the local building/electrical code jurisdiction. It would be more accurate to substitute local jurisdiction for inspector. OSHA NRTL and local code processes are independent of each other. I agree that it would be prudent of the local jurisdiction to accept OSHA NRTLs rather than establish other criteria which might exclude one or more NRTLs. I believe TUV-R has indeed applied for acceptance in most or all local jurisictions. (Don't rely on my belief.) Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: CE Marking - Prototypes
Hi Gregg: My understanding if that: where OSHA is applicable then UL or equivalent is mandatory. True. However, replace UL or equivalent with NRTL. where OSHA is not application then Local Code is mandatory - and LOCAL Code requires NRTL (UL or equivalent) Not true insofar as the conditional statement, where OSHA is not applicable... Compliance with the local code is mandatory and independent of OSHA. Here is the difference: OSHA rules are for the protection of employees in the workplace. They apply to products and installations used by employees. Local codes/rules are part of the local BUILDING code. They apply to ALL products and installations within the local jurisdiction. Local codes apply equally to residences, commercial buildings, factories, etc. -- everywhere except electric utility circuits. OSHA and local codes are *not* alternatives. For every place of employment, *both* OSHA rules and the local electrical code rules apply. For residences and schools and similar non-employment and government sites, only the local electrical code applies. (OSHA does not apply to government employees.) Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
Re: Telecommunications Vs. ITE Product
Hi Gregg: Let me start by asking one simple question - WHAT IS THE PURPOSE OF CERTIFICATION? 1- to meet the legal requirement 2- help market the product 3- do the 'right thing' 4- not to kill anyone 5- make sure that the product is nor recalled Most companies will answer (4) to make sure the product is not recalled. This is a GOOD answer - it may not optimized, in terms of immediate cost, but this is the one that I would opt for - particularly if I wanted to sleep at night. This is what the certification house would like you to believe. However, the process of certification is a simple matter of checking off requirements. (Have you looked at a CB Test Report lately?) There is very little further looking for hazards, (and there is a great deal of nit-picking for compliance). So, certification means compliance with the standard. To accomplish #4, the standard must be omniscient. Mere mortals put the standard together. We wouldn't certify products if there wasn't a legal requirement to do so. But, I agree that we expect a lot more from certification than meeting legal requirements. However, we don't get more than compliance to the standard. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
Re: Harmonic current emissions
Hi John: But whichever method is adopted, the customer pays the bill eventually and I have more confidence in the highly competitive world of electronic products to come up with a cost-effective solution in a timely manner. One of the USA's major objections to EN61003-2 is that remedying the load repeats with each new product that is introduced, while remedying the source is a one-time remedy. EN61000-3-2 requires continous cost to the consumer with each product. (The cost is NOT trivial -- nearly double the cost of the power supply.) No, that's certainly an exaggeration. We have been told various sums from USD1 to USD5, and I suspect that the lower value is nearer the truth. The additional cost for a PF-corrected SMPS is not a constant adder; it is proportional to power output. One must use higher power PF components for higher power output. Having actually purchased production quantities (1995) of the same SMPS in both non-PF-corrected and PF- corrected schemes, the additional cost for PF-corrected ranged from 50% to 75% higher than the non-PF-corrected supply. More recently (2001), the cost difference was indeed lower -- only about 25-30% premium. I suspect your sources wanted to sell PF-corrected SMPS's and exaggerated on the low side. Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
Harmonic current emissions
Hi Keith and Ghery: There are a number of effects of harmonic current emission from non-linear loads. 1) When a large number of loads rich in triplen harmonics are supplied from a 3-phase source, the neutral current can be as high as root 3 of the phase current. (This effect does not exist on a single-phase distribution system, or on a 3-phase system where each phase has its own neutral.) Where the neutral wire is sized for a balanced load, some authorities allow the neutral wire to be one size smaller than the phase wire. Such a wire is likely to be overheated by the triplen currents. Indeed, it is possible to overheat the neutral wire when it is sized the same as the phase wire. In the USA, authorities now require (for such loads) the wire to be larger than the phase wire, or two, parallel neutral wires. 2) Consider that the non-linear load generates current at harmonics of the mains frequency and injects it into the mains distribution system. This current must circulate in the distribution system and return to the source (load). Often, this current circulates in the delta primary of the first upstream delta-wye distribution transformer, and causes the transformer delta winding to overheat. (This effect is likewise mostly due to triplen harmonics.) In the USA, distribution transformers are specially designed to dissipate this power without overheating. Such transformers include a K-factor rating, which is a measure of the transformer to accommodate the current. 