[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-29 Thread Steve Leyton
panels throughout a multi-family residential building.If it’s a 13R design, sprinkler protection is not required UNLESS… The situation described does in fact complicate the assessment of building height by number of stories. The IBC does not specify or even infer when an attic might

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-29 Thread matthew.willis1
) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249> matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> From: Dapr Jones Sent: Monday, July 29, 2024 8:39 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerf

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-29 Thread Tony Silva
If it becomes 4 storey, you might require a standpipe. Tony On Mon, Jul 29, 2024 at 7:10 AM wrote: > I suggest a careful reading of 6.6.6 in 13R. > > > > While a 13D system ignores storage in attics, 13R does not allow the same > considerations. > > > > App

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-29 Thread Dapr Jones
Thanks. Yes I see now that sprinklers would definitely be required if the tenant has access to the attic. Follow up- You can't just install a wet pipe system up there if you add heaters to the attic can you? NFPA 13R has special requirements (from what I understand) for sprinklers in attic where

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-29 Thread matthew.willis1
I suggest a careful reading of 6.6.6 in 13R. While a 13D system ignores storage in attics, 13R does not allow the same considerations. Appropriately, I think Todd means, if the area becomes a “Story” or not as defined in IBC. Then it would be treated like a dwelling unit. Otherwise, you

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-28 Thread Dapr Jones
Thanks Todd, much appreciated. Yes, it would still be 13R I agree. When you say " it would need to be appropriately protected" do you mean the attic would need to be sprinklered? It would become accessible to the tenant and they would likely use it for storage. Does 13R allo

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-28 Thread Fpdcdesign
instead of 3 and it would still be 13R. Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Jul 28, 2024 at 1:31 PM, mailto:daprjo...@gmail.com)> wrote: > > > > > I'm working on a project that

[Sprinklerforum] NFPA 13R - Multifamily with attic access

2024-07-28 Thread Dapr Jones
I'm working on a project that is 3 stories with attic, multifamily residential, type VA construction. We designed the system to NFPA 13R, with no sprinklers in the attic. Now the architect wants to add access to the attic for the 3'rd floor tenant. (note, there's only one tenant on the 3rd fl

[Sprinklerforum] Re: Interior Stairwells 13R vs 13D

2024-06-27 Thread Anthony Johnson
Thanks Steve. Yeah, not talking about storage closet under the stairs but under the angled stair risers that would be open and part of the room. 13R does a fair job of addressing this. 13D does not. My first thought would be to address this as an obstruction but 13R acknowledges in the appendix

[Sprinklerforum] Re: Interior Stairwells 13R vs 13D

2024-06-26 Thread Steve Leyton
: Wednesday, June 26, 2024 2:53 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Interior Stairwells 13R vs 13D 13R 2019 states "6.6.9.2 Sprinklers shall not be required underneath stair risers in dwelling units where the walls and cei

[Sprinklerforum] Interior Stairwells 13R vs 13D

2024-06-26 Thread Anthony Johnson
13R 2019 states "6.6.9.2 Sprinklers shall not be required underneath stair risers in dwelling units where the walls and ceilings are surfaced with noncombustible or limited-combustible finishes." I do not see a similar statute in 13D. Is there a reason for this? What is you

[Sprinklerforum] Re: NFPA 13R residential system - Exposed CPVC

2024-04-26 Thread Greg McGahan
Dapr, The Installation Guidelines of the CPVC will give you the criteria for installing CPVC exposed rather than 13R. Greg McGahan Genesis Fire Services, LLC. From: Dapr Jones Sent: Friday, April 26, 2024 10:57 AM To: Discussion list on issues relating

[Sprinklerforum] NFPA 13R residential system - Exposed CPVC

2024-04-26 Thread Dapr Jones
A multi-family fit up project will have existing to remain upper floor and new first floor apt. units. Currently the building is not sprinkled and will have a new sprinkler system. The contractor wants to run the new sprinkler pipe exposed using CPVC in the existing upper level units. NFPA 13R

[Sprinklerforum] Re: 13R water supply question

2024-03-01 Thread lvaughn2450
al opinion. I do note, however that 13R in §9.3 seems to suggest that a combined domestic and fire service to the building is completely acceptable with certain qualifiers regarding domestic demand being accounted for. let us know how this is resolved, Ken Wa

