RE: NEC Questions
Richard - Bob Johnson's response on your Q1 is on the money. wrt your Q2 and outlet strips, there may be the additional consideration that you may impinge on the scope of UL1363, Relocatable Power Taps (formerly a desk standard for Temporary Power Taps), Listed under the CCN XBYS. Point being, the final assembled product may have to comply with UL1363, with the internal measurement device having requirements from UL3111-1. [This was the case for relocatable power taps that incorporated secondary protection for telecommunications circuits, where the latter, internal components were required to comply with UL497A.] Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Richard Meyette Sent: Tuesday, April 30, 2002 10:05 AM I have a couple of questions regrading the National Electrical Code: 2) Consider the same power measuring circuit installed into a direct plug-in (NEMA 5-15P) with a single outlet receptacle (NEMA 5-15R) or into an outlet strip with a 16 AWG power cord with several outlet receptacles. Assuming that the measuring circuit is provided with a suitable fuse for overcurrent protection, are the outlet receptacles required to be protected by a 15 A fuse or circuit breaker in the device or can they rely on the circuit breaker for the branch circuit for overcurrent protection? The UL product standard for this device is UL 3111-1 (Electrical Measuring and Test Equipment), which is harmonized with IEC 61010-1, requires an overcurrent protector to be fitted within the equipment for all devices connected to the mains supply (9.6.2). There are no US deviations in this standard that would allow the circuit breaker to provide this protection, so based on this I would assume that a 15 A circuit breaker of fuse would be required for the NEMA 5-15R receptacles. I would also assume that a 20 A overcurrent protector would be required for a NEMA 5-20R outlet receptacle. However, the UL product standard for household appliances (UL 60335-1) does have a US deviation to a similar requirement for overcurrent devices (19.1, Note 2) that states the The PROTECTIVE DEVICE in the fixed wiring does not provide the necessary protection. However, the US deviation states The circuit protection device is permitted to provide necessary protection. If I am interpreting this correctly, a household appliance in the USA could rely on the panel breaker for overcurrent protection. Any comments? Thanks in advance for anyone willing to wade through this and send me a response. Richard A. Meyette. PE meye...@pacbell.net --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Switch Inrush Ratings
I haven't followed the Woodgate approach :), hopefully the information Rich discovered also includes such relevant concerns as: power factor for general use power factor for inductive/motor loads power factor for pilot duty loads heavy power factor (perhaps as low as 0.10) incandescent There also used to be things called TV rated switches (UL had TV-1 through TV-5, IIRC) Further to the Woodgate approach, if it's not on the internet now, wait a few weeks and try again. Stuff and junk is added daily. This is no magic bullet; there're things I've been searching for for years that haven't shown up yet. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com From: Rich Nute Sent: Thursday, January 10, 2002 12:27 PM Taking John Woodgate's usual response to such an inquiry, I did a Google search on inrush. Surprisingly (to me), there is a wealth of reasonably good info on the web under the subject of inrush, including switches rated for inrush current. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
RE: Banned Substances in Sweden
Jim - Try the Swedish EPA at http://www.internat.environ.se/ Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Jim Eichner Sent: Friday, August 09, 2002 11:51 AM We have had a request from a customer to verify a lack of certain substances in one of our products. Rather than provide us with a regulatory-based list of substances, they have provided us with a particular company's proprietary list of substances it bans (and that company is in no way involved in the dealings between us and our customer). Does anyone know where I can get an official list of what substances Sweden bans in electronic products? Thanks as always, Jim Eichner, P.Eng. Manager, Engineering Services Xantrex Technology Inc. Mobile Power --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
IEC 60417 symbol library
All interested - The IEC has just announced an upcoming on-line IEC 60417 symbol library will be made available soon (I checked and it's not yet available through the IEC Web Store). Don't expect to access them gratis, as they once were on the Chiba University, Ikeda Lab web site (even though fee based, this could be very handy). Pricing was not announced. Access to the databases is by subscription: clients can purchase a subscription for a 3, 6, 12 or 24-month period giving them access to the full collection of graphical symbols. Refer to http://www.iec.ch/online_news/etech/prodserv.htm For further reading on the concept of database standards from the IEC, browse to http://www.iec.ch/online_news/etech/arch_2002/etech_0702/foc us.htm Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: NRTL/UL Safety Approval in California
Greg - In point of fact, no NFPA standards are addressed by federal law (keep in mind, regulation is not law, even if given the power of law). Even 29CFR, as far I have seen, doesn't outright adopt the Code in toto, but references portions of it variously as mandatory or recommended. NFPA 70 is an model/adoption code and no AHJ is under any obligation to use any version, save as required by municipal, county or state laws. Even so, there are some jurisdictions using NFPA 70-1984 (I don't recall which), rather than the latest (2002). Also, AHJs, at their discretion, may adopt only portions of NFPA 70, mix and match bits and pieces from various editions, or not use it at all. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Greg Galluccio Sent: Friday, August 02, 2002 9:07 AM My understanding is that the federal law (NFPA Code) is the minimum requirement and that state and local authorities can and do apply additional requirements as they deem appropriate. Greg Galluccio --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Marking Languages for Canada
I must throw in with Rich Nute on this topic. The need for a marking in this instance is very context sensitive: if the marking is required by the US standard, but not by the Canadian standard, the marking does not need to be translated into French. Otherwise, there is no legal requirement. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Nema 5-15R sockets
Jim - There are no orientation requirements in the NEC or CEC, except as required by product marking, such as for some GFCI receptacles. Dimension requirements are secret, donchaknow. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Jim Eichner Sent: Friday, July 19, 2002 10:40 AM A couple of questions about our standard North American 120Vac socket: 1. Orientation: We have lots of people in the office here on both sides of this one, and I can't find a normative reference in the CEC or the NEC. Which is the correct way up when installing a socket on a wall - ground pin above the L and N blades, or L and N above the ground? What is the code reference for this requirement, or is there none? 2. Dimensions: Can anybody share the spec's for the dimensions, with tolerances, of the line, neutral, and ground blades for this configuration? I'm sure it's in the UL and CSA standards but I don't want to spend hundreds of $ for a one-time question. We have no on-going need for these standards! Thanks in advance for your help, Regards, Jim Eichner, P.Eng. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Shock and Vibration
Bill - Go to the IEC web site (http://www.iec.ch/index.html). From Search, select Information on a TC/SC under Technical Work, then enter 48D when the page loads. You'll see the chair and secretary names and a link to a list of links to member states that then link to contacts from whom you might obtain a copy of the secretariat paper you need. Also, if you go to the IEC web store and search by committee, you'll find a host of standards created by TC48. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Fleury, Bill Sent: Wednesday, June 12, 2002 8:06 AM Hi All, Does anyone know what IEC 48D (Secretariat) 76 would be? It is called out in the IEEE 1386:2001 standard for CMC cards as shock and vibration requirements. I assumed that IEC 48D was a standard but apparently that is not the case. SC 48D is a Subcommittee dealing with Mechanical Structures for Electronic Equipment; so I'm thinking that IEC 48D (Secretariat) 76 is the proceedings from one of their meetings but I have had no luck in locating any information about it. My Marketing gurus are asking me if we meet these requirements but I don't know what the requirements are; so its kind of hard to give them an answer. :-) Thanks for your help. Bill --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
the experts (was: RE: Multiple Product Variants under EN60439)
This reaches back a bit and I hope you'll forgive my tardy entrance. I come from a test house background and would like to shed some light on certain assertions made in this thread. Scott Douglas tells us, In my years of being a compliance type, I have found many cases where I could not get an agency or test house to make a bold statement about this or that. Often one can accept that and understand why they will not commit. For one reason, they do not want to be the one sued by some disgruntled customer because something happened (or didn't happen). But just as often, I have found it extremely frustrating that I cannot get a straight answer from the same people. It's also important to keep in mind that anything said by the engineer might be contradicted, when presented to their reviewing engineer, leading to personal embarrassment. A bad decision could also lead to a precedent that is difficult to be rid of. Mulling things over is good for all concerned, especially the public's safety. I do agree, though, with Scott's advice to question anything that doesn't make sense. Insisting on clear engineering rationale is good practice and will even help the test house engineer maintain clarity. Sometimes the (unsatisfying) answer might only be it's a compliance issue, implying a standards revision is called for. Chris Maxwell advises, Personnel at a lab may deal with the same standard everyday. They should know the standard like the back of their hand. This is sometimes true and sometimes not true. In one department, I recall handling an average of 15-25 and as many as 40 projects at any given time, usually with little customer or technology overlap, often with only a little overlap in product standard. [In the case of industrial control equipment, the range covered products are so broad that it can be daunting to know even half of what an expert might need to know; a good understanding may be more difficult to muster (thank goodness for dash standards - a relatively recent innovation).] At any given time, for example: relays, branch circuit breakers, cartridge fuses, Class 2 transformers, unit substations, pool and spa equipment, panelboards, energy management equipment, printed wiring boards, general purpose transformers...the list goes on. It can be a juggling act to keep the requirements clearly in mind for any particular product and standard, especially in busy times. There are also relatively new employees that are still cutting their teeth on a standard, those that transfer between departments that handle different products and have to learn new standards, almost anything of the ilk. Nevertheless, there are some groups within these organizations that deal with relatively few standards and perhaps the back of the hand idea applies (for instance, ITE and telecom equipment, polymeric materials), but it depends sharply on the internal structure of the test house and how they run their businesses. The odds are great that we'll all act the teacher to test house engineers in our careers. Many serving on standards making panels on this forum fulfill this function regularly. Chris is right, though, that it can make a big difference if the test house engineer is familiar with a customers products and design philosophy. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Unit and prefix capitalization
While this is belaboring the issue and, other than if I happen to run across any relevant standards references, it should be noted that most new and many updated standards we have to deal with are written using SI as the primary and sometimes only units. Also, in most scientific and engineering circles, SI units have been in use for decades, including NASA, medicine, general research, and the like. The few hold outs are business interests and general populations (particularly in the US). An anecdote: my dad worked in heavy construction and was an ardent objector to adoption of SI units in the US. As a creature set in his ways, it was just so much rigmarole and he didn't want to take the time to understand a linear measurement system that wasn't divided as he was inured. Yet for many years, he'd been setting grade using tenths of feet. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Vit Gorod Sent: Wednesday, July 17, 2002 12:07 PM Dear Chuck and Peter, When there's no enforcement, ther's no will. Correct me if I am wrong. You may not get many enthusiastic responses because since 1997 the US governement gave up on all decades-long efforts to introduce metric system. Whether we like it or not, the SI comes into play only under customer pressure (EU requirements, etc.- let's not forget that only 3 countries in the world do not use SI). --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
unit and prefix capitalization
RE, our recent discussions on unit prefixes: I ran across a standard in my stash, IEC60027-1, Letter Symbols to be Used in Electrical Technology is another reference for this topic. The base standard is dated 1992, with Amendment 1 dated 1997. The IEC web site identifies four dash standards, the others being: Letter symbols to be used in electrical technology - Part 2: Telecommunications and electronics Letter symbols to be used in electrical technology. Part 3: Logarithmic quantities and units Letter symbols to be used in electrical technology. Part 4: Symbols for quantities to be used for rotating electrical machines Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: EN60950 3rd vs EN60950-1
Ron - I do not have a view on publication of EN60950-1 in the OJ, but the IEC Web Store indicates a Technical Report Form was created in APR2002 and is available. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Ron Pickard Sent: Friday, July 12, 2002 9:30 AM To all, I am trying to decide, not if, but to which of the above standards must be complied with on a logistics basis. Does anyone have any knowledge as to when EN60950-1 harmonization will get published in the OJ? When is it expected? I know that EN60950-1 is not yet officially harmonized under the LVD yet, but EN69050 3rd Edition is. I do not want to go through the time and expense (not insignificant) to acquire CB certs/reports to IEC/EN60950 3rd to only find out that I have to go through it all over again for conformance to IEC/EN60950-1 shortly thereafter. Management will not find it palatable going through this twice when only once would have sufficed. Best regards, Ron Pickard rpick...@hypercom.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Telecomm Safety clearance
Joe - I don't have a copy of EN60950-1, however IEC60950-1 includes a note to Subclause 6.1.2.1 that reads, In Finland, Norway and Sweden, there are additional requirements for the insulation. In the EN version, what is difference from the base standard this note refers to, if the Supplementary insulation requirement no longer exists? Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Joe Randolph Sent: Tuesday, July 09, 2002 9:23 AM Hi Alex: 1) In the Third Edition of EN 60950, Annex ZB no longer requires supplementary insulation for Norway and Sweden. Only the 0.4 mm distance through insulation requirement has been retained, along with the stipulation that capacitors bridging the isolation must be Y2 caps. The creepage/clearance requirement now reverts to the requirement called out in the main body of the standard (typically 1.6 mm and 1.0 mm). That being said, I continue to use the supplementary values of 2.5 mm and 2.0 mm in designs where the room is available in the layout. Joe Randolph --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: 21 CFR part 11 certified FDA