3) Depending on the source impedance, a large number of non-linear loads can cause voltage waveform distortion. Voltage distortion is caused by all of the harmonics, not just the triplen harmonics. Voltage waveform distortion can cause motors to overheat. Each of these effects is a separate and independent issue. They should not be lumped as a single issue. For each effect, there can be one or more remedies. The remedy can be either in the load or in the source. EN 61000-3-2 arises from the voltage distortion effect. Mr. Van den Bergh's comments (as quoted by Keith) appear to address voltage distortion, not the other effects. Because of the difference in the design of power distribution systems, voltage distortion is more of a problem in the EU than in the USA. I suspect the real reason for the computer industry's denial of harmonics problems, or else blaming them on a poor distribution system, is that US computer manufacturers simply want to make one model they can sell world-wide so they want whatever is permitted in their main market (the US) to be permitted everywhere else. Would you agree with this? I believe this is an oversimplification of the manufacturer's dilemma of addressing this problem. The USA computer industry has been quite forward in addressing effects 1 and 2. The computer industry was the force behind a series of academia-based seminars on the causes and solutions to effects 1 and 2 that resulted in changes to the USA National Electrical Code and to distribution transformer testing and ratings. (I presented in some of those seminars.) This is NOT denial. But whichever method is adopted, the customer pays the bill eventually and I have more confidence in the highly competitive world of electronic products to come up with a cost-effective solution in a timely manner. One of the USA's major objections to EN61003-2 is that remedying the load repeats with each new product that is introduced, while remedying the source is a one-time remedy. EN61000-3-2 requires continous cost to the consumer with each product. (The cost is NOT trivial -- nearly double the cost of the power supply.) Indeed, this has forced manufacturers to develop one supply for the EU, and one supply for the remainder of the world. And, forced two products for the world instead of one. (One of the benefits of EN61000-3-2 has been a real effort at power reduction so that more and more products are below the 50-watt exemption limit.) I have some knowledge of power-factor correction techniques in switch-mode supplies, and some of them can cost very little indeed. So I really don't know why the US computer industry is making such a fuss about controlling harmonic emissions. I certainly have not seen low-cost PF correction techniques. My experience is that the cost is nearly twice the cost of a non-PF corrected power supply. Best regards, Rich ps: EU power suppliers are taking an interesting approach to their customers. If the customer has a linear power factor problem, we will correct it. If the customer has a non-linear power factor problem, we will not correct for it, and we will not sell power to you if the effect is too great. Clearly a monopolistic view.
Re: Company close down due to EMC phenomena
Hi Amund: I suggest you and your client and the regulatory authority meet to address the situation. Here are the issues as I understand them from your message: 1. In idle mode, the emissions are comfortably below the maximum allowed emissions. 2. In transmit mode, the emissions exceed the maximum allowed emissions. The duration of the transmission is 25 ms. The repetition rate of the transmission is about 1/hour. 3. The emission level is probably related to the nature of the system, i.e., transmission via the power distribution network. I feel that 25 ms/hour is the important parameter. I suspect that most motor-starting events exceed the emission level, and for more than 25 ms. Like- wise, I suspect most igniter events also exceed the emission level and for more than 25 ms. Does your regulatory authority permit such emissions? Set up the system for normal operation. Ask the regulatory authority to measure the emissions. The emissions will be in compliance for 1 hour. The regulatory authority must be observing the emissions at the moment of the 25 ms transmission in order to determine if the emissions exceed the allowed level. I suspect this is a difficult measurement. The receiver or SA must be tuned to the transmit frequency during the 25 ms transmit interval. This probably requires advance knowledge of the transmit frequency, and therefore the measurment is not an agnostic measurement. (If you were submitting the equipment to the regulatory authority, do you have an obligation to inform them of expected performance of the unit, especially the specifics of the transmit mode?) And, there must be some means of capturing the data during the event. Short of staring at the SA screen for an hour or more, I'm not sure this can be done except with exceptional effort and additional equipment. The preceding paragraph is something of a game to play with the regulatory authority. So, why should the company close down ? Because if the national authority gets what they want, there will be one sale. Logical, but is it a correct prohibition the authority call? The company SHOULD have known that its product would exceed conducted emissions. The company SHOULD have taken appropriate steps with the regulatory authority to know whether or not its product would be approved BEFORE it invested in the product development. This is not a fault of the regulatory authority, but a fault of the company to not understand the regulations BEFORE it developed the product. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
Administrative message -- posting formats