[Sprinklerforum] Re: 13R water supply question

2024-02-28 Thread Fpdcdesign
duplicative to me, however that's just personal opinion. > > I do note, however that 13R in §9.3 seems to suggest that a combined > domestic and fire service to the building is completely acceptable with > certain qualifiers regarding domestic demand being accounted for. >

[Sprinklerforum] Re: 13R water supply question

2024-02-28 Thread Ken Wagoner
personal opinion. I do note, however that 13R in §9.3 seems to suggest that a combined domestic and fire service to the building is completely acceptable with certain qualifiers regarding domestic demand being accounted for. let us know how

[Sprinklerforum] Re: 13R water supply question

2024-02-28 Thread Steve Leyton
Wednesday, February 28, 2024 12:40 PM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] 13R water supply question I have a 13R sprinkler system whose water supply is a 2" combination domestic/fire line run from the city main into the mechanical room. The plumber installed the

[Sprinklerforum] 13R water supply question

2024-02-28 Thread Chris Dorn
I have a 13R sprinkler system whose water supply is a 2" combination domestic/fire line run from the city main into the mechanical room. The plumber installed the line and pulled the proper permits for the installation of that domestic line. The plumber left a 2" outlet l

[Sprinklerforum] Re: 13R basements

2023-01-19 Thread Bobby Welch
That's what I thought. Thanks From: Dane Long [mailto:da...@bamfordfire.com] Sent: Thursday, January 19, 2023 3:50 PM To: 'Discussion list on issues relating to automatic fire sprinklers' Subject: [Sprinklerforum] Re: 13R basements You didn't specify which yr. of 13R. But in the 2016 it talks

[Sprinklerforum] Re: 13R basements

2023-01-19 Thread Dane Long
You didn't specify which yr. of 13R. But in the 2016 it talks about areas outside dwelling units in sections 6.2.2 and 7.2. 6.2.2 gives a list of allowable areas. 7.2 give you the criteria for these areas. My guess is this area is probably going to be used for storage so most likely

[Sprinklerforum] Re: 13R basements

2023-01-19 Thread Matt Grise
' Subject: [Sprinklerforum] Re: 13R basements Please review 2016 ed. NFPA 13R , Chapter 7., Design Criteria - Outside Dwelling Unit. It should be pretty clear. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design

[Sprinklerforum] Re: 13R basements

2023-01-19 Thread tstone52
Please review 2016 ed. NFPA 13R , Chapter 7., Design Criteria - Outside Dwelling Unit. It should be pretty clear. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd

[Sprinklerforum] 13R basements

2023-01-19 Thread Bobby Welch
When sprinkling a basement in a 13R system can residential heads be used, when the compartments are 1000 sq. ft. and the structure is exposed (2"x12" truss)? Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SECURITY 3577 Concorde Rd, Vandalia, OH 45377 P 937.641.8403 |

[Sprinklerforum] Re: 13R: Hotel Corridors Open to Lobby

2022-12-15 Thread J H
Thanks Ron. I just found in the handbook commentary that "A dwelling unit also includes the corridor that leads to the guest rooms in a hotel or motel type facility" which would seem to imply some level of boundaries. On Thu, Dec 15, 2022 at 11:25 AM Ron Greenman wrote: > If I'm picturing this

[Sprinklerforum] Re: 13R: Hotel Corridors Open to Lobby

2022-12-15 Thread Ron Greenman
If I'm picturing this one way I'd say if there was no separation other than visual like a valance, a floor elevation difference, or a change of carpet pattern then there is no corridor. If in another visualization where there is a corridor to either side of a wide opening from the lobby then the

[Sprinklerforum] 13R: Hotel Corridors Open to Lobby

2022-12-15 Thread J H
Ref: NFPA 2013 6.4.7 Use of residential sprinklers are permitted in corridors, foyers, hall etc. under 6.4.7. However, lobbies in hotels and motels are expressly forbidden to have residential sprinklers in this section which leads me to a couple of questions: What about the corridors connecting

