underground loop
to the other side of the breezeway and I'm pretty sure the owner won't do it.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott A Futrell
Sen
It needs to be listed and why would you put something in with a limited life
expectancy? (Rhetorical question, I know why.) What will the
homeowner(s)/managers/owners do ten years down the road when 1) it fails,
and/or 2) it has to be replaced at greater cost?
NFPA 13, 2013:
6.7.2.2 Heat Traci
Heat tracing had a limited life expectancy (ten years) a few years ago when I
looked into it. That certainly would need to be a consideration.
I'm not sure heat tracing is listed for use with CPVC or vice versa and that's
a consideration.
Doesn't Tyco have a listed CPVC for dry residential sys
And a pet peeve of mine (besides flow tests that don't meet the minimum
sprinkler/hose demand already discussed thoroughly here) is that the
coefficient of the pumper connection required by NFPA 291 [2013] 4.8 is not
applied as required to flow tests through pumper outlets.
Also,
4.8.1 If it is
Agree, always pointed in at the column (usually in the web) regardless of the
type of sidewall.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack, SET
Sent: Mon
ible blown in insulation will not
spontaneously combust and burn on it's own. I can't think of why the AHJ would
consider displacement of oxygen to work on keeping the wooden trusses from
burning but not the paper.
On Tue, Jun 30, 2015 at 6:14 AM, Scott A Futrell wrote:
> Matt,
Thanks Scot.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of å...
Sent: Tuesday, June 30, 2015 8:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Insulation
orum-boun...@lists.firesprinkler.org] On
Behalf Of Scott A Futrell
Sent: Tuesday, June 30, 2015 7:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Insulation and combustible concealed ceiling space
Has anyone ever had an issue with a combustible concealed space that has one
layer of kraft-f
Batt insulation meeting noncombustible or
limited-combustible criteria", to start.
Mark at Aero
602 820-7894
Sent from my iPhone
> On Jun 30, 2015, at 5:34 AM, "Scott A Futrell" wrote:
>
> Has anyone ever had an issue with a combustible concealed space that has one
Has anyone ever had an issue with a combustible concealed space that has one
layer of kraft-faced batt insulation laying on the ceiling (kraft side up
toward the sky) and then the remainder filled full of blown-in, non-combustible
insulation and an AHJ saying the kraft-faced insulation had to be
"Tenting" can be problematic regardless of where the vapor barrier is located.
The tent must remain intact for the life of the structure and by intact I mean
free from being disturbed by anyone in the space (electrical, cable, satellite,
other) and if there are holes or gaps from the install, se
Yes Chris, they are still out there.
I'd like to say something about NFPA 25 inspections, but that would just change
the thread, so suffice to say that they are out there and the owner/occupants
have no idea when I tell them.
I am not aware of any follow up studies.
Scott
Office: (763) 425-
I do remember this, but I don't have the article. I would think that Jeff
Shapiro could assist you in obtaining it or someone from the
homefiresprinkler.org.
Scott
Office: (763) 425-1001 x 202
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@
Colin,
The best case scenario is that you flow more water than your highest
anticipated sprinkler and hose stream, or in the case of a fire department fire
flow requirements. Without knowing your specifics the answer is yes, you
should flow more than 386 gpm.
Scott
Office: (763) 425-1001 x
Jim,
The sky in my world is not as blue as yours. When the drain comes out the side
of the crossmain (not the bottom), and is hidden in the attic, the owner often
has no idea it is there. Or, if they were told, that person no longer works
there. And when I look at failures there rarely are si
nklerforum@lists.firesprinkler.org
Subject: Re: dry systems drains in attics
What would be the point of the valve if it wasn't in a heated space as even
with a valve the pipe would be self draing following the next freeze.
On Thursday, April 9, 2015, Scott A Futrell wrote:
> Whether it is a
Whether it is allowed or not, who, over the life of the building, is going to
go into an attic to drain a low point drain?
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of
I was gonna bring up Scandaliato's testing, but figured it wouldn't matter,
Roland!
Should be same questions as any storage, right? Packaging (cardboard or
plastic), height, arrangement (side or end), racks, aisles, and so on. Then
talk about protection after watching the fire test you are
Wow Alex. You didn't provide any of that information in you initial post.
