Depends on your needs from $125.00 and up...
Jaime Solorza
On Feb 6, 2018 1:05 PM, "Mathew Howard" wrote:
> What's the cost on those?
>
> On Tue, Feb 6, 2018 at 1:45 PM, Jaime Solorza
> wrote:
>
>> We have zero issues with these..
>> http://www.pulspower.com/?id=565
>>
>> Jaime Solorza
>>
>> O
My bad, I missed the voltage adjust hidden in the wire grid on the
bottom. It allows adjustment up to 28V output, which give the battery
float voltage I was looking for (27.4). Alas, that doesn't fix the bad
unit that I received that just sits there clicking an putting out 15-16V
under load.
What's the cost on those?
On Tue, Feb 6, 2018 at 1:45 PM, Jaime Solorza
wrote:
> We have zero issues with these..
> http://www.pulspower.com/?id=565
>
> Jaime Solorza
>
> On Feb 6, 2018 12:44 PM, "Josh Baird" wrote:
>
>> The SDR (eg SDR-240-48 [1]) is a 240W AC-DC 48V power supply. It does
>>
Adding a DR-UPS40 isn't really going to change anything as far as the
differences go between the SDR and DRP (unless I'm missing something... ),
the DR-UPS40 just puts out the same voltage to the battery that it's
getting in, so it's still going to be fixed at 24v (which is too low for a
proper flo
We have zero issues with these..
http://www.pulspower.com/?id=565
Jaime Solorza
On Feb 6, 2018 12:44 PM, "Josh Baird" wrote:
> The SDR (eg SDR-240-48 [1]) is a 240W AC-DC 48V power supply. It does not
> have a battery charger. This is what I was talking about.
>
> The unit to avoid is the SD
The SDR (eg SDR-240-48 [1]) is a 240W AC-DC 48V power supply. It does not
have a battery charger. This is what I was talking about.
The unit to avoid is the SD series of Meanwell's DC-DC converters (use RSD
instead).
[1]
https://www.mouser.com/ProductDetail/?qs=pg%252b85jAIcxtNOjEKDbfLJA%3D%3D
After receiving my DRP Meanwell, I can say that this was reversed. The
SDR is suitable as a battery charger the DRP is a fixed 24V output power
supply. I can team it with the DR-UPS40 to make it the same as the
SDR.Now I remember some people mentioned that there was a unit to
stay away
;>>> Unless your batteries are really stoned.
>>>> -Original Message- From: Seth Mattinen Sent: Wednesday, January
>>>> 31, 2018 5:20 PM To: af@afmug.com Subject: Re: [AFMUG] Dc plant
>>>> conversion
>>>> On 1/31/18 15:44, Josh Baird wrote:
&
- From: Seth Mattinen Sent: Wednesday, January
>>> 31, 2018 5:20 PM To: af@afmug.com Subject: Re: [AFMUG] Dc plant
>>> conversion
>>> On 1/31/18 15:44, Josh Baird wrote:
>>>
>>>> Do NOT use the SD series. Sager is a reputable supplier! The RSD
nd) nothing exploded, but
> you couldn't actually switch any of them off. If I turned off one port,
> the load moved to one of the other ports.
>
>
> -- Original Message --
> From: "Josh Baird"
> To: af@afmug.com
> Sent: 1/31/2018 3:03:25 PM
> Sub
e 6 units.
>
> I suppose we could have two PDU with 3 on each….
>
>
>
> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Mathew Howard
> *Sent:* Wednesday, January 31, 2018 12:23 PM
> *To:* af
> *Subject:* Re: [AFMUG] Dc plant conversion
>
>
>
> Yep, the
wn wrote:
>
>> Unless your batteries are really stoned.
>> -Original Message- From: Seth Mattinen Sent: Wednesday, January
>> 31, 2018 5:20 PM To: af@afmug.com Subject: Re: [AFMUG] Dc plant
>> conversion
>> On 1/31/18 15:44, Josh Baird wrote:
>>
>
Unless your batteries are really stoned.
-Original Message-
From: Seth Mattinen
Sent: Wednesday, January 31, 2018 5:20 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
On 1/31/18 15:44, Josh Baird wrote:
Do NOT use the SD series. Sager is a reputable supplier! The
2018 11:54
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] Dc plant conversion
>
>
>
> My problem with them (SD) was that a current in-rush would trip them, and
> the only way to get them to work again was to power cycle them. Not fun.
>
>
>
> On Wed, Jan 31, 2018 at 8:
Not fun indeed. When you say current in-rush, is that on the mains/supply side?