[Sprinklerforum] Re: 13R spacing

2022-06-21 Thread Sean Lockyer
have their own advantages and drawbacks. -Original Message- From: Sarah Sent: Tuesday, June 21, 2022 8:57 PM To: Sean Lockyer Cc: sprinklerforum@lists.firesprinkler.org Subject: Re: [Sprinklerforum] 13R spacing Most residential sprinklers can cover 18’x18’ or 20’x20’ spacing. Why not inc

[Sprinklerforum] Re: 13R spacing

2022-06-21 Thread Sean Lockyer
Larger pipe size as a result (most likely) = $$$ -Original Message- From: Sarah Sent: Tuesday, June 21, 2022 8:57 PM To: Sean Lockyer Cc: sprinklerforum@lists.firesprinkler.org Subject: Re: [Sprinklerforum] 13R spacing Most residential sprinklers can cover 18’x18’ or 20’x20’ spacing

[Sprinklerforum] 13R spacing

2022-06-21 Thread Sean Lockyer
Can the kitchen cabinetry/countertops, etc be eliminated from the floor space being protected in a 13R application ? I have a kitchen that is littered with multiple diffusers and lights and in order to make the spacing work out correctly, I won't be able to space the head in the kitchen

[Sprinklerforum] Re: Non-combustible patio/balcony in 13R Type V construction

2022-05-19 Thread Matthew Bristoll
Hello Sean- This is also a requirement of NFPA 13R. 6.6.5.1 Where a roof or deck is provided above, sprinklers shall be installed to protect attached exterior balconies, attached exterior decks, and ground floor patios serving dwelling units in buildings of Construction Type V. My opinion

[Sprinklerforum] Re: Non-combustible patio/balcony in 13R Type V construction

2022-05-18 Thread Matt Grise
is type 5 and not fire rated or FRT wood, then you will probably need sprinklers out there too! That is 13 and 13R even if it is not covered (by the letter of the code). [IBC 2018 edition, section 705.2.3.1] I would plan on sprinklers. Matt From: travis.m...@mfpdesign.com Sent: Wednesday, May 18,

[Sprinklerforum] Re: Non-combustible patio/balcony in 13R Type V construction

2022-05-18 Thread Travis.Mack
lHhABSexWY%3D=0> From: Sean Lockyer Sent: Wednesday, May 18, 2022 5:45:02 PM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Non-combustible patio/balcony in 13R Type V construction Per the Florida Building Code, Chapter 9, sprinkler prot

[Sprinklerforum] Non-combustible patio/balcony in 13R Type V construction

2022-05-18 Thread Sean Lockyer
Per the Florida Building Code, Chapter 9, sprinkler protection is required for an exterior balcony in a 13R system if the building is of Type V construction. However, that also assumes that the balcony overhang is also type V (I.E. - wood) but what would you do if the balcony is NOT combustible

[Sprinklerforum] Non-combustible patio/balcony in 13R Type V construction

2022-05-18 Thread Sean Lockyer
Per the Florida Building Code, Chapter 9, sprinkler protection is required for an exterior balcony in a 13R system if the building is of Type V construction. However, that also assumes that the balcony overhang is also type V (I.E. - wood) but what would you do if the balcony is NOT combustible

[Sprinklerforum] Re: Open attached corridor in 13R

2022-05-06 Thread Travis.Mack
56 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Open attached corridor in 13R I'm looking at a 13R project that has open attached corridors and stairs. The corridors are about 33' deep and dead end. Can sprinklers be omitted per 13R (2016), "6.6.5 Except as provided f

[Sprinklerforum] Open attached corridor in 13R

2022-05-06 Thread Bob Knight
I'm looking at a 13R project that has open attached corridors and stairs. The corridors are about 33' deep and dead end. Can sprinklers be omitted per 13R (2016), "6.6.5 Except as provided for in 6.6.5.1, sprinklers shall not be required in any porches, balconies, corridors, carports,

RE: 13R bathrooms

2022-01-11 Thread BILL MENSTER via Sprinklerforum
, January 11, 2022 2:14 PM To: sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com; wmens...@comcast.net Subject: RE: 13R bathrooms BE ADVISED - This email originated outside EMCOR. Tub area is