Based upon the information Tim provided, how do you leap to the conclusions and
assumptions that you made?
I would think a little more research might have to go into this before you
finalize your modifications.
Scott
O
This must be one of those design features of a hangar where the fire, the
building and the sprinkler system realize it isn't a NFPA 13 design and the
sprinklers operate differently (quicker and more effectively) with a slope
exceeding 2 in 12 then they do for a sprinkler system installed in a di
Jody,
NFPA 1031,
1.1* Scope. This standard identifies the minimum job performance requirements
(JPRs) for fire inspectors and plan examiners.
1031 doesn't delineate the requirements for life safety code inspections or
thorough inspections of fire suppression or sprinkler systems.
You need to
I'd add that there are several 'trap doors' Steve. What is being conveyed?
Do the conveyors need to be interlocked on sprinkler activation?
How wide are they?
Are there multiple levels/layers?
What is going on below the conveyors (process, fuel load, nothing, and so on)?
More...
Scott
Office: (
MIC can be present in most systems, just not active. You need to look for the
root cause. Often oxygenation.
Try Engineered Corrosion Solutions website for white papers and very good root
cause information.
http://ecscorrosion.com/
Scott
Office: (763) 425-1001 x 12
Cell: (612) 759-5556
---
I'm not sure you had any answers for your question before the thread was
hijacked.
In the long-term many things can go wrong with an underground main that is 'in
a trench' or under a floor. I've witnessed the problems with underground water
mains under floors and the cost to make repairs, and b
And, how old is the piping?
Scott
Office: (763) 425-1001x12
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mark A. Sornsin, P.E.
Sent: Monday, December 01, 2014 1:59 PM
To: sprinklerforum@lists.firesprin
the smaller droplet size which are shown to be flammable/explosive. Perhaps
because gas pockets are not supposed to be there?
On Nov 14, 2014 12:48 PM, "Scott A Futrell" wrote:
> In short, the theory was tested and it is combination of concentration
> of PG or Glycerin, type
In short, the theory was tested and it is combination of concentration of PG or
Glycerin, type of sprinkler, orifice size, pressure, and distance to ignition
source and is all available on the Fire Protection Research Foundation website.
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
This has been an interesting thread.
It's a retirement home so the sprinkler system would seem to be essential to
me, not that any aren't, but...I’d like to know my parents were living
somewhere that had a sprinkler system installed properly and not by cutting
corners, or making guesses. And
Jay,
Totes that "...are being cleaned of any solution that may have been in them..."
are considered FULL by definition in the International Fire Code (IFC). So, IF
the IFC is enforceable your client may have a different problem on their hands
that they are not aware of, and don't want to hear
Very well put Cecil.
RIP Dr. Bryan. He will be missed by many, and by our industry.
Scott
Office: (763) 425-1001 x 12
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Sprinkler Academy - C Bilbo
Sent: Fr
Usually it is something else related to it Craig. What is the make,
manufacturer and year of the sprinkler? I have files on sprinkler ops and
several do have a history of operating without known causes.
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message-
From: Spri
For 'control' mode sprinklers, but for suppression mode (e.g. ESFR), the spray
development around obstructions is a different consideration.
Scott
Office: (763) 425-1001 x 12
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler
Chris,
Call Muellar Gauge in New Hope. I'll bet they can explain and then let us know.
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo
How cold is the air conditioning the space? Are pipes and sprinklers in front
of, or near colder air used to maintain 38 degrees?
Scott
Office: (763) 425-1001 x 12
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
B
CH2MHILL Extension 74102
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott A Futrell
Sent: Monday, June 23, 2014 5:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: CMSA Sprinkler Question
74102
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott A Futrell
Sent: Monday, June 23, 2014 4:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FW: CMSA Sprinkler Question
Okay. Thanks John
r?
If not, who else has one?
Thanks and thanks John!
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message-----
From: Scott A Futrell
Sent: Monday, June 23, 2014 11:13 AM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: CMSA Sprinkler Question
Forumites:
Forumites:
I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013.