Regarding postings, here is a re-statement of our guidelines that were sent to you when you subscribed: 1. No attachments (because many of our subscribers use dial-up modems for which message size determines the download time). If an attachment is appropriate or necessary to your message, then a) offer to e-mail it separately upon request, or b) make it available on an FTP site, or c) post it to a web site and provide the URL in your message. 2. Post in ASCII plain text. Do not use RTF, HTML, or similar formats. Not all mail readers are compatible with these formats, but all mail readers are compatible with ASCII plain text. In most cases (especially Outlook), you can set your mailer to always use ASCII plain text for messages sent to emc-pstc. Also, please don't write messages without carriage returns. Some mailer readers can't handle long lines, so the line is truncated and part of the line disappears. If you use CR (ENTER) at the end of each line, then each reader will see the same format as the one you wrote. 3. Please don't re-post the entire message string when replying to a message. Instead, pick out the passages to which you want to respond, enter your response, and delete the other text. This makes your point easier to understand, and helps keep the message size down for our modem- connected colleagues. Don't forget to delete the emc-pstc footer! :-) (Each posted message gets the footer attached; multiple footers provide no useful information, and just make downloads longer.) 4. If appropriate, when responding to a message, change the subject line to agree with the major point or content of your contribution. You can append was 'original subject' to your subject if you want to reference the original subject. This will help us when the subject matter strays from the original. 5. If you want to attach a signature, please do so in ASCII (for the same reason as posting in ASCII), not the business card format that is gaining popularity. Best regards, Richard Nute Administrator, emc-pstc listserver Tel: +1-858-655-3329 FAX: +1-858-655-4374 e-mail: ri...@ieee.org --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
docopocoss
docopocoss This word was unknown to me. I checked an American dictionary and could not find it. Then, I called up the Google search engine and entered the word, hoping to find an English dictionary. Google immediately came back with the definition. Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Value of Using Non-NRTL Engineering Firms?
Hi Chris: OSHA rules apply to employers. OSHA electrical rules require employers (1) to use only electrical products that have been certified by an NRTL, or (2) in the case of custom products, to test the product in place. If you sell a non-NRTL-certified custom product to an employer who is subject to OSHA rules, then that employer must test the product in place, and file a suitable record of the testing. Few employers choose the test-in-place alternative. A listing by a non-NRTL is useless to an employer subject to OSHA rules. He can't use it for proof that the product meets OSHA rules. At the employer's discretion, you may be able to convince the employer (your customer) that your listing test report will provide a suitable record of testing to OSHA requirements. See OSHA rules, Sub-part S for complete treatment on OSHA electrical rules. See especially 1910.303(a) Approval and the respective definitions. http://www.osha.gov/pls/oshaweb/owastand.display_standard_group?p_toc_level=1p_part_number=1910p_text_version=FALSE Statement: Non-NRTL laboratories can provide Listings and publish the customers (thus Listing) however, based OSHA law, NEC requirements, Retailer specification, and other MOU/MRA with Canada/EU, it would not seem to be a significant accomplishment if not an NRTL. Except for NEC, I would agree with this statement. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: OFF is zero
Hi Stephen: I think I missed the beginning of this thread, so please forgive me if I rehash old ground. The 'vertical line' and 'circle' you refer to, are actually a 1 (One) and 0 (Zero); as in digital logic on/off respectively. My original posting on this subject was with regard to the ETYMOLOGY of the IEC 60417 symbols 5007 (a vertical line) and 5008 (a circle). The IEC 60417 symbols 5007 and 5008 are SYMBOLS. They are NEITHER numbers NOR letters. The ETYMOLOGY I quoted shows that these symbols were originally the numbers zero for OFF and any number one or greater for ON. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: OFF is zero
Hi Serge: O = Out of Circuit I = In Circuit Note: while many people believe the symbols are O 1, they are in fact O I IEC 60417 Symbols 5007 and 5008 are neither: the numbers 1 and 0, nor the letters I and O. They are the symbols depicted in the 60417 drawings, specifically a vertical line and a circle. My comment is that the ETYMOLOGY of the 5007 and 5008 symbols are the numbers one and zero. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: OFF is zero
Hi Neil: The origin may be true, but IEC60417 is quite clear. ON is a vertical line (symbol 5007) and OFF is a circle (symbol 5008). Agreed. And thank you for the clarification. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
OFF is zero
A week or so ago, I asked about the origin of the 0 and 1 symbols for off and on. I mentioned that it was my recollection that the the symbols came from early safety standards where the off and on functions were by means of a rotary switch where the 0/zero position was off. I found some very old standards that I still have on my bookshelf. IEC 380, First Edition, 1972: Electrical Safety of Office Machines Clause 7, Markings Sub-clause 7.10: If figures are used for indicating different positions, the off position shall be indicated by the figure 0, and the position for greater input, speed, cooling effect, etc., shall be indicated by a higher figure. The figure 0 shall not be used for any other indication, except that this shall not preclude the use of the figure 0 for the identification of an alphabetic or numeric key on an office machine. I believe this text is virtually the same as the text in CEE-10 mentioned in my previous message. CEE-10 was the predecessor to IEC 380 and addressed safety of office machines. I conclude that the 0 and 1 symbols came from the number zero and the number one. Today, the figure/symbol 0 is REQUIRED as the OFF symbol and the figure/symbol 1 is REQUIRED as the ON symbol. What have we done to ourselves? Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Origin of power symbols 0 and 1?