RE: 13R bathrooms

2022-01-11 Thread Mike Morey via Sprinklerforum
et Subject: RE: 13R bathrooms BE ADVISED - This email originated outside EMCOR. Tub area is to be included. I believe there was confusion as it wasn't always being applied correctly, so the committee just said 55 sq ft total. Travis Mack, CFPS, CWBSP, RME-G, COC, SET Senior Engineering Mana

RE: 13R bathrooms

2022-01-11 Thread Travis Mack via Sprinklerforum
8f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0> From: Sprinklerforum On Behalf Of BILL MENSTER via Sprinklerforum Sent: Tuesday, January 11, 2022 11:53 AM To: sprinklerforum Cc: BILL MENSTER Subject: 13R bathrooms I bel

13R bathrooms

2022-01-11 Thread BILL MENSTER via Sprinklerforum
I believe past editions of NFPA 13R (pre-2007) included an explanation that the bathtub area need not be included in the square foot area of the bathroom. However, current editions (in this case the 2016 edition) do not include this language. My question is, does the tub area need

RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread tstone52--- via Sprinklerforum
To: sprinklerforum@lists.firesprinkler.org Cc: Steve Leyton ; Salvatore Izzo Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies Good call Sal; as I said in my response, it's up to the Building Official to clarify whether that separation has to be two or three hours

RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread Steve Leyton via Sprinklerforum
| Planning | Training -Original Message- From: Sprinklerforum On Behalf Of Salvatore Izzo via Sprinklerforum Sent: Tuesday, November 09, 2021 1:29 PM To: sprinklerforum@lists.firesprinkler.org Cc: Salvatore Izzo Subject: Re: 13R Installation of Sprinkler Systems in Low-Rise

Re: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread 321 via Sprinklerforum
Gentlemen, The way we would interpret this in Florida per the "Florida Fire Prevention Code" would be based on the height of the top "Floor Level". I think at the least you are looking at 13 for the garage level, 13R for the Residential Levels, and an "Manual Wet"

Re: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread Salvatore Izzo via Sprinklerforum
iginal Message- > From: Steve Leyton > Sent: Tuesday, November 9, 2021 3:51 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: tston...@comcast.net > Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential > Occupancies > > Assuming the building code

RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread Dane Long via Sprinklerforum
Salina, KS  67401 -Original Message- From: Sprinklerforum On Behalf Of tstone52--- via Sprinklerforum Sent: Tuesday, November 9, 2021 2:42 PM To: sprinklerforum@lists.firesprinkler.org Cc: tston...@comcast.net Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupan

RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread tstone52--- via Sprinklerforum
...@comcast.net Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies Assuming the building code that's applicable to this project classifies this as two separate buildings (a four-story Type 3 on a single-story Type 1 podium), NFPA 13R can be used as a basis of design in many

Re: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread Fpdcdesign via Sprinklerforum
Is there a Code information sheet from the architect? Check to see what allowances have been taken. Is the separation enough for this to be treated as two buildings or is it a single building? My gut answer says no to 13R but the differences in construction could make

RE: 13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread Steve Leyton via Sprinklerforum
Assuming the building code that's applicable to this project classifies this as two separate buildings (a four-story Type 3 on a single-story Type 1 podium), NFPA 13R can be used as a basis of design in many (most?) jurisdictions. It is up to the building official to clarify whether a two

13R Installation of Sprinkler Systems in Low-Rise Residential Occupancies

2021-11-09 Thread tstone52--- via Sprinklerforum
Am I reading the Scope of 13R correctly? I am designing a Sprinkler system for a building which is five stories in height. Each floor is about 5,500 SF. The Ground floor is a parking garage of concrete & steel (Type 1a construction) with 4 stories of Residential above which constructed of

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread BILL MENSTER via Sprinklerforum
gt; behalf of BILL MENSTER via Sprinklerforum > > Sent: Tuesday, May 11, 2021 11:49:24 AM > To: sprinklerforum@lists.firesprinkler.org > > Cc: BILL MENSTER ; Fpdcdesign > Subject: Re: 13 / 13R IN SAME BUILDING? > > Thanks all for your input. > > Bill Menster > WFM Consul