Are the only CMSA sprinklers available the two below?
Reliable, N252 EC - CMSA, RA0842
Tyco, Ultra K-17-231, TY7153
Viking, K19.6, VK592
Thanks!
Scott Futrell
(763) 425-1001x12 Office
(612) 759-5556 Cell
___
That may be the best explanation ever!
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Roland Huggins
Sent: Friday, June 20, 2014 10:04 AM
To: sprinklerforum@lists.firesprink
Totally agree, however if the concept isn't understood it morphs to the email
that started this thread. 400 gpm through old 4" or 6" is a bigger problem.
The right way is to calculate to the flow, get the information to do it right.
If it is a single-feed loop and you are on the remote end o
It depends on how far away the flow test was taken, whether it is looped or
gridded, and what the elevation changes are. All of that needs to be
considered and isn't by just calculating to the "point of connection".
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message
Sprinklers included Duraspeed on the frame into about 1977, then the similar
sprinkler included F950 on the frame.
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Corco
F950's in the mid-seventies (1977 or so) with Duraspeed before that, and it
looked the same.
Steve, did you get my email about CA questions?
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.or
My posts are making it to the Forum Richard.
I would suggest you start by contacting the tube manufacturer and find out
exactly what temperatures could be expected in those areas under the most
extreme conditions.
Scott
(763) 425-1001x12 Office
(612) 759-5556 Cell
-Original Message-
No, but is water quality an issue? Is it non-potable? How old is the UG?
Scott Futrell
(763) 425-1001 x12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Le
Tony,
Sometimes people (especially older people) turn the heat up and it does get
above 100 in the closet.
Sometimes furnaces don't operate properly and the high limit switch on most
furnaces is >100, even greater than 130, I've seen them as high as 175 in
furnaces in apartments that serve the
I frequently see sprinklers rated at 155°F in utility closets with furnaces
that operate and cause a great deal of damage.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lis
Todd,
I have that problem here and the AHJ has required the owner to have an
engineering analysis that we are in the working on. Two wall hydrants were
added at some time and were never calculated. Then they added two hydrants
with overhead supply from the main valve assembly. All of that of
Todd,
The first question would be why were they there originally? If it is a hydrant
issue (lack of) and they conceivably could be used by FF's with either of the
sprinkler systems operating then I'd say you should add your hose at the point
of connection between the wall hydrant supply and th
Further to Brad's response, where is the insulation? Is freezing a concern?
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jay Stough
Sent: Tu
014 6:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 25 & Antifreeze Comment(s) RETORT
No Scott please don't tell me how it ends, I have not seen it yet ;) seriously,
I saw your name on that final report- are you totally Anti Anti freeze now, no
if ands or buts?
> On
A child lit a couch on fire with matches and the sprinkler operated with the
resulting fireball injuring her and her mother. Official damage report:
limited to point of origin, except for signs and damage from explosion -
windows blown out remote from the ignition.
Do we need to say more Brad?
How do you do that when 13 requires the drain off the bottom of the pipe and
the inspectors test off the top of the highest most remote sprinkler?
Scott Futrell
(763) 425-1001 x12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mail
Douglas,
You really need to accurately determine what the highest ambient temperature
will be in the paint booth before choosing a temperature rating.
Scott Futrell
(763) 425-1001 x12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
We've done this as a last resort with a dry system, without problem.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Thursday,
But, if you are doing an inspection in accordance with NFPA 25, and according
to that document and the Technical Committee it assumes the original
installation to be correct, you shouldn't comment on the incorrect location of
the gauge because that is not in your scope. Just record the pressure
Interesting analysis Chris that I would agree with in general, however, I
assume this is a dry system, right Steve?
If so, I would then assume that it is at least being partially trip tested
annually, right? Of course it should be fully tripped tested every three
years, but I am further assumi
I like the replace it all option...
How old is the system to start with?
You need to replace all the sprinklers, if some have "popped" you don't know
how many others may be damaged.
What about gaskets in grooved couplings?