I am looking for the origin of the power symbols 0 (off) and 1 (on). The earliest standards that I have are CEE 10 and similar where the standard specifies something like: Where a rotary switch is used for power, the 0 position shall be off and the 1 and higher position shall be on. Do you have the specific wording? Do you have something earlier than the CEE standards? Thanks for your help! Rich Richard Nute Hewlett-Packard Company 16399 West Bernardo Drive San Diego, California 92127-1899 Tel: 858-655-3329 FAX: 858-655-4374 e-mail: ri...@sdd.hp.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Creepage
Hi Richard: What is a good source that explains the rational for the values for creepage distances? There was a good deal of research done in the late '70s and early '80s on creepage distances and the deterioration due to deposition of foreign materials and the effects of humidity. As I recall, the results of this research was published as working papers of the IEC TC that did the research (TC 64?). I suppose you could ask the TC for copies of this research. In a nutshell, the voltage across the contaminants causes micro-arcing. The heat from these microarcs causes tracking on the surface of the insulator. Eventually, the micro-arcs develop into trees, and the leakage current becomes significant. The phenomenon is a long-term one, so the effective voltage across the insulator is the significant parameter. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Class III ID mark?
Hi Tom: With a bit further search, I found: http://w3.hike.te.chiba-u.ac.jp/iec417/html/doc/5180.html This site specifies the use and the referring standard: Application: On any kind of equipment. To identify equipment meeting the safety requirements specified for class III according to IEC Publication 536 : Classification of electrical and electronic equipment with regard to protection against electric shock. So, with thanks to you, my questions are answered! Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Class III ID mark?
Hi Tom: I guess what you think is IEC 60417 No. 5180, which shows III in diamond shaped frame (45 degree rotated square). (http://member.nifty.ne.jp/tsato/terms/iec417-5180.gif) Yes, this is the mark that was mentioned to me. However, I don't know which standard require the mark. I thought none of 60335, 60950 and 61010 require to put the mark on Class III equipment, although they require double-square mark on Class II equipment. Now, I need to confirm that this mark indeed indicates Class III equipment, and does not indicate something else. And, I need to determine what standards require this mark. Can anyone provide this info? Thanks, and best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Class III ID mark?
A colleague recently showed me a Class III identification mark. However, he had no further information about the mark. (The Class III mark would be used to identify a Class III product similar to the way the Class II mark square-within-a-square is used to identify a double-insulated product.) Have you seen this mark? If so, can you tell me its origin and provide me with a copy of the mark? Also, can you tell me the standards in which it is identified and requirements for its use? I suspect this mark originated at VDE. Thank you for your help, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: EN60950-1 Sect 2.5 Limited Power sources
Hi Tom: Is it permitted to use PTC as an overcurrent protective device for power sources not inherently limited? I don't have EN60950-1 here, but I remember it must be a fuse or other non-autoreset device. I said: The trick is to determine if your test houses can class the PTC as an 'overcurrent protective device.' Another subscriber said that the PTC is a resistor and therefore a PTC-protected LPS must be inherently limited. I suggested the PTC as an overcurrent protective device because as its resistance goes up, the PTC provides protection against overcurrent. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Green/Yellow Earthing Leads
Hello from San Diego: One of our subscriber colleagues has pointed out that my assertion that Europe uses yellow as the color of the earthing wire is incorrect. I recall when the green-yellow was agreed to for power cords and internal equipment wiring. My recall was that both yellow and green were used as earthing wire colors, hence the green-yellow compromise. My recollection is in error. I apologize for misleading you. Best regards, Rich In North America, the earthing conductor in building wiring is green. In Europe, the earthing conductor in building wiring is yellow. For power cords and equipment earthing conductors, a compromise was agreed to for green/yellow. Note that in North America, power cord and equipment earthing conductors may be green/yellow or green. In Europe, power cord and equipment earthing conductors may be green/yellow or yellow. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: electric strength test