From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird
Sent: Thursday, 1 February 2018 11:54
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
My problem with them (SD) was that a current in-rush
Wed, Jan 31, 2018 at 8:51 PM, Mark Frost wrote:
>
>> What dramas did you have with the SD units? Any model specifically?
>>
>>
>>
>>
>>
>> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Josh Baird
>> *Sent:* Thursday, 1 February 2018
..@afmug.com<mailto:af-boun...@afmug.com>] On Behalf
Of Josh Baird
Sent: Thursday, 1 February 2018 11:15
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] Dc plant conversion
Good info - thanks!
On Wed, Jan 31, 2018 at 7:20 PM, Seth Mattinen
mailto:se...@rollernet.us>>
>
> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Josh Baird
> *Sent:* Thursday, 1 February 2018 11:15
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] Dc plant conversion
>
>
>
> Good info - thanks!
>
>
>
> On Wed, Jan 31, 2018 at 7:20 PM, Seth Mattinen
What dramas did you have with the SD units? Any model specifically?
From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird
Sent: Thursday, 1 February 2018 11:15
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
Good info - thanks!
On Wed, Jan 31, 2018 at 7:20 PM, Seth Mattinen
Good info - thanks!
On Wed, Jan 31, 2018 at 7:20 PM, Seth Mattinen wrote:
> On 1/31/18 15:44, Josh Baird wrote:
>
>> Do NOT use the SD series. Sager is a reputable supplier! The RSD units
>> can be hard to find at times, but are super reliable.
>>
>
>
> SD-500 and larger does do constant curre
I wasted a small fortune with the SD series. what a joke.
On Wed, Jan 31, 2018 at 4:20 PM, Seth Mattinen wrote:
> On 1/31/18 15:44, Josh Baird wrote:
>
>> Do NOT use the SD series. Sager is a reputable supplier! The RSD units
>> can be hard to find at times, but are super reliable.
>>
>
>
> SD
On 1/31/18 15:44, Josh Baird wrote:
Do NOT use the SD series. Sager is a reputable supplier! The RSD units
can be hard to find at times, but are super reliable.
SD-500 and larger does do constant current limiting but with a 5 second
shutoff. All of the smaller SD series do not. 5 seconds sh
ny use, dissemination, copying, or storage of this
message or its attachments is strictly prohibited.
From: Af on behalf of SmarterBroadband
Reply-To: "af@afmug.com"
Date: Wednesday, January 31, 2018 at 6:05 PM
To: "af@afmug.com"
Subject: Re: [AFMUG] Dc plant conversion
Is that the
Good to know…
From: Af [mailto:af-boun...@afmug.com] On Behalf Of Adam Moffett
Sent: Wednesday, January 31, 2018 1:10 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
Careful. Packetflux PDU can't do positive ground. So no -48. Found that out
the hard way.
If neithe
PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
The ICT -48 Unit I have has a 4 position toggle switch breaker…the breakers can
be remote tripped via the easy to use web interface. You could get away with
that instead of the distribution panel.
Cheers,
Andreas Wiatowski
From: Af on behalf of Dustin Jurman
Reply-To: "af@afmug.com"
Date: Wednesday, January 31, 2018 at 5:19 PM
To: "af@afmug.com"
Subject: Re: [AFMUG] Dc plant conversion
We have been playing with some of these in -48 and IDC Netonix. Working very
well.
DSJ
From: Af [mailt
From: Af on behalf of Adam Moffett
Reply-To: "af@afmug.com"
Date: Wednesday, January 31, 2018 at 4:13 PM
To: "af@afmug.com"
Subject: Re: [AFMUG] Dc plant conversion
When I say "found out the hard way" I should clarify that was through no fault
of packetflux.
We have been playing with some of these in -48 and IDC Netonix. Working very
well.
DSJ
From: Af [mailto:af-boun...@afmug.com] On Behalf Of SmarterBroadband
Sent: Wednesday, January 31, 2018 2:58 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
I have been looking at ICT. The
t; -- Original Message --
> From: "Josh Baird"
> To: af@afmug.com
> Sent: 1/31/2018 3:03:25 PM
> Subject: Re: [AFMUG] Dc plant conversion
>
> PacketFlux (PDU) would be able to power cycle DC powered radios. This is
> likely what we'll be doing for Baice
offett"
To: af@afmug.com
Sent: 1/31/2018 4:10:10 PM
Subject: Re: [AFMUG] Dc plant conversion
Careful. Packetflux PDU can't do positive ground. So no -48. Found
that out the hard way.
If neither the load or the power supply has a ground on the positive
wire then you're good to g
#x27;t actually switch any of them off. If I turned off one
port, the load moved to one of the other ports.