Is the water supply now equal to the original pump and pond? If not, pipe s
ernational Drive
Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A
Fu
No code restrictions, but certainly foam systems concerns. 55 gallon drums to
second floor with stairs? Bladder tanks? Lay 'em down to replace bladder that
gets torn. Craig, am I missing something? If not, I've seen this before and
it gets ugly real fast. I've worked on an existing hanger
IMHO Roland, if I understand you correctly, I respectfully totally disagree.
We do not have anything in place, at any level, to verify the design,
installation, inspection, testing, or maintenance of existing or new sprinkler
systems. Technically, the legally adopted Fire Codes give the AHJ th
is going to
> be provided
if
> just those 3 sprinklers go off would be a strong argument...how big is
> the room?
>
> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell
>
> -Original Message-
> From: sprinklerforum-boun...@lists.firesprinkler.org
> [mailto:sprin
Sometimes...just sometimes, the AHJ might accept reduced hose streams if you
can get the calcs to work otherwise. It might be worth the try. 1) they
shouldn't need hose except for mop up and 2) it shouldn't take all the
sprinklers operating in the design area to control it, so if everything work
No one ever answered my first response. Who specified what?
What did you base your bid upon?
Owner/GC's fault IF they gave you the flow test and the design criteria and it
won't work, but if it works, but with larger pipe and bigger K's then you bid
it's not their fault.
Your fault if they didn'
More information please. Who gave who flow test and design criteria?
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Johnson
Sent: Thurs
forum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A
Futrell
Sent: Friday, September 06, 2013 2:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shoulder Nipple
Just for fun I looked in my first red book, 1974, it allows 1/
Just for fun I looked in my first red book, 1974, it allows 1/2" and 3/4" close
nipples - no pipe weight or schedule indicated. 3-7.5.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...
Again, first step is the Fire Code. I'm not writing a dissertation on what you
need step-by-step because that can be a long list and varies with every answer
(some of which Craig has below and some he doesn't); you need to know you have
to start with the fire code - unless it is military/govern
The proper place to start is the applicable Fire Code. Doesn't matter how
small, the Fire Code is the FIRST STEP. It will probably end up as Steve
wrote, between OH 2 and EH 2, but there may be other issues, too, that are
beyond the sprinkler design.
In open use has the potential to damage
Hydracad is great and flexible and Hydratec has been around since at least the
early 1980's.
Scott Futrell
(763) 425-1001 x12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Specifically what types of "leaks are excavated and repaired" every year?
Glands? Joints? Pipes? fittings? Valves? Hydrants? It seems if we know the
repairs (why it is leaking), then the questions others have posted might be
appropriate follow up.
Scott Futrell
(763) 425-1001 x12 Office
(612
Vince,
Not conflicting at all. You asked the Forum to answer a storage questions
without: 1) storage height; 2) storage configuration; 3) packaging materials;
and more. You shouldn't have gotten an answer without that information. Call
Steven.
Scott
(763) 425-1001 Office
(612) 759-5556 Ce
Steven Scandaliato has the video and we show it in our class...not OH 2. As
usual it is not what somebody else did, it should be storage configuration,
height, and packaging...
Scott Futrell
(763) 425-1001 x12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun..
Craig,
The details of where to use, where not to use, what percentages to use, and so
on are spelled out in NFPA 13, 13D or 13R, whichever is appropriate to your
project. If you don't have those documents they are available free online
through NFPA.
Scott Futrell
(763) 425-1001 x12 Office
(
Steve,
There is only a ten year life expectancy for the heat tracing, so that should
be a long-term consideration for the owner.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@list
That is happening all over. Builders won't let you do anything, including
sprinklers, until they are complete. Now how many will retrofit?
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-
.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
da...@mfp-inc.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A
Futrell
Sent: Tuesday, July
Forest,
Ben doesn't have to retrofit the Ponderosa, it is new homes only. That's one
of the misconceptions.
When I had my home built the builder would not allow me to have sprinklers
installed...that is one of the reasons we need to adopt the IRC.
Builders make more money repairing houses wi
Like that form gets filled out properly and thoroughly.
Did I hit send?