Terry - Part 11 of 21CFR is related to electronic reporting and electronic signatures for submittals to the FDA; I don't believe there's any certification program for Part 11, just a process/procedure to follow. Refer to http://www.fda.gov/ora/compliance_ref/part11/ for details. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Terry Meck Sent: Wednesday, July 03, 2002 11:22 AM To: emc-p...@majordomo.ieee.org Subject: 21 CFR part 11 certified FDA Hello again, Does anyone in this forum have any knowledge about United States FDA 21 CFR part 11 certification. What is the process? Are there independent labs that test or witness test software? I have been asked these questions and have no experience in this direction. This may not be the forum to ask. If so please ignore this message. Thanks! Best regards, Terry J. Meck Senior Compliance Engineer --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Question: Discharge capacitance 0.1 uF
John - I respectfully disagree that the standards bodies need to do anything. It is the designers that must be aware of the advancements of technology (such as described by Gert) and update their practices accordingly. [Low ESR / High Q caps are a good thing.] While I have no doubt about the potential effects of reaction hazards (I've put two fingers across a circuit calibrated to deliver 3.5 mA at 120V line potential; the infamous Walter Skuggevig apparatus), the safety standards should not be prescriptive. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: John Allen Sent: Thursday, September 19, 2002 4:13 AM Gert Thanks for that investigation that I have not had the time for recently! Now, maybe, the standards writing committees will begin to take this issue on board and do something about it as the problem is generally technically trivial to solve - the major issue then being to ensure that the bleeder device is always across the capacitor, and is not isolated from it by a switch or contactor that the operator can put in the open position before disconnecting the supply. John Allen --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Safety of Indicating LEDs
Rich and Scott - Irrespective of how any test house decides to address indicator LEDs, my discussions with TC76 members and contributing experts, including Bob Weiner and Jerome Dennis, as well as the remainder of the members at a panel discussion at the 1997 Laser Institute of America International Laser Safety Conference, it was not the intent of IEC60825-1 to apply to faceplate indicator LEDs of electrical equipment. Rather, the concern was for higher powered LEDs of up and coming technologies. It was the consensus of the aforementioned panel that the LED manufacturer's data sheets should be considered to provide adequate evidence of compliance, should the question arise. (One industry representative to the Infrared Data Association in attendance was particularly vociferous at his perception of injustice doled out to the lowly LED by IEC60825-1 and welcomed this as a step in the right direction.) It was further discussed that most LED data sheets use units of Lumens and Candela more often than W, Wcm-2, J, Jcm-2, or any other set of units found in IEC60825-1. The conversion is not always straight forward, since the measurements on data sheets aren't necessarily at the 20cm accommodation distance or using the measuring system in IEC60825-1, but if analysis supports compliance without extraordinary dalliance with the data, that the data sheets can and should be considered good enough. (Can and should are understood to not imply will or shall.) Far be it from certification houses to either be privy or care about the standards committee intent, when they are applying what amounts to a problematic standard (one hears how problems certainly didn't end with A11 to EN60825-1). There are also some certification houses that place so little faith in manufacturer's data sheets for either LEDs of diode lasers that they insist on performing wavelength measurements, in addition to power and energy measurements, with only the justification of needing to be certain, yielding uncertain value with respect to safety. I haven't heard from any TC76 member in many months, so if any members of this list are TC76 members or contributing experts, please add to this discussion. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Rich Nute Sent: Wednesday, February 20, 2002 10:25 AM Hi Scott: The scope of EN 60825-1 says LEDs are included whenever the word laser is used, meaning they are to be evaluated the same way lasers are. Does this apply to status indicating LEDs (non-lasing)? If so, are manufacturers expected to test every status-indicating LED on the product as if it were a laser? Yes. At least one certification house demands measurement data for each indicator LED. Emission class must be identified on the product or in the manual. (Note that emission class is determined under single-fault conditions in the driving circuit.) However, in practice, other certification houses use a get-out for indicator LEDs. Usually this is in the form of a not tested, but may be required by some authorities statement in the report. Most indicator LED manufacturers do not know of EN 60825-1, and have no idea how to test. Measurement is not easy, especially the determination of the aperture. Most indicator LEDs will open before achieving Class 2 emission levels. The above does not apply to automotive LEDs or to traffic signal LEDs. Best regards, Rich --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Japan mains voltage
Darren - the Japan mains voltage in the range you request is 100V. As I understand it, though this is open to correction, Japan has both 50Hz and 60Hz distribution systems, depending upon where you are located, even on the large island. I do note, however, that the US Dept. of Commerce's publication, Electric Current Abroad, indicates only 50Hz. I have other sources that indicate both 50Hz and 60Hz. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Darren Pearson Sent: Wednesday, February 20, 2002 4:46 AM Can anyone tell me what the mains voltage is in Japan, I think it is 110V but I do not know the frequency. apart from this, does any one know of a web site that gives information about the mains voltage and frequency of various countries ? Regards Darren. Darren Pearson Radio Telecom Approval Services Genesys Singleton Court, Wonastow Road Monmouth, NP25 5JA UK Tel: +44 1600 710300 Fax: +44 1600 710301 email: dar...@genesysibs.com web: www.genesysibs.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: [URGENT] Need some information about NEBS..
Joe - Your statement is not in all cases. Please refer to GR1089, 4.5.3, R4-3, -4, -5, 4.6.1, and CR4-29 Although not a requirement, refer also to 4.5.13, Item 10, related to R4-18. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Joe Finlayson Peter, NRTL Listing is not a requirement for CO equipment per GR-1089 although every one of our customers (CO's) requires it. You'd meet the requirements of the standards but you'd have a tough time selling it. Thx, Joe -Original Message- From: Peter Merguerian Tania, Your state that NEBS requires UL1950 safety testing. This may be true for CPE but not equipment sitting at the CO. Please correct if I am mistaken. This e-mail message may contain privileged or confidential information. If you are not the intended recipient, you may not disclose, use, disseminate, distribute, copy or rely upon this message or attachment in any way. If you received this e-mail message in error, please return by forwarding the message and its attachments to the sender. PETER S. MERGUERIAN -Original Message- From: Tania Grant Michelle, I am providing you with a generic test matrix of several years back of an actual product that underwent NEBS compliance testing. I have stripped out any product references. Please note that test duration and cost will differ depending upon your particular product, and does not include any safety testing to UL 60950 even though this is also a NEBS requirement. Thus, the time and cost will increase. Also note that, depending upon your location, not all of these tests can be performed by a single test laboratory;-- you get to ship your product around. Be also aware that the same can happen even though the lab states that they will take care of everything (then they sub-contract it to other labs!). You will also need to have one or more of your people at the labs to assist in EMC immunity testing ESD testing, to package and unpackage units/modules/equipment. Packaged tests require that certain parameters are tested prior to packaging (you need a viable product), then come the packaging stress tests, then you unpackage the equipment and repeat tests to see which parameters failed. Brutal it is, as Mike stated. The test duration increases as you find that certain parts of your product need to be redesigned. As was also previously stated, you need to make sure that the whole engineering team reads the GR-63 and GR-1089 standards and understands the requirements. No sense spending money on lab tests for obvious failures. Tania Grant taniagr...@msn.com - Original Message - From: Michelle Cho Dear all, I need some help about something called NEBS(Network Equipment Building System). The whole procedure... What exactly the NEBS is and where can I do the testing? How much? How long does it take? Thanks in advance! Michelle --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Flammabilty requirement for cloth used on loudspeaker / UL6500
Pierre Rich - At one time, I had to perform such testing, but it's too long ago and was so infrequently necessary that I've lost all details. However, I did save one of the tablets in a 35mm film canister. My note on the outside says hexamethylene tetramine C16H12N4, that last bit being the precise chemical composition. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Rich Nute Sent: Wednesday, February 13, 2002 11:07 AM Hi Pierre: Reading the standard, I understand that the cloth used on the front of the loudspeaker (external to fire enclosure) has to be tested according the tablet test (see Table 13). As I recall (from the UL standard), the tablet is hexamine. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: UL1492
Richard - If the monitor contains a CRT, the requirement in question may arise from 21CFR, rather than UL. The responsible company needs their name and address marked on products. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Andrew Carson Sent: Monday, February 11, 2002 2:41 AM Richard The only people for certain who know what should be on a label are UL, so a quick phone call to your local office should help. But we OEM manufacture raid systems and have never had a problem with only placing the File number on the label. The file numbers are public domain information and anyone can obtain a manufacturers name and address from it. Also I have evaluated many products badged by one company, but the file number tells me they were made by someone else. So does not seem right from my past experience. richwo...@tycoint.com wrote: An OEM of video monitors has obtained UL Listing under UL 1492. They tell us that the address of our company must appear on the rating label. Is that correct? Richard Woods Sensormatic Electronics Tyco International --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Product Safety Consultants in Bay area, California.
Tajudeen - Sanmina-SCI can provide these consulting services. Please refer to my contact information, below. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services 355 E. Trimble Rd. San Jose, CA 95131-1218 V: 408-474-1322 F: 408-474-1318 M: 408-234-3529 peter.tar...@sanmina-sci.com -Original Message- From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Tajudeen Oladele Sent: Friday, February 01, 2002 10:18 AM To: emc-p...@majordomo.ieee.org Subject: Product Safety Consultants in Bay area, California. Tajudeen Oladele wrote: A friend of mine need a product safety consulting service of someone living in Bay area whose background is in telecommunication equipment installed in central offices and remote locations on issues concerning UL60950/CSA requirements. My number is 707-792-7145. Thank you in anticipation. Tajudeen Oladele. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
RE: Medical devices in Asia
An excellent resource, John. Thank you. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Jon Griver Sent: Tuesday, January 22, 2002 9:59 PM Peter, An excellent place to start your search is: http://www.ita.doc.gov/td/mdequip/regulations.html which is the US Department of Commerce site, giving information on the medical device requirements for many countries. Good Luck Jon Griver www.601help.com The Medical Device Developer's Guide to IEC 60601-1 All - I have been asked to look into medical device requirements in Asia. This would include Pacific Rim and other Asian countries (the request was not specific, despite a little prodding). I am only beginning my research and would appreciate any pointers you might be able to provide that will shorten the time it takes me in discovery. Thank you. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
Medical devices in Asia
All - I have been asked to look into medical device requirements in Asia. This would include Pacific Rim and other Asian countries (the request was not specific, despite a little prodding). I am only beginning my research and would appreciate any pointers you might be able to provide that will shorten the time it takes me in discovery. Thank you. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
RE: ul 60950-1
Brian and others interested - CSA/UL90950-1 will be discussed in a tentatively scheduled meeting in April at the UL60950 Standards Technical Panel, followed by a meeting that includes the UL60950 Industry Advisory Conference, Canadian Technical Standards Committee and the Bi-National Working Group. As to your specific questions: 1) the draft presently includes Clause 7 as is, with a pointer to Annex NAE, where the Canadian Electrical Code, Section 57 and portions of the US National Electrical Code (Articles 810, 820 and 830) are referenced. 2) the DOP is tentatively set for sometime in 2003 3) as to DOW, I quote from the 28DEC2001 UL60950 STP meeting announcement, new product submittals through April 1, 2005 will be evaluated using all the requirements in this standard, or if requested in writing, evaluated using the requirements in UL60950, Third Edition. After April 1, 2005, all new product submittals are required to use this standard. Products that were previously certified by Underwriters Laboratories Inc. to requirements in other existing applicable standards, such as UL114, UL478, UL1459 or UL1950, First, Second or Third Editions, may continue to be certified without further reinvestigation. However, after April 1, 2005 any significant changes or revisions made to such products will be evaluated to this standard. It is probable that CSA will make similar statements, in the interest of harmonization. Item 3 is both beneficial to mature/static designs and requires an additional bit of caveat emptor. If components are allowed to continue certification under older standards, use in a new product submittals may cause additional grief of reviewing components' suitability to a greater degree. Good product specifications can offer relief on this issue, both for the immediate need and to hopefully lead to attrition of components not clearly compliant with the latest applicable standard. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Brian McAuliffe Can aybody advise on the status of UL 60950-1 ? In particular, will claue 7 of the IEC on CATV requirements remain unchanged and what are the DOP and DOW ? Brian McAuliffe MCA --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
RE: What about 480 VAC in Europe? RE: 2 Phases in North America
Andrew - Please clarify something for me. Is the utility distribution star configured (WYE connected), rather than DELTA? Or are you speaking only wrt typical distribution within a building? (In the US, distribution is generally used to reference utility power distribution, for instance, distribution transformer, as opposed to facility transformer.) I ask because DELTA is used by utilities in the US and Canada to simplify connections save the unnecessary cost of running a Neutral (star reference point conductor) between distribution transformers (or so it was 'splained to me, Lucy). Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com From: Andrew Carson Terry Then nominal EU phase to phase voltage is 400VAC with a +6/-10% Tolerance. Distribution is Three Phase Star, Earthed Neutral. Snip Andrew Carson - Senior Compliance Engineer, Xyratex, UK Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014 --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Michael Garretson:pstc_ad...@garretson.org Dave Healddavehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: No longer online until our new server is brought online and the old messages are imported into the new server.