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread John Drucker via Sprinklerforum
What Building Code are you using ? John Drucker From: Sprinklerforum on behalf of BILL MENSTER via Sprinklerforum Sent: Tuesday, May 11, 2021 11:49:24 AM To: sprinklerforum@lists.firesprinkler.org Cc: BILL MENSTER ; Fpdcdesign Subject: Re: 13 / 13R IN SAME

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread BILL MENSTER via Sprinklerforum
Thanks all for your input. Bill Menster WFM Consulting > On 05/11/2021 9:53 AM Fpdcdesign via Sprinklerforum > wrote: > > > Look under “Scope” in NFPA 13R, both the main part and the appendix. > > > > Todd G Williams, PE > Fire Protection Desig

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread John Denhardt via Sprinklerforum
Something to think about Keep in mind NFPA 13R has limited property protection compared to a NFPA 13 system. Can the community afford to lose the use of the firehouse due to a fire which was not contained by a NFPA 13R system. John John August Denhardt, P.E Vice President Engineering

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread Fpdcdesign via Sprinklerforum
Look under “Scope” in NFPA 13R, both the main part and the appendix. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell

RE: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread Matt Grise via Sprinklerforum
: Sprinklerforum On Behalf Of BILL MENSTER via Sprinklerforum Sent: Tuesday, May 11, 2021 8:33 AM To: sprinklerforum Cc: BILL MENSTER Subject: 13 / 13R IN SAME BUILDING? I have a fire station retro-fit project in Michigan. The A/E has specified NFPA 13 design for the entire facility and 13R design

13 / 13R IN SAME BUILDING?

2021-05-11 Thread BILL MENSTER via Sprinklerforum
I have a fire station retro-fit project in Michigan. The A/E has specified NFPA 13 design for the entire facility and 13R design for only the second floor of the 2-story section which is a sleeping area. This 2-story section is wood frame construction with attic space. The A/E is using

Re: 13R Balcony Protection - Any Depth Requirements?

2021-02-12 Thread Mike B Morey via Sprinklerforum
FWIW this was born out of the fire code as a hedge against exposure fires from grilling, primarily, probably patio heaters and what not as well now. It then migrated into 13R due to the near universal pairing of IBC/IFC with 13R. IFC/IFC commentary unfortunately doesn't give a ton of wiggle

13R Balcony Protection - Any Depth Requirements?

2021-02-12 Thread J H via Sprinklerforum
I notice that 13R 6.6.5.1 (2013 ed) requirement for sprinkler coverage for exterior balconies does not have a depth requirement unlike the 4ft rule found in 13. I have some apartments I'm bidding with a balcony at the upper level and the overhang is 3 ft.over the balcony. I'm going to put

RE: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread Steve Leyton via Sprinklerforum
: travis.m...@mfpdesign.com Subject: Re: NFPA 13R & NFPA 14 - (flow rates) But domestic demand is added at the split with domestic and fire. The domestic wouldn’t flow through standpipes. It would have to be some crazy accessory use. Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Man

Re: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread Travis Mack via Sprinklerforum
February 6, 2021 2:27:55 PM To: 'Jose Anibal Castillo' ; sprinklerforum@lists.firesprinkler.org ; st...@protectiondesign.com ; sbi...@wenteplumbing.com Cc: d...@engfirepro.com Subject: RE: NFPA 13R & NFPA 14 - (flow rates) I suspect that requirement is due more to the Domestic Demand

RE: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread David L. Miller, P.E. via Sprinklerforum
I suspect that requirement is due more to the Domestic Demand in a very (extremely) large apartment building. Table A.9.6(b) (NFPA 13R, 2016 Edition) shows a Domestic Demand of 500 gpm for a building with 3500 Fixture Units. Without a plumbing code handy I don't know where the domestic demand

Re: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread Jose Anibal Castillo via Sprinklerforum
. In that example, the apartment complex with the boat storage the part where it is required to be used nfpa 13. If that is the case, then section 7.10.1.3.1.1 would not have needed to add 13R since with 13 would have been good enough, I think. I followed back and found that the 13R was added in 2013