Scott
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron
Greenman
Sent: Friday, July 19, 2013 12:51 PM
To: sprinklerf
Todd,
Plastics Handbook. I don't have one though.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Tuesday, July 02, 2013 7:2
VERY WELL said, my friend.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John
Denhardt
Sent: Thursday, June 27, 2013 9:23 AM
To: sprinklerfor
Hmmm...back to the fire code and building code first. Is it required to be
sprinklered? Has the architect taken any advantages to area, height,
separation, etc., based upon sprinklers? If so, gas or dry chem. don't
substitute for required sprinklers...
Scott
(763) 425-1001 Office
(612) 759
231C goes back to 1971, but the real question is what did the building or fire
code require?
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Da
Mike,
NFPA 72, 2007, Disposition of Signals. 8.3.7
You'll find Central Station required responses.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behal
Too late for most anything. It is attached to a funding bill that will be
passed and although the Governor vetoed this NAHB/BAM (Builders Association of
Minnesota) direct bill in 2012, he cannot line item veto it as far as I know.
Ten legislators (almost all of whom have already voted for the
The Fire Code (regardless of NFPA 1 or IFC [2012 - 901.7]) and good practice
require it as well as NFPA 25 [2011 - 15.5.2(4)]. You can look at these
references for other ideas, but the AHJ has the codes and standards to use.
NFPA publishes statistics on fires in sprinklered buildings that have
This sprinkler appears to be listed for use with only four Reliable K5.6
sprinklers.
6.2.8 [2013] Sprinklers subject to mechanical injury shall be protected with
listed guards. If they aren't made by the manufacturer for their specific
sprinkler, then many are not listed...
Scott Futrell
(76
It does Craig if you add pg.png to the end of the link
Scott Futrell
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, March 18,
Is CPVC involved at all? Could be issues with the CPVC if it is exposed to the
temperatures either directly or through thermal expansion.
Scott Futrell
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-
Bill,
Diver - Wet or Dry Tank Inspection out of Kentucky. Jay Hoffman. He can
probably assist you with which way to go too.
Scott Futrell, PE, FSFPE, CFEI, CFPS
(763) 425-1001 x 12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:
Rod,
I know they are available on the NFPA subscription service website, I don't
know if they are available otherwise.
Scott Futrell
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkl
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Scott A Futrell
Sent: Tuesday, August 28, 2012 4:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Antifreeze Update
in Rod and Mark's neighborhood there are contractors using
in Rod and Mark's neighborhood there are contractors using propylene glycol in
CPVC systems (that's a no no) over 50% (that's another no no) and they know it
because "what else can they do?".
Scott Futrell
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerfo
If they aren't properly protected the bolts on the couplings will be the
Achilles heel. The safe, long-term way would be to use proper underground pipe
and fittings, in accordance with their listing.
Scott Futrell
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sp
Steve,
I probably have what you are looking for in the office if you don't get it by
tomorrow send me a note and I'll look for it.
Scott Futrell
(763) 425-1001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...
UL tests sprinklers at a minimum operating pressure of 7psig (UL 199). The
first of many questions (that I will not ask): Are you going to propose design
operating pressures less than their listing and testing?
Scott Futrell
(763) 425-1001 x 12 Office
(612) 759-5556 Cell
-Original Messa
Scot,
I responded to the specific question (and assumed everyone understood the 30%
increase would be applied to the roof/ceiling). However, I would not recommend
a dry system in-rack if you can avoid it. Quell, preaction, other might be
better if possible. Also, an engineered solution where
Scot,
I don't see anything that sends you back to 11.2.3.2.5 to increase the in-rack
design requirement by 30%. 11.2.3.2.5 is an area of sprinkler operation
increase, not a number of design sprinklers increase. Intuitively, yes.
Prescriptive, no.
Scott Futrell
(763) 425-1001 x 12 Office
Agreed. If they don't submit paper copies of plans, calcs, and product data it
doesn't get reviewed. You can't perform inspections without a plan, they need
a copy back with comments, and I need a copy for my files and there is no
reason for me to pay for the cost of plotting, printing and cop
To specifically answer this questions, yes, Chapter 7 Hydraulically Designed
Sprinkler Systems, 1976 edition with light hazard and the three ordinary hazard
curve sin Chapter 2.
Scott Futrell
(763) 425-1001 x 12 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun.