he differing wiring practices and regulations may make
it more difficult come up with a common practice for RCDs in products, although
Mr. Sherman’s suggestion may be a good starting place.
Does this list have a member of TC 23/SC 23E who may be more familiar with IEC
standards in regards to RCDs?
frequencies. In this case, there was constant nuisance tripping. The
solution was to rewire the computer room the way it should have been done in
the first place.
In summary, nuisance tripping of GFCIs has become relatively uncommon in the
United States.
Ted Eckert
Microsoft Corporation
The
in a workshop would likely not require
a GFCI. Much of this comes from the electrical code. Any standards that specify
the additional protection do so because the code requires it.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
testing, but shipping
batteries in products is fairly simple after that.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Doug Powell [mailto:doug...@gmail.com]
Sent: Thursday, January 25, 2018 12:45 PM
To: EMC-PSTC
Directives. Use for trade show or demonstration purposes should
be reviewed carefully to ensure that you are complying with both the letter and
the spirit of the law.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: John
, WEEE, ELV, and BFR Directives, all environmentally related. Maybe
I’m missing something, but I don’t see a declaration of any European safety
requirements.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Scott
, the cable does not need the
CE marking. If the cable is sold on its own, the CE mark is required for RoHS.
See pages 15 and 16 in the European Commission guidance document.
http://ec.europa.eu/environment/waste/rohs_eee/pdf/faq.pdf
Ted Eckert
Microsoft Corporation
The opinions expressed are my own
insulation between windings that
are overlaid on top of each other.
Ted Eckert
Microsoft
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Scott Xe [mailto:scott...@gmail.com]
Sent: Thursday, January 4, 2018 5:26 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject
extrapolate back to the
time when power was removed. The windings were enclosed well enough that they
were not getting much cooling from the moving air. As such, I did not expect
that there was overshoot when power was removed and the fan stopped.
Ted Eckert
Microsoft Corporation
The opinions
vie.
http://www.imdb.com/title/tt1637725/
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, Ted Bundy, Ted Kacynski, Ted Cruz, Teddy Roosevelt, Ted Turner, Ted
Danson or the anybody using the Ted word
processor<https:
xtreme.
I generally discount TED talks. My personal opinion is that there is some
amount of snake oil being sold in TED talks.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, TED LLC, or anybody else named Ted.
From: Joh
It appears that my copy of 60950-1 is a bit old. It was hand written on a
vellum scroll. My company antiquities director prohibits me from cutting off a
piece for spectrographic analysis.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of
A spectrographic analysis of a plum and coconut might find them to be quite
similar.
https://www.improbable.com/airchives/paperair/volume1/v1i3/air-1-3-apples.html
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From
equipment back into tolerance if needed.
The market for laser test equipment is small and there isn't enough business
for independent laboratories to gain proficiency through routine testing.
Best regards,
Ted Eckert
Microsoft Corporation
The opinions are my own and do not necessarily re
th any measurement at
hazardous voltages and with these currents, care should be taken to ensure that
the setup does not create a hazard for the laboratory staff.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original M
NFPA 70 allows 20 A connectors to be used at 20 A under a number of
circumstances. The derating issue only applies in certain cases. Just changing
the rating doesn’t resolve the issue as it would eliminate already accepted
safe use of the connectors at their full rating.
Ted Eckert
Microsoft
eliminating it would
result in too much expense and rework.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Tuesday, October 10, 2017 12:49 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
having a C13 connector
at the other end. It would need a C19 instead.
That being said, for some specialty industries, you can find some strange
combinations of plugs and receptacles.
http://www.marinco.com/en/s15-504
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not
n many flights, it
occurs with some regularity and might be considered “foreseeable misuse”.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Doug Powell [mailto:doug...@gmail.com]
Sent: Tuesday, October 3, 2017 8:29 AM
T
r" at your company who can grant you
access.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Rob Oglesbee [mailto:rob.ogles...@rheem.com]
Sent: Thursday, September 21, 2017 7:02 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
host product has a built-in battery charger, I presume that you are
already familiar with the energy requirements. These are proliferating in North
America for battery chargers and can be more of a challenge to track than the
safety requirements for the chargers.