Hi Greg: Why does True SELV require basic insulation between SELV and earth? What is the hazardous voltage source, and what is the current path through the body if that basic insulation should fail? I believe (and I could be wrong) that it's a philosophy of keeping SELV intact under single fault conditions. If there's a single fault bridging mains and earth, then an SELV circuit is exposed to mains voltage unless there is basic insulation protecting it. Since it is estamited that close to 50% of the homes in the US have improperly grounded outlets, the earth connection itself is not taken into consideration as a reliable means of protection. In other words, for the purposes of the standard, an open earth connection is not considered a fault. Thanks for the explanation. One implication of this explanation is that an open earth connection is not a fault condition, but a normal condition. (Failure of basic insulation is the fault condition.) This would suggest that it would be better to double/reinforce insulate the mains against earth, in which case SELV could be earthed. (This also solves the problem of accessible earthed parts becoming live when used on a system with no earthing connection.) But, unfortunately, the requirement remains that true SELV cannot be connected to earth, and must have basic insulation between it and earth. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: EN60950-1 Sect 2.5 Limited Power sources
Hi Alex: We use a linear (basically a transformer with a PTC thermistor) class II SELV O/P stand alone power supply rated 10Vac, 5A. One of the labs tested the O/P Isc with a direct application of the sc. The other lab tested the O/P Isc by applying a load of 8A. The results were therefore interpreted differently. 1. What is the correct method to test for a Limited Power source in determining what enclosure is required? Limited Power Source is a combination of a number of criteria: output voltage; output current; output volt-amperes. These are independent criteria. Note that Isc is defined as: Maximum output current after 60 s of operation with any non-capacitive load, including short-circuit. Both labs are wrong. If a power supply shuts down due to a short-circuit, then it is necessary to determine the maximum current where the power supply does not shut down. Typically, this is about twice rated output. Since your power supply is rated 5 A, then I would expect the overpower to take effect at about 10 A output. When testing a power supply output for LPS, start at rated load and gradually increase the load. If the output exceeds 8 amps or any other criteria, then the output is not LPS. Then, introduce the single, worst-case fault in the regulating circuit, and repeat the test. In your case, this means shorting the PTC, in which case the output will certainly exceed 8 amperes. By the way, your output also fails the output volt-amperes criteria. If the open-circuit output voltage is 10 volts, then the maximum VA is 50, or 5 amps. Since one lab only did the output short-circuit test, the results are not correct. Since the other lab did a single test at 8 amps, this is more-or-less okay, but for the wrong reasons. Neither lab did the VA test! The VA test would have proved the unit failed at 5 A output. Neither lab introduced a fault in the regulating network! (But, the didn't need to since the unit failed under normal operating conditions.) Both labs are wrong, but one came up with the correct determination. (Of course ONE had to be correct!) :-) If you use a PTC, then your output need not necessarily be considered inherently limited. In this case, your maximum output current is 100 amps and your maximum VA is 250, i.e., 25 amps (with the PTC shorted). The trick is to determine if your test houses can class the PTC as an overcurrent protective device. A colleague claims that very few test houses really know how to do LPS testing. I concur, and your report confirms this again. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Green/Yellow Earthing Leads
Hi Peter: What is the percentage of color over a surface area for the insulated green/yellow earthing conductor. Is it better to have more yellow than green or more green than yellow. I know North Americans prefer more green than yellow and Europeans like more yellow than green. Any historical reason? I hope it has nothing to do with the Boston Tea Party! Can the group we come up with some compromise? In North America, the earthing conductor in building wiring is green. In Europe, the earthing conductor in building wiring is yellow. For power cords and equipment earthing conductors, a compromise was agreed to for green/yellow. Note that in North America, power cord and equipment earthing conductors may be green/yellow or green. In Europe, power cord and equipment earthing conductors may be green/yellow or yellow. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: electric strength test
Hi John: True SELV . requires double or reinforced insulation from hazardous live parts/parts at hazardous voltages [different expressions used for the same things] and basic insulation from earth. '950 SELV' allows SELV circuits to be earthed (see 2.2.3.3 of IEC60950:1999 or EN60950:2000 or of IEC/EN 60950-1). Why does True SELV require basic insulation between SELV and earth? What is the hazardous voltage source, and what is the current path through the body if that basic insulation should fail? This is a question that has bothered me for a number of years. Thanks, and best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
IT power distribution and Norway (was electric strength test)