Re: NFPA 13R & NFPA 14

2021-02-04 Thread Skyler Bilbo via Sprinklerforum
I could dream up a scenario where a 13R system had a higher pressure requirement (with a lower flow) than a standpipe calculation. Being limited to 4 stories definitely makes this a lot less likely to occur in the real world. It could happen, but I have never seen it here in the real world

RE: NFPA 13R & NFPA 14

2021-02-04 Thread Steve Leyton via Sprinklerforum
In practice, probably not. As I'm sitting here today, I can't honestly recall how/when that section came into being or when we may have last tweaked it, but it's a CYA for sure.Maybe if I had a building projected with 13R that had an accessory use like... I dunno, boat storage. A marina

Re: NFPA 13R & NFPA 14

2021-02-04 Thread John Denhardt via Sprinklerforum
Jose Anibal Castillo via Sprinklerforum > Sent: Thursday, February 4, 2021 10:43 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Jose Anibal Castillo > Subject: NFPA 13R & NFPA 14 > > CAUTION: This email originated from outside of the organization. Do no

RE: NFPA 13R & NFPA 14

2021-02-04 Thread Cary Webber via Sprinklerforum
via Sprinklerforum Sent: Thursday, February 4, 2021 10:43 AM To: sprinklerforum@lists.firesprinkler.org Cc: Jose Anibal Castillo Subject: NFPA 13R & NFPA 14 CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you can confirm the se

RE: [EXTERNAL] NFPA 13R & NFPA 14

2021-02-04 Thread Kyle.Montgomery via Sprinklerforum
13R & NFPA 14 In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R system demand is higher than the standpipe demand it is supposed to be chosen the higher demand. Is it even possible to have a residential sprinkler system with a higher demand than the stand

NFPA 13R & NFPA 14

2021-02-04 Thread Jose Anibal Castillo via Sprinklerforum
In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R system demand is higher than the standpipe demand it is supposed to be chosen the higher demand. Is it even possible to have a residential sprinkler system with a higher demand than the standpipe? Regards José

Re: Domestic Demands 13R

2020-11-12 Thread BRUCE VERHEI via Sprinklerforum
: sprinklerforum@lists.firesprinkler.org > > Cc: travis.m...@mfpdesign.com > Subject: Domestic Demands 13R > > [EXTERNAL] > > Forumites: > > Per 13R 9.6 it requires the domestic demand for the building being calculated > to be added to the fire sprinkler system. This i

RE: Domestic Demands 13R

2020-11-12 Thread Jim Davidson via Sprinklerforum
On Behalf Of J H via Sprinklerforum Sent: Thursday, November 12, 2020 3:06 PM To: sprinklerforum@lists.firesprinkler.org Cc: J H Subject: Re: Domestic Demands 13R If the AHJ digs in there is always the route of using automatic domestic shutoff valves.. <https://www.avast.com/sig-em

Re: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
** From: Sprinklerforum on behalf of Matt Grise via Sprinklerforum Sent: Thursday, November 12, 2020 1:16:17 PM To: sprinklerforum@lists.firesprinkler.org Cc: Matt Grise Subject: RE: Domestic Demands 13R What if you just brought in a separate fire line? Then you

RE: Domestic Demands 13R

2020-11-12 Thread Matt Grise via Sprinklerforum
On Behalf Of Ed Kramer via Sprinklerforum Sent: Thursday, November 12, 2020 2:14 PM To: sprinklerforum@lists.firesprinkler.org Cc: e...@bamfordfire.com Subject: RE: Domestic Demands 13R Section 9.6 (2016) says "Domestic demand FOR THE BUILDING BEING CALCULATED shall be included . . .&quo

RE: Domestic Demands 13R

2020-11-12 Thread Ed Kramer via Sprinklerforum
ebarkerfire.com; sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com Subject: RE: Domestic Demands 13R Correct. However, they may be expected to have domestic demands. That is the plan reviewer rationale in one particular case. Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Man

Re: Domestic Demands 13R

2020-11-12 Thread J H via Sprinklerforum
_campaign=sig-email_content=webmail_term=link> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2> On Thu, Nov 12, 2020 at 9:34 AM Travis Mack via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Forumites: > > Per 13R 9.6 it requires the domestic demand for the buildi