-- Original Message --
From: "Josh Baird"
To: af@afmug.com
Sent: 1/31/2018 3:03:25 PM
Subject: Re: [AFMUG] Dc plant conversion
PacketFlux (PDU) would be able to power cycle
.com> ] On Behalf
Of can...@believewireless.net <mailto:can...@believewireless.net>
Sent: Saturday, January 27, 2018 3:51 AM
To: af@afmug.com <mailto:af@afmug.com>
Subject: Re: [AFMUG] Dc plant conversion
It's a little spendy but about how about 1 $670 option? Alpha Cordex PSU 24
uary 29, 2018 at 1:56 PM
> To: "af@afmug.com"
> Subject: Re: [AFMUG] Dc plant conversion
>
> That looks to meet alot of our need, though the 48 volt
>
> SAF recommended Eltek minipack system, i havent priced that
>
> This is what most of our sites have (theres so
;>
>>>
>>>
>>> Need a solution where we can power cycle DC powered radios.
>>>
>>>
>>>
>>> Adam
>>>
>>>
>>>
>>> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *
>>> can...@belie
>>
>>
>> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *
>> can...@believewireless.net
>> *Sent:* Saturday, January 27, 2018 3:51 AM
>> *To:* af@afmug.com
>> *Subject:* Re: [AFMUG] Dc plant conversion
>>
>>
>>
>> It's a litt
;mailto:af@afmug.com>" mailto:af@afmug.com>>
Subject: Re: [AFMUG] Dc plant conversion
That looks to meet alot of our need, though the 48 volt
SAF recommended Eltek minipack system, i havent priced that
This is what most of our sites have (theres some depreciating ubnt sectors too)
4x
an power cycle DC powered radios.
>
>
>
> Adam
>
>
>
> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *
> can...@believewireless.net
> *Sent:* Saturday, January 27, 2018 3:51 AM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] Dc plant conversion
>
>
>
> I
a bad deal.
-- Original Message --
From: "David Coudron" mailto:david.coud...@advantenon.com>>
To: "af@afmug.com <mailto:af@afmug.com>" mailto:af@afmug.com>>
Sent: 1/28/2018 10:39:56 PM
Subject: Re: [AFMUG] Dc plant conversi
all the wires running to the TPDIN to
monitor voltage, current, and Relays for the Fan, Heater and Netonix.
Regards,
David Coudron
From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird
Sent: Monday, January 29, 2018 3:45 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
We
;> supply as needed.
>>>>
>>>> What has held me back from that in the past is the DR-UPS is not
>>>> available in 48v, and the biggest power consumers I have are 48V. I went
>>>> to Traco to stay 48V. OTOH your rig is so much cheaper than Traco that
>&g
gt;>
>>
>>
>> Best part is, no coding necessary. Doing all this with the Monitor Web2
>> settings and/or SNMP.Let me know if you are interested in pictures.
>> For this second batch we have started using Terminal blocks to clean up the
>> wiring, the cabi
s so much cheaper than Traco that
>>> adding an RSD-300B-48 for another $100 is not a bad deal.
>>>
>>>
>>> -- Original Message --
>>> From: "David Coudron"
>>> To: "af@afmug.com"
>>> Sent: 1/28/2
in 48v, and the biggest power consumers I have are 48V. I went
>> to Traco to stay 48V. OTOH your rig is so much cheaper than Traco that
>> adding an RSD-300B-48 for another $100 is not a bad deal.
>>
>>
>> -- Original Message ------
>> From: "David Coudr
*To:* af@afmug.com <mailto:af@afmug.com>
*Subject:* Re: [AFMUG] Dc plant conversion
Hmm - do you know if the CCR1009 supports -/+48VDC?
On Mon, Jan 29, 2018 at 2:47 PM, George Skorup
mailto:george.sko...@cbcast.com>> wrote:
RackInjector, dude. RackInjector.
m <mailto:af@afmug.com>
*Subject:* Re: [AFMUG] Dc plant conversion
Hmm - do you know if the CCR1009 supports -/+48VDC?
On Mon, Jan 29, 2018 at 2:47 PM, George Skorup
mailto:george.sko...@cbcast.com>> wrote:
RackInjector, dude. RackInjector.
And you can swap
Sorry, not sure about that. We run them right from the Netonix.
David Coudron
From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird
Sent: Monday, January 29, 2018 1:57 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
Yeah - but I want to power it directly off a -48VDC
[mailto:af-boun...@afmug.com] *On Behalf Of *Josh Baird
> *Sent:* Monday, January 29, 2018 1:53 PM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] Dc plant conversion
>
>
>
> Hmm - do you know if the CCR1009 supports -/+48VDC?