Ted Eckert
Microsoft Corporation
topgap measure until testing to UL 60950-1 became common for rack mounted
power distribution.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: John Allen [mailto:09cc677f395b-dmarc-requ...@ieee.org]
Sent: Frid
s may be somewhat of a simplification, and I haven't described all of the
potential problems with this approach, but it is method that generally is
permitted.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From:
t is acceptable based on your specific products and processes.
Otherwise, you may want more margin to ensure that market surveillance
authorities won't get a measurement over the limit if they audit one of your
products.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own an
The Blue Guide opens properly in Microsoft Edge as well.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer. (Although my employer is likely happy to let me promote Microsoft
Edge.)
From: Doug Smith [mailto:d...@emcesd.com
commendable but the only law that
applies in Australia is the law of Australia.”
The full press release is
here.<https://www.pm.gov.au/media/2017-07-14/press-conference-attorney-general-senator-hon-george-brandis-qc-and-acting>
Ted Eckert
Microsoft Corporation
The opinions expressed are my own
I haven't worked with G&M Compliance<http://www.gmcompliance.com/> for quite a
while, they do a lot of work with Chinese certifications.
Disclosure notice: I have a professional relationship with a few people from
G&M Compliance through participation in some IEEE PSES commit
rity may look at a product declared to RED and LVD and decide
that the DoC is improper because of their reading of the Directives and
guidance. It may seem like a no-win situation, but that is where we are.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessa
.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Chuck Seyboldt [mailto:seybo...@gmail.com]
Sent: Thursday, July 20, 2017 7:50 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Harmonised
I recommend against following Ferrari’s practice. Apparently, portions of the
FXX K supercar are energized to 480 V when charging. There is a fin on the roof
with flashing LEDs. Red means stay away and green means safe.
http://jalopnik.com/the-ferrari-fxx-k-might-electrocute-you-1796961190
Ted
22,300 mile long ground wire? We are working on it.
https://en.wikipedia.org/wiki/Space_elevator
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, NASA, ESA or Arthur C.
Clarke<https://en.wikipedia.org/w
cally compatible. However, there are slight
difference such that it's not common for plugs and receptacles to have both
U.S. and Japanese approvals.
I wish you luck in finding a good English translation of Appendix 4. It's been
more than a decade since I bought a copy and that was th
materials would
behave in a moderately large structure fire. It determines whether the
materials would help the spread of the fire and whether the materials would
generate enough smoke to cause problems for occupants of the building.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own
ce. Finding an Ethernet cable that meets this
requirement, often called plenum rated, is easy. Finding a USB cable that meets
the requirement is hard.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, any NRTL or the code aut
In my opinion, a good tech pub combines the words “Free Wi-Fi” with “IPA”,
“Hefeweizen”, “Porter” and “Stout”.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Jim Hulbert [mailto:jim.hulb...@pb.com]
Sent: Wednesday
to reject marking as
being too small to be reasonably legible.
It is possible that another country may have a national difference regarding
the symbol, but I am unaware of it and I personally have not had marking
rejected on one of my products due to the double insulation symbol being too
small.
Arabia.)
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Scott Xe [mailto:scott...@gmail.com]
Sent: Thursday, June 1, 2017 9:19 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Min s
lass to be able to test to UL 50E. That
being said, my expectations are not always met.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, OSHA, the UL 50E STP or any rational human being who regularly tests
enclosures.
Fro
iki/The_Relativity_of_Wrong>” along with
Michael Shermer’s commentary “Wronger than
Wrong<https://en.wikipedia.org/wiki/Wronger_than_wrong>” on the Asimov essay.