Hi John: You may come across some distributors in Norway asking for DI or RI between PRI-EARTH, even for Class 1 power supplies. That's because Norway uses the 'IT' power distribution system, where neither mains conductor is earthed directly, but one is earthed through a quite high impedance to prevent common-mode charge build-up. I fail to understand how, in a Class I product on an IT power distribution system, PRIMARY-EARTH double or reinforced insulation provides protection against electric shock while, on a TN power distribution system, basic insulation is sufficient to provide protection against electric shock. If the product is earthed, then in the event of a fault of basic insulation, the voltage on accessible parts will remain close to earth potential. This applies equally to IT and TN power distribution systems. My understanding of the Norwegian unwritten requirement was because many of the socket outlets, while of the earthing type, do not have the earth terminal wired to earth. Under this condition, double or reinforced insulation makes sense. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: electric strength test
Hi John: That depends on which variety of SELV you mean. True SELV, as opposed to '950 SELV', requires double or reinforced insulation from earth Why? Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: electric strength test
Hi John: Y-caps have enough margin to easily withstand the 4300 V dc without damage. Without immediate failure, no doubt. But such a huge overstress may cause latent damage that later results in failure, and, since IEC 60384 doesn't call for such an over-voltage test, the failure might not be a fail-safe failure. According to my copy of 384 (1996), a Y1 cap is proof-tested at 4000 V ac. 4300 V dc should not be a problem. However, a Y2 cap is proof-tested at 1500 V ac, and this might be a problem just as you suggest. Note that I suggested this overvoltage not as a production test, but as a type test during product evaluation -- to learn the weakest point in the insulation system. If the cap should fail, then you know that the cap is the weakest part. I then remove the cap, and repeat the test to determine the next weakest link. Knowing the weakest link in an insulation system can be quite valuable when a production problem arises. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: electric strength test
Hi Brian: What I've always wondered about, at least for class 1 construction, is just what is really being tested by the pri/sec hi-pot, when the customer chooses to ground the power supply's return. (These comments presume the secondary is SELV.) When you use a ground for safety purposes, the ground circuit must be capable of carrying the fault current. (This construction is called bonding.) Typically, the construction of the secondary ground circuit does not meet the requirements of bonding. Consequently, the ground cannot be relied upon for safety. Therefore, pri-sec insulation must be double/ reinforced. So, the pri-gnd insulation is basic and is backed up by grounded/bonded parts. And, the pri-sec insulation is basic backed up by supplementary (or is reinforced). (Most switching-mode transformers don't use a grounded shield between pri-sec as this reduces coupling and does other things that reduce the effectiveness of the transformer. Therefore most switching-mode transformers use double or reinforced insulation between pri-sec.) By the way, another reason for not using the secondary ground for safety is that the sec winding may not be capable of carrying the fault current, and will open. The problem is that fault current is passing through the part of the winding that is grounded, that part of the winding opens, and the high side of the SELV secondary is now connected to primary. Also,as some of our output-to-chassis Y caps are just 100V decouple caps, and because SELV to P.E. spacing and insulation requirements would never withstand reinforced test levels, how does the end-use installation ever get pri/sec hi-pot to pass without removing the unit from the chassis? There is no requirement for SELV-to-PE spacings and insulation. After all, both the SELV and the PE are accessible parts and need not have any safety insulation or spacings between them. If your SELV is floating, then the pri-sec hi-pot test is simply pri-sec. No connection to chassis or ground. This will, however, damage your sec decoupling caps because there will be a capacitive voltage divider from primary to Y-cap to chassis to decoupler cap to sec. To prevent overvoltage of the decoupler, either short it out or open it. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: electric strength test
Hi Brian: I am attempting to comply with both the letter and spirit of 60950:2000, cl 5.2. Note that 5.2.2 allows for separate testing, according the type of insulation required. When testing a (class 1) power supply, the withstand level for primary to chassis is Basic; and for primary to secondary is Reinforced. Typically, I will apply approx 2500vdc for Basic and 4300vdc for reinforced. But to pass primary to secondary test, 60950 says that I can allow for following: care is taken that the voltage applied to the reinforced insulation does not overstress basic Good requirement and good advice. But, very difficult to apply in practice. Also to avoid damage to components or insulation which are not involved in the test, disconnection of ICs or the like and the use of equipotential bonding are permitted. Again, good advice but very difficult to apply in practice. For Pri/Sec testing, the screw connecting the Y-caps to the chassis is removed, insulation is inserted between the screw insert and chassis. Well... I would just lift the cap and let it hang in air for the test. Inserting solid insulation between the Y-cap terminal and the chassis means that you must also consider: the creepage and clearance around the solid insulation, and that most of the hi-pot voltage will appear across the solid insulation. A (new) agency engineer says that inserting a piece of insulator