Re: Domestic Demands 13R

2020-11-12 Thread John Denhardt via Sprinklerforum
That request is now our list of items to be considered or the 2025 edition of 13R. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org <ht

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
I think the rationale is that for a project in the downtown areas, your flow test is already accounting for those buildings being active. In the new development, your flow test is not accounting for those since they don't yet exist. However, I am glad the commentary in the 13R handbook (2016

RE: Domestic Demands 13R

2020-11-12 Thread Bob Knight via Sprinklerforum
- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack via Sprinklerforum Sent: Thursday, November 12, 2020 9:53 AM To: philli...@pyebarkerfire.com; sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com Subject: RE: Domestic Demands 13R Correct

RE: Domestic Demands 13R

2020-11-12 Thread Hinson, Ryan via Sprinklerforum
f Ron Greenman via Sprinklerforum Sent: Thursday, November 12, 2020 11:19 AM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: Re: Domestic Demands 13R My understanding of this is that the complex would have had a total fire flow and domestic flow calculated into the main

Re: Domestic Demands 13R

2020-11-12 Thread Skyler Bilbo via Sprinklerforum
ld do: add the domestic demand at the hydraulically remote building first, then add the incremental demand for the rest of the buildings along the way, knowing that the incremental demand is not the same as the demand for the furthest building (eg. looking at the table in my 13R, if all buildings had 50 fix

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
The commentary in the 2016 edition of the 13R handbook states that you don't include the demand for the other buildings. You only include the demand of the building being calculated. Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 NEW

RE: Domestic Demands 13R

2020-11-12 Thread Matt Grise via Sprinklerforum
I agree - we are starting to make assumptions about the design basis of the civil/underground water system. 13R 9.6 says "for the building being calculated"- not 'along with all of the other buildings that might use the same underground supply' The handbook goes

Re: Domestic Demands 13R

2020-11-12 Thread Ron Greenman via Sprinklerforum
=2591775=517003 > or > http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true=6=2591775=517003** > > From: Hinson, Ryan > Sent: Thursday, November 12, 2020 9:59 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Travis Mac

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
@lists.firesprinkler.org Cc: Travis Mack Subject: RE: Domestic Demands 13R Is this entire complex brand new or existing? Your answer will determine mine: 1. Taking a water flow test on an existing looped water main supplying both FW and domestic demands already accounts for the domestic demands of the other

RE: Domestic Demands 13R

2020-11-12 Thread Hinson, Ryan via Sprinklerforum
into the building in question, one only needs to include the domestic demand for that building where the domestic is not provided with a valve preventing domestic flow in the event of a sprinkler activation therein. NFPA 13R (2016) Section 9.6 states, "Domestic Demand. Domestic d

RE: Domestic Demands 13R

2020-11-12 Thread Sean.VanGaal via Sprinklerforum
, November 12, 2020 9:51 AM To: sprinklerforum@lists.firesprinkler.org; travis.m...@mfpdesign.com Cc: Mark Phillips Subject: [EXTERNAL] Re: Domestic Demands 13R From a practical perspective all of the apartment building would not be expected to be on fire at once. That was how a plan reviewer once

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
 or  http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true=6=2591775=517003** From: Mark Phillips Sent: Thursday, November 12, 2020 9:51 AM To: sprinklerforum@lists.firesprinkler.org; Travis Mack Subject: Re: Domestic Demands 13R From a practical

Re: Domestic Demands 13R

2020-11-12 Thread Mark Phillips via Sprinklerforum
Phillips via Sprinklerforum Sent: Thursday, November 12, 2020 11:46:23 AM To: travis.m...@mfpdesign.com ; sprinklerforum@lists.firesprinkler.org Cc: Mark Phillips Subject: Re: Domestic Demands 13R [EXTERNAL] Sorry if I was not clear only the demand of the building or buildings that share the 4

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
: RE: Domestic Demands 13R I understand you said you are designed per 13R, but since you have a large lead-in of 4" have you tried to use "the more stringent 13 standard" that essentially says UG mains less than 4" that are for fire/domestic you have to calculate both u