Ted Eckert
The opinions expressed are my own and do not necessarily reflect those of my
employer, IEC TC108, any TC108
to the discussion. I believe the guidance given
by Mr. Nyffenegger is correct and Mr. O’Connell has given accurate additional
information.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, the NFPA, ASHRAE, IEC TC108 or the Interna
that leak carbon monoxide into the passenger cabin.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Thursday, February
just because it's only a fire drill. The alarm is loud enough
that everybody in the building wants to get outside.
Ted Eckert
Microsoft
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Dürrer Bernd [mailto:bernd.duer..
sion’s intention was to restrict a manufacturer’s
ability to import large quantities of products prior to the implementation date
of a regulation with the intention of selling them to the end user well after
that date. However, this is my interpretation of the EC’s intent.
Ted Eckert
The op
outside of the EU on the DoC
unless specifically prohibited by the applicable Directives. I am not aware of
the LVD or EMC Directive overruling this statement.
I cannot respond regarding the Machinery Directive as I do not know it well
enough to comment accurately.
Ted Eckert
Microsoft Corporation
IEC 62040 series will mainly add
requirements based on the energy storage in the batteries and the risk of
feeding power back from the batteries to the line input depending on UPS
configuration. Your automotive inverter doesn't have that issue and may be
suitably tested to EN 60950-1 f
PS interfering with sensors.
Repeating all of the required testing is not likely necessary, but I would
recommend looking at all of the areas of compliance to determine which could be
affected by an alternate EPS and running the necessary testing to validate that
the new configuration is compliant
The newer model encabulators have more sophisticated computer control using the
Signetics Write-Only
Memory<http://www4.vmi.edu/faculty/squirejc/Research/IC_Datasheets/digital_cmos/Write%20Only%20Memory.pdf>.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and
delve deeply into the electrical codes, so I
may be a little off on the field-wired requirements. I encourage any of our
esteemed contributors to correct my errors.
Best regards,
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily represent those of my
ces was cheaper than rerouting the
motherboard and testing is properly to make sure no new problems were created.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: ce-test, qualified testi
the modial interaction of magnetoreluctance and capacitive directance.
https://www.youtube.com/watch?v=MXW0bx_Ooq4
Ted Eckert
The opinions expressed are my own and do not necessarily reflect those of my
employer, Fiat-Chrysler or the American Association of Turboencabulator
Engineers
. Admittedly, this is a somewhat outlandish though experiment,
but it is a case where “10 % below” in Centigrade becomes even more problematic
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Jim Hulbert [mailto:jim.hulb
modern appliances. The risks are greater for knob and tube wiring and the
general recommendation is to replace it with a modern system.
Best regards,
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer. I am not a licensed electrical
t his "precious" being
missing when that main breaker tripped.
Ted Eckert
Microsoft
The opinions expressed are my own and do not necessarily reflect those of my
employer or Sauron.
-Original Message-
From: John Allen [mailto:john_e_al...@blueyonder.co.uk]
Sent: Thursday, December
coffee all day
and tells you what it was like running testing when he was young.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, Nintendo, Niantic or my boss who like to tell me what it was like to
run testing when he was
The CPSC has more details on residential issues and repairs for aluminum wiring.
https://www.cpsc.gov/PageFiles/118856/516.pdf
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Richard Nute
ied to UL 60950-1 prior to that date may continue to be
sold without retesting or recertification unless such equipment undergoes
"significant" modification where it will be up to UL to determine whether any
modification is significant enough to warrant testing to the new standard.
equipment does not pass
these tests, suitable protective devices shall be included as an integral part
of the direct plug-in equipment, until the requirements of Annexes B.3.1 and
B.4 are met.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of
d hope that it works right.
Ted Eckert
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: john Allen [mailto:john_e_al...@blueyonder.co.uk]
Sent: Saturday, December 3, 2016 12:56 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] British question, a
the safety of direct plug-in
supplies and there is independent testing that occurs. The following press
release was issued yesterday.
https://www.tradingstandards.uk/news-policy/news-room/2016/warning-over-fake-chargers-and-second-hand-electrics
Ted Eckert
The opinions expressed are my own and do
I would also recommend considering the anticipated voltages on the connector.