defeats the purpose of the test. For class 1 construction, it is just not possible for me to pass 4300vdc test levels without inserting my little piece of valox, unless I physically remove all Y-caps (and the unit will not operate reliably with y-caps). I have inspected units from several other companies and have determined that it was not possible to have ever passed pri-sec test levels without isolating these circuits. Inserting the solid insulator DOES NOT defeat the purpose of the test. While it is true that the inserted solid insulation gets tested in parallel with the pri-sec reinforced insulation, the test results apply to the pri-sec insulation. If a failure should occur, then it would be necessary to sort out whether the failure was your inserted solid insulation or the pri-sec insulation. If your secondary is not grounded, then you can open the protective ground and test pri-sec without lifting the Y-cap. (Put the unit on an insulating surface, and be careful not to touch the unit during this test!) Our products are designed in the same way. We don't lift the Y-caps or anything else when we hi-pot pri-sec (secondary is functionally grounded). Y-caps have enough margin to easily withstand the 4300 V dc without damage. In other words, our pri-gnd meets 4300 V dc. In general, solid insulations have electric strengths in the neighborhood of 10 kV or more. The required spacings have electric strengths in the neighborhood of 5 kV. Y-cap electric strength usually is greater than the lead spacing. You should expect a system electric strength approaching 5 kV rms. During design, we always hi-pot test to failure or max voltage of the hi-pot tester, whichever is lower. In our designs, the weakest point (4500-5000 V rms) in the power supply is the pwb terminals of the Y-cap on the back side of the board (where the sharp points are located). The hi-pot test is a pass-fail test, and gives no data. Hi-pot to failure identifies and measures the weakest link. This is useful data for future evaluation of production-line hi-pot failures. Good luck, and best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Criteria for UL V0 plastic enclosure
Hi Scott: In the case of LPS, wouldn't the plastic enclosure still be considered decorative plastic outside a fire enclosure and required to meet HB flame class (per UL 60950, 4.7.3.3)? Yes. Virtually all plastic materials meet the HB flame class, hence my comment that he may use any plastic. Best regards, Rich Rich Nute wrote: The choice is yours. If your product is supplied by a Limited Power Source, then you may use any plastic for the enclosure. If your product is not supplied by a Limited Power Source, then you must use V1 or better plastic for --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: Don'r Get Caught Running a Red Traffic Light!
Hi Doug: I've only heard shortening the yellow light cycle as an unconfirmed rumor. But I've been watching. grin According to our local newspaper, the San Diego Union- Tribune, not only did the contract photo cops shorten the yellow light, they also moved the sensors. The contract photo cops get a percentage of the fine. The fine is $271, and the photo cops get $70 or so. The contract photo cops choose the intersections and set up the system. Only the intersections with known high-volume red-light runners were set up. The whole operation was based on maximizing revenue (in the name of vehicular safety) for the photo cops, a private business. The contract photo cops do the whole job without supervision from real cops. A class-action lawsuit has shut down the cameras. You may be able to find some articles on the UT web site. The hullabaloo was about a year ago. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: ventilation holes
Hi David: You probably already know this, but don't forget that the product will need to pass temp tests during abnormals i.e., blocked vents. I'm not sure if pass temp tests means compliance with the heating requirements or the abnormal requirements, so I offer this clarification. Under abnormal conditions (blocked vents), there are no temperature limits per se. According to Sub-clause 5.4.1, under abnormal conditions the unit must remain safe. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: UL Material flammability requirements for enclosures less than .3
Hi Paul: Can anyone give me any information on whether a box with less than .33 cubic feet needs to meet UL Flammability ratings? I have been told this is true, but I can not find the location of that information. I believe the requirement you are referring to is Sub-clause 4.3.3, UL1950/IEC 60950 Sub-clause 4.7.3.3, UL 60950-1/IEC 60950-1 This requirement exempts materials and components within an enclosure of 0.06 m^3 from flammablity requirements. The enclosure itself must be of metal and must have no ventilation openings. However, 0.06 m^3 = 2.12 ft^3 0.33 ft^3 = 0.01 m^3 so the volume you quote does not agree with the volume in the requirement. With this exception, and as far as I know, requirements for material flammability ratings are based on the circuit parameters, not on volume of the box. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: ventilation holes