>
>
>
> On Mon, Jan 29, 2018 at 2:47 PM, George
Yep, it says it will do 15-57V POE in. At least the model we use does.
David Coudron
From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird
Sent: Monday, January 29, 2018 1:53 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
Hmm - do you know if the CCR1009 supports
Doing all this with the Monitor Web2
>> settings and/or SNMP.Let me know if you are interested in pictures.
>> For this second batch we have started using Terminal blocks to clean up the
>> wiring, the cabinets look a little better, but we went to a smaller poly
>>
o:af-boun...@afmug.com>] *On Behalf Of *Carl Peterson
*Sent:* Saturday, January 27, 2018 5:39 PM
*To:* af@afmug.com <mailto:af@afmug.com>
*Subject:* Re: [AFMUG] Dc plant conversion
You can still do DC-DC off it and then hook up netonix. If I had
to do it now I'd go wit
just saw this, informative
https://www.meanwellaustralia.com.au/news/top-8-faqs-about-din-rail-power-supplies
On Mon, Jan 29, 2018 at 12:11 PM, Robert Andrews
wrote:
> What does SDR vs DRP mean for the meanwells?
>
>
> On 01/29/2018 09:56 AM, Steve Jones wrote:
>
>> That looks to meet alot of ou
ind a big 24-48 converter.
They make meanwell SD up to like 800 Watts or so. I prefer the RSD, but
those only go to 300W.
-- Original Message --
From: "Steve Jones"
To: af@afmug.com
Sent: 1/29/2018 12:56:18 PM
Subject: Re: [AFMUG] Dc plant conversion
That looks to meet
SDR is a power supply.
DRP is a UPS/battery charger.
On Mon, Jan 29, 2018 at 1:11 PM, Robert Andrews
wrote:
> What does SDR vs DRP mean for the meanwells?
>
>
> On 01/29/2018 09:56 AM, Steve Jones wrote:
>
>> That looks to meet alot of our need, though the 48 volt
>>
>> SAF recommended Eltek mi
What does SDR vs DRP mean for the meanwells?
On 01/29/2018 09:56 AM, Steve Jones wrote:
That looks to meet alot of our need, though the 48 volt
SAF recommended Eltek minipack system, i havent priced that
This is what most of our sites have (theres some depreciating ubnt
sectors too)
4x EPMP
+ 1 for Lewis also.
Duracomm is a bit pricey but very reliable and they also use some mean
well.
The issue I have is clean wire runs in the cabinet and fuse buss
distribution because mikrotik
dosent have a good industrial case for rear or front facing lugs for
connecting to fuse buss.
the one
is so much cheaper than Traco that adding an
> RSD-300B-48 for another $100 is not a bad deal.
>
>
> -- Original Message --
> From: "David Coudron"
> To: "af@afmug.com"
> Sent: 1/28/2018 10:39:56 PM
> Subject: Re: [AFMUG] Dc plant conversion
&
t;David Coudron" <mailto:david.coud...@advantenon.com>>
To: "af@afmug.com" mailto:af@afmug.com>>
Sent: 1/28/2018 10:39:56 PM
Subject: Re: [AFMUG] Dc plant conversion
Here is what we are doing, I think this is close to what Steve is
asking for:
Meanwell SDR-240-24 AC t
Sent: Monday, January 29, 2018 9:32 AM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
Yeah - the lack of a 48VDC UPS from Meanwell is annoying. For small-ish sites,
we have been running a Meanwell/Traco hybrid using the SDR-240-48 and a Traco
TSP-BCM48A or BCMU360.
On Mon, Jan 29, 2018
OTOH your rig is so much cheaper than Traco that adding an
> RSD-300B-48 for another $100 is not a bad deal.
>
>
> -- Original Message --
> From: "David Coudron"
> To: "af@afmug.com"
> Sent: 1/28/2018 10:39:56 PM
> Subject: Re: [AFMUG] Dc pl
V. I
went to Traco to stay 48V. OTOH your rig is so much cheaper than Traco
that adding an RSD-300B-48 for another $100 is not a bad deal.