RE: electric strength test
Brian - From what I can glean from your message, the equipment is Class 1, but the secondaries do not rely on earthing for SELV reliability (hence, the Reinforced Insulation EST value). However, there appears to be some functional earthing of secondary circuits or there would be no problems for your Y caps. If the above is true, the Y caps must provide Reinforced insulation. Alternatively, there are allowances for two Y caps in series you might be able to exploit (see 1.5.7.1). If the above is not true, in that earthing of secondary circuits is necessary to maintain compliance with SELV requirements, you should not need to perform an EST at Reinforced values. Basic Insulation will do, eliminating issue for the Y caps. Irrespective of these alternatives, the implication of only needing Basic Insulation for the Y cap and Reinforced Insulation for the purposes of your primary to secondary EST is that you should be able to completely disconnect the Y cap and leave it dangling, without connecting the Y cap at all. Challenge the test house engineer for a solid engineering rationale. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Brian O'Connell Sent: Thursday, August 22, 2002 6:57 AM To: emc-p...@majordomo.ieee.org Subject: electric strength test Good People of PSTC: I am attempting to comply with both the letter and spirit of 60950:2000, cl 5.2. Note that 5.2.2 allows for separate testing, according the type of insulation required. When testing a (class 1) power supply, the withstand level for primary to chassis is Basic; and for primary to secondary is Reinforced. Typically, I will apply approx 2500vdc for Basic and 4300vdc for reinforced. But to pass primary to secondary test, 60950 says that I can allow for following: care is taken that the voltage applied to the reinforced insulation does not overstress basic Also to avoid damage to components or insulation which are not involved in the test, disconnection of ICs or the like and the use of equipotential bonding are permitted. For Pri/Sec testing, the screw connecting the Y-caps to the chassis is removed, insulation is inserted between the screw insert and chassis. A (new) agency engineer says that inserting a piece of insulator defeats the purpose of the test. For class 1 construction, it is just not possible for me to pass 4300vdc test levels without inserting my little piece of valox, unless I physically remove all Y-caps (and the unit will not operate reliably with y-caps). I have inspected units from several other companies and have determined that it was not possible to have ever passed pri-sec test levels without isolating these circuits. What test technique generally accepted by your agency engineers? TIA. R/S, Brian O'Connell Taiyo Yuden (USA), Inc. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: ( More) Laser Safety Questions
Doug - I was in no way implying the flaw was yours. The flaw lies in the practical implementation of the system. Peter -Original Message- From: Massey, Doug C. [mailto:masse...@ems-t.com] Sent: Thursday, March 21, 2002 10:40 AM Peter - I humbly submit that there is no 'flaw' in reminding folks that audits do happen and that they may be subject to one, however rare they may be. Doug Massey --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: ( More) Laser Safety Questions
All - The only flaw with this is that, based on my previous discussions with CDRH folks, they have very few auditors and no budget to hire more (this was a few years ago). Therefore, by their admission, the primary methods of keeping manufacturers and importers honest is 1) trust in the manufacturer's basic honesty 2) complaints from competitors, customers, etc. 3) field incidents Their primary concern was keeping up with the laser light shows, which they said they could not set aside auditing on (and for good reason). As a test of the presumption, has anyone on this list ever had a CDRH auditor in their facility, other than related to a laser light show? Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Massey, Doug C. Sent: Wednesday, March 13, 2002 6:51 AM Hi Jeffrey, I've seen answers to this post regarding enforcement of the IEC standard, as well as to the CDRH rules. However, no one has mentioned FDA audits. The FDA does conduct periodic audits at the manufacturer's location as reported in the Product Reports and Annual Reports submitted to them. The auditor will check record keeping, quality control, and product design aspects such as proper labeling. My company has been producing laser products for many years, and only one audit has been conducted, that anyone can remember. I was the representative during that audit, and I commend the auditor on his professionalism and thoroughness. The auditor was a pleasure to work with, but he was very thorough. Rather than a 'let me see what I can nail you on' attitude, the auditor I dealt with had a 'let me see if I can help you improve your compliance process' attitude. The auditor will call ahead and let you know the date for the audit - an appreciated courtesy, but the date is not negotiable. Note that the FDA only has jurisdiction over manufacturing locations within the US. That's why it falls largely to customs to enforce imported goods, I presume. It is also noteworthy that the FDA has a very broad scope and generally has much bigger fish to fry than a manufacturer of low-power laser devices - I think that's why the frequency of audits for manufacturers like us is so low. You may never have the pleasure. For complete information about penalties and other administrative topics, check http://www.fda.gov/cdrh/radhlth/fdcact5c.html , the Electronic Product Radiation Control section of the Federal Food, Drug, and Cosmetic Act. Section 360pp covers Enforcement and Penalties. Hope this helps. Doug Massey Lead Regulatory Engineer LXE, Inc. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: CSA Mark
Peter - Browse to http://www.csa-international.org/certmarks/ At the bottom of the page is a notation to contact CSA customer service for artwork and a link to contact information. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Peter Merguerian Sent: Wednesday, March 13, 2002 4:52 AM Dear All, Does anyone know where I can download the CSA Mark? PETER S. MERGUERIAN --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: ( More) Laser Safety Questions
Jeffery - I have no answer to the enforcement question for the US, but I suspect it's complaint and incident driven, as the EMC regulations historically have been. For NRTLs, the acceptance of previously certified Class I lasers incorporated into other equipment is based on CDRH Laser Notice 42, available as a part of all Laser Notices at http://www.fda.gov/cdrh/radhlth/pdf/laspol01.pdf Links to other useful information is available at http://www.fda.gov/cdrh/radhlth/index.html Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Collins, Jeffrey Sent: Monday, March 11, 2002 7:32 PM Hello Group, There was a lot of good dialog recently regarding laser safety. Thanks to all that participated Questions: Who enforces the FDA CDRH 1040.1 laser safety standards in the US? How is it enforced? What are the penalties for noncompliance? Who enforces the IEC or EN 60825 laser safety standards in Europe / Globally? How is it enforced? What are the penalties for noncompliance? My questions are stemming from the Class 1 or 1M laser safety requirements particularly in Telecom networks. Some NRTL's and CAB's do not require or do not enforce their clients doing a submittal ( To the FDA ) for installing these types of laser products in your equipment. Their decision was based on your company using a class 1 laser that carries a current NRTL / CAB safety certification which was not modified from it's original design when installed into your products. Thanks in advance, Jeffrey Collins --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Flammability rating question
David and Gary - Gary has the name correct, but the difference in rating is derived due to complications related to the test method. VTM materials tend to curl up, wilt or shrink away from a flame when cut into test blanks normally used for the V-x small scale material testing. To overcome this, the test samples are formed into cylinders by wrapping them around a mandrel, to stiffen them. The samples are oriented the same as for the V-x testing and the mandrel is removed prior to applying a flame. Since the test methods are different and not directly comparable, the VTM rating scheme was devised. In VTM-x, the -x part of the rating is roughly comparable to V-x ratings and are generally treated as equivalent. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Gary McInturff Sent: Friday, March 08, 2002 6:52 AM Vertical thin material. The first part is the orientation of the test sample just as is 94 VX and the second part TM identifies thin material. Its thin enough that if used on its own it to would burn, but when used attached to someother surface it will not burn. Mostly I've sen it in tapes etc. If I remember correctly it has to be tested mounted to a madril of some sort to determine is ratings. Gary -Original Message- From: Gelfand, David [mailto:david.gelf...@ca.kontron.com] Sent: Thursday, March 07, 2002 2:06 PM What does UL 94 VTM-0 mean? I saw it in a spec for thin insulating plastic. Thanks, David. David Gelfand Regulatory Approvals Kontron Canada Inc. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Laser Safety
All - ANSI standards are not free, but some may be purchased in soft copy form and those standards are downloadable. If IEC60825-1 requirements are used for a product, you must review CDRH Laser Notice 50 to see how you are effected. This can't be a markings only type of thing; you have to use the whole standard. The certification marking mentioned in Laser Notice 50 is more verbose than the plain old 21CFR marking. Other marking differences exist for higher laser classes where the ANSI based logotype is replaced by IEC60825-1 markings. The harmonization project between IEC TC76 and 21CFR is ongoing. I don't know the status, but it's not completed. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: John Juhasz Sent: Wednesday, March 06, 2002 6:47 AM I tried looking real hard for free downloadable ANSI specs and couldn't find them - I had to buy them. Regarding labelling, there have been efforts (not sure of the status at this time - is there anyone out there who knows?) to harmonize the EN 60825 and 21CFR1040 to make it easier on manufacturers. As the final laser classifications are parallel (it's the methodology that has differences) the FDA, in the interest of manufacturer satisfaction(?) has been allowing the use of the Classification/Warning labels as described in EN 60825. But you still have to add the FDA-CDRH label This product complies with FDA Radiation Performance Standard 21 CFR Subpart J Hope this helps. John Juhasz Fiber Options Bohemia, NY --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Laser Safety
Mark - My first inclination is to ask: do you need Class I? In the US, the higher classes of laser products primarily require labeling and additional information in instruction manuals. As stated by Doug McKean, 21CFR allows the fiber optic system connections to provide a level of safety, in the sense that an open or broken fiber is not considered. If the product will be marketing internationally, IEC60825-1, Class 3B does have some potential design requirements, but is otherwise significantly similar to 21CFR. For IEC60825-1, fiber disconnection (as a maintenance/service activity) and breakage (as a fault condition) is considered in determination of laser class. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: Mark Schmidt Sent: Tuesday, March 05, 2002 11:17 AM I am trying to gain a better understanding of lasers and I have had some discussion and been told some things that don’t make much sense to me so I am asking the group for some guidance. Here is my question. If the unexpanded raw beam of a Class III b laser was incorporated into a larger system, is then expanded and used in this same system reducing the beam intensity to Class I levels. Would the overall system be classified as Class I ? Thanks. Mark Schmidt Regulatory Compliance X-Rite Incorporated U.S.A. (616) 257 2469 mschm...@xrite.com mailto:mschm...@xrite.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Laser Safety
Mark John - Since 21CFR is based on ANSI Z136.1, it seems the best of references. However, 21CFR is the ultimate judge for the US. ANSI Z136.2 is for fiber optic systems, rather than products, but is still a good reference. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: John Juhasz Sent: Tuesday, March 05, 2002 12:28 PM Your best bet in classifying your 'system' is to look at ANSI Z136.1 and .2 specs. In my opinion (some may disagree) it's a good guide. John Juhasz Fiber Options Bohemia, NY --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: ventilation holes
George - Please keep in mind that SELV alone, while addressing electric shock, does not address risks of fire. If, however, the external power supply complies with the requirements of a Limited Power Source, then you're home free, in terms of complying with the safety standard(s) (the enclosure becomes purely decorative). If the power supply in combination with the first circuit element or so in the power input circuitry inside the box cause the power source to comply with the requirements of a LPS, you'll need to have an electrical enclosure around the nonLPS supplied portions of the interior. You may want to further consider the long term effects on reliability and returns due to ingress of liquids, dust or other solid matter into the box. Oh, and thar's that EMC thangy I keep a-hearing 'bout. ;) Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services peter.tar...@sanmina-sci.com -Original Message- From: George Stults Sent: Tuesday, February 26, 2002 10:24 AM Hi Folks, I have a safety question for the group. I have a small (about 8 x 10 x 2 inch) piece of ITE equipment, SELV, enclosed in a plastic case, powered by an external 12 volt brick from AC mains. The problem is, the device tends to run a little hotter than desired. One proposed solution is to cut some vent holes in the top. These would be roughly (1/2) inch long by (1/6) inch wide, spaced (1/4) inch apart, running across the top near the front of the device. I haven't seen many (any?) devices with vent holes in the top, so I'm wondering if there is a basic reason why not, such as the cover must shed water, etc. My questions are, what considerations arise and what sections of EN 60950 apply to this, either to allow it or to exclude it. Thanks in advance George S. --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@mediaone.net For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Lasers in Fiber Optic Comm Networks
The scenario you describe is specifically addressed by the standard, IEC60825-1. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Collins, Jeffrey Sent: Friday, June 28, 2002 1:45 AM Group, And yet another laser question. How would one certify/classify Optical Gear in Europe Only where the transceiver may very well be a class 1 laser, but because you multiplex multiple channels before launching on the line coming out of the CO, your aggregate power can be significantly higher than class 1? Jeffrey Collins --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Units, symbols
I don't have a copy, but if we were to refer to ISO 31-0:1992, I'm certain answers to these questions would be revealed. Abstract from the ISO web site: Gives general information about principles concerning physical quantities, equations, quantity and unit symbols, and coherent unit systems, especially the International System of Units, SI, including recommendations for printing symbols and numbers. Annex A includes a guide to terms used in names for physical quantities, Annex B a guide to the rounding of numbers, Annex C international organizations in the field of quantities and units. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Hipot test at production - requirements for tester
All - From UL's NWGQ Standardized Appendix Pages (these are for ITE products) 2.1.2.2If the output of the test-equipment transformer is less than 500 volt-amperes, the equipment shall include a voltmeter in the output circuit to indicate the test potential directly. It's impossible to say that this applies across the board for all product categories and for all third party safety certifiers. I generally recommend a 500VA transformer for production line EST equipment, to avoid unexpected issues with factory auditors and feel confident that the production line staff have as little to monitor as possible; in my experience, the more they have to monitor, the less likely they are to monitor any given thing, especially if disgruntled. I also recommend, As Greg mentioned, that the trip current be set as low as practical for the product under test. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Gregg Kervill Sent: Wednesday, June 19, 2002 1:02 PM 500 VA (and greater) is used for TYPE TESTING only. Any kind of breakdown that pulls more than 5 mA is potentially lethal and non-compliant. There is good reason for limiting the EOL hot-pot current (dynamically - or even with a trip) as low as possible. Best regards Gregg --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
RE: Two Questions concerning the subject of Laser Safety