Higher voltages are capable of arcing across larger air gaps, and they would
require keeping the ground engaged past the point where the air gap is large
enough to suppress arcing.
Ted Eckert
Microsoft Corporation
when you
have high current available.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Scott Aldous [mailto:0220f70c299a-dmarc-requ...@ieee.org]
Sent: Thursday, December 1, 2016 9:04 AM
To: EMC-PSTC
my previous customer used UL as their NRTL and
this was sufficient for Los Angeles. The city has some differences in their
mechanical code, but that would only affect your equipment if it has cooling
water connections or such similar features.
Ted Eckert
Microsoft Corporation
The opinions
such cases have ended in the
plaintiff’s favor.
Ted Eckert
The opinions expressed are my own and do not necessarily reflect those of my
employer. I am not a professional constitutional scholar, although I will admit
to subscribing and listening to a number of podcasts on constitutional and
, gender and a few other aspects, but
speech is generally allowed to be restricted as a condition of employment.
Ted Eckert
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Tuesday, November 22, 2016 8:03
. Fortunately, the experts on this list can balance out my ignorance
when I show it.
Ted Eckert
The views expressed are my own and do not necessarily reflect those of my
employer, coworkers or the NSA agent who is monitoring this conversation.
From: Ed Price [mailto:edpr...@cox.net]
Sent: Tuesday
Terminator and Skynet?
Ted Eckert
The opinion express do not necessarily reflect those of my employer, Sarah
Conner, HAL or R. Susan Calvin.
-Original Message-
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Monday, November 7, 2016 2:36 PM
To: EMC-PSTC@LISTSERV.IEE
where a tree can fall on the road, large animals can jump out or a child
could run out into the road unexpectedly.
These aren’t situations that are new with self-driving cars. They just create a
new issue of liability.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do
ll be purchasers of self-driving cars
who will find ways to bend the rules to their own ends. In other words, humans
will be humans. In my opinion, it isn't the robots we should worry about.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect t
Europe in the summer.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
This email message may contain confidential and privileged information. Any
unauthorized use is prohibited. If you are not the intended recipient
be a multi-pole disconnect
switch.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, November 4, 2016 7:38 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] AC
Hello Scott,
I believe this is the website you are requesting.
http://www.productsafety.gov.au/
You will also find that there is significant harmonization with the
requirements for New Zealand.
Best regards,
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not
one country. The language of the applicable
statute should be used to determine what products are affected. General
guidance may not always be accurate for every case even within one country.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of
de evolves even more slowly.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, my previous employer, NFPA, IBEW, NAFI or OSHA.
From: Jim Hulbert [mailto:jim.hulb...@pb.com]
Sent: Friday, September 30, 2016 8:10 AM
To
Hello Brian,
Do you have an account on http://www.ulstandards.com/ ? If you do, go to
standard 9703 and you will find the September 7, 2012 bulletin.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Brian Gregory
It's slightly off topic, but I thought I would share this
sign<https://1drv.ms/i/s!Ap8stJM0LsH4jQzsx7ADEQ09XOkH> from the days when you
didn't want somebody to try to run their 25 Hz motor on a 60 Hz circuit.
Ted Eckert
Microsoft Corporation
The opinions expressed are m
one breaker. For example, if the
breaker had been reset by somebody with traces of food on their fingers, the
GFCI could become more attractive just by smell.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Gies
instead.
Ted Eckert
The opinions expressed are my own and do not necessarily represent those of my
employer, entomologist, biologist or the construction industry of New Jersey.
From: Adam Dixon [mailto:lanterna.viri...@gmail.com]
Sent: Thursday, September 15, 2016 6:05 AM
To: EMC-PSTC
ation can be an issue. Even within a
standards body, you can have different technical committees writing standards
for the same type of product. What is the proper IEC standards for the safety
of a power supply? Depending on the end use, it could fall under a number of
different standards from different
application. Arrows are clearly marked on the connectors
to ensure superior sound quality.”