-- Original Message --
From: "David Coudron"
To: "af@afmug.com"
Sent: 1/28/2018 10:39:56 PM
Subject: Re: [AFMUG] Dc plant co
[mailto:af-boun...@afmug.com] On Behalf Of Carl Peterson
Sent: Saturday, January 27, 2018 5:39 PM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
You can still do DC-DC off it and then hook up netonix. If I had to do it now
I'd go with the IDC switch. When we did our design, the idc d
n 27, 2018 at 12:59 PM, Gino A. Villarini
> wrote:
>> Used to, now with the IDC model is not needed (isolated dc)…
>>
>> From: Af on behalf of Josh Baird
>> Reply-To: "af@afmug.com"
>> Date: Saturday, January 27, 2018 at 1:51 PM
>> To: "af@afmug.co
quot;af@afmug.com"
> Date: Saturday, January 27, 2018 at 1:51 PM
> To: "af@afmug.com"
> Subject: Re: [AFMUG] Dc plant conversion
>
> Which Netonix are you running at - 48V? Or are you using an isolated
> DC/DC converter in between the -48V rectifier and Neton
ply-To: "af@afmug.com"
> Date: Saturday, January 27, 2018 at 1:51 PM
> To: "af@afmug.com"
> Subject: Re: [AFMUG] Dc plant conversion
>
> Which Netonix are you running at - 48V? Or are you using an isolated
> DC/DC converter in between the -48V rectifie
:51 PM
To: "af@afmug.com<mailto:af@afmug.com>" mailto:af@afmug.com>>
Subject: Re: [AFMUG] Dc plant conversion
Which Netonix are you running at - 48V? Or are you using an isolated DC/DC
converter in between the -48V rectifier and Netonix?
On Sat, Jan 27, 2018 at 12:49 PM, Gino
+1
I just bought some Eltek modules off of Ebay.
Came with the BC-2000 telemetry which I highly recommend.
From: Gino A. Villarini
Sent: Saturday, January 27, 2018 10:49 AM
To: af@afmug.com
Subject: Re: [AFMUG] Dc plant conversion
Refurb/ used Eltek/Valere –48 Rectifier shelf off Ebay
l done. You can power 90% of WISP gear
>
> From: Af on behalf of Steve Jones <
> thatoneguyst...@gmail.com>
> Reply-To: "af@afmug.com"
> Date: Friday, January 26, 2018 at 9:49 PM
> To: "af@afmug.com"
> Subject: [AFMUG] Dc plant conversion
>
> Any o
mug.com>"
mailto:af@afmug.com>>
Date: Friday, January 26, 2018 at 9:49 PM
To: "af@afmug.com<mailto:af@afmug.com>" mailto:af@afmug.com>>
Subject: [AFMUG] Dc plant conversion
Any of you folks who know both dc plant and even more know small wisp budget
interested in
y new
favorite thing in the world.
-- Original Message --
From: "Lewis Bergman"
To: af@afmug.com
Sent: 1/27/2018 10:55:12 AM
Subject: Re: [AFMUG] Dc plant conversion
Phoenix and Meanwell both make good AC to DC power supplies that have
battery managers available w
+ on Lewis. Phoenix Contact or Sola have several options
Jaime Solorza
On Jan 27, 2018 8:55 AM, "Lewis Bergman" wrote:
> Phoenix and Meanwell both make good AC to DC power supplies that have
> battery managers available with low voltage disconnects. They also have
> temp monitors to preve
Oh yeah, track makes them too I think but I never used those.
On Sat, Jan 27, 2018, 9:55 AM Lewis Bergman wrote:
> Phoenix and Meanwell both make good AC to DC power supplies that have
> battery managers available with low voltage disconnects. They also have
> temp monitors to prevent over charg
Phoenix and Meanwell both make good AC to DC power supplies that have
battery managers available with low voltage disconnects. They also have
temp monitors to prevent over charging and dry contracts for alarm states.
You pick the battery size and the and size of the power supply based on
your load
Give me a list of all the stuff you need to power, and I can tell you how
I'd do it... whether or not that's the best, or even a good way to do it,
is another matter. It is going to involve a pile of Packetflux stuff though
(of course most of that might already be there anyway... )
That Alpha Cord
These look nice. Any idea how much the 48V/650W model is? I like that it
has integrated battery charging and management.
On Sat, Jan 27, 2018 at 6:51 AM, can...@believewireless.net <
p...@believewireless.net> wrote:
> It's a little spendy but about how about 1 $670 option? Alpha Cordex PSU
> 24V
It's a little spendy but about how about 1 $670 option? Alpha Cordex PSU
24V 400W.
Remote monitoring, e-mailed alerts, swappable rectifier, DIN mount, etc.
Add a Netonix switch and you can power just about anything.
On Fri, Jan 26, 2018 at 8:49 PM, Steve Jones
wrote:
> Any of you folks who know
Any of you folks who know both dc plant and even more know small wisp
budget interested in looking at our gear and power setup and giving
realistic advice that doesnt have a 10 different 500 dollar components
combined with a full time linux guy and a full time coder?
Id love you to do it out of th
76 matches