Mike - See below. Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com -Original Message- From: Davis, Mike Sent: Wednesday, June 19, 2002 6:59 AM 1.Are manufacturers required by the FDA to record serial numbers of Laser modules. Where is this requirement located? Does this apply to photodiodes also? A) Not in so few words. The requirements imply the need for a tracking method by way of a QC program, but nothing is specifically identified. Also, if there's a field incident, traceability to a manufacturing lot would likely become an issue, especially if the field incident is serious enough to warrant a recall (you would, no doubt, prefer to recall only some modules from the field, rather than all of them). S/Ns are the most common method I've seen used for this. B) photodiodes are not controlled by the FDA; neither are noncoherent LED sources 2.I have a concern of what I need to know about Laser safety but was afraid to ask (because it would cost more than my compliance budget ($0) would allow without manager approval). In other words (what is the second question?... I am getting there.) I am looking to hire a consultant or take a course. My supervisor wants me to create for him a proposal answering the type of questions that support the need to either attend a course or have a consultant educate me or our professionals here so that he can decide whether or not we need to hire a consultant, etc, etc. To keep this short, I will paraphrase by saying that the type of questions he would like to have answered is it worth the expense to getting smart, as engineers and a manufacturer of ITE, in the manufacturing of laser systems? I believe it's worth getting smart. I recommend (you just missed the last one): International Laser Safety Conference March 10-13, 2003 Jacksonville, FL http://www.laserinstitute.org/conferences/ilsc2003/index2003 .htm Here is my question... Is there information available that summarizes the responsibilities to Laser Safety of Compliance, Design, Manufacturing, and Test Engineers that manufacture laser systems? Refer to 21CFR and the CDRH web site for all of this. You'll find copies of the initial and annual reports and links to 21CFR. Some of the information you want is in early sections of Section 1040 (1040.01, .02) so don't ignore them and only review 1040.10. http://www.fda.gov/cdrh/ --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://ieeepstc.mindcruiser.com/ Click on browse and then emc-pstc mailing list
Re: [PSES] Public Service: Opt Out From Online Behavioural Advertising
From: N. Shani [mailto:nshani...@gmail.com] Sent: Tuesday, October 01, 2013 18:28 This may apply to Canadian on-line advertising only, but I'm sure other jurisdictions around the globe have similar sites/tools available. To see more, and opt-out, see http://youradchoices.ca/choices I went to that site out of curiosity and it told me that to use the site to look at its content, I had to allow setting cookies in my browser (I have my browser to not allow third-party site cookies, but otherwise they're allowed). Must be Canadian humor.☺ Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] Standards copyright lawsuit
There is occasionally much haranguing regarding how standards should be free. The NFPA has joined ASHRAE and ASTMhttp://www.nfpa.org/newsandpublications/nfpa-journal/2013/september-october-2013/pov/first-word?order_src=C247to claim otherwise. Regards, Peter L. Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] standards update and legal madness
Brian - Threats of tort is commonly used to try to get someone else to absorb the types of costs described below. Depending on the actual cost of the required product fixes, one side or the other may decide to eat the costs, simply based on the typically exorbitant legal costs for pursuing a tort and the potential for losing. The contracted company's legal dweebs need to review the contract to see if professional incompetence is on their side or on the part of the contracting company. Meaning, how specific was the contract in specifying the applicable standards and was there any presumption of continuing compliance over time. This ties into John Shinn's question about, build to print, which is a contract manufacturer's backup Plan A. As far as the who's who, simply direct them to the committee responsible for the standard and let them tease out its membership. It should not be the contracted company's responsibility to take action beyond this minimal level, unless there's a desire to play extra nice until it's time to not play nice. If the contracted company's legal dweebs are on the ball, they're most likely already on these issues. Regards, Peter Tarver -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Friday, November 08, 2013 10:46 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] standards update and legal madness None of this is a representation of my employer. A company makes a component for North American market designed for the needs of a single customer. The company received notices from CSA and UL with tabulation of standards corrections. The company informed affected customer of time and cost to update. The company then receives letter from the customer's legal dweebs - they want to see complete list of organizations and individuals that contributed to the errors that caused a mandatory update to the standard. The company's customer is considering pursuing a tort for lost opportunity and professional incompetence. Has this ever been done? Has a member of a TC/WG ever been served with a subpoena for this stuff? Is this stupid or just insane? - --- - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc- p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product- compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] CPSC product recall
For those who don't subscribe to InCompliance magazine or track recalls through other methods, the below link is related to a US product recall of a relocateable power tap with surge protection. http://www.cpsc.gov/en/Recalls/2014/Schneider-Electric-Recalls-APC-Surge-P rotectors/ Regards, Peter L. Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] EN 50581 part/range of parts
From: Piotr Galka Sent: Friday, November 22, 2013 05:15 The fourth side: We (I hope I will not be alone) think point 1 is an error - it should call for No... (unique identification of document): I will propose yet another position. This position appears to me to logically suit the intent of the RoHS Dir. For a product with a given model designation, there may be multiple product revisions that don't affect the overarching model designation. I've worked at companies that had three levels of product identification (others may have more), each of which was marked on the product for traceability purposes that aided in customer support and failure analyses. Level 1: A model designation that is generally unvarying, but may have a revision code that changes only for large changes in functionality that marketing wants to make customers aware of. Level 2: A part number for the product that is used coincident with the model designation that contains a suffix that is allowed to change more frequently than the model designation. Level 3: A lower level part no. that changes frequently (even with every minor ECO or MCO addressing minor cosmetic issues as well as with more substantive changes) and may or may not change a suffix only. To address the RoHS Dir. for a product following the above (or a similar scenario), each level of product identification that can be or is RoHS compliance affecting must be identified in the DoC. This might include only the first two levels in the above example. As the revision levels roll up, a new DoC should be issued that covers the relevant product identifier levels. It is completely illogical that every S/N should be identified. For products that have high production rates, this is ridiculously onerous. Not that politicians are immune to being illogical or ridiculous, either by design or through ignorance or negligence. ☺ Regards, Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Categorizing a new product
TO,OB (did you really mean that?) – There are a number of devices designed for similar uses, but that are for wiring in. Example manufacturers include TeleHaase (http://www.tele-online.com), Lovato Electric (http://www.lovato.co.uk/) , ABB (http://www.abb.com/) and others. You can peruse their web sites for these devices and get the flavor of their certifications. Fair warning, many specs. are not available in English. Regards, Peter Tarver *From:* Brian Ceresney [mailto:bceres...@delta-q.com] *Sent:* Thursday, November 21, 2013 15:52 *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* [PSES] Categorizing a new product Dear Regulatory Wizards, I’ve been asked to provide the regulatory scope for a product type which is new to me, and I’d appreciate if you could provide me with a sanity check. We are considering Safety and EMC for Europe only here, of course other Directives(RoHS 2, REACH, WEEE, etc.) will apply. A CB report may be considered for additional countries, as required. The product is a small device which is intended to plug into the mains via a supply cord, and, in turn, provides a socket for another piece of mains operated equipment. The function of the device is to pass mains power through, and provide under- and over-Voltage protection by disconnecting the mains under extreme conditions(using a relay). It automatically re-connects the mains when Voltage returns to the normal range. It may also provide some surge protection. This device will be intended for use with small industrial appliances with input ratings of 100-250V, 50/60Hz, drawing maximum normal currents of less than 12A. This device is designed to prevent damage to the attached product only, the product itself is compliant with current standards for Europe and North America. Using my friend Google(thanks Brian O.), I’ve arrived at two European safety standards which seem applicable: EN 60255-27 :2005 Measuring relays and protection equipment - Part 27: Product safety requirements EN 50550-2011 Power frequency overvoltage protective device for household and similar applications (POP) Additionally, - plugs and sockets will comply with EN 60320-1. - if not specified within these standards, spacings will comply with EN60664-1. For EMC immunity and emissions: EN 61326-1:2006 Electrical equipment for measurement, control and laboratory use - EMC requirements - Part 1: General requirements Please provide your comments. Am I missing anything? If not, I’ll purchase my standards, and begin the process. Thanks for your help. Best Regards, Brian C. (The *other*, other Brian) This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Circuit Breakers - Branch Circuit Protection vs Supplementary
John - The simplest method is whether or not the breaker is Listed or Recognized. If it's Listed, it's suitable for branch circuit protection, within the caveats of the product category (some exceptions may exist, but should be detailed in the Listing). Recognized breakers are never suitable for branch circuit protection and are only suitable for supplementary protection applications, unless it's used as a part of a Listed assembly identified for use as branch circuit protection. QVNU2 breakers are not suitable for branch circuit protection. Regards, Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Circuit Breakers - Branch Circuit Protection vs Supplementary
From: Brian Oconnell Sent: Tuesday, December 03, 2013 12:31 To: EMC-PSTC@LISTSERV.IEEE.ORG But there are, in fact, listed CBs intended for supp interrupt protect. I'm aware of UL Listed supplementary overcurrent protection fuses, but not CBs. What's the product category? Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Cooling fan safety query
Ian - Another consideration, since you have more than one fan, is that you can disable *all* fans simultaneously to demonstrate that no cooling is necessary for safety reasons. This is a multiple fault scenario, but it's at your discretion to do so to prove your case and eliminates the need for cfm ratings. Stalled rotor testing should not be needed in the end product unless: 1) the test was not done on the fan when it was safety certified (very common, even among UL Recognized fans) 2) the fan if it is not safety certified at all (you state the fans you're using are UL Listed, but I think you mean UL Recognized) 3) the fan is a type whose motor current under stalled conditions can overload another component of the power supply (the impulse start dc motors I've tested can go an interminably long time without getting more than a smidgeon above the local ambient temperature) Disabling (removing power) serves most of the thermal concerns. There are flammability issues that may need to be met, as mentioned by another poster, and providing the manufacturer and model can provide a level of traceability to the relevant materials. If you can successfully eliminate the need for cfm ratings and stalled rotor testing, your only concerns are reduced to flammability and loading of the power supply. In some cases, you can use the fan ratings alone to meet the standard's and certifier's requirements. As a final word, alternate or substitution of components is an ongoing issue for everyone involved in product safety certifications. You can try to have a handful of alternates ready when the certification evaluation is performed and still have this concern because there's always a less expensive alternative available. Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Cooling fan safety query
From: Richard Nute Sent: Monday, December 16, 2013 11:03 Stalling the fan would be the better course of action as this would require the fan motor to dissipate some power as well as the series resistor, thus causing more heat -- but not much -- in the equipment. My experience with small impulse start fans is that that generate negligible heat when stalled, but this method would remove all doubt. Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Meaning of regulating network in 61010-1
From: Crane, Lauren Sent: Friday, January 31, 2014 12:27 John, Your reply makes sense to me, but it also brings me to notice that circuit is used freely in the surrounding text, and yet the standard says regulating network rather than regulating circuit perhaps this implies network is a narrower concept? In undergrad courses I attended, 'network' and 'circuit' were used interchangeably. Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Meaning of regulating network in 61010-1
From: sudhakar wasnik Sent: Tuesday, February 04, 2014 11:38 So in short impedence single element/combination is a network and RLC single element/combination is circuit. Any takers It's completely arbitrary whether or not a circuit is considered a network. A differentiation could be derived based on passive -v- active components, number of nodes, or based on function. Someone will always have a different opinion. In the standards world, they are used interchangeably. Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Critical Components definitions
From: Brian Oconnell Sent: Monday, February 24, 2014 10:38 Concur with Mr. Nute. Ditto. To add by way of example, there was a recent thread on regulating network. Components without which or the failure of which the network would lose it regulating function (within the context of the applicable standard) would be deemed critical. Regards, Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] use of AC contactor in PV application in US/CAN
From: Boštjan Glavič Sent: Thursday, March 13, 2014 01:01 Is anyone familiar if it is allowed to use a contactor instead of circuit breaker in PV application to disconnect inverter from the grid? NEC in Article 690 does not specify it precisely. What standard needs to comply this contactor? A circuit breaker is not required to be used as the disconnect device for the grid, but branch circuit overcurrent protection is required, so it's convenient to use a circuit breaker. Aldous gave you the relevant standards for contactors. Many fire marshals require a separate disconnect switch for inverter output connections to the grid. Whether or not this switch can operate a contactor will depend on the jurisdiction involved. Regards, Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] Greece and HAR cable
Visiting the EEPCA web site to look up some ENEC certification information, I did a little extra browsing and came across this statement: Due to the recent changes that happened in Greece, ELOT is obliged to abandon the maintenance of its issued HAR licences. http://www.eepca.eu/page.php?p=6 Following the link on the page to a HAR member list shows Greece is absent. Does anyone know the back story? Regards, Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] Exhaust fume hood recommendations
Hi. I'm doing some research and am looking for recommendations for fume hoods for abnormal condition testing for my lab. I have an opportunity to have an exhaust to outside air system and am looking for your thoughts on what has worked well for you in terms of cfm capacity and which manufacturers you've used. I'm thinking of a variable speed or at least multiple speed fan. Product types range from about the size of desktop feature phone to a large tower computer. I will likely also use the fume hood for flammability testing. I'm not interested in recirculating air types, since the filters can be expensive. Any insights you can give are solicited, even modifications you've made to improve performance or usability. Regards, Peter L. Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Exhaust fume hood recommendations