Re: Domestic Demands 13R

2020-11-12 Thread Mark Phillips via Sprinklerforum
; sprinklerforum@lists.firesprinkler.org Subject: RE: Domestic Demands 13R [EXTERNAL] So in this case, you would be adding a total demand of 2500 gpm (20 buildings at 125 gpm each) to your sprinkler calc? And yes, it would be included at the point of each 4” connection to the 8” main. Seems

RE: Domestic Demands 13R

2020-11-12 Thread Sean.VanGaal via Sprinklerforum
I understand you said you are designed per 13R, but since you have a large lead-in of 4" have you tried to use "the more stringent 13 standard" that essentially says UG mains less than 4" that are for fire/domestic you have to calculate both unless you have a way to a

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
/n1gewi5ud95byeftyuoy12/external?email=true=6=2591775=517003** From: Mark Phillips Sent: Thursday, November 12, 2020 9:41 AM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack Subject: Re: Domestic Demands 13R Assuming the 8 inch supply loops the complex Add the domestic demand at the 4” point

Re: Domestic Demands 13R

2020-11-12 Thread Mark Phillips via Sprinklerforum
, November 12, 2020 11:34:20 AM To: sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com Subject: Domestic Demands 13R [EXTERNAL] Forumites: Per 13R 9.6 it requires the domestic demand for the building being calculated to be added to the fire sprinkler system. This is generally

RE: Domestic Demands 13R

2020-11-12 Thread Matthew J Willis via Sprinklerforum
- From: Sprinklerforum On Behalf Of Travis Mack via Sprinklerforum Sent: Thursday, November 12, 2020 9:34 AM To: sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com Subject: Domestic Demands 13R Forumites: Per 13R 9.6 it requires the domestic demand for the building being

Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
Forumites: Per 13R 9.6 it requires the domestic demand for the building being calculated to be added to the fire sprinkler system. This is generally not an issue. If you have a complex of say 20 buildings on site that is supplied by a common water line serving both domestic and fire, are you

Re: 13R and Well Pump?

2020-07-21 Thread David Williams via Sprinklerforum
DESIGN From: Sprinklerforum on behalf of "sprinklerforum@lists.firesprinkler.org" Reply-To: "sprinklerforum@lists.firesprinkler.org" Date: Tuesday, July 21, 2020 at 9:56 AM To: "sprinklerforum@lists.firesprinkler.org" Cc: Mark Phillips , James Litvak Subject

RE: 13R and Well Pump?

2020-07-21 Thread Mark Phillips via Sprinklerforum
@lists.firesprinkler.org Cc: James Litvak Subject: 13R and Well Pump? [EXTERNAL] Would a well pump be allowed for a 13R system? It doesn't directly meet the definitions of one of the sources outlined in section 9.3, but I'm wondering if anyone has used one and been able to justify it, and have it approved

Re: 13R and Well Pump?

2020-07-21 Thread Fpdcdesign via Sprinklerforum
Not for.a 13R. For one thing, would the well pump be able to 60 gpm (4 sprinklers at 13 gpm + overage)?And do that at a 40 psi pressure? And sustain that for 30 minutes? Not likely that a well pump or residential sized well could do that. Todd G Williams, PE Fire

13R and Well Pump?

2020-07-21 Thread James Litvak via Sprinklerforum
Would a well pump be allowed for a 13R system? It doesn't directly meet the definitions of one of the sources outlined in section 9.3, but I'm wondering if anyone has used one and been able to justify it, and have it approved. ___ Sprinklerforum mailing

Comparison between NFPA 13R and NFPA 14

2020-06-22 Thread Jose Anibal Castillo via Sprinklerforum
Hope you are all doing well. I would like to ask if anyone in the forum has experience with NFPA 13R and NFPA 14. In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R system demand is higher than the standpipe demand it is supposed to be chosen the higher demand. I am

RE: Covered Parking in 13R

2020-06-01 Thread Greg McGahan via Sprinklerforum
Good points Skyler but it is worth mentioning that the decisions you mentions (13 vs 13r) etc. are subject to Geography and Jurisdiction. In Florida for instance, anything less than 50 sprinklers IS designed solely by the Sprinkler Contractor and we are responsible for answering that question