If you are wondering about the price, Amazon has the “Diamond” level HDMI
cables available for the low price of
$13,500<https://www.amazon.com/AudioQuest-Diamond-52-49-Braided-Cable/dp/B00IL3TZSQ>.
Ted
me part of the international standard.
All amendments to EN 60950-1 should be applied based on the dates in the
Official Journal of the European Union if you are declaring the presumption of
conformity based on the compliance with the standards.
Ted Eckert
Microsoft Corporation
The opinions exp
ike you to at least have the basic quality programs
in place.
I may be wrong as I've only dealt with declaring the presumption of conformity
via compliance with harmonized standards.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily refl
a.eu/legal-content/EN/TXT/?uri=uriserv:OJ.C_.2013.348.01.0001.01.ENG&toc=OJ:C:2013:348:TOC
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Brian O'Connell [mailto:oconne...@t
, and that can be easier to check in a state machine where there
are only a limited number of states possible.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Brian O'Connell [mai
automobile emission standards than most other
states. If you buy a car in Kentucky and then move to California, you may find
that your car can’t be registered in California. Such issues are less likely
with consumer electronics.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own
products. They typically only do inspections on new construction and remodeling
where a building permit is required.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Scott Xe [mailto:scott...@gmail.com]
Sent: Tuesday, July
ducts with a fairly broad scope of what
they can do. NRTL only covers safety standards for a few laboratories and is
much narrower in scope than A2LA.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, OSHA or A2LA. Your mile
then get back to work.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Pete Perkins [mailto:0061f3f32d0c-dmarc-requ...@ieee.org]
Sent: Monday, July 25, 2016 1:03 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re
any AHJs accepted products with meaningless Listing marks for
products covered under the NRTL program?
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Doug Powell [mailto:doug...@gmail.com]
Sent: Friday, July 22, 2016
I'm
translating the Latin correctly.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Tuesday, July 19, 2016 8:13 PM
To: Ted Eckert ; EMC-PSTC@LISTSERV.IEE
the capacitor standard.
However, if they have not, it should be acceptable to use capacitors certified
to the older standard.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Brian Ceresney [mailto:bceres...@delta
lation such as this without a high risk of being caught making things up
as I go.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, residents of Papua New Guinea or anybody who pressed the red button
from a previous message.
specific to the
scooters accomplishes this task better than proposing an existing standard.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer, Marty McFly, Biff, Doc Brown or the producers of Back to the Future
part 2 where we were
would consider BLE hearing
aids to be an issue. In addition, the FAA rules only apply to flights within
the FAA’s jurisdiction. I can make no statement for flights outside of the
United States.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect
ware safety. However,
with my employer's reputation, it is probably best for me to stay away from the
area. I don't think many engineers would want to buy a car that controlled the
antilock brakes with Windows 95. (Feel free to insert your favorite blue screen
joke here.)
http://
will be in San Jose California next May and this would be a great
topic. I would recommend that list server subscribers interested in the subject
come up with an idea for a presentation they can give. The ISPCE technical
program committee would likely be very interested in adding such presentations
. However, if you are willing to do the work, you will see
that there is more flexibility in the design options if you use the new
requirements over the old.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Kunde, Brian
cheapest option out there, but it does offer a lot of flexibility
in ordering and format for standards.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
From: Dan Roman, N.C.E. [mailto:danp...@verizon.net]
Sent: Tuesday, June 28
from the potential
hazard. The button doesn’t do any good to an operator trapped in a machine if
they can’t reach it.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my
employer.
█ STOP █
From: John Woodgate
to see clear research linking LED lighting to the
proposed problems before recommending changes. This research may exist and the
lack of references may just be the fault of the person who wrote the short
article.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not
uld likely be more inciteful than
insightful.
Ted Eckert
The opinions expressed are my own and they do not necessarily reflect those of
my employer.
-Original Message-
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Thursday, June 9, 2016 4:50 PM
To: EMC-PSTC@LI
101 - 200 of 442 matches
Mail list logo