Brian - I'm looking to control smoke and fumes during component and other abnormal conditions, as well as UL 94 testing. Lots of food for thought. Thanks. Regards, Peter Tarver -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Friday, June 20, 2014 16:49 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Exhaust fume hood recommendations My boss immediately said that below was a Freudian slip. Should have been You would probably not get this additional functionality on the stuff intended for chem or bio labs. Brian -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Friday, June 20, 2014 4:37 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Exhaust fume hood recommendations My current hood is stainless steel, with a large bubble in the exhaust tube just above the hood. The bubble has fans fore and aft. The bottom lip of the hood is used to hang Lexan 'shields' on three sides; this is because I wanted them removable so that I can also use the underlying bench as normal test area when not torturing stuff. The back wall surface is covered with a sheet of galvanized metal and has latches for the lexan shields. Unless you run a very well-sealed hood area, fans must have a high volumetric rating. In any case, doubt that even the fans for a large computer would suffice for any type of setup. Fans for my hood are rated 120V or 208V, direct drive, fused and rated at least 500 cfm, and not anything special and are mounted to be easily replaced (seem to be replacing them about one per year), so do nothing for filtration, just vent the smoke to the outside smog. If the vent stack is very short, there could be a possibility of the exhaust having burning embers. Most commercial hood setups use a venturi or are centrifugal so can be difficult to service and replace. Look at fans in the Dayton or Grainger catalogs for ideas - decent exhaust fan assemblies will be at least $250 USD. But the commercial lab stuff is an order of magnitude more expensive. My set up is also useful for the Type Test on end- use equipment that could cause smoke emissions. You would probably not get this additional fun! ctionality on the stuff intended for chem or bio labs. If you want a portable setup to exhaust a small area just for UL94 stuff, build a metal box, about 1 cubic meter with inlet louvers at bottom, and use a bathroom exhaust assembly on the top. Or you could just put a steel bench in the parking lot behind the building... Brian -Original Message- From: Peter Tarver [mailto:ptar...@enphaseenergy.com] Sent: Friday, June 20, 2014 3:45 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] Exhaust fume hood recommendations Hi. I'm doing some research and am looking for recommendations for fume hoods for abnormal condition testing for my lab. I have an opportunity to have an exhaust to outside air system and am looking for your thoughts on what has worked well for you in terms of cfm capacity and which manufacturers you've used. I'm thinking of a variable speed or at least multiple speed fan. Product types range from about the size of desktop feature phone to a large tower computer. I will likely also use the fume hood for flammability testing. I'm not interested in recirculating air types, since the filters can be expensive. Any insights you can give are solicited, even modifications you've made to improve performance or usability. Regards, Peter L. Tarver - - --- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com - - --- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well
Re: [PSES] Exhaust fume hood recommendations
Doug – I’m familiar with those fans. They were used in a PBX system I was associated with in an alternate universe. Good variable speed control on them. I’m not sure I’ll need a spark arrestor, but I appreciate the reference. Regards, Peter Tarver *From:* Douglas Nix [mailto:d...@mac.com] *Sent:* Saturday, June 21, 2014 14:47 I’ve had excellent success with backward curved impellers for high-flow, low noise applications. EBM makes some great ones http://www.ebmpapst.com/en/products/centrifugal-fans/centrifugal_fans.html. Also, if you’re concerned about burning embers, consider adding a spark arrestor into the exhaust duct: http://www.qamanage.com/SparkArrestor This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Exhaust fume hood recommendations
Good pointer, Rich. UL 94, §5.1 seems oriented at improving observation of the test. I had originally thought I might make a box out of polycarbonate. I either need to rethink that or add curtains or some low transmittance window film. I also need to consider a flame resistant table top surface. A simple stainless steel pan could transmit heat and create undesirable secondary effects.☺ An air gap might fix that, but then I need to come up with a good support system. Details, details ... Regards, Peter Tarver -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Friday, June 20, 2014 16:27 Hi Peter: Since you will be doing flammability tests, see 5.1 of UL94 which has specifications for the fume hood. Note that during the flammability test, the hood is draft free while permitting normal thermal circulation of air past the specimen. Best regards, Rich This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] question with regard of inverter
IEC 62109-1 considers “PV circuits in general” to be OVCII. Regards, Peter Tarver *From:* McDiarmid, Ralph [mailto:ralph.mcdiar...@schneider-electric.com] *Sent:* Friday, August 08, 2014 13:57 *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* Re: [PSES] question with regard of inverter My understanding as well, namely, OV categorization in power distribution is based on indirect (near-by) lightning strikes. ___ *Ralph McDiarmid* | * Schneider Electric | Solar Business* | *CANADA* | *Regulatory Compliance Engineering* From: John Woodgate j...@jmwa.demon.co.uk To: EMC-PSTC@LISTSERV.IEEE.ORG, Date: 08/06/2014 01:53 PM Subject: Re: [PSES] question with regard of inverter -- In message 53e28a32.4020...@ieee.org, dated Wed, 6 Aug 2014, Richard Nute ri...@ieee.org writes: . Your solar cell DC source is not subject to load switching, but is subject to a direct lightning strike. Your DC OVC due to load switching is zero, and your OVC due to lightning is beyond OVC IV. Is resistance to a direct lighting strike required of civilian products? I though that only 'indirect strike' was to be resisted, and OVC IV was based on that. -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk Quid faciamus nisi sit? John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com __ This email has been scanned by the Symantec Email Security.cloud service. __ - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) http://www.ieee-pses.org/list.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher j.bac...@ieee.org David Heald dhe...@gmail.com This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] weird stuff in agency agreement form
Not related to the specific content of this thread, but on topic for the Subject: A certain SCC/NRTL lab had asked last year for a newly signed agreement. The section on what constitutes confidential information in the new agreement explicitly excludes the name, title, business address or business phone number of employees of client. This smacks of a revenue enhancement scheme for the lab when they sell my contact information to third-parties wishing to spam me. Said lab could not be swayed to change anything in the agreement, so I didn't sign the new agreement and the lab still gladly accepts our business. Regards, Peter Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] Looking for Steven Holmes, formerly of UL
Anyone know how to contact him? All contact information I have for Steven is outdated. E-mails bounce and the last telephone number I have for him is kaput. Regards, Peter L. Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Looking for Steven Holmes, formerly of UL
Ben der, dun dat -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Tuesday, September 23, 2014 15:34 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Looking for Steven Holmes, formerly of UL see his linkedin page. Brian -Original Message- From: Peter Tarver [mailto:ptar...@enphaseenergy.com] Sent: Tuesday, September 23, 2014 3:11 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] Looking for Steven Holmes, formerly of UL Anyone know how to contact him? All contact information I have for Steven is outdated. E-mails bounce and the last telephone number I have for him is kaput. Regards, Peter L. Tarver - - --- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@radiusnorth.net Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] Serrated head screws for grounding/bonding
Good morning. I am reviewing the suitability of serrated head screws in grounding and bonding applications. I am aware that these screws are good at resisting vibration, but I've not seen them used for grounding and bonding purposes. I question this application since, while the serrations oppose loosening of the screw, they do not bite into the metal beneath the head and also seem unlikely to form a gas-tight connection, allowing degradation of the grounding/bonding interface over time. What are your opinions? Are you aware of any evidence of the reliability of an grounding/bonding connection using such screws? The screw will secure a wire, possibly with a crimp-on ring connector. (I also question the value of using a single toothed washer in these applications.) Regards, Peter L. Tarver This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Accreditation for standard comprehension?
ISO 17025 (General requirements for the competence of testing and calibration laboratories) has some requirements related to knowing what you’re doing. Regards, Peter Tarver *From:* Brian Gregory [mailto:brian_greg...@netzero.net] *Sent:* Wednesday, May 13, 2015 11:30 *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* Re: [PSES] Accreditation for standard comprehension? The only ones that come to mind are ISO audits, and the contractual requirements between you entity and the NRTL/NB you engage to provide your certifications. These only require that you possess the standard in question and employees can locate it when necessary, thereby establishing familiarity. None that I know require any demonstration of competence. NRTL's must establish competence, and adequacy of their facilities, to their auditors. Colorado Brian -- Original Message -- From: Crane, Lauren lauren.cr...@kla-tencor.com To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] Accreditation for standard comprehension? Date: Mon, 11 May 2015 23:15:53 + Does anyone know of any conformance assessor certification schemes that have provisions requiring the applicant to demonstrate familiarity with the standards to which they will be assessing? I am familiar with a couple lab certification schemes that appear to focus on general business practices and professional qualifications and rigor of assessment, but not necessarily needing to demonstrate the assessor knows well what the standard requires. Regards, Lauren Crane KLA-Tencor - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) http://www.ieee-pses.org/list.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher j.bac...@ieee.org David Heald dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) http://www.ieee-pses.org/list.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher j.bac...@ieee.org David Heald dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] UL HTTPS
UL recently changed a number of URLs and other items, probably as a matter normal churn. Several bookmarks no longer worked. This is probably a related thing that they'll work through in time. Regards, Peter Tarver -Original Message- From: Brian Oconnell Sent: Friday, May 15, 2015 12:39 Anyone know what is with UL's CDA site? Seems to have lost the secure connect for last several days. The pages seem only partially encrypted or perhaps mixed scripts, but cannot detect anything using inspect mode on browser. Hopefully they just need to renew cert. Sent email to them several days past - no response. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] Different surge test equipment, different results
David - Thank you. In one case, the output was after the CDN. In the other, the CDN was not in the circuit. I will ask for calibration screen captures with and without the CDN on both cases. This could prove informative. Regards, Peter Tarver -Original Message- From: Schaefer, David Sent: Friday, August 21, 2015 12:11 Peter, Are the open circuit waveforms identical out of the surge generator, or out of the coupling decoupling network? -4-5 relaxes the waveform limits for the rise time and duration at the output of a CDN, based on amperage. Check out tables 6 and 7 of the 2nd Edition for more information. Two generators should produce identical waveshapes out of the generator itself, but the CDNs could have drastically different durations. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] Different surge test equipment, different results
Good morning. I'm wondering if others have experienced cases where different manufacturers' surge test equipment (ANSI/IEEE C62.41 ring and combination waves) with nearly identical open-circuit voltage and short-circuit current calibrations have led to very different results. In these cases, other than addressing the issue by using the surge generator that produces the worst-case result, what were thought to be the causes for the different results (ignoring the real possibility of a marginal design). Regards, Peter L. Tarver - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] 208V/30A/3PH NEMA 3R power distribution question
Adam – Brian’s suggestion I a good one. Answer from electrician should include three 20 A, two-pole branch circuit breakers for each single-phase load, possibly one main 45 A, three-pole breaker (with dependencies), plus Neutral bar (if needed) and ground bar. Miscellaneous assorted potpourri to fit the application. Regards, Peter Tarver *From:* Adam Dixon [mailto:lanterna.viri...@gmail.com] *Sent:* Thursday, August 20, 2015 13:36 *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* Re: [PSES] 208V/30A/3PH NEMA 3R power distribution question Thanks for the suggestion, Brian. I just contacted the company that did some of my office building's infrastructure, so will see how that goes. Regards, Adam On Thu, Aug 20, 2015 at 4:16 PM, Brian Oconnell oconne...@tamuracorp.com wrote: Have you talked to a certified industrial electrician? Had a customer that bought several 250kVA distribution transformers that also wanted some custom wiring harness and downstream panel boxes. So hired an industrial electrician to advise us on materials and build it up. Passed on-site assessment with no problems. Probably saved hundreds of hours of engineering time, and $ in wasted material costs. Brian From: Adam Dixon [mailto:lanterna.viri...@gmail.com] Sent: Thursday, August 20, 2015 12:39 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] 208V/30A/3PH NEMA 3R power distribution question First-time post with an application question after getting guidance from many of you earlier this year about how/where to learn more about safety. So here goes.I would appreciate recommendations for either reference materials I should read or hardware options to convert a 208V/30A/3PH branch circuit to support qty. 6 of 208V/15A/1PH loads while trying to minimize the hardware volume. Loads do not have internal supplementary protection devices, so I cannot rely on the 30A branch circuit protection w/simple disconnect switch for service support, similar to my home 240V air conditioning compressor circuit. I've searched the PSES archives with a variety of terms (208V, 3 phase, load center, molded case breaker, DIN rail, NEMA, etc.) and have been looking at online (well-known load center/circuit breaker suppliers, electrical supply companies, Mike Holt forums, etc.) and just started calling/visiting local electrical supply companies and big box home improvement stores. Haven't landed on a clear option yet. 3PH load centers all appear rated for 100A or larger capacity requiring larger AWG supply conductors than what I am told the branch circuit will have (10AWG or possibly 8AWG depending on final building construction plans). Descriptions of DIN Rail circuit breakers/supplementary protection devices sounded promising for the smaller form factors, but I haven't found a source that puts all of the hardware pieces together (supplementary protection devices, DIN rails, housing, etc.) into a system that meets NEC requirements -- this doesn't look like a common configuration. I also looked at suppliers of rack mount PDU gear and found one option that is about the size of a 12 circuit load center, but doesn't have a NEMA 3R requirement (surprise..) and would require a larger housing. The 208V PDU's that I have seen and in a couple of cases, peeked inside, have double-pole breakers with C19 outlets rated for 12A continuous load. Are there other options worth investigating or aspects of the power distribution design that I likely am not understanding? Kind regards, Adam - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee
[PSES] 208 split-phase?
Good morning. There are oftensmall, legacy grids that you come across or hear about. I was recently told that some areas of the Northeast US have a 208 V, split-phase power system to some residences and small businesses. Still 180° phase-to-phase and presumably 104 V phase-to-Neutral. A specific area cited was "around Boston." Has anyone heard of or directly experienced this voltage system? Is it split-phase or was I misinformed and it's from a WYE connected transformer? Peter Tarver ptar...@ieee.org - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] 208 split-phase?