Hi George: I have a safety question for the group. I have a small (about 8 x 10 x 2 inch) piece of ITE equipment, SELV, enclosed in a plastic case, powered by an external 12 volt brick from AC mains. The problem is, the device tends to run a little hotter than desired. One proposed solution is to cut some vent holes in the top. These would be roughly (1/2) inch long by (1/6) inch wide, spaced (1/4) inch apart, running across the top near the front of the device. I haven't seen many (any?) devices with vent holes in the top, so I'm wondering if there is a basic reason why not, such as the cover must shed water, etc. My questions are, what considerations arise and what sections of EN 60950 apply to this, either to allow it or to exclude it. Top openings are specified in Sub-clause 4.6.1, 4.6.4, and Annex T of IEC 60950-1. There are no restrictions on openings if the source (brick) is SELV and LPS and the unit is intended for indoor use, i.e., does not need to be protected against ingress of water. You told us the source is SELV, but you did not tell us whether the source is also LPS. If the source is both SELV and LPS, then there are no restrictions on opening sizes. Indeed, there is no requirement for an enclosure. (With SELV and LPS supply, there is no shock or fire hazard, and the enclosure is not required to prevent access, ingress of foreign objects, or containment of fire.) If the source is SELV but not LPS, then the top openings cannot exceed 5 mm maximum dimension, or 1 mm maximum width. Generally speaking, physically small devices are also low- power devices. Consequently, they require little or no cooling that would require ventilation openings. So, for physically small products, there are no openings in the enclosures. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: double-pole switching and fusing
Hi John: I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in 200202202227.oaa19...@epgc264.sdd.hp.com) about 'double-pole switching and fusing', on Wed, 20 Feb 2002: Tables 2E and 2F are invoked only by the Note 2 to Sub-clause 2.7.4. A Note is informative, not a requirement. Yes, well, Note 2 is weasel-worded. It claims to be 'informative' but some test houses hold that if Table 2E or 2F is not observed, the 'essential requirements' of the LVD are not met. Sigh... I agree with your assessment. I suppose such test houses do not understand that the LVD does not necessarily require compliance to a standard? Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: [PSES] UL 60950-1 clause 2.2.3
Hi John: I believe the authors of 60950-22 expected that user-accessible parts would comprise SELV circuits rather than grounded parts. See 2.1.1 and 2.2 in 60950-1. Grounded parts would be subject to 5.1 in 60950-1. Best regards, Rich - Original Message - From: John Cochran jcoch...@strongarm.com Date: Sunday, September 7, 2014 1:42 pm Subject: RE: [PSES] UL 60950-1 clause 2.2.3 Actually I need to meet the standard for outdoor enclosures, UL 60950-22, and clause 6.1 refers back to UL 60950-1 clause 2.2.2 and 2.2.3. The difference is the voltage limits are reduced, due to contact resistance of the body being reduced when subjected to wet locations. The clause states the voltage difference under a single fault must not exceed 30 V ac, without any mention of current. Am I reading this correctly? John Cochran STRONGARM Designs 425 Caredean Drive Horsham, PA 19044 PHONE: 215-443-3400 X193 FAX: 215-443-3002 - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] UL 60950-1 clause 2.2.3
HI John: As mentioned in my first response, you will have the same problem (half the mains on the enclosure) if you use a Class II power supply. If you talk with your NRTL, I'm sure he will accept your construction based on 60950-1, 5.1 rather than 60950-22. Your equipment is not unsafe with the ground open if it complies with 5.1. (And it will!) Best regards, Rich - Original Message - From: John Cochran jcoch...@strongarm.com Date: Monday, September 8, 2014 8:04 am Subject: Re: [PSES] UL 60950-1 clause 2.2.3 It appears that I can only meet this requirement for outdoor enclosures by either using a Class 2 power supply, or require the installer to use the external ground connection in addition to the internal PE ground. The system is safe under normal conditions, but only has hazardous voltages on the enclosure when the PE ground is broken. Are there any opposing opinions? John Cochran STRONGARM Designs 425 Caredean Drive Horsham, PA 19044 PHONE: 215-443-3400 X193 FAX: 215-443-3002 -Original Message- From: John Woodgate [mailto:j...@jmwa.demon.co.uk] Sent: Monday, September 08, 2014 2:42 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] UL 60950-1 clause 2.2.3 In message f6d1e59f218e.540c8...@bendbroadband.com, dated Sun, 7 Sep 2014, Rich Nute ri...@bendbroadband.com writes: I believe the authors of 60950-22 expected that user-accessible parts would comprise SELV circuits rather than grounded parts. See 2.1.1 and 2.2 in 60950-1. Grounded parts would be subject to 5.1 in 60950-1. Thank you. So what can the OP do? Does this need to be taken into account in a revision or replacement of 60950-22? -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk Quid faciamus nisi sit? John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] input current rating
Dear Bostjan: One of the uses of current rating on equipment is to determine that the equipment, with all of the other equipment, would not overload the mains circuit. If the actual current exceeds the marked current, then the equipment, with all of the other equipment, can overload the mains but there is no means to identify the culprit equipment. Note, however, that there is no limit on lower current than rated current. I suspect this is because much equipment has an idle mode during which the input current is minimum. Best regards, Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com