Ralph – I’m less familiar with the CEC, but the NEC does not preclude 208/120 V WYE to a single-family home (residence). It all depends on how much one is willing to pay the utility for the service and proper provisioning and system design at the use location. Peter Tarver *From:* McDiarmid, Ralph [mailto:ralph.mcdiar...@schneider-electric.com] *Sent:* Thursday, October 22, 2015 15:00 *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* Re: [PSES] 208 split-phase? NEC art 210.4 and 210.5 seem to allow it and the CEC here in Canada certainly allows it. For large residential highrises, it's probably simpler and cost effective to distribute 120/208 throughout the building (1/3 of the suites on one 208 leg, and so on) Phase balancing would be part of the building electrical plan. Sending a single-phase MV feeder to 1MVA, 120/240V transformer is likely a comprehmise It's different for low density residential where stringing a mile or two of single-phase MV to feed 120/240 pole transformers throughout the neighborhood makes more sense. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] 208 split-phase?
Doug – I’m not certain what I’m referring to. Hence the question. Since typical 120/240 V split-phase distribution in the US is from a center grounded delta, my inclination is to believe this follows that same method. Or the original proposition I received is incorrect and a three-phase WYE is used on the load side of the distribution transformer. I think I prefer “bastard leg.” Peter T *From:* Doug Powell [mailto:doug...@gmail.com] *Sent:* Wednesday, October 21, 2015 09:01 *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* Re: [PSES] 208 split-phase? Peter, The idea of a 208 V split phase is unusual and probably not the case here. The number 208 is obviously derived from a three phase system. I believe the system you are talking about is a red-leg or high-leg three phase system. Wikipedia does have a good review in this case ( https://en.wikipedia.org/wiki/High-leg_delta; https://en.wikipedia.org/wiki/Split-phase_electric_power). In the figure on Wikipedia this is a 240 VAC delta with the neutral applied between L1 & L2, creating 120 V split-phases in 180 degree opposition. The 208 is the high leg, L3 in the figure. You can verify the voltages using the bit of trig further down the page. This voltage system is used in many parts of the world but is no longer very common in the USA. The alternative system this could be is a 416 V three phase, delta configured with split phase secondaries at 208 V. I have worked with this configuration in the past. All the best, Doug doug...@gmail.com http://www.linkedin.com/in/dougp01 On Wed, Oct 21, 2015 at 8:21 AM, Peter Tarver <ptar...@ieee.org> wrote: Good morning. There are oftensmall, legacy grids that you come across or hear about. I was recently told that some areas of the Northeast US have a 208 V, split-phase power system to some residences and small businesses. Still 180° phase-to-phase and presumably 104 V phase-to-Neutral. A specific area cited was "around Boston." Has anyone heard of or directly experienced this voltage system? Is it split-phase or was I misinformed and it's from a WYE connected transformer? Peter Tarver ptar...@ieee.org - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to < emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com> -- Douglas E Powell doug...@gmail.com http://www.linkedin.com/in/dougp01 - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to < emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) <http://www.ieee-pses.org/list.html> List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org> David Heald <dhe...@gmail.com> - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw
Re: [PSES] 208 split-phase?
Brian of the nonburrito ilk - This is usually called 208 V single-phase. I'm still trying to clarify the specifics of the request. Peter Tarver > -Original Message- > From: Kunde, Brian > Sent: Wednesday, October 21, 2015 12:34 > > snip < > > I have heard the term "208 split-phase" many times from our > customers who claim to have this but in reality what they have > is 208 3-phase wired into a 230V split-phase receptacle but > only using 208 Phase to Phase with the Grounded Neutral. > > snip < - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
[PSES] 802.11 built into a product for Australia
We are marking a product with the RCM and have done relevant emissions testing for the complete product. The intent from the start has been to leverage the testing and certifications the supplier obtained to reduce the amount of testing needed for the end product (a "modular approach" in a global scale). An IEEE 802.11 intentional radiator is incorporated into the product. The product incorporates a supplier's reference design that has been tested against relevant ETSI standards for EU deployment. These ETSI standards are referenced by AS 4268. However, we do not have a test report that explicitly mentions AS 4268 or a certificate indicating compliance with AS 4268 from the supplier. In reading the Radiocommunications Labeling Notice, a 2014 revision adds AS 4268 as a requirement. I am asking the supplier to obtain at least a certificate showing compliance with AS 4268, but they are pushing back, indicating they would need to mark their chipset with the RCM. This is an inappropriate use of the RCM, since it apples to complete products. The supplier has not been able to identify the marking the claim is needed for their chipset. The 802.11 intentional radiator is not being used for audio signals. I am asking for the certificate or an amended report that explicitly mentions AS 4268 to avoid having to go through unnecessary gyrations should the compliance status of the intentional radiator come into question. My intent is also to no have to explain why the ETSI testing covers the requirements in AS 4268 to a bureaucrat with limited technical knowledge and to also satisfy customer requests for evidence of compliance. Am I asking too much of the supplier? Regards, Peter L. Tarver - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail toAll emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] Cd exemption for art material
One hopes, then, that artists will not lick their brushes or hold them in their mouths, the same way one hopes science academy janitors will not do the same with their mops and brooms. Peter Tarver > -Original Message- > From: Brian O'Connell > > The chemical principle of local concentration vs equilibria, and > likelihood for direct exposure to users, seems to have been > ignored. > > Brian > Sr Janitorial Assistant For the Vulcan Science Academy > - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
[PSES] IEC 61010-1 and VDRs in OVC III environments
Howdy, howdy, howdy. Product incorporates Type 5 component VDRs and is installed in an OVC III environment via field wiring connections. Evaluation for a CB Scheme Certificate and Test Report. In recent dealings with a CBTL, I was told that the VDRs in a product needed to be Type 2. In referencing UL 1449 (for convenience), a Type 2 VDR has the assumption of fixed wiring for the VDR itself and mounting by solder onto a board is not a consideration (except that a Type 2 VDR may include a system of Type 4 and/or Type 5 VDRs and other components) . Per the CBTL, the Type 5 VDR certifications used may or may not be suitable for the application, depending on the level of testing performed on the VDR during its component evaluation, primarily associated with the combination wave open-circuit voltage amplitude related to the OVC. I checked the CTL Decisions and OSM Decisions for 61010-1 for both the third edition and fourth edition and found zero related decisions. The CBTL was unmoved by my efforts, claiming this matter has been a long term discussion in TC66 and imposed their will irrespective of a defined requirement in the IEC. Likewise, the CBTL was unmoved by the testing performed by another division of the mothership that applied 6 kVpk surge testing to the complete product as a part of another evaluation to type. This may be because the staff and intent of the testing was not under the accreditation of the CBTL/NCB, but I'm not certain. In checking publicly available databases for components, the kind of information needed to preselect an appropriate Type 5 VDR is not possible. This ultimately boils down to evaluation of each Type 5 VDR by the CBTL for each and every prospective alternate or substitute VDR. Has anyone else encountered this sort of requirement? The CBTL either could not or would not provide a written requirement, so this smells off. Regards, Peter L. Tarver - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail toAll emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] Ambient temperature
Alternatively, assuming the typical wire rack shelving in the chamber and a relatively small EUT, free air flow can be limited by placing three wire rack shelves onto adjacent levels that are out of the main air circulation pattern in the chamber and placing pieces of cardboard or corrugated fiberboard onto the two outer shelves, with the EUT on the center of the middle shelf. Place a thermocouple 25mm to 50 mm above the EUT to provide an ambient temperature measurement. Never rely on the environmental chamber's controls or internal thermocouples for internal ambient air temperature measurement. They will rarely give the temperature at the location the EUT is placed. If the EUT is large the environmental chamber needs to be much larger than the EUT, as indicated by others. Peter Tarver - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Ambient temperature
Date sent: Wed, 2 Mar 2016 15:55:06 -0800 Send reply to: ri...@ieee.org > I've used a 5-sided cube inside the chamber to create a > draft-free environment for performing flammability tests. > Rich This technique works well for heating tests on lab benches as well and quickens thermal equilibrium. Open face of the cube toward the benchtop. Especially nice in drafty or heavily air conditioned areas. Peter Tarver - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] IEC 61010-1 and VDRs in OVC III environments
Fine and valuable responses. Thank you. Can anyone respond to my question? > Has anyone else encountered this sort of requirement? The CBTL either > could not or would not provide a written requirement, so this smells off. Peter Tarver Date sent: Fri, 26 Feb 2016 14:59:02 -0800 From: Peter Tarver <ptar...@enphaseenergy.com> > Howdy, howdy, howdy. > > Product incorporates Type 5 component VDRs and is installed in an OVC III > environment via field wiring connections. Evaluation for a CB Scheme > Certificate and Test Report. > > In recent dealings with a CBTL, I was told that the VDRs in a product > needed to be Type 2. In referencing UL 1449 (for convenience), a Type 2 > VDR has the assumption of fixed wiring for the VDR itself and mounting by > solder onto a board is not a consideration (except that a Type 2 VDR may > include a system of Type 4 and/or Type 5 VDRs and other components) . > > Per the CBTL, the Type 5 VDR certifications used may or may not be > suitable for the application, depending on the level of testing performed > on the VDR during its component evaluation, primarily associated with the > combination wave open-circuit voltage amplitude related to the OVC. > > I checked the CTL Decisions and OSM Decisions for 61010-1 for both the > third edition and fourth edition and found zero related decisions. The > CBTL was unmoved by my efforts, claiming this matter has been a long term > discussion in TC66 and imposed their will irrespective of a defined > requirement in the IEC. > > Likewise, the CBTL was unmoved by the testing performed by another > division of the mothership that applied 6 kVpk surge testing to the > complete product as a part of another evaluation to type. This may be > because the staff and intent of the testing was not under the > accreditation of the CBTL/NCB, but I'm not certain. > > In checking publicly available databases for components, the kind of > information needed to preselect an appropriate Type 5 VDR is not possible. > This ultimately boils down to evaluation of each Type 5 VDR by the CBTL > for each and every prospective alternate or substitute VDR. > > Has anyone else encountered this sort of requirement? The CBTL either > could not or would not provide a written requirement, so this smells off. > > > Regards, > > Peter L. Tarver > > - > > This message is from the IEEE Product Safety Engineering Society emc-pstc > discussion list. To post a message to the list, send your e-mail to > <emc-p...@ieee.org> > > All emc-pstc postings are archived and searchable on the web at: > http://www.ieee-pses.org/emc-pstc.html > > Attachments are not permitted but the IEEE PSES Online Communities site at > http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used > formats), large files, etc. > > Website: http://www.ieee-pses.org/ > Instructions: http://www.ieee-pses.org/list.html (including how to > unsubscribe) > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > Scott Douglas <sdoug...@ieee.org> > Mike Cantwell <mcantw...@ieee.org> > > For policy questions, send mail to: > Jim Bacher: <j.bac...@ieee.org> > David Heald: <dhe...@gmail.com> > - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] crimp hardware for multiple conductors?
In general, and for UL and CSA in particular, crimped terminals are evaluated for the number, size, stranding and types of wire under the crimp. In most cases, only single wires are evaluated, unless the manufacturer specifies that they want additional testing. Wire sizes are critical for any particular crimp design. Too large and all strands might not consolidate well under the crimp or might prevent adequate “squish” of the crimped joint and the crimp will fail. Too small and the crimp will never hold. Either case could serve sources of risk of fire and electric shock. For UL standards, the default stranding is Class B. Other stranding counts require additional evaluation. I suspect, but have not confirmed, the same is true for CSA standards. It is not necessarily true that the more strands these better, since too many strands can form a poor crimp and the crimp tool or the crimp itself can cut or nick strands, which is not a good result. (I have asked both UL and CSA about decimating strands to get a wire size to fit into a connector crimp and was told this was unacceptable. An understandable response.) Copper is the default wire type used for evaluation. Evaluations using aluminum conductors (or anything more exotic) must be done separately. There is no magic method to find crimp terminals that are safety certified for multiple conductors under a crimp. They do exist, but it requires creative internet searches and contacting suppliers. Make certain you get copies of their certification test reports to verify any claims. Regards, Peter Tarver The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] PV Connectors: UL 6(9)703?
Brian - 6703 and 6703A are for PV connectors, as you stated. 9703 is for cable assemblies that have cable with connectors integrated into an assembly. The connectors used in a 9703 product means the connectors themselves would also have to undergo a 6703 evaluation. "Upgrading to 9703," is not a consideration. These outlines are for different product types. Peter Tarver From: Brian Gregory [mailto:brian_greg...@netzero.net] Sent: Wednesday, September 28, 2016 14:33 I'm trying to find out if UL 6703 (connectors for PV systems) is being upgraded to UL 9703 or the other way around. UL's site isn't helpful - it could be drawings I got are just misprinted, but there was a UL 9703, "Outline for Investigation" thanks, Colorado Brian 720-450-4933 The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Risk Assessment of Air Filter
Brian - UL will generally accept a Class 1 air filter. These are evaluated against UL 900. Otherwise, it depends on the standard for the end product what requirement apply. I recall 60950-1 accepting HF-1. Peter Tarver From: Kunde, Brian [mailto:brian_ku...@lecotc.com] Sent: Monday, September 19, 2016 09:43 But what type of Fault Testing or Risk assessment needs to be done regarding the filter? With the filter removed, the instrument passes the construction requirements for a Fire Enclosure. But with the filter installed and because of its close proximity to the fan/blower; 1.does this filter have to meet Flammability requirements? Does the filters have to be certified (expensive)? UL 94 HF-1?, UL 94 HF-2?, UL 900? How are these ratings/certifications viewed outside of North America? Will they have to meet local requirements?? 2. If the fan/blower is certified and limited energy circuit does the filter have to have any kind of rating or certification? In other words, with a certified fan/blower, do I have to consider the fault condition of the fan failing in a way where it could catch the filter on fire? 3. How is a fault and/or risk assessment performed on an air filter? 4. Are we responsible to consider the hazards from a burning filter when it is dirty? How would we know what type of contaminates might collect in a filter? 5. If the filter we provide is UL 94 HF-1 and UL 900 rated/certified, what would stop our customer from replacing it with whatever filter they wanted? Are we responsible to include a warning label and statements in the manual regarding this? Example, "Use only Air Filter part number XYZ". 6. Any other suggestions or issues that we are not considering? Thanks in advance. Have a nice day. The Other Brian LECO Corporation Notice: This communication may contain confidential information intended for the named recipient(s) only. If you received this by mistake, please destroy it and notify us of the error. Thank you. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)<http://www.ieee-pses.org/list.html> List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>> Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>> The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Fire ants
Reminds me of a movie, Them! From: Ed Price [mailto:edpr...@cox.net] Sent: Wednesday, September 14, 2016 23:09 Plutonium is probably not a good answer; The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail toAll emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] Fuses can affect performance other than safety!
Some of the articles I'd read in some magazine or other (copies available if you know Mr. Peabody and his boy Sherman), stated some equipment designers were paying extraordinarily close attention to maintaining the phase relationships between channels and between voltage and current, as signal passed through a system. Claims were made that doing so improved the accuracy of the reproduced sound. I heard stories in the early 1980s of people standing around rooms, dropping a set of keys onto a glass coffee table and recording it, then everyone else closing their eyes while someone made them guess if the next sound they heard sound was recorded or live. Folklore to people like me, but gospel to some audiophiles. Peter Tarver > -Original Message- > From: Ken Javor > [mailto:ken.ja...@emccompliance.com] > Sent: Thursday, August 25, 2016 17:32 > > A very simple and inexpensive means of arranging staging is > to introduce > delays between left and right channels such that the sound > appears to be > coming from a particular direction. This is much easier to > accomplish with > headphones than loudspeakers, but it's the same principle. > I've seen a > convincing demonstration at the US Army Aeromedical > Research Lab (USAARL), > where something like five different radios can be going at > once and a > helicopter crew have to be able to intelligently respond in a > crisis > situation, and what people normally do in a situation like > that where they > can't pay attention to everyone is they zero in on one > conversation and > ignore the others, and to do that we use directionality. > Originally there > was none and the headphones could be blaring all channels > at once, and the > crew would simply turn off he radios they didn't want to > hear, which wasn't > good. By introducing specific delays for each radio, the > various radios > could be made to sound as if one conversation was from > 12:00, another at > 3:00 another at 6:00 and so on. That allowed the crew to > mentally focus in > on the conversation of interest and tune out the others > temporarily. But > that is all software and digital circuitry: no fancy audiophile > equipment > necessary. > > Ken Javor > Phone: (256) 650-5261 > > > > From: Peter Tarver <ptar...@enphaseenergy.com> > > Reply-To: Peter Tarver <ptar...@enphaseenergy.com> > > Date: Thu, 25 Aug 2016 21:37:04 + > > To: <EMC-PSTC@LISTSERV.IEEE.ORG> > > Conversation: [PSES] Fuses can affect performance other > than safety! > > Subject: Re: [PSES] Fuses can affect performance other > than safety! > > > > I have heard of and known a few audiophiles that go to > great lengths to have > > sound reproduced as accurately as possible and spend > enormous sums to > > accomplish that. > > > > The term that was most silly in my view was holography; > but I understood what > > was meant. The aforementioned audiophiles claim to > recreate the spatial > > relationship between the physical locations musical > instruments when recorded. > > The needs for recording and reproduction are entirely > impractical and don't > > seem achievable for simple stereophonics, so it seems on > the bovine > > scatological side of the olfactory sense. > > > > BUT, I have stood in and moved about a room that was > carefully put together. > > In one part of the room one instrument (say clarinet) > could be heard more > > distinctly than in other areas, and so on for other > instruments, giving the > > impression that one was moving from musician to > musician on a sound stage. > > > > Pretty clever, but outlandishly expensive. > > > > > > Peter Tarver > > > >> -Original Message- > >> From: Ken Javor > >> [mailto:ken.ja...@emccompliance.com] > >> Sent: Monday, August 22, 2016 19:55 > >> > >> Next, the terms are not entirely gibberish. They may be > >> unfamiliar to those not in the hi-fi hobby, but I can make > out > >> all but one of these terms: > >> > >> Sound staging means stereo separation. Or whatever > >> passes fro that in the age of five and six different > channels (I > >> haven't kept up with this stuff since it departed from two > >> channels). I don't know how a fuse aids or degrades > >> channel separation, but at least we can understand what > is > >> being claimed. > >> > > > > The information contained in this message may be > privileged and confidential. > > It is intended to be read only by the individual or entity to > whom it is > > addres
Re: [PSES] Ball pressure test of thermoplastic parts
Kristiaan – Most of the responses agree with my understanding. I will add that my recollection of the origins of the test in 60950 was related to electrical connections under compressive loading where the compression is needed to establish and ensure an electrical connection. Some custom made terminal blocks were made using inexpensive materials, including polyamide without inorganic fillers (like glass). As time moved on, the application of the testing expanded to cover other design features. http://www.ulttc.com/en/solutions/test-methods/physical/ball-pressure-test.html It appears the testing was simplified to a single temperature with the pass/fail criterion simply being the 2.0 mm diameter dimple, rather than finding the temperature at which the 2.0 mm dimple forms. Maybe Pete Perkins or Rich Knute recall further back than I do. Peter Tarver From: Carpentier Kristiaan [mailto:kristiaan.carpent...@technicolor.com] Sent: Wednesday, August 24, 2016 05:58 Hi group, Does any-one know the reason/background of the ball pressure test of thermoplastic parts (IEC60950-1, clause 4.5.5) and the chosen temperature of 125C. This test is performed - for example – on the plastic parts of a direct plug-in power supply as these parts “carry” the mains power supply pins. I can’t imagine a situation there that requires such a test and certainly not at 125C. Thanks for your feedback! Best regards Kris Carpentier - The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Fuses can affect performance other than safety!
I have heard of and known a few audiophiles that go to great lengths to have sound reproduced as accurately as possible and spend enormous sums to accomplish that. The term that was most silly in my view was holography; but I understood what was meant. The aforementioned audiophiles claim to recreate the spatial relationship between the physical locations musical instruments when recorded. The needs for recording and reproduction are entirely impractical and don't seem achievable for simple stereophonics, so it seems on the bovine scatological side of the olfactory sense. BUT, I have stood in and moved about a room that was carefully put together. In one part of the room one instrument (say clarinet) could be heard more distinctly than in other areas, and so on for other instruments, giving the impression that one was moving from musician to musician on a sound stage. Pretty clever, but outlandishly expensive. Peter Tarver > -Original Message- > From: Ken Javor > [mailto:ken.ja...@emccompliance.com] > Sent: Monday, August 22, 2016 19:55 > > Next, the terms are not entirely gibberish. They may be > unfamiliar to those not in the hi-fi hobby, but I can make out > all but one of these terms: > > Sound staging means stereo separation. Or whatever > passes fro that in the age of five and six different channels (I > haven't kept up with this stuff since it departed from two > channels). I don't know how a fuse aids or degrades > channel separation, but at least we can understand what is > being claimed. > The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] ETSI EN 302 195 V2.1.1
Charlie – Article 49 Transposition 1. Member States shall adopt and publish, by 12 June 2016, the laws, regulations and administrative provisions necessary to comply with this Directive. They shall forthwith communicate the text of those measures to the Commission. They shall apply those measures from 13 June 2016. Article 50 Repeal Directive 1999/5/EC is repealed with effect from 13 June 2016. RED is effective now. Unless I missed something deferring it’s adoption. Peter Tarver From: Charlie Blackham [mailto:char...@sulisconsultants.com] Sent: Wednesday, November 02, 2016 09:00 The RED doesn’t need to be used until next June, so I would wait as it may well be published in the next listing which is likely to be within next 2 months. Regards Charlie The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] UL Go?
My experience to date is that UL only has knowledge being advertised below for only specific product categories/countries/markets. I have witnessed/heard claims of expertise that when it comes time to take action, they know less than the client does. When asked to provide a list of competencies relative to several countries' requirements for grid compliance of distributed generators, we received an exorbitant quote for UL to research their own capabilities. I have been less than impressed so far with such claims of aid, so I'm reluctant to entertain a subscription service. Peter Tarver From: Kortas, Jamison [mailto:jamison.kor...@ecolab.com] Sent: Tuesday, December 13, 2016 09:04 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] UL Go? Has anyone taken a look at this? It was just sent to me by my UL representative. Here is the text, as I do not think I can send an attachment: UL-Go For more information, contact us today at g...@ul.com What is UL-Go? UL-Go is an online subscription service created to solve your problems for finding current, correct and complete Global Market Access (GMA) regulatory requirements that apply to your products for the countries you're selling or wish to sell to. What GMA Information is provided in UL-Go? In partnership with UL, UL-Go can be customized to meet your company's specific needs. * This means you tell us the products, countries and regulations you want access to, and we'll provide you with in-effect regulations (updated quarterly) as well as updates on developing requirements.* * We provide you with the expertly organized information you'll need to understand the impacts each regulation has on your product, country by country. Is UL-Go a new Service Offering? Yes, UL-Go is a pilot product launched with comprehensive regulatory information and great features and functionality. As a pilot participant, you can help us develop UL-Go in a way that will deliver even more value to you! Partner with UL Identify your most important needs, and help validate our solutions. * What's first on your list? Do you to know the GMA services UL provides or do you need mobile alerts or do you want collaborations spaces that will help you get to your markets faster? * We've got the basics right - now let's get the interactions right! Are there additional benefits to subscribing to UL-Go? * You can make side-by-side comparisons for up to three countries simultaneously. * You can download, print or share results easily and bookmark your favorite searches. * Your global staff can have unlimited access to GMA information they can have confidence in. What does it cost to subscribe to UL-Go? * Each subscription will be quoted separately based on your selections. * UL-Go is a customizable subscription-you select the countries and products you want access to for the regulations you need most. What if I want only a one-time delivery of the latest regulatory requirements? We're happy to provide one-time GMA research to you at any time. Just select the products and countries you are interested in receiving regulation information about, and we will provide you with a quote for services. UL and the UL logo are trademarks of UL LLC (c) 2016 CONFIDENTIALITY NOTICE: This e-mail communication and any attachments may contain proprietary and privileged information for the use of the designated recipients named above. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)<http://www.ieee-pses.org/list.html> List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>> Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>> The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you
Re: [PSES] UL Go?
It should be kept in mind that all of these so-called services are sales tools. My experience with all of the agencies discussed have been less than stellar on the delivery side, once a PO is placed. Peter Tarver The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
[PSES] Switchgear in Europe
Greetings. I am researching requirements for switchgear in Europe and there are two prevailing series of standards: 60947-x and 61439-x. These series of standards are both produced by TC 121/SC 121A and there seems to have more than significant overlap in their scopes.. It does appear that 60947-x are for individual devices, while 61439-x appears to be for assemblages of devices, perhaps any number of 60947-x devices. I'm not certain I have that right. I have seen products the identify compliance with 60947-x and don't mention 61439-x. Neither standard series is mentioned in the list of harmonized standards for the LVD and are not excluded in Annex II. The application is for less than 1 kVac. Some 60947-5-x are mentioned in the Mach Dir., but 61439-x are not. (For the end-product application, the MD does not apply, though low voltage switchgear is in scope of the MD.) Interestingly, several 60947-x and 61439-x are mentioned in the list of harmonized standards for the EMCD. I note that the CENELEC web site identifies these standards as intended for use to demonstrate conformity with the essential requirements of the: * LVD * EMCD * RED and of these three, only the EMCD mentions any 60947-x or 61439-x standard. CENELC doesn't mention the MD at all, except for 60947-5-3 and 60947-5-5, which is at least consistent with the lists of harmonized standards for the MD. How does one choose the correct standard(s) between the two series? I am aware of 61439-0, but haven't yet purchased that document to discover what guidance it can give. Peter Tarver The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] MD vs LVD for Laboratory Equipment
I’m with you here, Dave. Just because a product contains a cooling fan should not mean the MD applies. But then, the products you cite are explicitly excluded from the scope of the MD (I’m sure you know this, since it appears you took the text directly form the MD). However, in Article 2 of the MD, where the text Doug mentions is located, goes on to say that they’re, “intended for lifting loads and whose only power source is directly applied human effort.” This encompasses: • automotive lifts and jacks • come-alongs • block and tackle sets (if sold as a unit) Peter Tarver From: Nyffenegger, Dave Sent: Thursday, March 30, 2017 17:40 But there are products meeting that definition of machine that are covered by the LVD and specifically excluded from the MD: — household appliances intended for domestic use, — information technology equipment, — ordinary office machinery, -Dave From: Douglas Nix Sent: Thursday, March 30, 2017 5:20 PM I concur with Michael Loerzer. IMO, the test labs didn’t feel comfortable doing MD evaluations, so they used the “out” that was in the text of the previous MD (98/37/EC) that said that if the hazards were ‘predominantly electrical in nature” then the MD needn’t apply. Many machines were “slid-past” based on this misuse of the text of the MD, which is why the text was changed in the 2006 edition. If the device is “an assembly of linked parts, at least one of which moves” it’s a machine. -- Doug Nix d...@mac.com<mailto:d...@mac.com> The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
[PSES] Kikusui TOS3200 Leakage Current Meter
Hello. I am using a Kikusui TOS3200 to measure touch current for a 61010-1 application. The product is double-insulated and has accessible USB port connector shells connected to the secondary circuit reference. When using the TOS3200 in meter mode (using the two external meter leads), I obtain different results than if I measure using the faceplate 5-15R outlet and one external meter lead. For each test, I'm using the same measurement networks when attempting to correlate the results. When using the outlet, the meter lead connects to the USB shell. When in meter mode, I am connecting one lead to the USB connector shell and one lead to the power conductor of interest. Has anyone experienced this with either the TOS3200 or other leakage/touch current meters? FWIW, the manual does not indicate any special considerations are needed when using meter mode. The instrument is in good condition and went through a calibration verification in AUG2016. The currents are within "Measurement range setting Range 1," but the meter is set in auto range mode. I plan some additional experiments using defined ranges, rather than auto in the next day or so. Peter Tarver The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Inrush Current
Customers sometimes want both the highest peak current and an rms over a defined number of line cycles. If the request is exclusively standards based, John's suggestion works well. You'll need to perform five to ten tests randomly closing on the supply cycle and pick the highest values. If an rms value is also needed, you can capture the inrush on a scope and gate the measurement over the relevant number of line cycles. Regards, Peter Tarver From: John Woodgate [mailto:jmw1...@btinternet.com] Sent: Thursday, August 10, 2017 05:32 Well, no-one has challenged Annex B since it was first included in the standard. Note that the standard applies up to 16 A/phase, so no big motors, etc. From: Nyffenegger, Dave [mailto:dave.nyffeneg...@bhemail.com] Sent: 10 August 2017 13:15 I think it also depends on what your EUT is. Machinery will typically be full of all sorts of loads, motors, transformers, power supplies, computers, inductive, capacitive, etc. The inrush would still be the peak current when the mains is switched on or also when the machine is started as they are typically two separate events. These could last several seconds depending on the machinery and the incoming power sine wave would probably have little effect on it. -Dave From: John Woodgate [mailto:jmw1...@btinternet.com] Sent: Thursday, August 10, 2017 8:00 AM Look at Annex B of IEC/EN 61000-3-3. I did a lot of work on this for that Annex and you will often get different results each time, because of differences in how the current is interrupted at the previous switch-off. You do not select a point on the voltage waveform for the switching instant; you can't, anyway, because you must use the product's own mains switch (unless it doesn't have one). You switch at random points, because that is what happens in practice. For duration, you leave the mains voltage applied until the inrush transient is over (look at the current waveform); this is usually after three or fewer cycles, but for some products it can be rather longer. Normally, the first current peak is the highest, but occasionally the second peak is higher. From: Kim Boll Jensen [mailto:k...@bolls.dk] Sent: 10 August 2017 12:30 Hi We have several times been asked to test Inrush Current and have this function on our Harmonic tester, but it is not defined how it measure and we get very different measurements each time we switch ON the same EUT. I can't find an IEC definition on the measurement other than "peak current". I asume that it is most correctly to measure the current by switching ON at the top of the sine (90 deg), but what about duration? A peak current with a duration of 0.1 ms is not as interresting as the same current for 1 ms. And what if there are several current peaks after each other such as ringing wave form? Best regards, Kim Boll Jensen - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Kikusui TOS3200 Leakage Current Meter
Thank you, John. Agreed, but I have also moved the conductors around, used multiple wire routings, multiple power sources, power systems in two buildings, on a ground plane (this was happenstance in the second building)... While the results have minor differences, the effects I'm seeing are always there. I plan to try an isolation transformer, a la 60950-1 to see if there's a different response. I have written to Kikusui and asked them a similar question. I'll report back Peter Tarver > -Original Message- > From: John Woodgate > Sent: Monday, April 24, 2017 23:30 > > Stray capacitances are different in the two modes, but > probably only affect > measurements if there are relatively strong high-frequency > components in the current. The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Kikusui TOS3200 Leakage Current Meter
Thank you, Nute. Page 70 of the manual indicates the ability to select a measuring network. According to the first paragraph on this page, it's a meter only for voltage measurements. Page 71 shows how to select a measurement network when using meter mode. FWIW, I used Networks A, B and G on Page 114 and can see the effects of frequency filtering between these networks. Also FWIW, I have a Simpson 228 and see similar results to meter mode measurements, though the levels are below the resolution of the 228 to accurately read the result. Because the EUT is double insulated, the PE is always "faulted." I can't use the faceplate outlet for PCC (Protective Conductor Current) measurements, but I can for touch current measurements. Peter Tarver > -Original Message- > From: Richard > Sent: Tuesday, April 25, 2017 10:42 > > Hello Peter: > > I downloaded the TOS3200 manual to better > understand your problem. > > When the TOS3200 is in "meter mode," the terminals > A-B comprise an ammeter (without the body > impedance network). This will yield a higher > current than in the TC (touch current) mode. I'm > not sure if A-B can have the body impedance > network switched in, although this is implied in > Figure 4-11. > > For a two-wire (double-insulated) product, there > is no earth wire so you cannot use the outlet for > the measurement. You must use the A-B terminals. > The connections to a two-wire product are shown in > "b" of Figure 4-7. The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Kikusui TOS3200 Leakage Current Meter
Thank you, Pete. I have received an initial response from Kikusui requesting additional information about the EUT and the test setup. I haven't looked at the waveforms yet, other than voltage. That's on the docket. Regarding the matter of scale, (as I'm sure you're aware) the Simpson 228 uses multiple measurement networks and was the first commercially available leakage current meter to address UL 1459 requirements. The Burn Hazard setting (corresponding to 61010-1, Figure A.3, and the Kikusui TOS3200, Network A) is 100 mA full scale and I am trying to measure current below 1 mA. For shock hazard (Let Go and Reaction), the scale is OK. Peter Tarver > -Original Message- > From: Pete Perkins > Sent: Tuesday, April 25, 2017 23:17 > > Peter, > > Altho I have no experience with the Kikusui meter, I > believe that > you are on the right track chasing these differences. > > Since you have a Simpson 228 are you using a scope > to look at the > waveforms and get the readings for the scope display? In > my work with that > meter I always looked at the scope display because of the > better numerical > resolution from the scope display. If you have looked at the > collexion of > scope pix provided on safetylink you will see these details in > each scope > display - the waveforms as well as the digital readout of rms > and pk-pk > values. > > Not sure what your measured touch current is when > you say the 228 > doesn't have the sensitivity you need. The 0.3mA scale > should easily read > down to <0.03mA (<30uA) or below. Or is it you can't read > the differences > between two measurements on the meter face? Use your > scope reading to get > the numerical values, as discussed above. > > Not sure whether or not you can get scope > waveform pix from the > Kikusui unit. > > Unfortunately, the use of complex equipment takes > some training > and/or experience to get the correct result each time. The > mfgr makes it > sound so easy but the proof is in the use pudding. > The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Kikusui TOS3200 Leakage Current Meter
This afternoon's update: the resolution of the inductive current probes I have are limited to 10 Ma. All currents look like noise. Peter Tarver > -Original Message- > From: Peter Tarver > Sent: Wednesday, April 26, 2017 09:29 > > Thank you, Pete. > > I have received an initial response from Kikusui requesting > additional information about the EUT and the test setup. > > I haven't looked at the waveforms yet, other than voltage. > That's on the docket. > > Regarding the matter of scale, (as I'm sure you're aware) the > Simpson 228 uses multiple measurement networks and was > the first commercially available leakage current meter to > address UL 1459 requirements. The Burn Hazard setting > (corresponding to 61010-1, Figure A.3, and the Kikusui > TOS3200, Network A) is 100 mA full scale and I am trying to > measure current below 1 mA. > > For shock hazard (Let Go and Reaction), the scale is OK. > > > Peter Tarver The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Old editions of IEC 65
fifth edition, 1976 (original) has been spoken for. Priority: normal Date sent: Mon, 21 Aug 2017 06:31:55 -0700 Send reply to: ptar...@ieee.org > Hello, everyone. > > I'm going through old papers and discarding items I'm no > longer interested in keeping. I came across two old IEC 65 > editions. If anyone on the list has an historical (or other) > interest in having these documents, I'm happy to save them > from the bin. > > fourth edition, 1972 (photocopied) > fifth edition, 1976 (original) > an erratum to the third edition (photocopied) > > I'll hang onto these for a couple weeks, but they'll be in > the recycling bin or donated to a library after that. > > > Regards, > > Peter Tarver > - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] -60Vdc Telecom supply voltage
This reaches back twenty years and things change whether you're looking or not, but: DBP Telekom FTZ 19 Pfl 1 "Voltage Limits for 60 V Consumers in Telecommunication Installations of the Federal German Post Office" (no date): Normal range: -57.4 V to -67.7 V Short duration: -50.0 V to -75.0 V Austrian Telecommunications Authority Dbh VI 0128 "Requirements for Power Systems using Cell Switching for 48/60 V Telecommunication Installations" (1981): 60 V Normal range: 57.5 V to 63.0 V for switching installations 51.0 V to 65.0 V for microwave systems 48 V Normal range: 44.0 V to 49.5 V My recollection is that this existed mostly in the region along both sides of the border of Germany and Austria, rather than Germany as a whole. Peter Tarver From: Kannan Dhamodaran [mailto:kan...@india.tejasnetworks.com] Sent: Monday, August 14, 2017 21:36 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] -60Vdc Telecom supply voltage Thank you Joe Randolph and Bostjan for your information. I'm surprised many have not answered. Or maybe that's all the info available. Once again thanks to everyone in the group. Best regards, Kannan From: Joe Randolph [mailto:j...@randolph-telecom.com] Sent: Friday, August 11, 2017 9:22 PM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Subject: Re: [PSES] -60Vdc Telecom supply voltage Germany has historically been 60V, and I believe they still are. Joe Randolph Telecom Design Consultant Randolph Telecom, Inc. 781-721-2848 (USA) j...@randolph-telecom.com<mailto:j...@randolph-telecom.com> http://www.randolph-telecom.com From: Boštjan Glavič [mailto:bostjan.gla...@siq.si] Sent: Thursday, August 10, 2017 11:43 PM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Subject: Re: [PSES] -60Vdc Telecom supply voltage Hello Kannan, As far as I know it was used in Russia, however they switch now to 48VDC. In deed there are many different systems and somewhere they might still use 60VDC. Maybe also in some other ex-Soviet Union countries. Best regards, Bostjan From: Kannan Dhamodaran [mailto:kan...@india.tejasnetworks.com] Sent: Friday, August 11, 2017 5:10 AM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Subject: [PSES] -60Vdc Telecom supply voltage Dear valued members, can you guide me on nations that uses -60Vdc supply for telecom installations? Appreciate your valued inputs in advance. Best regards, Kannan - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)<http://www.ieee-pses.org/list.html> List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>> Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>> - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)<http://www.ieee-pses.org/list.html> List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>> Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>> - -
Re: [PSES] IEEE1547 - Unintentional Islanding
Hi, Ralph (say hello to Sarah U also). UL 1741, Supplement A has this as a requirement in Tables SA8.1 and SA8.2. Peter Tarver > -Original Message- > From: Ralph McDiarmid > Sent: Wednesday, May 03, 2017 10:59 > > Has anyone been asked to perform the Unintentional > Islanding tests in IEEE1547.1 at different static PF settings? > > > Ralph McDiarmid > Product Compliance > Solar Business > Schneider Electric > The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] Scientific principles behind Surface Creepage & Air Clearance
Hi, Vincent. As Bernd pointed out, IEC 60664 gives the best information on the scientific basis for Clearance and Creepage distances. Paschen’s Law will (theoretically) have no effect on Creepages. Theoretically, Creepages exists in two dimensions. Realistically, even the thinnest copper on a board has some height, so it’s possible that, under the right circumstances, Paschen’s could have an effect on Creepages as well as Clearances. Peter Tarver From: Vincent Lee Sent: Tuesday, May 09, 2017 21:00 Hi all, Good day, 1) May I know what is the scientific relationship between Paschen's Law (https://en.wikipedia.org/wiki/Paschen%27s_law) and surface creepage and air clearance distance ? 2) If there is a relationship, how can one calculate the surface creepage and air clearance distance (such as those in IEC 60601-1 3rd) based on Paschen's Law ? 3) If Paschen's Law is not applicable for such calculation, then how are the surface creepage and air clearance distance (such as those in IEC 60601-1 3rd) obtained ? On what scientific basis or principles ? The information contained in this message may be privileged and confidential. It is intended to be read only by the individual or entity to whom it is addressed or by their designee. If the reader of this message is not the intended recipient, you are on notice that any distribution of this message, in any form, is strictly prohibited. If you have received this message in error, please immediately notify the sender and delete or destroy any copy of this message! - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>